2014-11-06 Thread Faisal Imtiaz
Here is the info on AC power arrangement 

http://www.oempanels.com/what-does-single-and-three-phase-power-mean 

The CCR specs show it having : 
Dual power supplies for redundancy, 110-250V input, IEC connectors 

which means that, you can use either 110 or 220 or 240 on the same power 
supply. 
All you would have to do is match the power cables... 

Regards. 

Faisal Imtiaz 
Snappy Internet  Telecom 
7266 SW 48 Street 
Miami, FL 33155 
Tel: 305 663 5518 x 232 

Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net 

- Original Message -

 From: Scott Carullo sc...@brevardwireless.com
 To: WISPA General List wireless@wispa.org
 Sent: Wednesday, November 5, 2014 11:55:36 PM
 Subject: Re: [WISPA] Off topic sorta power question

 Cloud core. There is a difference between having a hot (80-250v), a neutral
 and a ground, vs. a neutral and two 120v hots. I believe the router can
 handle more than 120v but not in the sense that its being delivered on two
 120v legs with a neutral and no ground. Its a 3 prong twist lock type
 receptacle. If there is a way I'd like to be educated (aside from pulling
 one of the hots and hooking the neutral to ground as well on my new non-code
 engineered power cable. Educate me.
 I think I'm just going to plug it into the normal 120v 20amp plug on the wall
 behind the rack though, seems like the best way forward considering the
 options I was just trying to accommodate the customers request prior to plan
 B.
 Thanks
 Scott Carullo
 Technical Operations
 855-FLSPEED x102

 From : TJ Trout t...@voltbb.com
 Sent : Wednesday, November 05, 2014 3:21 PM
 To : WISPA General List wireless@wispa.org
 Subject : Re: [WISPA] Off topic sorta power question

 Everything can use 240 now days probably just need a new power cord
 On Nov 5, 2014 12:10 PM, Bob M  lakel...@gbcx.net  wrote:
  Keep in mind that it is breakered for 240. Splitting the legs after a 240
  vac
  circuit breaker is not code.
 
  Sent from my Verizon Wireless 4G LTE smartphone
 

   Original message 
 
  From: Brett Woollum  br...@tekify.com 
 
  Date:11/05/2014 12:00 PM (GMT-05:00)
 
  To: WISPA General List  wireless@wispa.org 
 
  Subject: Re: [WISPA] Off topic sorta power question
 
  Tim,
 

  In most cases you can split the hot leads on the 240v outlet into two 120v
  circuits. There are adapter pigtails for this if you don't want to hardware
  it.
 

  From memory, our local hardware store sells these (in the US).
 

  A quick Google search revealed this:
  http://www.wayfair.com/Champion-Power-Equipment-Generator-Y-Adapter-for-Champion-Power-Equipment-48035-L771-K~CXP1067.html?refid=GX50899353420-CXP1067device=cptid=75696510540gclid=CJ_Fktv348ECFUdffgod3z4ANw
 
  Brett Woollum
 
  Senior Sales Engineer
 
  br...@tekify.com
 

  Tekify Broadband Internet Services
 
  Web: http://www.tekify.com
 
  Phone: 510-266-5800 , ext 6200
 

  From: Tim Way  t...@way.vg 
 
  To: sc...@brevardwireless.com , WISPA General List  wireless@wispa.org 
 
  Sent: Wednesday, November 5, 2014 7:50:52 AM
 
  Subject: Re: [WISPA] Off topic sorta power question
 
  I would think something like this might be the safer option:
  http://www.certifiedmtp.com/step-up-step-down-transformer-500w/?gclid=CNWj1Kro48ECFQipaQodB74ADQ
 
  That said I'm not an electrician and I think that question might be best
  answered by one.
 
  Tim Way
 
  On Wed, Nov 5, 2014 at 9:38 AM, Scott Carullo  sc...@brevardwireless.com 
  wrote:
 
   I need to place a 120v normal 1U router in a rack that only has 240v
   twist
   lock receptacles available for power. I need to put a UPS there so I just
   looked for a 240v UPS with the right plugs but because they are made for
   a
   lot larger load they were way bigger (and more expensive) than what I was
   looking for. SO... anyone have a better way to do this? I have considered
   taking one leg and bonding the neutral and ground, but.
  
