On Fri, 30 Mar 2018, Stilez Stilezy wrote:
My own UPS setup is an APC SUA 1500i + AP9630 card, and the default user on
the UPS has been changed, so that's what I'll test anything with, to check my
understanding and appropriate inputs.
Perhaps this question is even more off-topic, but given
On Thu, 1 Feb 2018, Lee Damon wrote:
I've "fixed" this problem by modifying the nutshutdown script:
#!/bin/sh
# stop nut driver to free up access to the device
/sbin/systemctl stop nut-driver
# make sure it has time to die
sleep 2
# check to see
On Fri, 2 Feb 2018, nut.user.u...@neverbox.com wrote:
I have an older box set up this way for continuous integration, and it needs
to see more than a few seconds of power loss for the "always turn
on" BIOS setting to work. I forget how many different intervals I tried,
but 30
On Thu, 1 Feb 2018, nut.user.u...@neverbox.com wrote:
I am installing a UPS with NUT on Ubuntu for the first time. I could
follow the instructions up to "testing shutdowns" but on executing the
recommended command the computer shuts down and never comes back on,
Have you checked the BIOS
On Thu, 28 Dec 2017, Charles Lepple wrote:
On Dec 28, 2017, at 6:35 AM, Roger Price <ro...@rogerprice.org> wrote:
It would be clearer to users if the service unit file was also called
/lib/systemd/service/nut-monitor.service
From what I can tell, the "nut-client.service"
I reported a minor bug in nut 2.7.4 on Debian stretch and got the number 885592
https://bugs.debian.org/cgi-bin/bugreport.cgi?bug=885592
The systemd service unit /lib/systemd/system/nut-client.service reports itself
as nut-monitor.service on command systemctl status nut-client.service.
It
On Sun, 17 Dec 2017, Hervé Bastet wrote:
Bonjour,
Je fais suite au message que vous avez posté en 2015 :
http://lists.alioth.debian.org/pipermail/nut-upsuser/2015-February/009568.html
J'ai le même problème et ne trouve pas la solution. Comment vous en êtes-vous
sorti ?
D'avance, merci pour
On Sun, 10 Dec 2017, Jim Klimov wrote:
I am not sure the rights offered in that bug are fully ok: generally you
wouldn't want the configs to be writable by the service daemon if you
can avoid it (so if it's hacked - it can be abused to a lesser extent).
I think the only writable bit is the
On Sun, 10 Dec 2017, Charles Lepple wrote:
Either way, the default permissions are under the packager's control, so
I would recommend that you file a bug with Debian:
https://www.debian.org/Bugs/Reporting (feel free to mention the bug
number here)
Debian Bug Tracker told me that the URL is
I installed nut 2.7.4-5 on a fresh Debian 9.2.1 system. I updated the
configuration files, started nut in standalone mode, and got the error
message
Can't open /etc/nut/upsd.users: Permission denied
This is because the file has ownership and permissions
-rw--- 1 root nut 91
On Fri, 8 Dec 2017, Common Granger wrote:
I am using Ubuntu 16.04 LTS using NUT 2.7.4 with an APC Back-UPS
RS1000G. The problem is I do test shutdown using sudo upsmon -c fsd
and my computer shuts down ok but no matter how long I wait it never
turns back on. Is there a way to fix this. I
On Mon, 4 Dec 2017, Mikael Imperatori Festa wrote:
I had a look on the website, but I can¹t see a detailed list of supported
units.
Try installing and using apcupsd. Does it work correctly with the
BX700UI? Which protocol is it using?
Roger___
On Mon, 4 Dec 2017, Mikael Imperatori Festa wrote:
driver = apcupsd
port = auto
I meant the « APC UPS Daemon » at http://www.apcupsd.org/
Does this support your UPS unit? If so, what protocol is it using?
What is the model number of your unit? BX650CI ?
On Fri, 1 Dec 2017, Mikael Imperatori Festa wrote:
Hi there,
I tried all the driver on the list for this UPS, but they don’t work. Could you
help me please?
Have you tried with apcupsd? Which protocol does apcupsd use for the
Back-UPS 390 ?
