Brian,
We need a little mor information about the Underground.
I ran a Calculation based on 100' of 2" Type M Copper flowing 324 GPM.
This created 88 PSI pressure loss.
Regards,
G. Tim Stone
AutoSPRINK 2020, 16.3.28.0
Xi Powergo XT
Intel Core i7-8700k CPU@ 3.70GHz
Windows 10 Pro; 64 Bit
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638
[email protected] <mailto:[email protected]>
From: Brian Harris <[email protected]>
Sent: Friday, January 6, 2023 8:46 AM
To: [email protected]
Subject: [Sprinklerforum] 2" Underground
Been asked to verify a 2" underground supply will work for a NFPA-13 Dry
system for a small Patio/Bar. Water supply is good, S=114 / R=106 / F=1556.
Preliminary numbers I've ran show a system demand of 324gpm @ 46psi. That's
assuming a 10psi loss for underground pipe (BFP is 10 as well), the loss for
2" underground is the part I'm not real comfortable about. Any thoughts?