This problem is not limited to one manufacturer. One example is the Enphase
smart controller. While the small holes are big enough for #6 ground and
neutral, you have to strip the wires perfectly and have the hand of a heart
surgeon to get them in there. And conduit entry is a royal pain because the
enclosure is tapered on the bottom and sides.

Fortunately, all of these manufacturers seem to be making strides to make
the roof installation easier. A little more attention to the electrical
enclosures would be appreciated.

Jason Szumlanski



On Thu, Apr 14, 2022, 10:30 AM Dana Orzel via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> We have done one Solark installation & I was shocked as to the lack of
> ground wire landing terminals & space. We added a 12126 metal box below to
> ease the # of entrances to two 11/4”.
>  I jumpered a # 8 to a second ground bar to allow for additional landing
> locations. I called Solark to question this & the response to the question
> was “yeah we have heard this from other installers “.
> End of call.
> Dana Orzel
> C: 208.721.7003
> E- d...@solarwork.com
>
> On Apr 13, 2022, at 8:21 PM, Maverick Brown via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> Ron
>
> The Sol-Ark has two MPPT channels and has two separate landing spots for
> each MPPT channels. Each landing pair needs matching strings. 8 AWG wire
> barely fits so the Sol-Ark PV terminals so they may only be rated for
> 10AWG.
>
> I’m assuming you have a ground array  The most common stringing method
> would be to use a trench with conduit and THHN wire. You could also sleeve
> a direct-burial cable into the ground.  Calculate the voltage drop over the
> distance to make sure 10AWG is adequate. If not, then make a junction, like
> a MidNite or Outback combiner or an IMO switch at the array to get up the
> right wire size, with an added MidNite Surge Protector or EMP shield
> device. If it’s a long distance (larger wire size), add another combiner at
> the inverter building entrance to get back to 10 AWG.
>
> https://practicalpreppers.com/product/imo-4-pole-16-amp-dc-disconnect/
>
> Also, The Sol-Ark sizing guide helps with string calculations.
>
> https://www.sol-ark.com/solar-panel-sizing/SolarPanelSizing.html
>
> Contact me off list with additional questions.
>
>
>
> Maverick Brown
> Off-Grid Solar Commander since 2006
> *Maverick Solar Enterprises, Inc.*
> * • Solar Commander Remote Power*
>
> * • SunFlow Systems Cathodic Protection *maver...@mavericksolar.com
> 512-460-9825
>
>
> On Apr 12, 2022, at 9:42 PM, Ron Young via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> Hi Wrenches, trying to wrap my head around a first time Sol-Ark install.
> Because the max DC voltage is 500v at 18a  and the PV I’m using is 40v DC
> each I will have to create three strings each 480v. What would be the best
> choice for a home run wire? I’ve always used smaller strings with micro
> inverters, a combiner at the array and a single Teck home run cable but the
> string inverter presents a different scenario and it looks like I’ll need
> to use three home run cables, one for each string.
>
> Ron Young
>
> earthRight Products - Solareagle.com
> Alternative Energy Solutions ~ Renewable Energy Products
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to