Factory Mutual has begun limiting K factors and increasing design densities as 
ceiling heights increase.  NFPA has begun to migrate some of these concepts 
into the 2025 edition of NFPA 13.  I don’t know that there’s an explicit limit 
for light hazard, but there’s some language in the design approach chapter that 
may start to limit them in the higher occupancy groups.  In FM 2-0 there are 
specific combinations of heads and ceiling heights allowed by Hazard Category.

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Estimator • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625
email [email protected]<mailto:[email protected]>
24/7<outlook-data-detector://2/> SERVICE LINE 888.217.7055<tel:888.217.7055>
[cid:[email protected]]

From: James Crawford <[email protected]>
Sent: Monday, November 4, 2024 4:22 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Ceiling Heights for 5.6K Heads

Throwing this out there, I was asked if there is a maximum ceiling height for 
5. 6K sprinkler heads, can’t find anything in the code but may have missed it. 
Thank You James Crawford Phaser Fire Protection Ltd. Phone 604-888-0318 Cel: 
604-790-0938
ZjQcmQRYFpfptBannerStart
This Message Is From an Untrusted Sender
You have not previously corresponded with this sender.
ZjQcmQRYFpfptBannerEnd
Throwing this out there, I was asked if there is a maximum ceiling height for 
5.6K sprinkler heads, can’t find anything in the code but may have missed it.

Thank You

James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Cel: 604-790-0938
Email [email protected]<mailto:[email protected]>
Web: 
www.phaserfire.ca<https://urldefense.com/v3/__http:/www.phaserfire.ca__;!!FaxH778!bf-im6feHGCKEqpmx9mV5fPJ8x9DayF4on7VRkN-eC5NHf2uCj-XlEDuoJ3l3FuueD999I6maeDD8usowdfET6A$>


This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to