Roger
This e-mail message may contain
On Thu, 19 Oct 2017, Drew Plaster wrote:
The topology is:
UPS TOPAPC, Data link to master, Power supply to master, slave1 and
slave2
UPS MIDAPC, Data link to master, Power supply to master, slave1 and
slave2
UPS BOTAPC, Data link to master, Power supply to master,
On Wed, 18 Oct 2017, Drew Plaster wrote:
MASTER SYSTEM
nut.conf
MODE=netserver
ups.conf
[TOPAPC]
driver = usbhid-ups
port = auto
pollonly
serial = "IS1309002707"
desc = "TOPAPC"
[MIDAPC]
driver = usbhid-ups
port = auto
On Wed, 18 Oct 2017, Drew Plaster wrote:
there are three APC smart ups connected via usb cables
to the master system, the master system shuts down as expected but the
slave systems never shutdown eventhough I believe that all the configs
are properly set the slaves should
The program ``wall´´ used by NUT to put notifications in front of the
users is now well past it's best-before date. It has not been
internationalized, does not support accented letters or non-latin
characters, and is ignored by popular desktop environments such as Gnome
and KDE. It's
On Thu, 3 Aug 2017, Roger Price wrote:
On Thu, 3 Aug 2017, Tomas Larsson wrote:
Hi there. I need some advise on how to configure NUT, if it is possible to
do it. My UPS, a Compaq R3000
I thought the Compaq R3000 Line was a Series of laptops designed and built by
Hewlett-Packard Corporation
On Thu, 3 Aug 2017, Tomas Larsson wrote:
Hi there. I need some advise on how to configure NUT, if it is possible
to do it. My UPS, a Compaq R3000
I thought the Compaq R3000 Line was a Series of laptops designed and built
by Hewlett-Packard Corporation, not a UPS?
has three individual
On Sun, 16 Jul 2017, Mike Schaffner wrote:
I have 2 APC UPS systems, one is connected to my ESXi host and the other
to my FreeNAS. The battery for the FreeNAS will run out before the
battery for the ESXi, so I need ESXi to shutdown first. If I wait
until BatteryLow on ESXI, it will be too
My understanding is that NUT provides a mechanism to shut down multiple
systems protected by multiple UPS's in a given order. For example to
shutdown the users before their NFS server.
1. man ups.conf says
sdorder Optional. When you have multiple UPSes on your system, you
usually need to
Here are three wishes for the future of upsmon:
1. The NOTIFYMSG texts should allow UTF-8 encoded messages.
2. The flags used in NOTIFYFLAG should be extended to include USER. This
flag says that the message is to be sent to the notify daemon, perhaps
with the command
notify-send -a NUT
On Tue, 4 Jul 2017, Charles Lepple wrote:
Since you are using Ubuntu, upsmon.conf should contain "NOTIFYCMD
/sbin/upssched". Similarly, upssched.conf should contain "CMDSCRIPT
/usr/local/bin/upssched-script".
Thanks. I have updated the Configuration Examples to include these Ubuntu
specific
On Mon, 3 Jul 2017, Andrea de Lutti wrote:
MONITOR dummy@artu 1 user pass master
SHUTDOWNCMD "/sbin/shutdown -h +0"
NOTIFYCMD /usr/local/bin/upssched-script
Hi, As far as I can see, what you are getting in syslog corresponds
correctly to what you have specified. You have specified that
I have written up a collection of NUT configurations. The chapters are
1. Introduction
2. Simple server with no local users
3. Server with multiple power supplies
4. Workstation with local users
5. Workstations share a UPS
6. Workstation with heartbeat
7. Workstation with timed shutdown
On Thu, 22 Jun 2017, Ambrogio Coletti wrote:
Hello
I am not a linux expert.
The output of uname -r on my system returns:
2.6.32-696.3.1.el6.x86_64
Hi, Linux 2.6.32 was released 3 December, 2009. That's nearly 8 years
ago. Linux has now reeched version 4.11.
hence I am trying to install
On Fri, 9 Jun 2017, Robbie van der Walle wrote:
... and also still open is the notification on the Mac.
