100% agree with Kirpal. Had the same issue on a multi-stacked 8048 setup.

 

 



 

 

 

From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of jay
Sent: Sunday, July 18, 2021 9:26 PM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] outback grid tie help

 

HI Kirpal,

 

This sure seems like a real possibility.  

 

I don’t know that there have been any firmware updates.  I know its one REV 
behind, but tech support didn’t think that was an issue.  

 

As to the installer menu, does anyone know where I can find a map/menu of all 
the options?

 

thx

 

jay





On Jul 18, 2021, at 7:46 PM, Kirpal <solarwo...@gmail.com 
<mailto:solarwo...@gmail.com> > wrote:

 

Hi Jay.  We had a similar situation arise once after we updated the firmware of 
a 4048 radian.  The inverter was a circa 2015 unit.  After updating it would 
only sell about 1/4 of the normal array output to the grid.  

We talked to Chris at tech support and he had us go into the installer menu and 
look up the max sell current and somehow the inverter firmware update had 
changed a setting deep in the installer menu to limit sell amps.  It was a menu 
which we had never been in.  Adjusting to the normal 16a of sell current up 
from the 4A immediately corrected the issue.  

Your problem sounds exactly like the one we experienced. 

Did you update firmware recently?

I believe you have to be on site to access the installer menu....

Chris is typically on the job at 6am pacific time and easy to get ahold of 
early....I recommend trying to get ahold of him to walk you thru the steps.  

Best of luck.

Kirpal 

Oregon Solarworks 

 

 

On Sun, Jul 18, 2021, 12:26 PM jay <jay.pe...@gmail.com 
<mailto:jay.pe...@gmail.com> > wrote:

HI All,

I”m trying to diagnose the following system I didn’t install.

4 year old system grid tie battery back up.

Radian 4048
flexmax 80
3500 watts PV
fndc
it is on opticsRE

The symptoms are that its not selling much at all.  Mostly when it is about 1kw 
max PV production and .8kw selling.  I have disconnected the FNDC and after 
that it did seem to work better.  

Usually it will sell a bit, then buy a bit then sell and so on.  Grid voltage 
is very constant at around 246vac. 

I’ve been through the settings a few times with tech support, made adjustments 
and for a while it was selling pretty normally, but again today 0 production, 
CC is at float.  

I have not been to the site, I was just trying to do this all by optics.  But 
I’m going to have to go.   I think there are 3 possible issues.  

1. the customer has always thought the production is low.  And from what I’ve 
seen that is true.  This is in a very sunny place, no shade so with 3.5kw, 1kw 
is very low which I think they may have  a few strings of the array are not 
connected. However why that bothers me is that the VOC/VMP voltages are too 
close in looking at the CC.  Which leads me to think its been told to back off 
to the 1.0kw, by some setting, see #2. And its always around .8 selling and 
around 1kw output from the array. 

2.  There is a programing issue.  

3. There is a hardware issue.


If someone wants to look at the site, I have the info and they can log in.  
Or if they want to provide settings for me to triple check, that would be great
and 
if they have any ideas as to why its acting like it is, very much appreciated 
So far even though tech support has viewed in on Optics and have had some 
recommendations as to settings, its not fixed the issue.

thanks in advance,

jay

peltz power







_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/> 

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to