All good points. Still collecting info but I will be sure to ask. Thank you.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: Fpdcdesign <[email protected]>
Sent: Friday, January 06, 2023 9:20 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: 2" Underground

You don’t specify what type of pipe and how long the run is. Does the type of 
2” meet the requirements of NFPA 13?

Section 5.1.3 (2019) permits underground smaller than 6” if it can support 
hydraulics. You would need to do the full calculation with the actual 2” 
underground main included, not an assumption. 324 gpm going through 2” copper 
pipe has a friction loss of .58 psi/ft. Your 10 psi assumption would include 
only 17 equivalent feet of 2” copper. The velocity would be over 30 ft per 
second.

You should also check with the water purveyor to see if they have a minimum 
size for sprinkler system connections.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)



On Jan 6, 2023 at 8:47 AM, <Brian Harris<mailto:[email protected]>> 
wrote:
Been asked to verify a 2” underground supply will work for a NFPA-13 Dry system 
for a small Patio/Bar. Water supply is good, S=114 / R=106 / F=1556. 
Preliminary numbers I’ve ran show a system demand of 324gpm @ 46psi. That’s 
assuming a 10psi loss for underground pipe (BFP is 10 as well), the loss for 2” 
underground is the part I’m not real comfortable about. Any thoughts?

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935


_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to