Ray, 
Have you heard bought about using the Aux relay to control the AC output at 
what ever voltage you want?

Jay




> On Mar 22, 2020, at 3:13 PM, Ray <r...@solarray.com> wrote:
> 
> 
> That's the whole point: we need the LBCO to be higher than 48v to catch the 
> beginning of that steep drop off, so that there is still enough reserve left 
> to keep the monitoring and solar charge controllers in operation, and avoid 
> the dreaded dark start.  With Simpliphi, we don't have the dark start, but it 
> still requires manual reset.   This isn't theoretical, we have been having 
> serious trouble with a system because of Schneider's inability to set the LVD 
> above 48 v.  Also setting the voltage higher (lower DOD) extends the cycle 
> life of these batteries.  Otherwise, I love the stable 51 volts of Li+, even 
> under load.  
> 
> Ray Walters
> Remote Solar
> 303 505-8760
>> On 3/22/20 4:15 PM, Jerry Shafer wrote:
>> Wrenches
>> Don't let the LBCU scare you as this battery has such a flat SOC line that 
>> when it falls off there is not much left in the tank. In addition set the 
>> flex net to low SOC at 15% and critical to 10%.
>> 
>> On Sun, Mar 22, 2020, 12:15 PM Sindelar Solar <al...@sindelarsolar.com> 
>> wrote:
>>> Specifically with Blue Ion, the installation manual recommends 48V as LBCO, 
>>> but also recommends setting it a bit higher:
>>> 
>>> "Recommended Low Voltage Disconnect Setting: 48 VDC (~2-10% State of Charge)
>>> BMU will power down the Blue Ion 2.0 cabinet at 44 VDC (<1% State of Charge)
>>> Based on system discharge patterns, SoC and voltage correlations will vary.
>>> We recommend you err on the side of caution with a higher LVD setting and 
>>> adjust as necessary.
>>> To prevent a dark start event, we recommend leaving a little reserve “fuel 
>>> in the tank”."
>>> 
>>> I have used 48VDC with success, and had one system indeed shut down at 44V, 
>>> leaving 1% left to reboot.
>>> 
>>> Allan
>>> 
>>>> On 3/22/2020 12:44 PM, Ray wrote:
>>>> Blue Ion, and Simpliphi that I know of.
>>>> 
>>>> Ray Walters
>>>> Remote Solar
>>>> 303 505-8760
>>>> On 3/21/20 2:48 PM, Dave Angelini Offgrid Solar wrote:
>>>>> I see what you mean Ray. Sorry I misread your mail. There are not too 
>>>>> many batteries out there that need LBCO above 48V. Which ones are you 
>>>>> talking about please?
>>>>> 
>>>>> Dave Angelini Offgrid Solar
>>>>> 
>>>>> "we go where powerlines don't"
>>>>> http://members.sti.net/offgridsolar/
>>>>> e-mail  offgridso...@sti.net
>>>>> text 209 813 0060
>>>>>> On Sat, 21 Mar 2020 11:18:21 -0700, Dave Angelini Offgrid Solar 
>>>>>> <offgridso...@sti.net> wrote:
>>>>>> 
>>>>>> Hi Ray,
>>>>>> 
>>>>>> Which XW? There are 3 now. The old graybox XW defaults at 44V LBCO and 
>>>>>> the range is 40 to 48V. There also was firmware back in its day that got 
>>>>>> older units updated. Schneider still has the firmware under discontinued 
>>>>>> products.
>>>>>> 
>>>>>> XW+ is default 44V and adjustable 36 to 44 vdc.
>>>>>> 
>>>>>> XW pro is running downstairs and I will take a look. It would be my 
>>>>>> guess that it is the same as XW+. I think one needs to be sure they are 
>>>>>> in Advanced settings to tweak LBCO also.
>>>>>> 
>>>>>> I am not plugging Schneider and have done work for both Outback and 
>>>>>> Schneider as well as my clients. Hope this helps. 
>>>>>> 
>>>>>> Dave Angelini Offgrid Solar
>>>>>> "we go where powerlines don't"
>>>>>> http://members.sti.net/offgridsolar/
>>>>>> e-mail  offgridso...@sti.net
>>>>>> text 209 813 0060
>>>>>> On Sat, 21 Mar 2020 11:46:21 -0400, Ray <r...@solarray.com> wrote:
>>>>>> 
>>>>>> We've been having good luck with SImpliphi, the pricing has recently 
>>>>>> gotten much more competitive.  As it's names states, its simple.  Each 
>>>>>> 3.8 kWh unit has an 80 amp breaker built into the top, weigh about 75 
>>>>>> lbs, and are a bit smaller than an L16 but with carry handles.  We use 
>>>>>> an insulated 2 pole combiner block to run all the parallel conductors to 
>>>>>> the main 2/0 cable.  No monitoring, but they do have an handy setup 
>>>>>> guide with recommended settings, specific for each manufacturer 
>>>>>> (including Outback). 
>>>>>> 
>>>>>> Note to all:  Schneider XW can still not set its LVD above 48, which 
>>>>>> basically makes it incompatible with most Li+ batteries.  Their tech 
>>>>>> support has been abysmal as well.   We're looking forward to them as one 
>>>>>> of the larger companies in the business, to put additional resources 
>>>>>> into their engineering, and come out with at least a firmware update to 
>>>>>> correct this problem.  
>>>>>> 
>>>>>> Ray Walters
>>>>>> Remote Solar
>>>>>> 303 505-8760
>>>>>> On 3/20/20 3:59 PM, David Katz wrote:
>>>>>> Hello Wrenches,
>>>>>> I am working with some people that want to use a 20 kw-hour to 30 
>>>>>> kw-hour 48 volt lithium-ion battery with an Outback Radian and Outback 
>>>>>> FM charge controllers.
>>>>>> They are considering using Discover, Blue-Ion, Battle Born or SimpliPhi 
>>>>>> batteries.
>>>>>> Does any one have any recommendations of which battery functions best 
>>>>>> with the Outback system.
>>>>>> Thanks,
>>>>>> David Katz
>>>>>> 
>>>>>> 
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>> 
>>>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>>> 
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> List-Archive: 
>>>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>>> 
>>>>>> List rules & etiquette:
>>>>>> www.re-wrenches.org/etiquette.htm
>>>>>> 
>>>>>> Check out or update participant bios:
>>>>>> www.members.re-wrenches.org
>>>>>> 
>>>>> 
>>>>> 
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> 
>>>>> List-Archive: 
>>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>> 
>>>>> List rules & etiquette:
>>>>> www.re-wrenches.org/etiquette.htm
>>>>> 
>>>>> Check out or update participant bios:
>>>>> www.members.re-wrenches.org
>>>>> 
>>>> 
>>>> 
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> List-Archive: 
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>> 
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>> 
>>> -- 
>>> Allan Sindelar
>>> al...@sindelarsolar.com
>>> NABCEP Certified PV Installation Professional
>>> New Mexico EE98J Journeyman Electrician
>>> Founder (Retired), Positive Energy, Inc.
>>> 505 780-2738 cell
>>> 
>>>  
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to