Brian,

416 volts is the phase to phase voltage of a 240/416 v three phase
distribution circuit. If you had a circuit with a heavy single phase load from
phase A to neutral and a light single phase load from phase B to neutral and
then opened the neutral, they would be in series with the phase voltage
highest across the lightest load. Depending on what loads and how they are
connected, the voltages resulting would be hard to predict but somewhere from
zero to approaching the phase to phase voltage. This test would cover almost
all conditions for the small single phase appliances in international markets
we were discussing.

Bob Johnson
ITE Safety <http://www.itesafety.com> 

Brian O'Connell wrote: 

Sir



Interesting requiremensts. What is the basis of 416V ?



Thanks,

yet another Brian







From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf Of Robert

Johnson

Sent: Wednesday, November 08, 2006 2:01 PM

To: emc-p...@ieee.org

Subject: Re: Worst Case AC Power Conditions



It's also useful to know what your product does under non operating

conditions. A common fault is open neutral and can happen anywhere from the

power cord to across town. This leaves your equipment in series with other

unknown loads from phase to phase.

This is not something you should expect to use as an operating point.

Planning operation under such conditions would appropriately require a UPS.

However knowing what your equipment does is good safety practice. It may

trip overcurrent protection or just sit and malfunction, but you don't want

it to catch fire. Running it at a few operating points between 0 and 416 V

gives you an idea of how it will fail. This is not a failure mode tested by

the product standards.



Bob Johnson

ITE Safety











  


______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email 
______________________________________________________________________

- ---------------------------------------------------------------- This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas emcp...@ptcnh.net Mike Cantwell mcantw...@ieee.org 


For policy questions, send mail to: 


Jim Bacher: j.bac...@ieee.org David Heald: emc-p...@daveheald.com 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc 


Reply via email to