Rich,

Thank you and everyone for the great input and advice. It has been very
helpful.

The Other Brian
 


From: Richard Nute [mailto:rn...@san.rr.com] On Behalf Of ri...@ieee.org
Sent: Thursday, November 09, 2006 3:42 PM
To: Kunde, Brian
Cc: emc-p...@ieee.org
Subject: RE: Worst Case AC Power Conditions





Hi Brian:


This additional information is crucial to understanding the issue and
providing suggestions for resolving the issue.

As I interpret your explanation, your equipment triggers on the input
voltage waveform.  If that waveform is distorted, the triggering will be
in error.

The triggering switches on the ac at various points on the waveform; the
circuits then control the furnace temperature.

I believe it is impossible to anticipate all the various supply voltage
distortions.  Non-linear loads create harmonic distortion.  Rotating
machines create transient overvoltage distortion.  Large loads turning
on or off create short-term low or high voltages.

I suggest you consider internally generating a sinusoidal voltage that
tracks the input voltage and use that for triggering the actual line
voltage.  Since heating is proportional to the rms value of the voltage,
you might want to continuously measure the rms of the distorted line
voltage, and use that value together with the regenerated sine wave to
determine the trigger point.  


Best regards,
Rich





> -----Original Message-----
> From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Kunde,

> Brian
> Sent: Wednesday, November 08, 2006 8:43 AM
> To: David Cuthbert; emc-p...@ieee.org
> Subject: RE: Worst Case AC Power Conditions
>
>
> Dave,
>
> Thanks for the reply.
>
> I should have explained further. Our equipment is designed to work 
> only in the 230V nominal voltage range at both 50 and 60 hz. Our 
> equipment has furnaces that we must regulate the temperature within a 
> very tight spec. To do this we must fire control relays (SSRs) either 
> at the zero crossing or use phase control method. These methods 
> require us to monitor the AC line so to fire the SSR properly. As you 
> can image, such methods would be susceptible to AC line noise, 
> harmonics, dips, etc.. So we design immunity to such noise into our 
> products, but sometimes it is not enough.
>
> The other Brian
>
>

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas           emcp...@ptcnh.net
     Mike Cantwell           mcantw...@ieee.org

For policy questions, send mail to:

     Jim Bacher:             j.bac...@ieee.org
     David Heald:            emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email 
______________________________________________________________________

Reply via email to