 
   Thanks
  
 
   Scott Carullo
  
 
   Technical Operations
  
 
   855-FLSPEED x102
  
 

   ___
  
 
   Wireless mailing list
  
 
   Wireless@wispa.org
  
 
   http://lists.wispa.org/mailman/listinfo/wireless
  
 

  ___
 
  Wireless mailing list
 
  Wireless@wispa.org
 
  http://lists.wispa.org/mailman/listinfo/wireless
 

  ___
 
  Wireless mailing list
 
  Wireless@wispa.org
 
  http://lists.wispa.org/mailman/listinfo/wireless
 

 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Off topic sorta power question....

2014-11-06 Thread Scott Carullo
Ok...  sorry to beat this horse but I'm apparently not following you.
  
 There are three lugs my shiny new male plug has.
 1-120v leg1 from single phase source
 2-120v leg2 from single phase source
 3- Neutral wire which bonds to ground at building main panel from power 
company.
  
 Cloud Core has three wires feeding the power supply.
 1-120v leg (1 or 2) from single phase source
 2-Neutral
 3-Ground
  
 A) I completely understand how I can take a single 120v wire from leg1 or 
leg2 of the power source and then take the neutral to both neutral and 
ground of the router power supply and make this work - thats easy - but not 
code.
  
 B) I also understand how I could take a neutral, a ground and one hot wire 
with voltage anywhere from 110-250v and it will work with cloud core power 
supply. (but not I do not have this configuration at source)
  
 C) I do not understand how you can take two hots and a neutral and turn 
that into anything (just by using a cable) that the router can use unless 
that cable is doing nothing more than what I described above in A
  
 Thanks
  
 Scott Carullo
Technical Operations
855-FLSPEED x102

  


 From: Faisal Imtiaz fai...@snappytelecom.net
Sent: Thursday, November 06, 2014 8:53 AM
To: sc...@brevardwireless.com, WISPA General List wireless@wispa.org
Subject: Re: [WISPA] Off topic sorta power question   
  Here is the info on AC power arrangement
  
 http://www.oempanels.com/what-does-single-and-three-phase-power-mean
  
 The CCR specs show it having :
 Dual power supplies for redundancy, 110-250V input, IEC connectors
  
 which means that, you can use either 110 or 220 or 240 on the same power 
supply.
 All you would have to do is match the power cables...
  
 Regards.
  
 Faisal Imtiaz
Snappy Internet  Telecom
7266 SW 48 Street
Miami, FL 33155
Tel: 305 663 5518 x 232  
Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net
  


 From: Scott Carullo sc...@brevardwireless.com
To: WISPA General List wireless@wispa.org
Sent: Wednesday, November 5, 2014 11:55:36 PM
Subject: Re: [WISPA] Off topic sorta power question   
 Cloud core.  There is a difference between having a hot (80-250v), a 
neutral and a ground, vs. a neutral and two 120v hots.  I believe the 
router can handle more than 120v but not in the sense that its being 
delivered on two 120v legs with a neutral and no ground.  Its a 3 prong 
twist lock type receptacle.  If there is a way I'd like to be educated 
(aside from pulling one of the hots and hooking the neutral to ground as 
well on my new non-code engineered power cable.  Educate me.
  
 I think I'm just going to plug it into the normal 120v 20amp plug on the 
wall behind the rack though, seems like the best way forward considering 
the options I was just trying to accommodate the customers request prior to 
plan B.
  
 Thanks
  
 Scott Carullo
Technical Operations
855-FLSPEED x102

  


 From: TJ Trout t...@voltbb.com
Sent: Wednesday, November 05, 2014 3:21 PM
To: WISPA General List wireless@wispa.org
Subject: Re: [WISPA] Off topic sorta power question   

Everything can use 240 now days probably just need a new power cord  On Nov 
5, 2014 12:10 PM, Bob M lakel...@gbcx.net wrote:Keep in mind that 
it is breakered for 240.  Splitting the legs after a 240 vac  circuit 
breaker is not code.
  
  
  Sent from my Verizon Wireless 4G LTE smartphone

  

 Original message 
From: Brett Woollum br...@tekify.com
Date:11/05/2014 12:00 PM (GMT-05:00)
To: WISPA General List wireless@wispa.org
Subject: Re: [WISPA] Off topic sorta power question
  Tim,

In most cases you can split the hot leads on the 240v outlet into two 120v 
circuits. There are adapter pigtails for this if you don't want to hardware 
it.