If notify-send is available on the Mac, then perhaps this will work:
In upsmon.conf on the Mac you need
NOTIFYCMD /usr/sbin/upssched(or wherever this goes on a Mac)
NOTIFYFLAG
On Fri, 9 Jun 2017, Robbie van der Walle wrote:
# NOTIFYMSG - change messages sent by upsmon when certain events occur
#
# You can change the default messages to something else if you like.
#
# NOTIFYMSG "message"
#
# NOTIFYMSG ONLINE "UPS %s on line power"
# NOTIFYMSG ONBATT "UPS %s on
On Thu, 8 Jun 2017, Robbie van der Walle wrote:
After the first test and the NAS is restarted I had to change the
setting battery.charge.low again to 80
Does the NAS DSM reset battery.charge.low to 10 or is it internal to the
UPS? You will have to experiment by disconnecting the UPS
On Thu, 8 Jun 2017, Robbie van der Walle wrote:
The "upsrw" command contacts upsd, so it sounds like you should be able
to add a user to upsd.users on the NAS, and then run something like
this on the Mac:
upsrw -s battery.charge.low=80 -u upsmaster -s sekret UPS@synology
On Thu, 8 Jun 2017, Robbie van der Walle wrote:
I suppose I have to use -u for user? Which user? and -p for password?
Sorry, my typo, it should be
upsrw -s battery.charge.low=80 -u upsmaster -p sekret UPS@NAS
upsmaster is the "user" declared in the NAS file upsd.users in square
On Wed, 7 Jun 2017, Robbie van der Walle wrote:
Out of curiosity, when you shut down the NAS, do you run the
command "upsdrvctl shutdown" ? Do you see or hear anything to
suggest that the delayed UPS shutdown has happened?
I don’t know where to search to answer this. The
On Wed, 7 Jun 2017, Robbie van der Walle wrote:
I am running NUT on a Synology NAS with attached a USB APC UPS.
Do you have upsd and upsmon running as daemons on the Synology DSM?
Yes I have them both running on the Synology DSM:
root 7236 1 0 Jun01 ?
On Tue, 6 Jun 2017, Robbie van der Walle wrote:
I am running NUT on a Synology NAS with attached a USB APC UPS.
Do you have upsd and upsmon running as daemons on the Synology DSM?
Does the NAS shut down (and restart) correctly when wall power fails?
I am trying to connect and shutdown a Mac
On Wed, 17 May 2017, Dinow Hsieh wrote:
CC. Does a Ubuntu user with no xterm window open see the message as part of
the
==> The root and remote user(ssh-putty) get the broadcasting message all
from
On Tue, 16 May 2017, Dinow Hsieh wrote:
BB. Could you show us the output of command "upsc pcmups"?
==> Yes. Below 2 mode were the outputs of command "upsc pcmups"
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 30
battery.date: 2010/12/20
...
ups.date: 2010/12/20
On Mon, 15 May 2017, Dinow Hsieh wrote:
==> I have tried this command "upsdrvctl shutdown" as below results (However
the UPS still sustain the power)
Network UPS Tools - UPS driver controller 2.7.1
Network UPS Tools - Generic HID driver 0.38 (2.7.1)
USB communication driver 0.32
On Thu, 11 May 2017, Dinow Hsieh wrote:
==> AA. I confront an issue that can't shutdown the ups With the nut,
I can get the ups status(upsc) and shutdown the linux-ubuntu when power
failure occurs(upsmon) But don't know which configuration I ignore to
setup for ups shutdown
Hi, Could
On Tue, 4 Apr 2017, Arnaud Quette wrote:
Hi Jon, Stuart and the list
2017-04-04 1:09 GMT+02:00 Stuart Gathman :
Which NOTIFYCMD is run when there is an ALARM?
Have you specified that in your upsmon.conf?
And that is the question of the hour. How do you
On Mon, 3 Apr 2017, Spike wrote:
I'll see if I can implement it some time soon.
Hi Spike, I tested the heartbeat proposal on openSUSE 13.1 and 42.2, and
made some changes so that it would work. I wrote out some documentation
which includes the required changes, which you will find at
On Mon, 3 Apr 2017, Jon Bendtsen wrote:
On 03/04/17 17.10, Roger Price wrote:
On Mon, 3 Apr 2017, Jon Bendtsen wrote:
Power seem to be lost immediately.
But my APC Smart-UPS 1500 always reported everything OK.
battery.charge : 100
...
battery.mfr.date : 2005/08/26
Hi
On Mon, 3 Apr 2017, Jon Bendtsen wrote:
Power seem to be lost immediately.
But my APC Smart-UPS 1500 always reported everything OK.
battery.charge : 100
...
battery.mfr.date: 2005/08/26
Hi, Could you confirm that the battery is nearly 12 years old? Roger
This note describes a heartbeat technique for validating the integrity of
a NUT installation.
