NFPA 13, 2019 Table 21.6.1a
(5) Open portable rack storage, on side or on tread 0.60/3000 (SR High Temp
Heads) Over 5'-0 up to 12'-0 high.



Thanks

Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
[email protected]
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca


On Fri, Feb 6, 2026 at 8:05 AM mattgrise5 <[email protected]> wrote:

> Sounds like an asrs system. Maybe fm 8-34?
>
>
>
> Sent from my T-Mobile 5G Device
>
>
> -------- Original message --------
> From: Fpdcdesign <[email protected]>
> Date: 2/6/26 8:47 AM (GMT-06:00)
> To: Sprinklerforum <[email protected]>
> Subject: [Sprinklerforum] Multiple row rack tire storage
>
> This is something I haven’t seen before. Rack storage of tires on edge 3
> tiers high (about 8 ft). The rack structure is on tracks and is about 87 ft
> wide.The racks move to create a single aisle up to 4 ft wide wherever
> needed. Similar to medical records storage. Consequently, there is a large
> concentration of tire racks with no aisle spaces. I couldn’t find anything
> in NFPA or FMGlobal that addresses this. Has anyone seen this before nad
> how did they handle it?
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080 (ofc)
> 860-554-7054  (fax)
> 860-608-4559 (cell)
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to