I agree with this statement.  I think you are taking it too literal adding all 
the buildings together into your flow.  Where do you stop? Why not flow every 
building on the water network?  Have you considered flipping your logic in the 
other direction?  The civil guy may have had to design the underground to 
support all 20 buildings flowing 125gpm each for 2500gpm total simultaneously 
(or whatever his requirements are). But you would only have to design 1 remote 
area in 1 building to operate at a time.  Probably 100gpm or less then add your 
hose.  You are looking to change their required design flow by less than 10%, I 
bet they have that covered and probably considered into their calculations.  
You wouldn't be the driver...just along for the ride.

Thanks,
Sean VG

-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Mark Phillips via Sprinklerforum
Sent: Thursday, November 12, 2020 9:51 AM
To: sprinklerforum@lists.firesprinkler.org; travis.m...@mfpdesign.com
Cc: Mark Phillips <philli...@pyebarkerfire.com>
Subject: [EXTERNAL] Re: Domestic Demands 13R

From a practical perspective all of the apartment building would not be 
expected to be on fire at once.

That was how a plan reviewer once explained it to me.


Sent from my mobile device
Please excuse spelling, grammar, and auto correction.

Mark Phillips
Branch Manager
Fire Sprinkler Design, Install, Inspections Service, Backflows, Fire Alarm 
Inspections

832-101 Purser Drive
Raleigh NC 27603
Phone: 919-779-4010
Fax : 919-779-4014
Cell : 919-268-7587
Email : philli...@pyebarkerfire.com
Web : 
https://urldefense.proofpoint.com/v2/url?u=http-3A__www.pyebarkerfire.com&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=TjhyumA9TbPzedcnwqv0vDplfwDWwzFB_ObrQ0YGgf4&s=wyj4MoVWDgbfD4l_QTft88TxBW37X1F4j2ehwCyAEi0&e=
 

________________________________
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> on behalf 
of Mark Phillips via Sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Sent: Thursday, November 12, 2020 11:46:23 AM
To: travis.m...@mfpdesign.com <travis.m...@mfpdesign.com>; 
sprinklerforum@lists.firesprinkler.org <sprinklerforum@lists.firesprinkler.org>
Cc: Mark Phillips <philli...@pyebarkerfire.com>
Subject: Re: Domestic Demands 13R

[EXTERNAL]

Sorry if I was not clear only the demand of the building or buildings that 
share the 4 inch supply .

Sent from my mobile device
Please excuse spelling, grammar, and auto correction.

Mark Phillips
Branch Manager
Fire Sprinkler Design, Install, Inspections Service, Backflows, Fire Alarm 
Inspections

832-101 Purser Drive
Raleigh NC 27603
Phone: 919-779-4010
Fax : 919-779-4014
Cell : 919-268-7587
Email : philli...@pyebarkerfire.com
Web : 
https://urldefense.proofpoint.com/v2/url?u=http-3A__www.pyebarkerfire.com&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=TjhyumA9TbPzedcnwqv0vDplfwDWwzFB_ObrQ0YGgf4&s=wyj4MoVWDgbfD4l_QTft88TxBW37X1F4j2ehwCyAEi0&e=
 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.pyebarkerfire.com&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=TjhyumA9TbPzedcnwqv0vDplfwDWwzFB_ObrQ0YGgf4&s=wyj4MoVWDgbfD4l_QTft88TxBW37X1F4j2ehwCyAEi0&e=
 >

________________________________
From: travis.m...@mfpdesign.com <travis.m...@mfpdesign.com>
Sent: Thursday, November 12, 2020 11:44:10 AM
To: Mark Phillips <philli...@pyebarkerfire.com>; 
sprinklerforum@lists.firesprinkler.org <sprinklerforum@lists.firesprinkler.org>
Subject: RE: Domestic Demands 13R

[EXTERNAL]

So in this case, you would be adding a total demand of 2500 gpm (20 buildings 
at 125 gpm each) to your sprinkler calc?  And yes, it would be included at the 
point of each 4” connection to the 8” main.  Seems excessive, but I have seen 
it requested that way.  I have more commonly done what Matt states to only 
include the building of interest in the calc.


