That request is now our list of items to be considered or the 2025 edition
of 13R.

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Our members are at the heart of everything we do.*

*Don’t miss another issue!*

Sign up to get your exclusive copy of the industry’s leading membership
magazine *Sprinkler* *Age* delivered straight to your mailbox, inbox, or
both! Subscribe <https://sprinklerage.com/subscribe/> now to get the latest
information you need to know and never miss another issue.


On Thu, Nov 12, 2020 at 1:30 PM Travis Mack via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> I think the rationale is that for a project in the downtown areas, your
> flow test is already accounting for those buildings being active.  In the
> new development, your flow test is not accounting for those since they
> don't yet exist.
>
> However, I am glad the commentary in the 13R handbook (2016) specifically
> states it is only to include one building when you have multiple on a
> site.  It would be great if that could make it in to the body of the
> standard.
>
>
> Travis Mack, CFPS, CWBSP, RME-G, SET
> Engineering Manager
> MFP Design
> 3356 E Vallejo Ct
> Gilbert, AZ 85298
> NEW EXTENSION: 480-505-9271 ext. 700
> NEW MOBILE: 480-272-2471
> mailto:travis.m...@mfpdesign.com
> www.mfpdesign.com
>
> Send large files to us via:
> https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0
> LinkedIn:
> https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0
>
> “The bitterness of poor quality remains long after the sweetness of low
> price is forgotten.”
>
> Need/Want a faster way to check material pricing?  Build a material
> quote?  Check availability ?   Searching for an invoice?
> *If you do not already have an account with ferguson.com, click
> https://www.ferguson.com/account-registration to register.*
> **Have a Ferguson account? Download the Ferguson app for on-the-go access
> to your favorite ferguson.com features.
> http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/1qtklpp37l9byeftyuoy12/external?email=true&a=6&p=2591775&t=517003
>  or
> http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true&a=6&p=2591775&t=517003**
>
> From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On
> Behalf Of Bob Knight via Sprinklerforum
> Sent: Thursday, November 12, 2020 11:27 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Bob Knight <b...@firebyknight.com>
> Subject: RE: Domestic Demands 13R
>
> "However, they may be expected to have domestic demands. That is the plan
> reviewer rationale in one particular case."
> Does the reviewer apply this same logic when doing a project in a downtown
> area with hundreds of buildings all using water at the same time?
> I would assume not. So, why would this be any different? The domestic
> demand needs to be added only when sharing the water supply from the same
> line for each individual building. This is not a collective requirement.
>
>
>
> Thank you,
>
> Bob Knight, CET III
> Fire by Knight, LLC
> 208-318-3057
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis Mack
> via Sprinklerforum
> Sent: Thursday, November 12, 2020 9:53 AM
> To: mailto:philli...@pyebarkerfire.com; mailto:
> sprinklerforum@lists.firesprinkler.org
> Cc: mailto:travis.m...@mfpdesign.com
> Subject: RE: Domestic Demands 13R
>
> Correct. However, they may be expected to have domestic demands. That is
> the plan reviewer rationale in one particular case.
>
>
> Travis Mack, CFPS, CWBSP, RME-G, SET
> Engineering Manager
> MFP Design
> 3356 E Vallejo Ct
> Gilbert, AZ 85298
> NEW EXTENSION: 480-505-9271 ext. 700
> NEW MOBILE: 480-272-2471
> mailto:travis.m...@mfpdesign.com
> http://www.mfpdesign.com
>
> Send large files to us via:
> https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0
> LinkedIn:
> https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0
>
> “The bitterness of poor quality remains long after the sweetness of low
> price is forgotten.”
>
> Need/Want a faster way to check material pricing? Build a material quote?
> Check availability ? Searching for an invoice?
> *If you do not already have an account with ferguson.com, click
> https://www.ferguson.com/account-registration to register.*
> **Have a Ferguson account? Download the Ferguson app for on-the-go access
> to your favorite ferguson.com features.
