Section 9.6 (2016) says "Domestic demand  FOR THE BUILDING BEING CALCULATED 
shall be included . . ."  I took the liberty of adding capitalization.  I 
assume the intent is to include the added friction loss caused by the domestic 
demand in the private part of the UG system.  So you might be able to argue it 
doesn't matter how many buildings take supply from your 4" UG because we only 
calc 1 building at a time.

Ed K


-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Travis Mack via Sprinklerforum
Sent: Thursday, November 12, 2020 10:53 AM
To: philli...@pyebarkerfire.com; sprinklerforum@lists.firesprinkler.org
Cc: travis.m...@mfpdesign.com
Subject: RE: Domestic Demands 13R

Correct.  However, they may be expected to have domestic demands.  That is the 
plan reviewer rationale in one particular case.


Travis Mack, CFPS, CWBSP, RME-G, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
NEW MOBILE: 480-272-2471
mailto:travis.m...@mfpdesign.com
www.mfpdesign.com

Send large files to us via: 
https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0
LinkedIn: 
https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

Need/Want a faster way to check material pricing?  Build a material quote?  
Check availability ?   Searching for an invoice?
*If you do not already have an account with ferguson.com, click 
https://www.ferguson.com/account-registration to register.* **Have a Ferguson 
account? Download the Ferguson app for on-the-go access to your favorite 
ferguson.com features. 
http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/1qtklpp37l9byeftyuoy12/external?email=true&a=6&p=2591775&t=517003
 or 
http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true&a=6&p=2591775&t=517003**

From: Mark Phillips <philli...@pyebarkerfire.com>
Sent: Thursday, November 12, 2020 9:51 AM
To: sprinklerforum@lists.firesprinkler.org; Travis Mack 
<travis.m...@mfpdesign.com>
Subject: Re: Domestic Demands 13R

From a practical perspective all of the apartment building would not be 
expected to be on fire at once.

That was how a plan reviewer once explained it to me.


Sent from my mobile device
Please excuse spelling, grammar, and auto correction.

Mark Phillips
Branch Manager
Fire Sprinkler Design, Install, Inspections Service, Backflows, Fire Alarm 
Inspections

832-101 Purser Drive
Raleigh NC 27603
Phone: 919-779-4010
Fax : 919-779-4014
Cell : 919-268-7587
Email : mailto:philli...@pyebarkerfire.com
Web : http://www.pyebarkerfire.com

________________________________________
From: Sprinklerforum <mailto:sprinklerforum-boun...@lists.firesprinkler.org> on 
behalf of Mark Phillips via Sprinklerforum 
<mailto:sprinklerforum@lists.firesprinkler.org>
Sent: Thursday, November 12, 2020 11:46:23 AM
To: mailto:travis.m...@mfpdesign.com <mailto:travis.m...@mfpdesign.com>; 
mailto:sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Mark Phillips <mailto:philli...@pyebarkerfire.com>
Subject: Re: Domestic Demands 13R 
 
[EXTERNAL]

Sorry if I was not clear only the demand of the building or buildings that 
share the 4 inch supply .

Sent from my mobile device
Please excuse spelling, grammar, and auto correction.

Mark Phillips
Branch Manager
Fire Sprinkler Design, Install, Inspections Service, Backflows, Fire Alarm 
Inspections

832-101 Purser Drive
Raleigh NC 27603
Phone: 919-779-4010
Fax : 919-779-4014
Cell : 919-268-7587
Email : mailto:philli...@pyebarkerfire.com
Web : http://www.pyebarkerfire.com

________________________________
From: mailto:travis.m...@mfpdesign.com <mailto:travis.m...@mfpdesign.com>
Sent: Thursday, November 12, 2020 11:44:10 AM
To: Mark Phillips <mailto:philli...@pyebarkerfire.com>; 
mailto:sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Domestic Demands 13R

[EXTERNAL]

So in this case, you would be adding a total demand of 2500 gpm (20 buildings 
at 125 gpm each) to your sprinkler calc?  And yes, it would be included at the 
point of each 4” connection to the 8” main.  Seems excessive, but I have seen 
it requested that way.  I have more commonly done what Matt states to only 
include the building of interest in the calc.


