Thank you.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: August Hoffman <[email protected]>
Sent: Tuesday, July 11, 2023 4:57 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Storage Tank

Really depends on the tank, I have seen ones that fill from the top, some fill 
from the side, but I don't think I have seen above ground tanks that fill from 
the bottom (but they may very well exist). For the exposed pipe it will most 
likely need to be insulated (or heat traced) unless they plan on building a 
heated space around the tank. If it is an existing tank, you might be able to 
get cut sheets from the manufacturer if you can get a model number somewhere on 
the tank. If it is a new tank, then it should be easier to find cut sheets from 
whoever ordered it/ is installing it. Most larger tanks I have seen are top fed.

AUGUST HOFFMAN
CET

From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Tuesday, July 11, 2023 12:43 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Storage Tank

Might be a silly question but when using a storage tank for a pump where is the 
tank fill located? Top, Bottom, Side, etc. This is in an area where it does get 
cold enough to freeze so I'm wondering if it can be filled from under the tank. 
The city supply psi will overcome the head pressure in the tank so technically 
it would work.

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,Cl5jNux_4aHTA_lshMw_BP4vubRWsbj6FRso6_Qea6w5B6fQtU3pylLFqcjsULXq1yQPrWn56LJBtTGw1lNC_tt_VE2_TEvVs0-n525WGudQ6ElWpY0LYukesjor&typo=1>
Phone: 704.896.9989
Fax: 704.896.1935


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to