> http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/1qtklpp37l9byeftyuoy12/external?email=true&a=6&p=2591775&t=517003
> or
> http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true&a=6&p=2591775&t=517003**
>
> From: Mark Phillips <mailto:philli...@pyebarkerfire.com>
> Sent: Thursday, November 12, 2020 9:51 AM
> To: mailto:sprinklerforum@lists.firesprinkler.org; Travis Mack <mailto:
> travis.m...@mfpdesign.com>
> Subject: Re: Domestic Demands 13R
>
> From a practical perspective all of the apartment building would not be
> expected to be on fire at once.
>
> That was how a plan reviewer once explained it to me.
>
>
> Sent from my mobile device
> Please excuse spelling, grammar, and auto correction.
>
> Mark Phillips
> Branch Manager
> Fire Sprinkler Design, Install, Inspections
> Service, Backflows, Fire Alarm Inspections
>
> 832-101 Purser Drive
> Raleigh NC 27603
> Phone: 919-779-4010
> Fax : 919-779-4014
> Cell : 919-268-7587
> Email : mailto:philli...@pyebarkerfire.com
> Web : http://www.pyebarkerfire.com
>
> ________________________________________
> From: Sprinklerforum <mailto:
> sprinklerforum-boun...@lists.firesprinkler.org> on behalf of Mark
> Phillips via Sprinklerforum <mailto:sprinklerforum@lists.firesprinkler.org
> >
> Sent: Thursday, November 12, 2020 11:46:23 AM
> To: mailto:travis.m...@mfpdesign.com <mailto:travis.m...@mfpdesign.com>;
> mailto:sprinklerforum@lists.firesprinkler.org <mailto:
> sprinklerforum@lists.firesprinkler.org>
> Cc: Mark Phillips <mailto:philli...@pyebarkerfire.com>
> Subject: Re: Domestic Demands 13R
>
> [EXTERNAL]
>
> Sorry if I was not clear only the demand of the building or buildings that
> share the 4 inch supply .
>
> Sent from my mobile device
> Please excuse spelling, grammar, and auto correction.
>
> Mark Phillips
> Branch Manager
> Fire Sprinkler Design, Install, Inspections
> Service, Backflows, Fire Alarm Inspections
>
> 832-101 Purser Drive
> Raleigh NC 27603
> Phone: 919-779-4010
> Fax : 919-779-4014
> Cell : 919-268-7587
> Email : mailto:philli...@pyebarkerfire.com
> Web : http://www.pyebarkerfire.com
>
> ________________________________
> From: mailto:travis.m...@mfpdesign.com <mailto:travis.m...@mfpdesign.com>
> Sent: Thursday, November 12, 2020 11:44:10 AM
> To: Mark Phillips <mailto:philli...@pyebarkerfire.com>; mailto:
> sprinklerforum@lists.firesprinkler.org <mailto:
> sprinklerforum@lists.firesprinkler.org>
> Subject: RE: Domestic Demands 13R
>
> [EXTERNAL]
>
> So in this case, you would be adding a total demand of 2500 gpm (20
> buildings at 125 gpm each) to your sprinkler calc? And yes, it would be
> included at the point of each 4” connection to the 8” main. Seems
> excessive, but I have seen it requested that way. I have more commonly done
> what Matt states to only include the building of interest in the calc.
>
>
> Travis Mack, CFPS, CWBSP, RME-G, SET
> Engineering Manager
> MFP Design
> 3356 E Vallejo Ct
> Gilbert, AZ 85298
> NEW EXTENSION: 480-505-9271 ext. 700
> NEW MOBILE: 480-272-2471
> mailto:travis.m...@mfpdesign.com
> http://www.mfpdesign.com<http://www.mfpdesign.com>
>
> Send large files to us via:
> https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0
> LinkedIn:
> https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0
>
> “The bitterness of poor quality remains long after the sweetness of low
> price is forgotten.”
>
> Need/Want a faster way to check material pricing? Build a material quote?
> Check availability ? Searching for an invoice?
