We have done one Solark installation & I was shocked as to the lack of ground wire landing terminals & space. We added a 12126 metal box below to ease the # of entrances to two 11/4”. I jumpered a # 8 to a second ground bar to allow for additional landing locations. I called Solark to question this & the response to the question was “yeah we have heard this from other installers “. End of call. Dana Orzel C: 208.721.7003 E- d...@solarwork.com
> On Apr 13, 2022, at 8:21 PM, Maverick Brown via RE-wrenches > <re-wrenches@lists.re-wrenches.org> wrote: > > Ron > > The Sol-Ark has two MPPT channels and has two separate landing spots for each > MPPT channels. Each landing pair needs matching strings. 8 AWG wire barely > fits so the Sol-Ark PV terminals so they may only be rated for 10AWG. > > I’m assuming you have a ground array The most common stringing method would > be to use a trench with conduit and THHN wire. You could also sleeve a > direct-burial cable into the ground. Calculate the voltage drop over the > distance to make sure 10AWG is adequate. If not, then make a junction, like a > MidNite or Outback combiner or an IMO switch at the array to get up the right > wire size, with an added MidNite Surge Protector or EMP shield device. If > it’s a long distance (larger wire size), add another combiner at the inverter > building entrance to get back to 10 AWG. > > https://practicalpreppers.com/product/imo-4-pole-16-amp-dc-disconnect/ > > Also, The Sol-Ark sizing guide helps with string calculations. > > https://www.sol-ark.com/solar-panel-sizing/SolarPanelSizing.html > > Contact me off list with additional questions. > > > > Maverick Brown > Off-Grid Solar Commander since 2006 > Maverick Solar Enterprises, Inc. > • Solar Commander Remote Power > • SunFlow Systems Cathodic Protection > maver...@mavericksolar.com > 512-460-9825 > > >>> On Apr 12, 2022, at 9:42 PM, Ron Young via RE-wrenches >>> <re-wrenches@lists.re-wrenches.org> wrote: >>> >> Hi Wrenches, trying to wrap my head around a first time Sol-Ark install. >> Because the max DC voltage is 500v at 18a and the PV I’m using is 40v DC >> each I will have to create three strings each 480v. What would be the best >> choice for a home run wire? I’ve always used smaller strings with micro >> inverters, a combiner at the array and a single Teck home run cable but the >> string inverter presents a different scenario and it looks like I’ll need to >> use three home run cables, one for each string. >> >> Ron Young >> >> earthRight Products - Solareagle.com >> Alternative Energy Solutions ~ Renewable Energy Products >> >> >> _______________________________________________ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org >> > _______________________________________________ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org >
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org