Introduction
A NUT configuration may run for months with little or no output to a
system administrator to assure that the combined processes are running
correctly. The technique
On Sat, 1 Apr 2017, Stuart Gathman wrote:
On 04/01/2017 03:14 PM, Dan Craciun wrote:
On my Nagios monitoring system I use check_nut_plus (that in turn
calls upsc) to monitor the status (ups.status), load (ups.load),
battery charge (battery.charge) and runtime (battery.runtime).
If these
Hi Arnaud,
On Wed, 22 Mar 2017, Arnaud Quette wrote:
The technique is very general and is to send SIGUSR1/SIGUSR2 to the upsd
daemon. SIGUSR1 and SIGUSR2 are events just like ONBATT and ONLINE.
The patch runs successfully on my opensuse 13.2 box, and solves my
problem. In
On Tue, 21 Mar 2017, Arnaud Quette wrote:
Hi Roger,
reviving this discussion, since we have a Github ticket for 2.7.5:
https://github.com/networkupstools/nut/issues/293
...
I've made some additions to clarify things on the timer, and complete the
script:
On Thu, 2 Mar 2017, Garrett Michael Hayes wrote:
I would like to set up a Linux host as a central monitoring system for
UPSs throughout our network. I’d like that system to be able to see the
various UPSs basically in one of two ways:
1) Tapping into a native network interface on the
On Sun, 5 Feb 2017, Tim Richards wrote:
Setup: Active/Passive Two Node Cluster. Two UPSes (APC Smart-UPS 1500 C)
with USB communication cables cross connected (ie UPS-webserver1
monitored by webserver2, and vice versa) to allow for stonith/fencing
OS OpenSuse Leap 42.2
NUT version
On Wed, 11 Jan 2017, Merk - Oliver wrote:
nas4free: /# more /usr/local/bin/upssched-cmd
#!/bin/sh
I would strongly recommend specifying which script interpreter is to be
used: dash, bash, csh, ksh, ... For example
#!/bin/bash
There seem to be too many case statements in this script.
On Sat, 24 Dec 2016, Spike wrote:
... from reading the docs it seems the UPS should power off, is that the
case?
Yes, The UPS should be sent a "delayed shutdown" command, upsdrvctl
shutdown, to tell it to shut down _after_ the box. The amount of the
delay can be set in ups.conf. The UPS
On Tue, 20 Dec 2016, Merk - Oliver wrote:
Last week I need to change the battery pack and then I needed to perform
a runtime calibration. I used the web interface of the AP9630 card to
start the runtime calibration. However, after 2min. of runtime
calibration the SAN shut down!
This is
On Fri, 25 Nov 2016, Jonah Naylor wrote:
I'm still getting "Connection refused on the client cgi screen as well
as in the shell it gives me UPS upsname@ipaddresshere is unavailable...
You reported that access works correctly from elsewhere on the master
subnetwork. Does access from the
On Fri, 25 Nov 2016, Jonah Naylor wrote:
upsd : ipaddressofclientgoeshere
If it were me I would write
upsd : ipaddressofclient :\
spawn (/bin/mail -r hosts.allow@localhost\
-s '%s@%h accepted access to %d from %c'\
sysadmin@somedomain) &
On Fri, 25 Nov 2016, Jonah Naylor wrote:
I don't think nut is built with TCP wrappers support, although the
package is listed as depending on libwrap...
Why would you have such a dependency if nut didn't use TCP Wrappers?
I ran this command: ldd /sbin/upsd | grep libwrap.so and it has
On Thu, 24 Nov 2016, Jonah Naylor wrote:
I installed Nut via apt-get, not from source (which I'd rather stick
with if possible just for ease of security updates etc) - so I'm not too
sure if TCP wrappers are there or available...
This could be the problem, am I still able to add the wrappers
On Thu, 24 Nov 2016, Jonah Naylor wrote:
Hi can anyone please help.
Although I have two servers in the same cabinet/room and sharing the same UPS -
they're on different networks.
I've tried everything I can find online, but whatever I do I can't get the
slave nut client to connect to the
On Sat, 15 Oct 2016, Jonah Naylor wrote:
HI again, Sorry I didn't mean to cause a security debate.