> *If you do not already have an account with ferguson.com, click
> https://www.ferguson.com/account-registration to register.*
> **Have a Ferguson account? Download the Ferguson app for on-the-go access
> to your favorite ferguson.com features.
> http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/1qtklpp37l9byeftyuoy12/external?email=true&a=6&p=2591775&t=517003
> or
> http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true&a=6&p=2591775&t=517003**
>
> From: Mark Phillips <mailto:philli...@pyebarkerfire.com>
> Sent: Thursday, November 12, 2020 9:41 AM
> To: mailto:sprinklerforum@lists.firesprinkler.org
> Cc: Travis Mack <mailto:travis.m...@mfpdesign.com>
> Subject: Re: Domestic Demands 13R
>
> Assuming the 8 inch supply loops the complex
> Add the domestic demand at the 4” point on the loop for each building
>
> Sent from my mobile device
> Please excuse spelling, grammar, and auto correction.
>
> Mark Phillips
> Branch Manager
> Fire Sprinkler Design, Install, Inspections
> Service, Backflows, Fire Alarm Inspections
>
> 832-101 Purser Drive
> Raleigh NC 27603
> Phone: 919-779-4010
> Fax : 919-779-4014
> Cell : 919-268-7587
> Email : mailto:philli...@pyebarkerfire.com
> Web : http://www.pyebarkerfire.com
>
> ________________________________________
> From: Sprinklerforum <mailto:
> sprinklerforum-boun...@lists.firesprinkler.org> on behalf of Travis Mack
> via Sprinklerforum <mailto:sprinklerforum@lists.firesprinkler.org>
> Sent: Thursday, November 12, 2020 11:34:20 AM
> To: mailto:sprinklerforum@lists.firesprinkler.org <mailto:
> sprinklerforum@lists.firesprinkler.org>
> Cc: mailto:travis.m...@mfpdesign.com <mailto:travis.m...@mfpdesign.com>
> Subject: Domestic Demands 13R
>
> [EXTERNAL]
>
> Forumites:
>
> Per 13R 9.6 it requires the domestic demand for the building being
> calculated to be added to the fire sprinkler system. This is generally not
> an issue. If you have a complex of say 20 buildings on site that is
> supplied by a common water line serving both domestic and fire, are you
> required to include the domestic demand for each building on the site water
> main.
>
> For example, if I have a project with a 8" main going through the complex,
> and 4" lead-ins to each building, with a domestic demand of 125 gpm for
> each building, how are you doing the domestic demand? With the domestic /
> fire split in the building, it is required to include the 125 gpm demand in
> addition to the fire sprinkler system demand in the 4" line. Are you
> including the other 2375 gpm (19 additional buildings at 125 gpm domestic
> allowance), in your calculations back to the city main?
>
> This seems quite excessive. If it were a 13 system, you would have similar
> flows and a 100 gpm hose allowance. There is no requirement in this example
> to include the domestic in a 13 system. But, if you are required to include
> the additional 2375 gpm, that could be quite taxing on the site supply.
> Again, how is everyone handling it.
>
> We have seen AHJ's take both approaches on this.
>
>
> Travis Mack, CFPS, CWBSP, RME-G, SET
> Engineering Manager
> MFP Design
> 3356 E Vallejo Ct
> Gilbert, AZ 85298
> NEW EXTENSION: 480-505-9271 ext. 700
> NEW MOBILE: 480-272-2471
> mailto:travis.m...@mfpdesign.com
> http://www.mfpdesign.com
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> LinkedIn: https://www.linkedin.com/in/travismack
>
> “The bitterness of poor quality remains long after the sweetness of low
> price is forgotten.”
>
> Need/Want a faster way to check material pricing? Build a material quote?
> Check availability ? Searching for an invoice?
> *If you do not already have an account with ferguson.com, click here to
> register.*
> **Have a Ferguson account? Download the Ferguson app for on-the-go access
> to your favorite ferguson.com features. Apple iOS devices or Android
> devices**
>
> _______________________________________________
> Sprinklerforum mailing list
> mailto:Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> mailto:Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> mailto:Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> mailto:Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org