So like I said, although logic may dictate that it will operate at a high 
voltage DC level, having not been tested explicitly for that, it does not have 
UL listing – we will not use them on the DC side of our installations for that 
reason.

 

-Glenn

 

From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of Dan 
Fink
Sent: Friday, May 07, 2021 7:01 PM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Wago Connectors (221 series)

 

Jason; From the Wago 221 data sheet, it's listed to UL 486C, 600V, 30A, Use 
Group C (industrial) . I have a copy of UL486C, and voltage is just specified 
for dielectric testing. That standard specifies tests with AC, because it is 
easier (and cheaper) to generate and ramp up compared to DC, and DC test 
platforms are relatively rare. 

 

So my interpretation of UL486C is that because of AC voltage peaks compared to 
RMS (Vpeak = Vrms x 1,414), a 1000VAC rated connector under UL486C would need 
to be tested to 1414VDC. Working that math backwards, a 600VAC rating would 
mean the DC dielectric rating would be equivalent to 424.33 VDC.

 

How that would apply to AHJs asking you questions, I do not know!

 

Dan Fink

Owner, Buckville Energy Consulting LLC

IREC Certified Instructor for PV and Small Wind Installation

NABCEP Certified PV System Inspector

d <mailto:dan.f...@greendustrialtraining.com> anbo...@gmail.com 
<mailto:anbo...@gmail.com> 

970-672-4342


 

 

 

On Fri, May 7, 2021 at 3:43 PM Jason Szumlanski 
<ja...@floridasolardesigngroup.com <mailto:ja...@floridasolardesigngroup.com> > 
wrote:

In another thread these connectors were discussed recently. There was a 
question regarding the suitability for DC circuits. I don't think we came up 
with any answers or consensus on that. I see the connectors are UL listed to 
the 486C standard. I can't determine whether that is applicable to AC and DC 
circuits. Does anyone know?

 

I have only used these on AC circuits and they have been very effective. Now 
I'm curious whether they can be used on DC circuits up to 600 volts. 

 

While on the subject, I noticed they are UL 467 listed for grounding and 
bonding. That's helpful where you have EGC splices for conductors up to #10 AWG 
inside junction boxes. 

 

Jason Szumlanski

Florida Solar Design Group

 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to