This technology has been in use for a dozen years in European equipment and has 
been used in many inverters that we install. It creates a gas-tight connection 
and is fully vetted through many manufacturers. I don’t think we need to be 
concerned about its ability to create a reliable connection when properly used 
– just as screw terminals and compression connections require proper 
preparation and installation, so do these.

The metallurgy used in the springs is not that of a simple malleable material, 
but is specifically formulated to retain its tension throughout its lifetime. 
Of course heat will affect any connection, however it is not more of a concern 
with this type of connector than any other one in my opinion and experience. 
And they are not really like those terminals in the back of a duplex outlet, 
except in functionality…

We can’t fight progress and technology continues to move ahead. These terminals 
have been reliable and less expensive, as well as less prone to user error that 
most other options available currently. IEC testing and millions of deployed 
parts show a history of reliability.

 

-Glenn

 

From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of 
William Miller
Sent: Friday, May 07, 2021 8:48 PM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Wago Connectors (221 series)

 

Friends:

 

Call me old fashioned, but I cannot get any confidence on the Wago connector.  
It seems somewhat akin to the back-wire mechanism on a 15A receptacle.  This 
connection relies on a spring that is subject to reduction in force when it 
gets hot.  We have seen many of the back-wire receptacles heat up and get more 
resistive as heat increases, creating more heat, etc.  

 

We have learned when connecting battery cables to inverters or batteries that 
the best connection does not have any washer or any intermediate object between 
one conductor and the other.  

 

I know wire nuts are not ideal (pun intended) but I like my conductors to be in 
direct contact, or under a screw terminal where I can determine and reconfirm 
the pressure placed on the conductor.  It is also necessary to have control 
over the pressure applied to the connection, which is why there are listed 
torque specs.

 

Yesterday I was measuring the line voltage on an SB Series 22 inverter.  This 
unit uses the Wago terminal.  There was no way I could get a meter probe into 
the Wago to measure line voltage.  I had to take the cover off the electronics 
sections and measure voltage at the circuit board.  I much prefer a screw 
terminal I can adjust the torque and get a meter probe onto it.

 

William Miller

 

Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com <http://www.millersolar.com/> 

CA Lic. 773985

 

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org 
<mailto:re-wrenches-boun...@lists.re-wrenches.org> ] On Behalf Of Dan Fink
Sent: Friday, May 7, 2021 4:01 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Wago Connectors (221 series)

 

Jason; From the Wago 221 data sheet, it's listed to UL 486C, 600V, 30A, Use 
Group C (industrial) . I have a copy of UL486C, and voltage is just specified 
for dielectric testing. That standard specifies tests with AC, because it is 
easier (and cheaper) to generate and ramp up compared to DC, and DC test 
platforms are relatively rare. 

 

So my interpretation of UL486C is that because of AC voltage peaks compared to 
RMS (Vpeak = Vrms x 1,414), a 1000VAC rated connector under UL486C would need 
to be tested to 1414VDC. Working that math backwards, a 600VAC rating would 
mean the DC dielectric rating would be equivalent to 424.33 VDC.

 

How that would apply to AHJs asking you questions, I do not know!

 

Dan Fink

Owner, Buckville Energy Consulting LLC

IREC Certified Instructor for PV and Small Wind Installation

NABCEP Certified PV System Inspector

d <mailto:dan.f...@greendustrialtraining.com> anbo...@gmail.com 
<mailto:anbo...@gmail.com> 

970-672-4342


 

 

 

On Fri, May 7, 2021 at 3:43 PM Jason Szumlanski 
<ja...@floridasolardesigngroup.com <mailto:ja...@floridasolardesigngroup.com> > 
wrote:

In another thread these connectors were discussed recently. There was a 
question regarding the suitability for DC circuits. I don't think we came up 
with any answers or consensus on that. I see the connectors are UL listed to 
the 486C standard. I can't determine whether that is applicable to AC and DC 
circuits. Does anyone know?

 

I have only used these on AC circuits and they have been very effective. Now 
I'm curious whether they can be used on DC circuits up to 600 volts. 

 

While on the subject, I noticed they are UL 467 listed for grounding and 
bonding. That's helpful where you have EGC splices for conductors up to #10 AWG 
inside junction boxes. 

 

Jason Szumlanski

Florida Solar Design Group

 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to