FMDS 02-00 (Jan-2024) unobstructed construction

  *   Table 2.5.2.3.1.1(a) limits 5.6k for HC-1 to 60’ ceiling height.
  *   Table 2.5.2.3.1.1(b) limits 5.6k for HC-2 to 60’ ceiling height.
  *   Table 2.5.2.3.1.1(c) limits 5.6k for HC-3 to 45’ ceiling height.
  *   Table 2.5.2.2.1 requires a minimum 8.0k sprinkler for HC-2 and HC-3 where 
solid structural members are deeper than 4”.



Thank you,

Jackie “JW” Ward
1-405-240-7076

From: Prahl, Craig <[email protected]>
Sent: Monday, November 4, 2024 3:42 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Ceiling Heights for 5.6K Heads

Have you checked the manufacturer’s data sheet of the specific sprinkler? 
Height limitations are often dependent upon the application. Craig Prahl | 
Jacobs | Fire Protection SME – EV, AM, DC, Special Hazards craig. prahl@ 
jacobs. com

Have you checked the manufacturer’s data sheet of the specific sprinkler?

Height limitations are often dependent upon the application.

Craig Prahl | Jacobs | Fire Protection SME – EV, AM, DC, Special Hazards
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: James Crawford <[email protected]<mailto:[email protected]>>
Sent: Monday, November 4, 2024 4:22 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] [Sprinklerforum] Ceiling Heights for 5.6K Heads

Throwing this out there, I was asked if there is a maximum ceiling height for 
5.6K sprinkler heads, can’t find anything in the code but may have missed it.

Thank You

James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Cel: 604-790-0938
Email [email protected]<mailto:[email protected]>
Web: 
www.phaserfire.ca<https://urldefense.com/v3/__http:/www.phaserfire.ca__;!!B5cixuoO7ltTeg!CxVMhmjaYUZNamP6Ay1laHKii-G2EDiRbUAXpmFU1s5E6vl1Ll8mzt5hwSdkQJpYb0t1OUtXsrid3DFX2eJ6dPIg9Q$>


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to