fortress is making improvements to their firmware for sure.
The fortress envy 12 has generator warmup/cool down which is a really important feature IMO.
The eg4 not. Nor does the Deye sol ark.
Jay
On Feb 16, 2024, at 8:48 PM, Chris Sparadeo via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:
The EG4 18K and the Fortress Envy are both made by the same manufacturer, LuxPower. Google the LXP 12K and it will all make sense. I can’t speak for EG4, but I know that Fortress has progressed from simply white labeling this unit to doing a significant amount of programming and additional integration, specifically with regards to their monitoring platform.
Personally, I have always had a skeptical approach with EG4. The EX line was chintzy at best. Every prospective client I have crossed paths with that has called out EG4 equipment thinks they know more and want it cheaper because they watched a few YouTube videos where unqualified DIY hacks free air conductors. I don’t want to write EG4 off completely, and am interested in their PowerPro battery. But with the ebb and flow of battery manufacturers, I wouldn’t be surprised if they weren’t around in 5 years. I feel differently about Fortress Power and although they have been a little overactive in the inverter market, I do believe that they are well intentioned and that their products and business are solid.
There has been some recent LFP bashing, and respectfully, I will agree to disagree. Early iterations of LFP had frequent issues with BMS and cell failure, but all in all, LFP has been a shining star in off-grid applications. I say this having installed 100+ eVault Max 18.5 in strictly off-grid scenarios. Sure there are phone calls and necessary firmware updates (however never a single BMS failure with the eVault Max), but I’m not having the heartbreaking conversations of “when we came back from vacation our 48v lead acid battery bank was at 15 volts”. I don’t like those phone calls. I also don't like holes in my pants and shirts or calls that CO monitors are alarming because of dead vent fans. I’m not dying on the hill of LFP, but I will say that I am firmly in support of the measurable improvements they have made for my customers. Paired with remote monitoring, the truck rolls a lot less.
Kindly,
Chris
The issue I'm having with EG4 specifically and Signature Solar in general is a scattershot approach to UL and NRTL listings. Those listings may not be important to various DIY folks of varying levels of "git-er-done," but listings are critical for my business. Some products they sell are Listed per NEC, some are not, and some EG4 are listed, some are not. I recently contacted Signature Solar regarding their EG4 rack mount ESS modules and did not receive a satisfactory response, unfortunately a new off-grid client had already purchased an entire rack of them before consulting with me. Our county AHJ is very strict. I can't risk recommending or installing a system that would fail inspection. Here in Colorado they often even cross check the altitude ratings on all inverters. (sorry Schneider XW-Pro that I like so much, limit on your spec sheet is 2000m altitude)
Signature Solar provided the usual NRTL stamp for UL 1741SA etc etc on the EG4 rack batteries, then also a UL 9540A testing certificate that they said should be sufficient, and it disturbed me that they did not seem to understand that UL 9540A is NOT a listing - it's a fire-resistance test that an ESS manufacturer can use as a document to help obtain their actual UL9540 listing, and also gain exemptions to spacing and other requirements....but from my understanding it's NOT an actual UL or NRTL listing to UL 9540. When I inquired about that, Signature Solar stopped communicating with me.
I'm pretty sure my understanding of UL 9540 listing vs. 9540A testing is correct, but I would appreciate any input before again gently confronting both AHJs and manufacturers. Dan Fink Owner, Buckville Energy Consulting LLC IREC Certified Instructor for PV and Small Wind Installation NABCEP Certified PV System Inspector NABCEP PV Associate 970-672-4342
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org
|