We have done one Solark installation & I was shocked as to the lack of ground 
wire landing terminals & space. We added a 12126 metal box below to ease the # 
of entrances to two 11/4”.
 I jumpered a # 8 to a second ground bar to allow for additional landing 
locations. I called Solark to question this & the response to the question was 
“yeah we have heard this from other installers “.
End of call. 
Dana Orzel
C: 208.721.7003
E- d...@solarwork.com

> On Apr 13, 2022, at 8:21 PM, Maverick Brown via RE-wrenches 
> <re-wrenches@lists.re-wrenches.org> wrote:
> 
> Ron
> 
> The Sol-Ark has two MPPT channels and has two separate landing spots for each 
> MPPT channels. Each landing pair needs matching strings. 8 AWG wire barely 
> fits so the Sol-Ark PV terminals so they may only be rated for 10AWG. 
> 
> I’m assuming you have a ground array  The most common stringing method would 
> be to use a trench with conduit and THHN wire. You could also sleeve a 
> direct-burial cable into the ground.  Calculate the voltage drop over the 
> distance to make sure 10AWG is adequate. If not, then make a junction, like a 
> MidNite or Outback combiner or an IMO switch at the array to get up the right 
> wire size, with an added MidNite Surge Protector or EMP shield device. If 
> it’s a long distance (larger wire size), add another combiner at the inverter 
> building entrance to get back to 10 AWG. 
> 
> https://practicalpreppers.com/product/imo-4-pole-16-amp-dc-disconnect/
> 
> Also, The Sol-Ark sizing guide helps with string calculations. 
> 
> https://www.sol-ark.com/solar-panel-sizing/SolarPanelSizing.html
> 
> Contact me off list with additional questions. 
> 
> 
> 
> Maverick Brown
> Off-Grid Solar Commander since 2006
> Maverick Solar Enterprises, Inc.
>  • Solar Commander Remote Power
>  • SunFlow Systems Cathodic Protection 
> maver...@mavericksolar.com
> 512-460-9825
> 
> 
>>> On Apr 12, 2022, at 9:42 PM, Ron Young via RE-wrenches 
>>> <re-wrenches@lists.re-wrenches.org> wrote:
>>> 
>> Hi Wrenches, trying to wrap my head around a first time Sol-Ark install. 
>> Because the max DC voltage is 500v at 18a  and the PV I’m using is 40v DC 
>> each I will have to create three strings each 480v. What would be the best 
>> choice for a home run wire? I’ve always used smaller strings with micro 
>> inverters, a combiner at the array and a single Teck home run cable but the 
>> string inverter presents a different scenario and it looks like I’ll need to 
>> use three home run cables, one for each string. 
>> 
>> Ron Young
>> 
>> earthRight Products - Solareagle.com
>> Alternative Energy Solutions ~ Renewable Energy Products
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to