Travis Mack, CFPS, CWBSP, RME-G, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
NEW MOBILE: 480-272-2471
mailto:travis.m...@mfpdesign.com
http://www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0
LinkedIn: 
https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

Need/Want a faster way to check material pricing?  Build a material quote?  
Check availability ?   Searching for an invoice?
*If you do not already have an account with ferguson.com, click 
https://www.ferguson.com/account-registration to register.* **Have a Ferguson 
account? Download the Ferguson app for on-the-go access to your favorite 
ferguson.com features. 
http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/1qtklpp37l9byeftyuoy12/external?email=true&a=6&p=2591775&t=517003
 or 
http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true&a=6&p=2591775&t=517003**

From: Mark Phillips <mailto:philli...@pyebarkerfire.com>
Sent: Thursday, November 12, 2020 9:41 AM
To: mailto:sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack <mailto:travis.m...@mfpdesign.com>
Subject: Re: Domestic Demands 13R

Assuming the 8 inch supply loops the complex Add the domestic demand at the 4” 
point on the loop for each building

Sent from my mobile device
Please excuse spelling, grammar, and auto correction.

Mark Phillips
Branch Manager
Fire Sprinkler Design, Install, Inspections Service, Backflows, Fire Alarm 
Inspections

832-101 Purser Drive
Raleigh NC 27603
Phone: 919-779-4010
Fax : 919-779-4014
Cell : 919-268-7587
Email : mailto:philli...@pyebarkerfire.com
Web : http://www.pyebarkerfire.com

________________________________________
From: Sprinklerforum <mailto:sprinklerforum-boun...@lists.firesprinkler.org> on 
behalf of Travis Mack via Sprinklerforum 
<mailto:sprinklerforum@lists.firesprinkler.org>
Sent: Thursday, November 12, 2020 11:34:20 AM
To: mailto:sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: mailto:travis.m...@mfpdesign.com <mailto:travis.m...@mfpdesign.com>
Subject: Domestic Demands 13R

[EXTERNAL]

Forumites:

Per 13R 9.6 it requires the domestic demand for the building being calculated 
to be added to the fire sprinkler system.  This is generally not an issue.  If 
you have a complex of say 20 buildings on site that is supplied by a common 
water line serving both domestic and fire, are you required to include the 
domestic demand for each building on the site water main.

For example, if I have a project with a 8" main going through the complex, and 
4" lead-ins to each building, with a domestic demand of 125 gpm for each 
building, how are you doing the domestic demand?  With the domestic / fire 
split in the building, it is required to include the 125 gpm demand in addition 
to the fire sprinkler system demand in the 4" line.  Are you including the 
other 2375 gpm  (19 additional buildings at 125 gpm domestic allowance), in 
your calculations back to the city main?

This seems quite excessive.  If it were a 13 system, you would have similar 
flows and a 100 gpm hose allowance.  There is no requirement in this example to 
include the domestic in a 13 system.  But, if you are required to include the 
additional 2375 gpm, that could be quite taxing on the site supply.  Again, how 
is everyone handling it.

We have seen AHJ's take both approaches on this.


Travis Mack, CFPS, CWBSP, RME-G, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
NEW MOBILE: 480-272-2471
mailto:travis.m...@mfpdesign.com
http://www.mfpdesign.com

Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

Need/Want a faster way to check material pricing?  Build a material quote?  
Check availability ?   Searching for an invoice?
*If you do not already have an account with ferguson.com, click here to 
register.* **Have a Ferguson account? Download the Ferguson app for on-the-go 
access to your favorite ferguson.com features. Apple iOS devices or Android 
devices**

_______________________________________________
Sprinklerforum mailing list
mailto:Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
mailto:Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to