From memory, our local hardware store sells these (in the US).

A quick Google search revealed this: 
http://www.wayfair.com/Champion-Power-Equipment-Generator-Y-Adapter-for-Cham
pion-Power-Equipment-48035-L771-K~CXP1067.html?refid=GX50899353420-CXP1067d
evice=cptid=75696510540gclid=CJ_Fktv348ECFUdffgod3z4ANw
  Brett Woollum
Senior Sales Engineer
br...@tekify.com

Tekify Broadband Internet Services
Web: http://www.tekify.com
Phone: 510-266-5800, ext 6200


 From: Tim Way t...@way.vg
To: sc...@brevardwireless.com, WISPA General List wireless@wispa.org
Sent: Wednesday, November 5, 2014 7:50:52 AM
Subject: Re: [WISPA] Off topic sorta power question
  I would think something like this might be the safer option: 
http://www.certifiedmtp.com/step-up-step-down-transformer-500w/?gclid=CNWj1K
ro48ECFQipaQodB74ADQ   
 That said I'm not an electrician and I think that question might be best 
answered by one.
  
 Tim Way

   On Wed, Nov 5, 2014 at 9:38 AM, Scott Carullo 
sc...@brevardwireless.comwrote:   I need to place a 120v normal 1U router 
in a rack that only

Re: [WISPA] Off topic sorta power question....

2014-11-06 Thread Faisal Imtiaz
http://www.samlexamerica.com/support/documents/WhitePaper-120240VACSingleSplitPhaseandMultiWireBranchCircuits.pdf
 

This document has info on what you are looking for. 

The configuration you describe is called dual / split phase ... which happens 
to be the most common configuration on how power is delivered to our homes in 
the US. 

:) 

Faisal Imtiaz 
Snappy Internet  Telecom 
7266 SW 48 Street 
Miami, FL 33155 
Tel: 305 663 5518 x 232 

Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net 

- Original Message -

 From: Scott Carullo sc...@brevardwireless.com
 To: Faisal Imtiaz fai...@snappytelecom.net, sc...@brevardwireless.com,
 WISPA General List wireless@wispa.org
 Sent: Thursday, November 6, 2014 2:40:35 PM
 Subject: Re: [WISPA] Off topic sorta power question

 Ok... sorry to beat this horse but I'm apparently not following you.
 There are three lugs my shiny new male plug has.
 1-120v leg1 from single phase source
 2-120v leg2 from single phase source
 3- Neutral wire which bonds to ground at building main panel from power
 company.
 Cloud Core has three wires feeding the power supply.
 1-120v leg (1 or 2) from single phase source
 2-Neutral
 3-Ground
 A) I completely understand how I can take a single 120v wire from leg1 or
 leg2 of the power source and then take the neutral to both neutral and
 ground of the router power supply and make this work - thats easy - but not
 code.
 B) I also understand how I could take a neutral, a ground and one hot wire
 with voltage anywhere from 110-250v and it will work with cloud core power
 supply. (but not I do not have this configuration at source)
 C) I do not understand how you can take two hots and a neutral and turn that
 into anything (just by using a cable) that the router can use unless that
 cable is doing nothing more than what I described above in A
 Thanks
 Scott Carullo
 Technical Operations
 855-FLSPEED x102

 From : Faisal Imtiaz fai...@snappytelecom.net
 Sent : Thursday, November 06, 2014 8:53 AM
 To : sc...@brevardwireless.com, WISPA General List wireless@wispa.org
 Subject : Re: [WISPA] Off topic sorta power question
 Here is the info on AC power arrangement
 http://www.oempanels.com/what-does-single-and-three-phase-power-mean
 The CCR specs show it having :
 Dual power supplies for redundancy, 110-250V input, IEC connectors
 which means that, you can use either 110 or 220 or 240 on the same power
 supply.
 All you would have to do is match the power cables...
 Regards.
 Faisal Imtiaz
 Snappy Internet  Telecom
 7266 SW 48 Street
 Miami, FL 33155
 Tel: 305 663 5518 x 232
 Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net
 - Original Message -

  From: Scott Carullo sc...@brevardwireless.com
 
  To: WISPA General List wireless@wispa.org
 
  Sent: Wednesday, November 5, 2014 11:55:36 PM
 
  Subject: Re: [WISPA] Off topic sorta power question
 
  Cloud core. There is a difference between having a hot (80-250v), a neutral
  and a ground, vs. a neutral and two 120v hots. I believe the router can
  handle more than 120v but not in the sense that its being delivered on two
  120v legs with a neutral and no ground. Its a 3 prong twist lock type
  receptacle. If there is a way I'd like to be educated (aside from pulling
  one of the hots and hooking the neutral to ground as well on my new
  non-code
  engineered power cable. Educate me.
 
