I would think residential sprinklers meet the intent of NFPA 13R. Foyers, corridors, and hallways [6.2.2.2(2), 6.2.2.2(3), and 6.2.2.2(4)] are used for egress; hallways generally contain negligible combustibles and present a low fire challenge. Stairways are very similar, paths of egress and almost no fire load is present due to egress.
Look very close ate the FAQ of 7.2.1, NFPA 13R requires only that the design discharge, number of design sprinklers, sprinkler coverage, and position of sprinklers comply with NFPA 13, for areas outside the dwelling. Joe Burtell | SET, CFPS Fire Sprinkler Manager D C 406-204-4653 406-861-4507 3004 1st Ave South Billings, MT 59101 Office: 406-652-7697 www.summitfiresecurity.com This information transmitted, including attachments, is intended only for the person(s) or entity to which it is addressed and may contain confidential and/or privileged material. Any review, retransmission, dissemination or other use of, or taking of any action in reliance upon this information by persons or entities other than the intended recipient is prohibited. If you received this in error, please contact the sender and destroy any copies of this information. From: Trevor Spain <supp...@igneusinc.com> Sent: Wednesday, September 20, 2023 7:13 AM To: Fpdcdesign via Sprinklerforum <sprinklerforum@lists.firesprinkler.org> Subject: [Sprinklerforum] Residential heads in stairways CAUTION: This email originated from outside the organization. Do not follow guidance, click links, or open attachments unless you KNOW the content is safe. Good Morning Everyone, Our design team is debating the use of residential heads in stairways. For a predominately residential occupancy (like an apartment) designed to 2016 NFPA 13R, do stairways qualify for residential heads under 6.2.2.2 (8) “Other areas with fire loads similar to residential fire loads”? If the design is to 2016 NFPA 13 instead, can a stairway be considered “corridor” to meet the requirement of 8.4.5.1 for use of residential heads? Trevor Spain The Fire Group, Inc. www.thefiregroupinc.com<http://www.thefiregroupinc.com> On 9/18/2023 2:25 PM, Alan Brinson wrote: Calcium phosphate is inert. Alan Brinson ________________________________ From: JOSEPH MCCAFFERTY <joemccaffe...@virginmedia.com><mailto:joemccaffe...@virginmedia.com> Sent: Monday, September 18, 2023 7:16:19 PM To: Discussion list on issues relating to automatic fire sprinklers <sprinklerforum@lists.firesprinkler.org><mailto:sprinklerforum@lists.firesprinkler.org>; Michael de Gabriele <mpdegabri...@gmail.com><mailto:mpdegabri...@gmail.com> Subject: [Sprinklerforum] Re: Best fire protection solution for dirty environment Do the sprinklers etc need corrosion protection from the stored product as well? On 17/09/2023 01:56 Michael de Gabriele <mpdegabri...@gmail.com><mailto:mpdegabri...@gmail.com> wrote: Has anyone ever done this to a 10000m2 warehouse? On Sun, 17 Sep 2023 at 2:37 am, Jackie Ward <jw...@firetrol.net<mailto:jw...@firetrol.net>> wrote: For paint spray areas, we bag our heads. It sounds like your environment would be similar. The following is from the 2019 edition of NFPA-13 for reference. [cid:image001.png@01D9EBC4.33154690] Thank you, Jackie “JW” Ward 1-405-240-7076 From: Michael de Gabriele <mpdegabri...@gmail.com<mailto:mpdegabri...@gmail.com>> Sent: Friday, September 15, 2023 6:05 PM To: Discussion list on issues relating to automatic fire sprinklers <sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>> Subject: [Sprinklerforum] Best fire protection solution for dirty environment Good morning I trust that everyone is well I currently have a project in Geelong Australia where the product bulk stored within the buildings make for a extremely dusty environment when unloading. Sprinkler protection is proposed to protect the building and wanted to ask the question about “excessive loading of sprinklers” and what the best option would be to minimise this I am aware that NFPA 25 mentions this, our code in Australia does not mention this term but states that yearly the sprinklers must be visually checked and suggest that a more stringent maintenance routine be in place for these environments. The product bulk stored is phosphate rock typically and is used for the fertiliser manufacturing plant across the road. Any suggestions to the above query would be much appreciated. Kind regards Michael Paul de Gabriele Fire protections engineer _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org> _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org> _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org