Brad,

Your suggested practice makes an overwhelming assumption that by opening and closing the hydrant quickly that the flow will stabilize enough during that momentary opening and give your equation a proper reading of the available flowing pressure. While your proposed solution does not address a possible closed or damaged valve in the supply (as others have suggested) it _*directly*_ contradicts the procedures in NFPA 291 §4.5.7 which notes that the water should allowed to flow for a sufficient time to clear all debris and foreign substances from the stream.

Now that I've shared this I'll also note that you're welcome to make a public input to the -291 committee Aut-Pri, for their consideration, as is any member of the public.  Speaking as one who has had any number of PI's rejected over the years I caution you to be prepared for a similar response.

I would also share the wisdom a mentor of mine a long time ago shared with me regarding conducting water flow tests at a hydrant.  I believe his quote was "don't measure with a micrometer when you're making cuts with a chainsaw."

sincerely,
*Ken Wagoner, SET*
*Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235*
*Phone: (760) 745-6181 *
*Visit the website <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>*

On 9/7/2022 11:34 AM, Brad Casterline wrote:

I like seeing how far water shoots out the hydrant nearest my base of riser.

Say that is 10 ft, and the butt is 3 ft high. From The Law of Falling Bodies I know if I drop water straight down from 3 ft it will be going

v=SQRT(2gh) when it hits the ground, and the Time of Flight, t=v/g.

v=(2*32.2*3)^.5=~14 ft/s.

t=14/32.2=.43 s.

If the water goes straight out 10 ft in ~half a second it is going 20 ft/s.

If the butt is nominal 2.5", smooth and well rounded, (like yours truly):

((2.5/24)^2)*pi=~.034 ft^2, times .9=.031 ft^2,

times 20 ft/s=.68 ft^3/s,

times 7.48 gallons per cubic foot, times

60 seconds per minute= 305 GPM.

So if all I can get is a Purveyor Representative with a hydrant wrench and authorization to quickly, fully open the hydrant and just as quickly, fully shut it down, I'll take it!

Brad Casterline

**

*From:* Greg McGahan <[email protected]>
*Sent:* Tuesday, September 6, 2022 9:10 AM
*To:* Discussion list on issues relating to automatic fire sprinklers <[email protected]>
*Subject:* [Sprinklerforum] Re: [EXTERNAL] Hydrant flow tests

How many flow tests have you seen that underperformed due to a closed valve, broken valve (appeared to be open), disconnected piping that was never reconnected etc?

Personally? Too many to not be concerned about solely relying on models.

My two cents worth (adjusted for inflation).


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to