  I think I'm just going to plug it into the normal 120v 20amp plug on the
  wall
  behind the rack though, seems like the best way forward considering the
  options I was just trying to accommodate the customers request prior to
  plan
  B.
 
  Thanks
 
  Scott Carullo
 
  Technical Operations
 
  855-FLSPEED x102
 

  From : TJ Trout t...@voltbb.com
 
  Sent : Wednesday, November 05, 2014 3:21 PM
 
  To : WISPA General List wireless@wispa.org
 
  Subject : Re: [WISPA] Off topic sorta power question
 

  Everything can use 240 now days probably just need a new power cord
 
  On Nov 5, 2014 12:10 PM, Bob M  lakel...@gbcx.net  wrote:
 
   Keep in mind that it is breakered for 240. Splitting the legs after a 240
   vac
   circuit breaker is not code.
  
 
   Sent from my Verizon Wireless 4G LTE smartphone
  
 

    Original message 
  
 
   From: Brett Woollum  br...@tekify.com 
  
 
   Date:11/05/2014 12:00 PM (GMT-05:00)
  
 
   To: WISPA General List  wireless@wispa.org 
  
 
   Subject: Re: [WISPA] Off topic sorta power question
  
 
   Tim,
  
 

   In most cases you can split the hot leads on the 240v outlet into two
   120v
   circuits. There are adapter pigtails for this if you don't want to
   hardware
   it.
  
 

   From memory, our local hardware store sells these (in the US).
  
 

   A quick Google search revealed this:
   http://www.wayfair.com/Champion-Power-Equipment-Generator-Y-Adapter-for-Champion-Power-Equipment-48035-L771-K~CXP1067.html?refid=GX50899353420-CXP1067device=cptid=75696510540gclid

Re: [WISPA] Off topic sorta power question....

2014-11-06 Thread Blair Davis
Set your device for 220-240VAC  Many devices have a switch on the power 
supply for this.  Some devices simply have an input range of 100-250VAC.

Tie your device hot to leg 1
Tie your device neutral to leg 2
Tie your device ground to the neutral/ground of the power outlet.

Can you post a picture of the outlet and of the power cord recptical on 
your device?


--




On 11/6/2014 2:40 PM, Scott Carullo wrote:

Ok...  sorry to beat this horse but I'm apparently not following you.
There are three lugs my shiny new male plug has.
1-120v leg1 from single phase source
2-120v leg2 from single phase source
3- Neutral wire which bonds to ground at building main panel from 
power company.

Cloud Core has three wires feeding the power supply.
1-120v leg (1 or 2) from single phase source
2-Neutral
3-Ground
A) I completely understand how I can take a single 120v wire from leg1 
or leg2 of the power source and then take the neutral to both neutral 
and ground of the router power supply and make this work - thats easy 
- but not code.
B) I also understand how I could take a neutral, a ground and one hot 
wire with voltage anywhere from 110-250v and it will work with cloud 
core power supply. (but not I do not have this configuration at source)
C) I do not understand how you can take two hots and a neutral and 
turn that into anything (just by using a cable) that the router can 
use unless that cable is doing nothing more than what I described 
above in A

Thanks
Scott Carullo
Technical Operations
855-FLSPEED x102


*From*: Faisal Imtiaz fai...@snappytelecom.net
*Sent*: Thursday, November 06, 2014 8:53 AM
*To*: sc...@brevardwireless.com, WISPA General List wireless@wispa.org
*Subject*: Re: [WISPA] Off topic sorta power question
Here is the info on AC power arrangement
http://www.oempanels.com/what-does-single-and-three-phase-power-mean
The CCR specs show it having :
Dualpowersuppliesforredundancy,110-250Vinput,IECconnectors
which means that, you can use either 110 or 220 or 240 on the same 
power supply.

