We're not too worried about reducing the surge at this point; the
existing soft start controller is currently programmed for a fast start,
because their electrician was worried about motor damage if the
controller was set to limit current. It is currently surging to 700% of
run current, so we should be able to easily bring that down to 200% with
some programming. We just need to convince them that the motor will not
be damaged. It will only see one start/ day.
Grid is 3 miles away, but they may be required to suspend their
operations for months or years, while all the necessary studies,
easements, and approvals are obtained. Also, in this case, there is a
strong incentive from their management to try off grid, as they have
other operations that they want to wean off of gen-sets that will never
have grid.
I agree with both of you, and suggested the grid option first. With the
right technology, we could use PV and battery storage off grid, then
once grid power is available, go to a GT system with the battery storage
used to reduce demand charges.
I still haven't heard from anyone here that has actually done large
scale (over 100kW) inverters off grid. I don't want to spec the next
Studebaker of solar.
Thanks everyone for your help,
Ray
On 4/26/18 8:17 AM, Dave Angelini Offgrid Solar wrote:
Agree with Daryl here at the end. You have to solve the motor surge with
variable frequency drive and go 3 phase. If there is a reasonable cost to
use the grid I would not even bother with quoting an off the grid
solution. It is what the grid is best at and batteries are the wrong way
for this.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridso...@sti.net
text 209 813 0060
you have a problem that is much bigger than I work on. But on a large
motor heavy starting loads problem, we used an extra capacitor on the DC
bus of the frequency drive. the drive on its own greatly reduced the
start
surge, if the load can be started slowly. If the motor must ramp up
quickly the voltage would drop and the capacitor reduced the bump on the
line. This was a few years ago but we put a 200 HP drive on a 100 HP
motor
and added the extra capacitor. Another trick on a different job was to
run
a 3 phase motor with a flywheel and start this motor slowly when the motor
that had to start rapidly the running motor acts as a frequency
stabilizer and dumps it energy into the rapidly starting motor. again
this
was maybe 15 years ago. these kluge solutions were applied when the
inverter could in no way handle the surge and would kick the inverter off
the line. Another solution used by Catipiller they had a unit that could
give 3000 amps 480 v0lts for I think 30 seconds running a motor as a
flywheel for UPS giving the generator set time to start. Check with
Catapiller. again another project we clutched the running motor to the
load to start the load fast and not have to face starting current. One
last comment we had a 5000 HP motor to start a very heavy load, this motor
had a hydraulic coupling that filled with oil to control the motor load.
But I think a speed drive is more practical. And there are regen drives
also.
There are some other kluges that can be applied, good luck, sorry if this
is of no value.
On Wed, Apr 25, 2018 at 2:36 PM, Ray <r...@solarray.com> wrote:
Greetings Fellow Wrenches;
We are consulting on a power system for a large off grid facility that
is
currently operating on a 1500 kW gen set. The loads are enormous for
normal off grid: in the neighborhood of 600 amps continuous at 480 v 3
phase. Surges are close to 2000 amps, but we are working on control
programming to bring that number down substantially. That is due
primarily
to a 250 Hp motor start. (that's not a typo!). EPA and local regulations
are dictating that the current generator be retired in the near future.
Grid power is a possibility, but we need to offer a viable off grid
option
as well.
My question to the group: does anyone have real off grid experience with
large format battery based inverters? I've heard of some micro-grid
systems running in Haiti on Princeton Power inverters, and Dynapower has
a
250 kW inverter that has a "grid forming" mode. As we all know, it is
easier to make claims in spec sheets than to deliver hard motor starting
power in a remote location. We need proven products, with a track
record
of reliability.
We are considering SMA type systems that use AC coupled PV to offset
fuel
consumption of a generator, but those seem dependent on the generator to
maintain the stability of the micro grid during hard starting loads.
Ideally we would want to reduce the generator run time to under 200 hrs/
yr
and reduce its size to 500 kW. We have excellent solar resources year
round, and the possibility of limiting operations during cloudy weather
to
meet these goals.
Thanks,
Ray Walters
Remote Solar
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.or
g/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org