I'd like things to be secure of course, but I've got a dilema that I don't use
DHCP and instead have a block of static IPs from my ISP.
So my nut server has 68.68.452.02 for example
and my two
On Wed, 5 Oct 2016, Jeff Bowman wrote:
I’m trying to better understand OffDelay and OnDelay:
http://networkupstools.org/docs/man/usbhid-ups.html#_extra_arguments
My server requires ~3½ minutes to shut itself down. Considering this I’m
comfortable setting OffDelay to 300 (five minutes).
How
On Sat, 17 Sep 2016, Yevgeniy Kuksenko wrote:
Hello all, I have been having a problem with upsmon on Fedora 24 on boot. NUT
is configured as a netclient to a Raspbian NUT server. After boot up upsmon
repeatedly says "connect failed: No such host". It is not able to connect at
all until the
On Mon, 12 Sep 2016, Jonah Naylor wrote:
I have two linux servers both with static IPs not using NAT.
My slave can't connect to my host. Whatever I try.
I assume that these two machines are on the same LAN, so here are a few
suggestions. Can you ping from each one to the other? Can you ssh
On Sun, 11 Sep 2016, Jeff Bowman wrote:
But first I have to get it working :-)
Have you seen
https://grafenthal.de/wiki/index.php/Installation_Network_UPS_Tools_%28NUT%29_unter_Windows_Server_2012_USB
which shows a working NUT configuration under Windows Server 2012. It's in
german, but
On Fri, 9 Sep 2016, Jeff Bowman wrote:
All of this leads me to the conclusion that NUT isn't working on my system.
Here is my configuration:
What command(s) do you use to start NUT? Do usbhid-ups, upsd and upsmon
start up?
Roger
___
Nut-upsuser
On Thu, 8 Sep 2016, Jeff Bowman wrote:
That said, is there a way to manually poll the driver for UPS/power line
status? I ask because I can foresee a scenario such as this:
...
So I'd like to be able to remote in and check the status to make sure
everything is OK. If not, then I can manually
On Thu, 8 Sep 2016, Jeff Bowman wrote:
I’ve been able to get the latest Windows port installed on my Hyper-V 2012 R2
instance and start the service.
But as I’m an absolute beginner I’m not sure how to proceed further. I’ve
browsed the archives, but discussions here tend to assume at least an
On Wed, 17 Aug 2016, Brian Hilmers wrote:
Hello, I am looking for good instructions on how to configure NUT to receive
SNMP Trap signals and how to shutdown a server. My setup is:
NUT: version 2.7.1-1ubuntu1, from package
OS: Ubuntu 14.04.5 LTS
UPS: Tripp Lite SMART3000RM2U
The only thing I
On Thu, 14 Jul 2016, Dmitri Stepanov wrote:
Some of those hosts haven't NUT including upsmon (and other software
which is not included by suppliers of the hosts) for a number of
reasons. I don't need to inform not-NUT hosts about any UPS events,
etc... but only shutdown all the hosts after
On Wed, 13 Jul 2016, Dmitri Stepanov wrote:
shutdown-all-hosts.sh contains:
# Linux hosts
HOSTLIST="sim iogate br"
for host in $HOSTLIST
do
...
ssh $host halt -p
...
done
shutdown-all-hosts.sh works fine if it runned manually.
But it does not work even if I insert sleep 30 sec
On Wed, 13 Jul 2016, Dmitri Stepanov wrote:
Hi
I need to shutdown a number of hosts which has not NUT from one which has it.
I tried to do it from upssched script (after upssched's timer) like this:
case $1 in
earlyshutdown)
logger -t upssched-cmd "Early
Sorry if this is a duplicated message.
On Tue, 12 Jul 2016, Barbieri, Matteo wrote:
... a new model "Inform Sinus SS 230". Obviously I already saw on the
official NUT website that the model is not supported, but I was wondering if
there are some compatible drivers or maybe someone who are
On Wed, 22 Jun 2016, André Hänsel wrote:
Now, what I see is that when the UPS feeding server-1 goes LB, server-1 is
indeed shut down, but it seems that the UPS is never switched off.
This is a problem because when power is restored after shutdown, but before
the battery runs out (with no load,
On Tue, 14 Jun 2016, Philippe Le Mesle wrote:
I finally received a delayed SMS saying power was back.
