I hate running copper that big so I haven't pulled that much.   I try to
contract that out if possible.   I do find that the jam probably on the
southwire wire fill calculator is helpful as it gives a likihood of wires
getting stuck.

Just curious what are you powering that needs 4/0 copper?   That's a lot of
power.    If this is this 120/208 is moving to 277/480 a possibility?  (And
if this is 480V, I'm really curious about what you're hooking up)   And do
you really need a neutral?

One note is that aluminum is a fair bit easier to pull and has similar
ampacity at the larger sizes.   Plus it's a lot cheaper.



On Fri, May 27, 2022, 2:13 PM Chuck McCown via AF <af@af.afmug.com> wrote:

> I gotta run 4 x 4/0 copper THHN and one #6 to a machine.
>
> The online raceway calculators say I can do this with 2” conduit.
>
> I will have two sweeps and at least 2 LBs.  As much as I hate to, I really
> think I should use larger conduit.  I really hate it when I have trouble
> pulling larger cables in too small of a conduit.
>
> Any raceway fill experts on here?
> --