Kirk:


If my memory is correct:  What you describe below are port assignments if
one is stacking FXR inverters for 120/240 with a Hub 10.3.  It also
requires changing DIP jumpers from factory defaults.  This is not accurate
for stacking Radians.  With Radians I think secondary inverters can use any
port but I have always used 2 through X for secondaries.



William





*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Kirk Herander
*Sent:* Thursday, June 25, 2020 2:07 PM
*To:* re-wrenches@lists.re-wrenches.org
*Subject:* Re: [RE-wrenches] Slave Radian not showing up on Hub10 or @
Mate3s



The master-slave config types and port assignments have always been
confusing. The quick start guide lists a config where the master is port 1
and the slave is port 7. I believe port 7 is called the sub-master in this
config. With only 2 inverters it functions as the slave to the master in
port 1. This config has always worked for me.



Hope this is accurate info.

On 6/25/2020 1:35:55 PM, Chris Schaefer <ch...@solarandwindfx.com> wrote:

G'Day All,



So I started up a system recently with two Radian 8048A's. The master is
connected to port 1 and the slave connected to port 2 with the FlexNet at
port 3. There are no OB charge controllers in the system. When the hub is
polling (led's scrolling) nothing shows up for the slave at port 2. It's
like the slave inverter doesn't exist. So I moved the slave and flexnet
down to port 3 and 4. No change in the polling. I swapped out comm (factory
green) cables. Again no change. Looking at the control board of the slave
there is only one green led on which is located at the upper right-hand
side. Otherwise no led's are on. I have 57v at the buss bar terminals of
the inverter. Of course since there is no polling at the hub there is no
way to view port 2 to view the slave at the Mate.



Now the only thing that I didn't do was to try and use the manual on/off
switch-jumper to start the slave. But in the past regardless of the
inverter being on or off it would still show up on the hub. This is  a new
one and I'm looking for some direction here.



Thanks,

Christopher-

Chris Schaefer’s
*Error! Filename not specified.* <http://www.solarandwindfx.com>

*Tel/Fax 585-229-2083 or Cell 585-748-1870 *
*5115 South Hill Road ~ Canandaigua New York 14424www.solarandwindfx.com
<http://www.solarandwindfx.com> ~ E-mail: **ch...@solarandwindfx.com
<ch...@solarandwindfx.com>*

*Error! Filename not specified.*

Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."

_______________________________________________ List sponsored by Redwood
Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver
email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or
update participant bios: www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to