I'm guessing that your test action is to disconnect the building power
from the UPS for a certain time and then re-connect. How long do you
wait?
Even when all the gear is permanently
On Tue, 14 Jun 2016, Philippe Le Mesle wrote:
Roger? Can your read me?
I receive a single e-mail from you via the list. Remember that the
mailing list very probably removes duplicates. If you do not receive a
copy of your own messages to the list, check your options on the list
On Tue, 14 Jun 2016, Philippe Le Mesle wrote:
"essayer la commande /usr/bin/upssched-cmd upssms manuellement sans
passer par NUT." Là je ne comprends pas (je débute en Linux). Comment
puis-je exécuter cette commande ,
PS: préférez-vous que cet échange soit en anglais ?
It is better to
On Tue, 14 Jun 2016, Philippe Le Mesle wrote:
Voici ma configuration :
**
3/ le script /usr/bin/upssched-cmd
#!/bin/bash
case $1 in
upssms)
logger -t upssched-cmd "The UPS has been gone for 30 secs. Warn by sms..."
/bin/echo "Power
On Sat, 4 Jun 2016, Charles Lepple wrote:
On Jun 3, 2016, at 6:48 AM, Roger Price <ro...@rogerprice.org> wrote:
... the timer. I don't see it in /var/lib/ups where the locate tool
finds upsd.pid, and I don't see it in /run or /var/run where I see
upsmon.pid.
... it seems that the
Hi, I'm trying to get a better understanding of what a timer is, so I
added the following line to upssched.conf
# Debug - turn on long-running timer to find out where upssched puts it
AT ONBATT * START-TIMER where-am-I 1000
I can then start this timer by pulling the power cord from the wall
On Fri, 13 May 2016, Kamran Khan wrote:
I have a TrippLite SMART2200RM2UN UPS. I have installed and configured
NUT as instructed on the website, and am able to monitor the status of
the UPS without much problem. The only problem I am seeing is that I
cannot get the machine to actually send
On Sun, 8 May 2016, Min Wang wrote:
Hi
centos 6.3 uses traditional SysV script ( not systemctl)
here is the /etc/init.d/ups ( script) assuming it similar to nutshutdown
File /etc/init.d/ups is an administrative script which is used to set up
the nut daemon - I was looking for a run-time
On Sat, 7 May 2016, Min Wang wrote:
I am using centos 6.3, and nut-2.6.5-2.el6.x86_64.
could you explain why not sending "a delayed command to the UPS to turn it off"
may cause that issue?
You need to stop the UPS from beeping. Only then can you get a clear
restart when power returns.
On Sat, 7 May 2016, Min Wang wrote:
Hi I have CP825AVR-G UPS. sometimes the UPS is shutdown due to
whatever reason.
But the annoying thing is even if the electrical power is back, that UPS
will continue to beep, and I have to manually turn on the switch button
in order for it to supply
On Wed, 28 Oct 2015, George Anchev wrote:
> However there was no any notification on desktop at
I'm guessing you use KDE and this may be a problem in the default way
KDE treats the output of the "wall" program. I don't have a KDE setup
to test with,
Hi George, I finally have a 42.1 Leap
On Wed, 2 Dec 2015, Olav Seyfarth wrote:
I'd ideally set it to "shut down when only 20% battery left" (which
should give at least five minutes power left, shutdown takes far less
than one minute). BUT:
# upsc eaton@localhost
battery.charge: 89
*battery.charge.low: 20*
...
... but mine does
On Wed, 2 Dec 2015, George Anchev wrote:
Did find a solution regarding the wall notifications?
Hello George, I'm still struggling to install openSUSE 42.1 with KDE.
When I have this (almost) working, I will have a look at the effect of
wall on KDE.
Roger
On Wed, 28 Oct 2015, George Anchev wrote:
P.S. There is a typo in your nut-delayed-ups-shutdown.service. Line:
ExecStart=/usr/bin/logger -t upsdrvctl "nut-delayed-ups-shudown.service calling
upsdrvctl to shut down UPS unit"
shudown is missing a 't'. It is in the log message but might still be
On Thu, 29 Oct 2015, George Anchev wrote:
Today I experienced something weird. As I was working, the system
started a shutdown and did shut down, then the UPS got powered off and
then back on - an expected behavior for a power fail situation. However
there was no power failure!
...
