Edd,
to add to what Gary said...

any measurement of the remaining capacity of the battery bank is tricky, 
because it depends on how accurate your in- and out- meters are, what the 
actual (current) total battery bank capacity is (it changes over time, never 
up) and at what SoC (state of charge) you started the measurements.

I assume that your 450 Ah is a nominal capacity, but you don’t know how much of 
that is left.

The 6 A you mention, is it 6 A over several hours (let’s say 3), i.e. 6 A times 
“several (3)” hours = ~18 Ah or just 6 Ah? However, on a 450 Ah battery bank, 
even 20 Ah is just under 5%, so if you started with 100% SoC you should be at 
95% (if it was 6 Ah, the SoC should be 98.5%).

As Gary mentioned, re-synchronisation is a must.

The voltage you are seeing depends heavily on what is using the battery at the 
given time (as you check it). I can almost guarantee that if you were watching 
the monitor at the time of starting the motor, the voltage meter would show 
some number much lower than 12 V (even if the SoC was almost 100%).

I am not sure if it helped you much, though

Marek
1994 C270 Legato
Ottawa, ON

From: Gary Russell via CnC-List
Sent: Friday, July 5, 2019 13:08
To: C&C List
Cc: Gary Russell
Subject: Re: Stus-List Voltage / Amp Hours

Hi Edd,
    The battery voltage is only an indication of the state of charge of a 
lead-acid battery when the battery has been without load (or charge) for 
several hours.  Otherwise, the voltage is pretty much meaningless.  Many 
devices measure the state of charge by noting the difference between the number 
of amp-hours drawn and the number of amp-hours charged into the battery.  It is 
a more accurate indication of the state of charge but has it's limitations as 
well.  Any inaccuracy in measuring the current into or out of the battery will 
accumulate over time requiring the device to be "re-synchronized".

Gary
S/V Kaylarah
'90 C&C 37+
East Greenwich, RI, USA
~~~~~~~_/)~~~~~~



On Fri, Jul 5, 2019 at 12:23 PM Edd Schillay via CnC-List 
<cnc-list@cnc-list.com> wrote:
Listers,

Last year, I installed a Blue Sea battery monitor and I’m a little perplexed 
about the readings I am seeing.

Last night, before an amazing fireworks display at Hempstead Harbor (thanks to 
fellow Lister Neal Gallagher for the guest mooring), I looked at the display. 
Out of the 450 amp hours in the House bank, we had used around 6 amps between 
using the electric head, cell phone charging, etc. for several hours — with the 
display showing 99% capacity.  But the voltage was showing 12.38, which I 
understand to mean closer to 75%.

Someone on a YouTube video said that the Voltage reading is not really the one 
to go by, as the voltage will increase when you start switching things off.

Is that all true? Is what I’m seeing normal? Can one of you Amperage Aces or 
Voltage Vixens explain this to me? (Please keep it simple - way too much 
Romulan Ale and Klingon Blood Wine flowing last night.)

- Confused on City Island

All the best,

Edd

-------------------------------—-
Edd M. Schillay
Captain of the “Starship Enterprise”
C&C 37+ | Sail No: NCC-1701-B
Venice Yacht Club | Venice, FL
www.StarshipSailing.com<http://www.StarshipSailing.com>
-----------------------------------
914.774.9767   | Mobile
-----------------------------------


Sent via iPhone X
iPhone. iTypos. iApologize

_______________________________________________

Thanks everyone for supporting this list with your contributions.  Each and 
every one is greatly appreciated.  If you want to support the list - use PayPal 
to send contribution --   https://www.paypal.me/stumurray

_______________________________________________

Thanks everyone for supporting this list with your contributions.  Each and 
every one is greatly appreciated.  If you want to support the list - use PayPal 
to send contribution --   https://www.paypal.me/stumurray

Reply via email to