As long as it has gate valves and not butterfly valves, then I think 10 pipe 
diameters is all you need.

I’m curious about what makes the fire pump “untestable”.

-Kyle M

From: Fpdcdesign <[email protected]>
Sent: Tuesday, June 24, 2025 7:45 AM
To: Sprinklerforum <[email protected]>
Subject: [External][Sprinklerforum] Backflow turbulence

I am working on an untestable fire pump with an “N” shaped RPZ in the suction 
line. They (just) have the 10X diameter distance on the feed, but the suction 
pressures are very low (15 psi). It seems that an “N” shaped device would 
create a lost more turbulence than a standard straight one. Consequently, 
should the distance of straight pipe requirement be greater for this 
arrangement?

Todd G Williams, PE
Fire Protection Design/Consulting