FYI

Here is what the annex to the section below from NFPA 13 (2022) states:

A.16.2.4.2 Plastic bags should not be used for this purpose due to the fact 
that shrinkage prior to development of temperatures needed to ensure sprinkler 
activation can interfere with proper sprinkler operation and development of 
spray patterns.  The prohibition against plastic bags should include 
polypropylene bags commonly marketed as "cello" bags. True cellophane degrades 
rather than melts and, like paper, does not display shrinkage.

As has already been recommended, I would second wax-coated sprinklers or paper 
bags over sprinklers...along with a robust maintenance plan with either route 
chosen.

Hope this helps,

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Associate Fire Protection Engineer
O 612-900-3755 \  M 763-688-4045 \  F 952-229-2923
[email protected]<mailto:[email protected]>  \  
burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437
*Registered in: AK, LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout

From: JOSEPH MCCAFFERTY <[email protected]>
Sent: Monday, September 18, 2023 1:16 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>; Michael de Gabriele 
<[email protected]>
Subject: [Sprinklerforum] Re: Best fire protection solution for dirty 
environment

Do the sprinklers etc need corrosion protection from the stored product as well?
On 17/09/2023 01:56 Michael de Gabriele 
<[email protected]<mailto:[email protected]>> wrote:


Has anyone ever done this to a 10000m2 warehouse?

On Sun, 17 Sep 2023 at 2:37 am, Jackie Ward 
<[email protected]<mailto:[email protected]>> wrote:
For paint spray areas, we bag our heads.  It sounds like your environment would 
be similar.  The following is from the 2019 edition of NFPA-13 for reference.

[cid:[email protected]]



Thank you,

Jackie "JW" Ward
1-405-240-7076

From: Michael de Gabriele 
<[email protected]<mailto:[email protected]>>
Sent: Friday, September 15, 2023 6:05 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Best fire protection solution for dirty environment

Good morning
I trust that everyone is well
I currently have a project in Geelong Australia where the product bulk stored 
within the buildings make for a extremely dusty environment when unloading.
Sprinkler protection is proposed to protect the building and wanted to ask the 
question about "excessive loading of sprinklers" and what the best option would 
be to minimise this
I am aware that NFPA 25 mentions this, our code in Australia does not mention 
this term but states that yearly the sprinklers must be visually checked and 
suggest that a more stringent maintenance routine be in place for these 
environments.

The product bulk stored is phosphate rock typically and is used for the 
fertiliser manufacturing plant across the road.

Any suggestions to the above query would be much appreciated.

Kind regards
Michael Paul de Gabriele
Fire protections engineer


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to