I just got back from being out of the office for a week+ and just read a few ofthese. I hope this is not redundant.

6AWG is the size that meets several tests for exposed installations.By that I mean that it is not protected.  If you arerunning the array EGC exposed, you would use at least 6AWG depending upon the size of the overcurrent protection device towards the charge controller/array disconnect. 250.120(C) and T250.122.

We have run into the conductor covering rating problemtoo. #4 can be color coded so you can use black conductor. A reasonable inspector should allow this for 6 since a lot of the non black coverings are not holding up as well to sunlight as black.  I think NEC2017 takes this into consideration and allows you to color code because of the superior performance of black coverings.

Chris


On 4/20/2018 9:00 AM, Dana wrote:
That makes two of us that would like to understand, why #6? I think it dates to 
early grounding with grid tie systems.
I remember back to 20+ years ago when the code required that the EGC was the 
size of the largest conductor which with 24 volt inverters was OOOO.

----------------------------------------------------------------------------
Dana Orzel                              Great Solar Works, Inc.
C - 208.721.7003                       d...@solarwork.com
Idaho Contractor - # 028765         Idaho PV # 028374
NABCEP # 051112-136                       www.solarwork.biz
"Responsible Technologies for Responsible People since 1988"
 Please consider the environment before printing this email.


-----Original Message-----
From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of Dave 
Angelini Offgrid Solar
Sent: Thursday, April 19, 2018 3:57 PM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Looking for insulated #6 bare standoff

  Dana, I understand the need to use #6 in exposed places on the earth. I have 
had inspectors require the same wire size that is used to the battery. I have 
had them require the same size as the array wiring. I have never seen them do 
what they are doing to you so thanks for the info....  Be well!  --Dave
The bare #8 is an EGC for #10 USE PV wire on the tracker to the array
mounted combiner box.

----------------------------------------------------------------------------
Dana Orzel                              Great Solar Works, Inc.
C - 208.721.7003                       d...@solarwork.com
Idaho Contractor - # 028765         Idaho PV # 028374
NABCEP # 051112-136                       www.solarwork.biz
"Responsible Technologies for Responsible People since 1988"
 Please consider the environment before printing this email.


-----Original Message-----
From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On
Behalf Of Hilton Dier
Sent: Thursday, April 19, 2018 3:39 PM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Looking for insulated #6 bare standoff

Would #8 meet code? I thought that exposed ground wire had to be #6
minimum.

Hilton Dier III
Renewable Energy Design
Missisquoi River Hydro LLC
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist
.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist
.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridso...@sti.net
text 209 813 0060

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


--

         Christopher Warfel, PE
       ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
               (401)466-8978

EEI logo <http://entech-engineering.com>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to