Travis Mack, CFPS, CWBSP, RME-G, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
NEW MOBILE: 480-272-2471
mailto:travis.m...@mfpdesign.com
https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=TjhyumA9TbPzedcnwqv0vDplfwDWwzFB_ObrQ0YGgf4&s=mYddpiGsci2-eQ8LMtNGESlDY6RduvzIU38q_Iuk30A&e=
 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=TjhyumA9TbPzedcnwqv0vDplfwDWwzFB_ObrQ0YGgf4&s=mYddpiGsci2-eQ8LMtNGESlDY6RduvzIU38q_Iuk30A&e=
 >

Send large files to us via: 
https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.hightail.com-252Fu-252FMFPDesign-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DeGdMZGu2wXhUupGwgGTrqF3b54OP5-252BAZvlHhABSexWY-253D-26reserved-3D0&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=TjhyumA9TbPzedcnwqv0vDplfwDWwzFB_ObrQ0YGgf4&s=7MFYm7oDEaZjf3kpdaYcXAk6mlix4JdBEhaHEHzqtDc&e=
LinkedIn: 
https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.linkedin.com-252Fin-252Ftravismack-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DtT5E7LsZjSmyreKi4gDCa70EWN-252BZodi-252FhbeCbHNRijI-253D-26reserved-3D0&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=TjhyumA9TbPzedcnwqv0vDplfwDWwzFB_ObrQ0YGgf4&s=Wzq5bburBna6qMkh878jGJMn_luHs27M5hK-P0xG7YI&e=
 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

Need/Want a faster way to check material pricing?  Build a material quote?  
Check availability ?   Searching for an invoice?
*If you do not already have an account with ferguson.com, click 
https://urldefense.proofpoint.com/v2/url?u=https-3A__www.ferguson.com_account-2Dregistration&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=TjhyumA9TbPzedcnwqv0vDplfwDWwzFB_ObrQ0YGgf4&s=QhTUAi7DdEPI8eQ9_19pfhKANXpWM0rf_LNo4cSV57s&e=
  to register.* **Have a Ferguson account? Download the Ferguson app for 
on-the-go access to your favorite ferguson.com features. 
https://urldefense.proofpoint.com/v2/url?u=http-3A__fergusoncommunications.us.newsweaver.com_hq7bgesq7f_1qtklpp37l9byeftyuoy12_external-3Femail-3Dtrue-26a-3D6-26p-3D2591775-26t-3D517003&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=TjhyumA9TbPzedcnwqv0vDplfwDWwzFB_ObrQ0YGgf4&s=V-z-76QC5UR76nHmitFA6WcChybBacwrKI8fyC_-yS0&e=
  or 
https://urldefense.proofpoint.com/v2/url?u=http-3A__fergusoncommunications.us.newsweaver.com_hq7bgesq7f_n1gewi5ud95byeftyuoy12_external-3Femail-3Dtrue-26a-3D6-26p-3D2591775-26t-3D517003-2A-2A&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=TjhyumA9TbPzedcnwqv0vDplfwDWwzFB_ObrQ0YGgf4&s=BeBeJ3FYTnU-D3xijgBuKHefehAR0YUNmDYv5BfwcXo&e=
 

From: Mark Phillips <philli...@pyebarkerfire.com>
Sent: Thursday, November 12, 2020 9:41 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack <travis.m...@mfpdesign.com>
Subject: Re: Domestic Demands 13R

Assuming the 8 inch supply loops the complex Add the domestic demand at the 4” 
point on the loop for each building

Sent from my mobile device
Please excuse spelling, grammar, and auto correction.

