IS 38 psi the municipal residual pressure?  At what flow rate as compared to 
the pump’s rating?

Craig Prahl | Jacobs | Fire Protection SME – EV, AM, DC, Special Hazards
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Fpdcdesign <[email protected]>
Sent: Tuesday, June 24, 2025 12:17 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: [EXTERNAL] Backflow turbulence

The water supply tested in the street to 38 psi with less than 5 ft elevation 
to the pump room. The suction pressure they are getting during the pump test is 
15 Todd Williams Fire Protection Design/Consulting Stonington, CT 860-608-4559 
On Jun

The water supply tested in the street to 38 psi with less than 5 ft elevation 
to the pump room. The suction pressure they are getting during the pump test is 
15

Todd Williams
Fire Protection Design/Consulting
Stonington, CT
860-608-4559



On Jun 24, 2025 at 11:39 AM, <Craig Prahl<mailto:[email protected]>> wrote:
Are suction pressures low due to the water supply?  Since there is a BFP, I 
assume you’re drawing from a city service, correct?  Got any data on that 
system?

Craig Prahl | Jacobs | Fire Protection SME – EV, AM, DC, Special Hazards
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Tuesday, June 24, 2025 10:45 AM
To: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] [Sprinklerforum] Backflow turbulence

I am working on an untestable fire pump with an “N” shaped RPZ in the suction 
line. They (just) have the 10X diameter distance on the feed, but the suction 
pressures are very low (15 psi). It seems that an “N” shaped device would 
create a lost
I am working on an untestable fire pump with an “N” shaped RPZ in the suction 
line. They (just) have the 10X diameter distance on the feed, but the suction 
pressures are very low (15 psi). It seems that an “N” shaped device would 
create a lost more turbulence than a standard straight one. Consequently, 
should the distance of straight pipe requirement be greater for this 
arrangement?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!B5cixuoO7ltTeg!BXROdjlCH_HD1dZflm5fL36y1RAbtph6W8gzx597Os4quHJL6bZFbNK9RNGmC-iqtDj9Jm6hwWx28cWKWCAuUw$>
 To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to