Gabi,

The topic of an air-discharge spark gap is a little bit more complicated. 

1) The breakdown voltage in air for a homogeneous field is given by the 
Paschen-equations, providing
   that the breakdown is a gas discharge process, not an explosive surface 
process (happens at
   high pressure, distances less than about 5um and if the gap is highly 
overvoltaged)
   Even for a homogenous field, the breakdown fieldstrength is a strong 
function of voltage.

2) A spark gap will need some time to turn on. There are two processes:
   Statistical time lag: this is the time it takes before the first electron 
appears that can start the avalange
   process. Time lags may be ps to seconds, depending on the field strength and 
many other factors.

3) Formative time: The time the spark needs from its start until its impedance 
is low. The time may be ns to us.
   

4) Clamping voltage. Typically spark gaps clamp at about 25 V for currents of 
less than 100 A in time frames
   of 10ns to a few hundred ns. I do not know the physical reason for the 25 V. 
If anyone knows, please let me know.

5) In my experience a PCB using the footprint of an 0805 part (not loaded) will 
break down at about 2000-3000V.

6) It is not easy to get breakdown voltages consistantly below 500 V with spark 
gap structures in air. The needed
   distances are so small that surface properties, contamination etc. start to 
dominate.

Regards

David Pommerenke
Associate Professor             
Electromagnetic Compatibility Laboratory
ECE Department
University of Missouri-Rolla
1870 Miner Circle
Rolla, MO 65409-0040

pommere...@ece.umr.edu
Phone: (573) 341-4531
Home:  (573) 341 5835
FAX:   (573) 341-4532






-----Original Message-----
From: Gabi Hoffknecht [mailto:gab...@simex.ca]
Sent: Wednesday, February 20, 2002 10:33 AM
To: emc-p...@majordomo.ieee.org
Subject: Using PCB traces as transient voltage suppressor



Hi all,

I have seen PCB designs with two triangular shaped copper pads pointed
towards each other at very close proximity, meant as an air gap discharge
path for transients. Does anyone have information about such designs,
whether they work and how well ? At a breakdown voltage for air of 1
Megavolt per meter, they should theoretically work: 10mil distance would
have a breakdown voltage of only 254V. Such a PCB design basically comes for
free, so I was thinking of adding it on top of my already existing series
impedance - TVS network. 
Thanks in advance for your comments.

Best regards,
Gabi Hoffknecht

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              emc-p...@hypercom.com
     Dave Heald:               davehe...@mediaone.net

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              emc-p...@hypercom.com
     Dave Heald:               davehe...@mediaone.net

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

Reply via email to