The possibility of dark start and 30% higher cost are 2 reasons we have preferred Simpliphi lately. Simpliphi just requires resetting its breaker on top of the battery.  Also the Simpliphi allows more layouts, so it doesn't stick out into the room.  We have one customer that has a system with each, and so far they prefer the Simpliphi over the Blue Ion.  Both are high quality solutions, but being able to afford more kWh of storage solves many issues.

Ray Walters
Remote Solar
303 505-8760

On 3/22/20 3:14 PM, Sindelar Solar wrote:

Specifically with Blue Ion, the installation manual recommends 48V as LBCO, but also recommends setting it a bit higher:

"Recommended Low Voltage Disconnect Setting: 48 VDC (~2-10% State of Charge) BMU will power down the Blue Ion 2.0 cabinet at 44 VDC (<1% State of Charge) Based on system discharge patterns, SoC and voltage correlations will vary. We recommend you err on the side of caution with a higher LVD setting and adjust as necessary. To prevent a dark start event, we recommend leaving a little reserve “fuel in the tank”."

I have used 48VDC with success, and had one system indeed shut down at 44V, leaving 1% left to reboot.

Allan

On 3/22/2020 12:44 PM, Ray wrote:

Blue Ion, and Simpliphi that I know of.

Ray Walters
Remote Solar
303 505-8760
On 3/21/20 2:48 PM, Dave Angelini Offgrid Solar wrote:

I see what you mean Ray. Sorry I misread your mail. There are not too many batteries out there that need LBCO above 48V. Which ones are you talking about please?

*Dave Angelini Offgrid Solar*

*"we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net <mailto:offgridso...@sti.net> text 209 813 0060*

On Sat, 21 Mar 2020 11:18:21 -0700, Dave Angelini Offgrid Solar <offgridso...@sti.net> wrote:

Hi Ray,

Which XW? There are 3 now. The old graybox XW defaults at 44V LBCO and the range is 40 to 48V. There also was firmware back in its day that got older units updated. Schneider still has the firmware under discontinued products.

XW+ is default 44V and adjustable 36 to 44 vdc.

XW pro is running downstairs and I will take a look. It would be my guess that it is the same as XW+. I think one needs to be sure they are in Advanced settings to tweak LBCO also.

I am not plugging Schneider and have done work for both Outback and Schneider as well as my clients. Hope this helps.

*Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net <mailto:offgridso...@sti.net> text 209 813 0060*

On Sat, 21 Mar 2020 11:46:21 -0400, Ray <r...@solarray.com> wrote:

    We've been having good luck with SImpliphi, the pricing has
    recently gotten much more competitive.  As it's names states,
    its simple.  Each 3.8 kWh unit has an 80 amp breaker built into
    the top, weigh about 75 lbs, and are a bit smaller than an L16
    but with carry handles. We use an insulated 2 pole combiner
    block to run all the parallel conductors to the main 2/0
    cable.  No monitoring, but they do have an handy setup guide
    with recommended settings, specific for each manufacturer
    (including Outback).

    Note to all:  Schneider XW can still not set its LVD above 48,
    which basically makes it incompatible with most Li+ batteries. 
    Their tech support has been abysmal as well.   We're looking
    forward to them as one of the larger companies in the business,
    to put additional resources into their engineering, and come
    out with at least a firmware update to correct this problem.

    Ray Walters
    Remote Solar
    303 505-8760

    On 3/20/20 3:59 PM, David Katz wrote:

        Hello Wrenches,
        I am working with some people that want to use a 20 kw-hour
        to 30 kw-hour 48 volt lithium-ion battery with an Outback
        Radian and Outback FM charge controllers.
        They are considering using Discover, Blue-Ion, Battle Born
        or SimpliPhi batteries.
        Does any one have any recommendations of which battery
        functions best with the Outback system.
        Thanks,
        David Katz

        _______________________________________________
        List sponsored by Redwood Alliance

        List Address:RE-wrenches@lists.re-wrenches.org

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        
List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm

        Check out or update participant bios:
        www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

--

*Allan Sindelar*
al...@sindelarsolar.com <mailto:al...@sindelarsolar.com>
NABCEP Certified PV Installation Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to