Computer Programs  --  DATA --  garbage in = garbage output

Locally Most information is Good with the computer models having a 10%  or
10 psi safety factor.

I have received Information that has been has been BOTH  high psi Static
and  LOW   psi  static  &  GPM at 20 psi  that goes off the HASS HRSS chart
(over 9999 gpm)

I have helped Local AHJ and Water Dist.  to confirm DATA
 and   asked to put Gauge on Hydrant to check static psi.
 flushed a Local private hydrants  and Collected Data to compare to Water
Info
flushed UNDERGROUND  and Collect DATA

A few local Water Districts oversee Hydrant Flow Tests  (Are they being
flushed every 5 years?)

and a Few jobsites  may have 88 psi Static  ....  but  10% off  another 5%
for worst case in 25 years   and they give us 72 psi static
well with a few
74' building with Attic Dry    or   a
50 year old Warehouse  with storage
I NEED ACTUAL  STATIC   PSI   FOR  possible fire pump  design
NOT flow test from a computer model that says 66 psi  and  flowing  3000
gpm at 50 psi  and  limits water to 10 fps (how many hydants are flowing?)

(Does City of R....& L....  Fire think about velocity ? when we do actual
of standpipe flow tests NO )  around
200 psi @ Pumper Truck  +- 175 psi at FDC  165 @ Riser flowing 1100 - 750
gpm with 100 psi residual at High Point

RECOMMENDATIONS  when Water Districts flush hydrants Collect Data for
Computer Models.

Chuck Bamford S.E.T.





On Wed, Aug 31, 2022 at 11:22 AM Fpdcdesign <[email protected]> wrote:

> I think a lot of this depends on the sophistication of the software and
> hardware used, which could also be a function of the size of the water
> company. In the Northeast, we have a lot of small water companies that only
> service a specific town or section of town. Near the larger cities, you get
> regional authorities that cover several towns but there may or not be any
> interconnections. Also, several municipal water companies have been bought
> up by holding companies but they still operate as independent units. They
> don’t have the resources to spend on a sophisticated modeling system.
>
> One of the companies that services the town I live in tried a modeling
> system. It consisted of little more than a 3D computer model of the system
> connected to a pump. Something I could do with Autosprink. I believe they
> had a run of unlined cast iron pipe from 1888 listed as C=120 (or the D-W
> equivalent). Needless to say the accuracy is a joke. I think it has been
> abandoned.
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080 (ofc)
> 860-554-7054  (fax)
> 860-608-4559 (cell)
>
>
> On Aug 31, 2022 at 1:15 PM, <Steve Leyton <[email protected]>>
> wrote:
>
> T-Mack’s comments reminded me of one other distinct advantage to models –
> I can get two or more per project relatively easily if I need to.   Our
> firm designs a lot of private hydrant systems in addition to building
> sprinkler systems, so the benchmark we need for highest accuracy might be
> 3,000 GPM flow or 350 gpm flow.  As others have noted, the higher the flow
> rate the more accurate the data (vs. extrapolation), and with most
> agencies, I can request models at whatever fire flow rate I choose.
>
>
>
> Steve
>
>
>
> *From:* [email protected] <[email protected]>
> *Sent:* Wednesday, August 31, 2022 9:46 AM
> *To:* [email protected]
> *Subject:* [Sprinklerforum] Re: [EXTERNAL] Hydrant flow tests
>
>
>
> Maybe because I am in the SW with Steve, I agree 100% with his statements
> here.  We can get situations modeled for basically anything we want
> regarding the water supply.  As Steve mentioned, many water agencies have
> decades of data to accurately model this stuff.  I have to ask why we will
> rely on hydraulic calculation models for our fire sprinkler systems, if we
> won’t rely on similar calculation models for the water supply?  The math
> doesn’t change just because it is a sprinkler vs a hydrant.
>
>
>
> Our experience has been more positive with models than with actual flow
> testing.  We’ve had customers go “flow test shopping” where I found out
> later that they did multiple flow tests and gave us the best one that they
> obtained.  Well, that’s great if you can guarantee a fire will only occur
> during that time frame.  The computer models will account for peak demand,
> anticipated changes, and other things that a simple flow test can not
> account for.
>
> While I am old school and do like to have it confirmed by an actual flow
> test if possible, I tend to feel the models are more reliable and accurate
> over longer periods.  Now, all of this is to say that it is based on the
> model database of information to be accurate.  If there are errors in the
> database or user entering the information for the model it fails.  That is
> no different than someone using an un-calibrated gauge, not applying pumper
> coefficients or getting incorrect hydrant coefficients, let alone not
> choosing the worst-case time of day for a flow test.
>
>
>
> *Please rate our customer service
> <https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fsurvey.medallia.com%2f%3femailsignature%26fc%3d3539%26bg%3dFire%2520and%2520Fabrication&c=E,1,wv1KVigAKuTRqcaSNc4pOZWCeagx-cP1kMlCKE8h7pS48OQSn6sq5itvRRdcmq8opQ2Q6Jx5GIdlWoWFi--9DawdWzMxzMf3H9pfJ-7GSaKFDeY,&typo=1>*
>
>
>
> *Travis Mack, RME-G, COC, SET*
>
> *Senior Engineering Manager*
>
> *MFP Design*
>
> 480-505-9271 ext. 700 C: 480-272-2471
>
> [email protected]
>
> [email protected]
>
> www.mfpdesign.com
> <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.mfpdesign.com&c=E,1,i9qf3bbsyv8viIjgOz35g6OUEOU8y_Fb35HidPh5Fy5fUjakm34El4fK3J0RuCX-nr30TdcTmyQhK0NBpYGnIn02l4eaRI9g28fnhDYTPSDjBA,,&typo=1>
>
>
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
>
>
>
> *From:* Steve Leyton <[email protected]>
> *Sent:* Wednesday, August 31, 2022 9:35 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: [EXTERNAL] Hydrant flow tests
>
>
>
> I respectfully, but stridently disagree.   To this comment and Rick’s
> overarching question, I would offer that our experience over the past 10+
> years has been that these models are not only accurate, they are highly so
> and can be programmed for eventualities and conditions that flow tests
> simply cannot reflect, because they are a measurement of the “right now”
> only.  But I would offer an bold asterisk on my comments because they are
> based on regionality and I’m in the SWUSA, where water management has been
> a critical thing for a full generation now.
>
>
>
> Because of drought concerns going back 20+ years, many water agencies
> stopped doing flow tests and began to meter their systems.  Today, nearly
> all water agencies in California will only grant a permit to do a physical
> flow test if there are compelling circumstances, and we rely on models.
> Using San Diego County as an example, water districts began installing
> sensors 25 years ago and have been collect metadata on overall system
> performance for dozens of years; these systems are in fact predictable if
> the database used to calculate performance is well-populated and highly
> detailed.   I was going to offer Rick the anecdote of how we designed a
> whole campus high school 15 years ago, in a subdivision that was brand
> new.  The only “flow data” we had to work with was the master developer’s
> civil engineering water study, which was based on the zone model from the
> water district.   And it said that the static was going to be so high (182)
> that we needed to install pressure reducing valves on the supply side of
> the backflows feeding the site loop.   We also used the model for sprinkler
> hydraulics, but corrected the pressures downward for the PRV settings.
> When the permanent system was commissioned into service (two years later
> and with sprinkler systems 80-90% installed) the static pressure was 181
> and the residual was exactly the same as modeled.
>
>
>
> Programmability of models enables simulation of worst-case scenarios,
> particularly peak day demand, annual drought predictions and legacy drought
> conditions.   This is extremely important in the West as our water levels
> are literally dropping every year, so maybe that’s why our water agencies
> have established such high standards of care for modeling.   City of San
> Diego doesn’t require that you take 10% off of their models any longer –
> why?  Because they program peak day demand, legacy drought levels and an
> additional safety factor.   When they first started this practice, the FP
> community was going nuts – field conditions showed 10-20 PSI more pressure
> at the hydrants in some cases.  Yes, pipe sizing was affected,  but if
> we’re talking about safety and prudence (without consideration for the
> cost-impact, obviously), this methodology yields solidly conservative data
> for basis of design.
>
>
>
> Chains are only as strong as their weakest link and physical flow testing
> only reflects current conditions.  Was the test done during a peak day
> demand window?  Was the test measured with a $10-15 spring loaded gauge (up
> to 8-10% error) or a calibrated liquid-filled one with a 1% error or
> less?   Was the test even taken by skilled personnel?    My opinion on this
> has swung – I’m now pro-model and we look at physical testing as an archaic
> practice, and I’m a shamelessly analogue Boomer.
>
>
>
>
>
> Yours in the name of fire safety and progress,
>
> Steve L.
>
>
>
>
>
>
>
> *From:* Prahl, Craig <[email protected]>
> *Sent:* Wednesday, August 31, 2022 8:10 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: [EXTERNAL] Hydrant flow tests
>
>
>
> Having experienced bogus results from computer modeling on more than one
> occasion, nothing matches the actual flow of the hydrant systems.
>
>
>
> Most recently I got a water report from a local municipality who generated
> the info via their water modeling software.  It said I could expect 6700
> gpm from the system……. via 8” lines at 10 fps!   Nope, don’t think that’s
> going to be a real thing.
>
>
>
> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection |
> [email protected] | www.jacobs.com
>
> 1041 East Butler Road   Greenville, South Carolina  29606
>
> CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS
>
>
>
>
>
>
>
> *From:* Rick Matsuda <[email protected]>
> *Sent:* Wednesday, August 31, 2022 9:51 AM
> *To:* [email protected]
> *Subject:* [EXTERNAL] [Sprinklerforum] Hydrant flow tests
>
>
>
> I know that an accurate flow test is critical for the sprinkler system
> design, but I’ve heard several discussions recently about water
> conservation during our drought conditions across the SW states.
>
>
>
> With all our technology, is it possible to develop an accurate computer
> modeling program for water departments to use in lieu of flow tests? Even
> with the program, I think there would still be a need for some flow tests
> to verify the program results, but maybe not as many as now.
>
>
>
> I’m not taking any pro/con position regarding this issue. I’m just
> providing food for thought for the future as our need for water increases
> and our resources diminish. Adequate water is the key for our industry.
>
>
>
> It’s ironic cause we get more wild fires due to the drought, and then we
> have to use more water to fight the fires.
>
> Rick Matsuda
>
>
>
>
> ------------------------------
>
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
> _________________________________________________________ SprinklerForum
> mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to