The suction side is coming from an aboveground suction tank which is on the 
same slab as the pump house.  There shouldn’t be any movement there to deal 
with.

Craig Prahl | Jacobs | Fire Protection SME – EV, AM, DC, Special Hazards
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS

From: Parsley Consulting <[email protected]>
Sent: Monday, March 9, 2026 4:22 PM
To: [email protected]
Subject: [EXTERNAL] [Sprinklerforum] Re: Flexible assembly on pump discharge in 
seismic cat D area

Craig, If you're looking to provide that much flexibility, my thought is that 
the solution Mike provided would certainly suffice. I admit to never having run 
across this requirement before, however the question popped into my head - 
wouldn't

Craig,

If you're looking to provide that much flexibility, my thought is that the 
solution Mike provided would certainly suffice.

I admit to never having run across this requirement before, however the 
question popped into my head - wouldn't the same requirement apply to the 
suction side of the pump as well?  It would seem applicable that the same 
motion would need to be accounted for on the suction side of the pump as well 
as the discharge side.

my thoughts only,
Ken Wagoner, SET
Parsley Consulting
3002 Younger Drive
Harrisonville, Missouri 64701-3909
Phone: (760) 745-6181
Visit the 
website<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.parsleyconsulting.com*2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1__;JSUlJQ!!B5cixuoO7ltTeg!GVh_9N5VeUHxlgaF5com-QskRr_PcVcgngXIjbdc42Q4A-TYIcpdPC__zbypHnwkzElc-MRNQM6Ffh81mLyovw$>



On 2/10/2026 9:28 AM, Prahl, Craig wrote:
I have a packaged fire pumphouse, discharge exists horizontally through the 
wall and then turns down to connect to the underground outside of the bldg.

The seismic design category SDC) is “D”.

I am being told by the project ME that we should have a flexible connection on 
the discharge side outside the bldg. to accommodate the potential of 8-inches 
of movement between the pumphouse and underground piping system.

I’ve looked around to try and find such an assembly for 8” pipe suitable for an 
outdoor installation and so far haven’t found such a device.

So, my question for those out there in seismically active areas, is this 
standard practice and who makes such an assembly?

Craig Prahl | Jacobs | Fire Protection SME – EV, AM, DC, Special Hazards
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.





_________________________________________________________

SprinklerForum mailing list:

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!B5cixuoO7ltTeg!GVh_9N5VeUHxlgaF5com-QskRr_PcVcgngXIjbdc42Q4A-TYIcpdPC__zbypHnwkzElc-MRNQM6Ffh-ovFHTDw$>

To unsubscribe send an email to 
[email protected]<mailto:[email protected]>


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.