gene heskett wrote:
> Those were SWAG's, pulled out of you know where, Jon.  The x taps on that 
> autoformer we've been putzing with say 370-390 volts at 22 amps, but do not 
> say total, or per phase, so I chose the worst case scenario or 22 
> amps/phase, which in power in kw would be 390*66=25,740 watts, aka 26kw.  
> Probably, likely wrong.  Feel totally free to correct that assumption.  KVA 
> to kilowatts is one conversion that has NEVER made sense to me.
>   
Well, you can't, unless you know the power factor.  And, as this thing 
is a rectifier,
the power factor is not linear, either.  But, a well-behaved 3-phase 
rectifier shouldn't
have a power factor less than about 80%, so multiplying KW by 1.25 
should give
a reasonable guess at KVA.

It is insanity to try to run a real 25 KVA machine from a 200 A 240 V 
single-phase service.
Although that service is capable of 48 KVA, the imaginary currents of 
the machine
PLUS the horrible imaginary current of a rotary phase converter will 
play havoc
with the service.  If you have your own, private pole transformer (like 
I am so lucky
to have) that helps, but it is still pushing what you are supposed to 
do.  If you are
sharing the transformer with neighbors, it could really cause problems.

Jon

------------------------------------------------------------------------------
Live Security Virtual Conference
Exclusive live event will cover all the ways today's security and 
threat landscape has changed and how IT managers can respond. Discussions 
will include endpoint security, mobile security and the latest in malware 
threats. http://www.accelacomm.com/jaw/sfrnl04242012/114/50122263/
_______________________________________________
Emc-users mailing list
[email protected]
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to