Wrenches It sounds like a out of the box board failure, even if the slave is in standby it is connected to the hub and you see it, if you swapped the cable, port location, its time to talk to OB tech and get a board sent out, Jerry
On Thu, Jun 25, 2020, 12:37 PM William Miller <will...@millersolar.com> wrote: > Christopher; > > > > Just spit-balling here: is the secondary inverter asleep (hate the > master/slave terminology…)? Try changing power save settings to make sure > the secondary is awake and see if that changes the situation. Seems > unlikely this will solve the problem, but it may provide some kind of clue. > > > > Also, did you try swapping primary and secondary? Run with secondary > alone as primary? > > > > William Miller > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On > Behalf Of *Chris Schaefer > *Sent:* Thursday, June 25, 2020 10:35 AM > *To:* RE-wrenches > *Subject:* [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s > > > > G'Day All, > > > > So I started up a system recently with two Radian 8048A's. The master is > connected to port 1 and the slave connected to port 2 with the FlexNet at > port 3. There are no OB charge controllers in the system. When the hub is > polling (led's scrolling) nothing shows up for the slave at port 2. It's > like the slave inverter doesn't exist. So I moved the slave and flexnet > down to port 3 and 4. No change in the polling. I swapped out comm (factory > green) cables. Again no change. Looking at the control board of the slave > there is only one green led on which is located at the upper right-hand > side. Otherwise no led's are on. I have 57v at the buss bar terminals of > the inverter. Of course since there is no polling at the hub there is no > way to view port 2 to view the slave at the Mate. > > > > Now the only thing that I didn't do was to try and use the manual on/off > switch-jumper to start the slave. But in the past regardless of the > inverter being on or off it would still show up on the hub. This is a new > one and I'm looking for some direction here. > > > > Thanks, > > Christopher- > > Chris Schaefer’s > <http://www.solarandwindfx.com> > > *Tel/Fax 585-229-2083 or Cell 585-748-1870 * > *5115 South Hill Road ~ Canandaigua New York 14424www.solarandwindfx.com > <http://www.solarandwindfx.com> ~ E-mail: **ch...@solarandwindfx.com > <ch...@solarandwindfx.com>* > > Thomas Jefferson, the author of our great Constitution, once said, > "democracy" will cease to exist when you take away from those who are > willing to work and give to those who would not." > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > >
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org