Mark Phillips
Branch Manager
Fire Sprinkler Design, Install, Inspections Service, Backflows, Fire Alarm 
Inspections

832-101 Purser Drive
Raleigh NC 27603
Phone: 919-779-4010
Fax : 919-779-4014
Cell : 919-268-7587
Email : mailto:philli...@pyebarkerfire.com
Web : 
https://urldefense.proofpoint.com/v2/url?u=http-3A__www.pyebarkerfire.com&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=TjhyumA9TbPzedcnwqv0vDplfwDWwzFB_ObrQ0YGgf4&s=wyj4MoVWDgbfD4l_QTft88TxBW37X1F4j2ehwCyAEi0&e=
 

________________________________________
From: Sprinklerforum <mailto:sprinklerforum-boun...@lists.firesprinkler.org> on 
behalf of Travis Mack via Sprinklerforum 
<mailto:sprinklerforum@lists.firesprinkler.org>
Sent: Thursday, November 12, 2020 11:34:20 AM
To: mailto:sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: mailto:travis.m...@mfpdesign.com <mailto:travis.m...@mfpdesign.com>
Subject: Domestic Demands 13R

[EXTERNAL]

Forumites:

Per 13R 9.6 it requires the domestic demand for the building being calculated 
to be added to the fire sprinkler system.  This is generally not an issue.  If 
you have a complex of say 20 buildings on site that is supplied by a common 
water line serving both domestic and fire, are you required to include the 
domestic demand for each building on the site water main.

For example, if I have a project with a 8" main going through the complex, and 
4" lead-ins to each building, with a domestic demand of 125 gpm for each 
building, how are you doing the domestic demand?  With the domestic / fire 
split in the building, it is required to include the 125 gpm demand in addition 
to the fire sprinkler system demand in the 4" line.  Are you including the 
other 2375 gpm  (19 additional buildings at 125 gpm domestic allowance), in 
your calculations back to the city main?

This seems quite excessive.  If it were a 13 system, you would have similar 
flows and a 100 gpm hose allowance.  There is no requirement in this example to 
include the domestic in a 13 system.  But, if you are required to include the 
additional 2375 gpm, that could be quite taxing on the site supply.  Again, how 
is everyone handling it.

We have seen AHJ's take both approaches on this.


Travis Mack, CFPS, CWBSP, RME-G, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
NEW MOBILE: 480-272-2471
mailto:travis.m...@mfpdesign.com
https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=TjhyumA9TbPzedcnwqv0vDplfwDWwzFB_ObrQ0YGgf4&s=mYddpiGsci2-eQ8LMtNGESlDY6RduvzIU38q_Iuk30A&e=
 

Send large files to us via: 
https://urldefense.proofpoint.com/v2/url?u=https-3A__www.hightail.com_u_MFPDesign&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=TjhyumA9TbPzedcnwqv0vDplfwDWwzFB_ObrQ0YGgf4&s=jsDe2AT_JwF5pX1MvUz-Ph9ODTDnH95fwTV2ph4TFJ4&e=
LinkedIn: 
https://urldefense.proofpoint.com/v2/url?u=https-3A__www.linkedin.com_in_travismack&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=TjhyumA9TbPzedcnwqv0vDplfwDWwzFB_ObrQ0YGgf4&s=ILInD4F4C3fcpLecRYiGZixo3HT2zYklNgkPx54rReM&e=
 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

Need/Want a faster way to check material pricing?  Build a material quote?  
Check availability ?   Searching for an invoice?
*If you do not already have an account with ferguson.com, click here to 
register.* **Have a Ferguson account? Download the Ferguson app for on-the-go 
access to your favorite ferguson.com features. Apple iOS devices or Android 
devices**

_______________________________________________
Sprinklerforum mailing list
mailto:Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=TjhyumA9TbPzedcnwqv0vDplfwDWwzFB_ObrQ0YGgf4&s=oX68k85Zin1gaWXTyQEX0cho7vrwOoyfT7ea7zdMCZU&e=
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=TjhyumA9TbPzedcnwqv0vDplfwDWwzFB_ObrQ0YGgf4&s=oX68k85Zin1gaWXTyQEX0cho7vrwOoyfT7ea7zdMCZU&e=
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=TjhyumA9TbPzedcnwqv0vDplfwDWwzFB_ObrQ0YGgf4&s=oX68k85Zin1gaWXTyQEX0cho7vrwOoyfT7ea7zdMCZU&e=
 
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to