Good Morning Everyone,

Our design team is debating the use of residential heads in stairways. For a predominately residential occupancy (like an apartment) designed to 2016 NFPA 13R, do stairways qualify for residential heads under 6.2.2.2 (8) “Other areas with fire loads similar to residential fire loads”?

If the design is to 2016 NFPA 13 instead, can a stairway be considered “corridor” to meet the requirement of 8.4.5.1 for use of residential heads?

Trevor Spain

The Fire Group, Inc.
www.thefiregroupinc.com

On 9/18/2023 2:25 PM, Alan Brinson wrote:
Calcium phosphate is inert.

Alan Brinson
------------------------------------------------------------------------
*From:* JOSEPH MCCAFFERTY <[email protected]>
*Sent:* Monday, September 18, 2023 7:16:19 PM
*To:* Discussion list on issues relating to automatic fire sprinklers <[email protected]>; Michael de Gabriele <[email protected]> *Subject:* [Sprinklerforum] Re: Best fire protection solution for dirty environment Do the sprinklers etc need corrosion protection from the stored product as well?
On 17/09/2023 01:56 Michael de Gabriele <[email protected]> wrote:


Has anyone ever done this to a 10000m2 warehouse?

On Sun, 17 Sep 2023 at 2:37 am, Jackie Ward <[email protected]> wrote:

    For paint spray areas, we bag our heads.  It sounds like your
    environment would be similar.  The following is from the 2019
    edition of NFPA-13 for reference.

    Thank you,

    Jackie “JW” Ward

    1-405-240-7076

    *From:* Michael de Gabriele <[email protected]>
    *Sent:* Friday, September 15, 2023 6:05 PM
    *To:* Discussion list on issues relating to automatic fire
    sprinklers <[email protected]>
    *Subject:* [Sprinklerforum] Best fire protection solution for
    dirty environment

    Good morning

    I trust that everyone is well

    I currently have a project in Geelong Australia where the product
    bulk stored within the buildings make for a extremely dusty
    environment when unloading.

    Sprinkler protection is proposed to protect the building and
    wanted to ask the question about “excessive loading of
    sprinklers” and what the best option would be to minimise this

    I am aware that NFPA 25 mentions this, our code in Australia does
    not mention this term but states that yearly the sprinklers must
    be visually checked and suggest that a more stringent maintenance
    routine be in place for these environments.

    The product bulk stored is phosphate rock typically and is used
    for the fertiliser manufacturing plant across the road.

    Any suggestions to the above query would be much appreciated.

    Kind regards

    Michael Paul de Gabriele

    Fire protections engineer


    _________________________________________________________
    SprinklerForum mailing list:
    https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org

    To unsubscribe send an email to
[email protected]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to