Oct 29
On Wed, 28 Oct 2015, George Anchev wrote:
${sbinPath}upsmon -c fsd
In 'upsmon --help' I read: "- fsd: shutdown all master UPSes (use with
caution)". What exactly does this line do?
My understanding is that it calls upsmon running as root to execute the
command specified by SHUTDOWNCMD in
On Wed, 28 Oct 2015, George Anchev wrote:
Beautiful! The shutdown succeeded.
Did you see a line in the journal similar to this ?
Oct 06 22:49:54 pinta nut-delayed-ups-shutdown[1854]:
nut-delayed-ups-shudown.service calling
upsdrvctl to shut down UPS unit
On Tue, 27 Oct 2015, George Anchev wrote:
Oct 26 21:02:56 i7 upsd[2227]: Startup successful
...
Oct 26 21:02:56 i7 upsmon[2229]: Startup successful
...
Oct 26 21:04:51 i7 upsmon[2230]: UPS myups@localhost on battery
Oct 26 21:05:11 i7 upsmon[2230]: UPS myups@localhost on line power
Power
On Tue, 27 Oct 2015, George Anchev wrote:
Yes, that was the power off test. However the upssched-cmd script gave
absolutely no signs of activity. Even it's logger lines don't show up in
journalctl. No any permission error messages - nothing. Only the 2
messages from upsmon - on battery and
On Mon, 26 Oct 2015, George Anchev wrote:
Hello,
I have been following the details in this article to configure my UPS:
http://rogerprice.org/NUT.html
However the system won't shutdown although file permissions look ok:
ls -alF /usr/sbin/ups*
-rwxr--r-- 1 upsd daemon 64984 Oct 15 2014
On Mon, 26 Oct 2015, George Anchev wrote:
> The best way to shut down becomes a power disconnection.
Hm. Not quite convenient for a dual boot system. Actually that
contradicts the very idea of being the power being non-interrupted.
Isn't there any way to reporgram the service to distinguish
On Wed, 14 Oct 2015, Davide Baldini wrote:
Is there any command in the list provided by "upscmd -l myups" which is
accepted by this UPS?
None of the command sin the list successfully completes, not even
beeper.toggle.
It looks as if the problem is more general than turning off the UPS. The
On Wed, 14 Oct 2015, Davide Baldini wrote:
the full output of upsc ${myups} is at https://pastebin.mozilla.org/8849188 ;
in particular:
ups.delay.shutdown: 30
ups.delay.start: 180
However, the UPS does not shut down, not immediately nor well after the
timeout of the command:
On Wed, 14 Oct 2015, Davide Baldini wrote:
upsdrvctl shutdown
...
instcmd(shutdown.return, [NULL])
instcmd: FAILED
Shutdown failed!
Driver failed to start (exit status=1)
This time /var/log/syslog doesn't register anything about the UPS after
issuing the command above. Instead, It logged
I have been looking closely at using NUT with openSUSE 13.2. Here is
a quick summary.
1. Like the alien plant in the Quatermass Experiment, systemd is
reaching into every corner of the distribution. New systemd service
units exist in /usr/lib/systemd/system:
Power devices information server,
On Tue, 8 Sep 2015, Rob Groner wrote:
I executed lsusb to verify the USB device is there, and it is. I tried
the shutdown command again with debug enabled, but it didn't seem to
reveal much more:
---
On Tue, 8 Sep 2015, Rob Groner wrote:
Roger,
rtd@linux-5048> sudo /usr/local/ups/bin/usbhid-ups -a rtdups -k -DDD
Network UPS Tools - Generic HID driver 0.39 (2.7.2.6_RTD)
USB communication driver 0.32
0.00 debug level is '3'
0.000405 upsdrv_initups...
...
0.004555
On Fri, 4 Sep 2015, Rob Groner wrote:
Well, I tried the same script method with openSUSE 13.2, and it still did not
execute.
So I tried the system method, and it worked 1 time out of 3 attempts. I
captured the last failure:
2015-09-04T11:43:38.825317-04:00 linux-5048 upsdrvctl[1887]: Can't
Hello Bob,
I had preferred the shutdown script method because it was a little more
straight-forward, and possibly more portable. This guide is meant to
help people get the UPS up and running, whatever their Linux distro. I
don't know how common the systemd implementation is across various
1 - 100 of 152 matches