Yes…and no…

Before the 2025 version of NFPA 13 there are no restrictions accept for in storage occupancies. The new NFPA 13 (2025 Ed.) introduces new restrictions for ceilings over 30 feet in height. These restrictions include limiting sprinkler types, minimum K factors, minimum density requirements and design area. 

Mike Stewart
Unemployed Dog Walker 

On Nov 4, 2024, at 4:54 PM, Jackie Ward <[email protected]> wrote:



FMDS 02-00 (Jan-2024) unobstructed construction

  • Table 2.5.2.3.1.1(a) limits 5.6k for HC-1 to 60’ ceiling height.
  • Table 2.5.2.3.1.1(b) limits 5.6k for HC-2 to 60’ ceiling height.
  • Table 2.5.2.3.1.1(c) limits 5.6k for HC-3 to 45’ ceiling height.
  • Table 2.5.2.2.1 requires a minimum 8.0k sprinkler for HC-2 and HC-3 where solid structural members are deeper than 4”.

 

 

 

Thank you,

 

Jackie “JW” Ward

1-405-240-7076

 

From: Prahl, Craig <[email protected]>
Sent: Monday, November 4, 2024 3:42 PM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: Ceiling Heights for 5.6K Heads

 

Have you checked the manufacturer’s data sheet of the specific sprinkler? Height limitations are often dependent upon the application. Craig Prahl | Jacobs | Fire Protection SME – EV, AM, DC, Special Hazards craig. prahl@ jacobs. com

Have you checked the manufacturer’s data sheet of the specific sprinkler? 

 

Height limitations are often dependent upon the application. 

 

Craig Prahl | Jacobs | Fire Protection SME – EV, AM, DC, Special Hazards

[email protected] | www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS

 

 

From: James Crawford <[email protected]>
Sent: Monday, November 4, 2024 4:22 PM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Ceiling Heights for 5.6K Heads

 

Throwing this out there, I was asked if there is a maximum ceiling height for 5.6K sprinkler heads, can’t find anything in the code but may have missed it.

 

Thank You

 

James Crawford

Phaser Fire Protection Ltd.

Phone 604-888-0318

Cel: 604-790-0938

Email [email protected]

Web: www.phaserfire.ca

 

 



NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to