All you would have to do is match the power cables...
Regards.
Faisal Imtiaz
Snappy Internet  Telecom
7266 SW 48 Street
Miami, FL 33155
Tel: 305 663 5518 x 232
Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net


*From: *Scott Carullo sc...@brevardwireless.com
*To: *WISPA General List wireless@wispa.org
*Sent: *Wednesday, November 5, 2014 11:55:36 PM
*Subject: *Re: [WISPA] Off topic sorta power question
Cloud core.  There is a difference between having a hot (80-250v),
a neutral and a ground, vs. a neutral and two 120v hots.  I
believe the router can handle more than 120v but not in the sense
that its being delivered on two 120v legs with a neutral and no
ground.  Its a 3 prong twist lock type receptacle.  If there is a
way I'd like to be educated (aside from pulling one of the hots
and hooking the neutral to ground as well on my new non-code
engineered power cable.  Educate me.
I think I'm just going to plug it into the normal 120v 20amp plug
on the wall behind the rack though, seems like the best way
forward considering the options I was just trying to accommodate
the customers request prior to plan B.
Thanks
Scott Carullo
Technical Operations
855-FLSPEED x102


*From*: TJ Trout t...@voltbb.com
*Sent*: Wednesday, November 05, 2014 3:21 PM
*To*: WISPA General List wireless@wispa.org
*Subject*: Re: [WISPA] Off topic sorta power question

Everything can use 240 now days probably just need a new power cord

On Nov 5, 2014 12:10 PM, Bob M lakel...@gbcx.net
mailto:lakel...@gbcx.net wrote:

Keep in mind that it is breakered for 240. Splitting the legs
after a 240 vac  circuit breaker is not code.
Sent from my Verizon Wireless 4G LTE smartphone


 Original message 
From: Brett Woollum br...@tekify.com mailto:br...@tekify.com
Date:11/05/2014 12:00 PM (GMT-05:00)
To: WISPA General List wireless@wispa.org
mailto:wireless@wispa.org
Subject: Re: [WISPA] Off topic sorta power question
Tim,

In most cases you can split the hot leads on the 240v outlet
into two 120v circuits. There are adapter pigtails for this if
you don't want to hardware it.

From memory, our local hardware store sells these (in the US).

A quick Google search revealed this:

http://www.wayfair.com/Champion-Power-Equipment-Generator-Y-Adapter-for-Champion-Power-Equipment-48035-L771-K~CXP1067.html?refid=GX50899353420-CXP1067device=cptid=75696510540gclid=CJ_Fktv348ECFUdffgod3z4ANw

http://www.wayfair.com/Champion-Power-Equipment-Generator-Y-Adapter

Re: [WISPA] Off topic sorta power question....

2014-11-06 Thread lar
On Thu, 06 Nov 2014 18:19:44 -0500
  Blair Davis the...@wmwisp.net wrote:
 Set your device for 220-240VAC  Many devices have a switch on the power 
 supply for this.  Some devices simply have an input 
range of 100-250VAC.
 Tie your device hot to leg 1
 Tie your device neutral to leg 2
 Tie your device ground to the neutral/ground of the power outlet.
 
 Can you post a picture of the outlet and of the power cord recptical on your 
 device?
 

While this should work in theory you cannot assume that
neutral and ground are the same. The farther you get from the service
the greater the possibility that neutral varies from ground, and if
you have a corroded junction somewhere between your location and the bonding 
point
you can have significant voltage on neutral. Just try and make digital
equipment work if your feed 5-10 volts AC in on the ground.

To do this properly requires an isolation transformer to separately derive the 
source and
a new bonding point or better yet a four wire source pigtail where neutral and 
ground are
separately presented on the plug. (Be careful about over current protection.)

I've had to do this in a remote locations with 240 V generator.
I used a one-to-one isolation transformer with a center tap. The primary is 
connected to
the two hot legs. The secondary center tap is bonded to earth ground and both 
neutral
and ground originate at that point. 110 is present on either end of the 
secondary relative
to the center tap.
The whole thing has to go to a fuse/breaker box for protection. All in all if 
there is
service anywhere close it's easier and cheaper to hire an electrician to drop a 
110
receptacle close by. Fires and/or electrocuted kids/pets are a PR problem of 
the first order.

Larry Ash
Mountain West Technologies Corp.
 --
 
 
 
 
 On 11/6/2014 2:40 PM, Scott Carullo wrote:
 Ok...  sorry to beat this horse but I'm apparently not following you.
 There are three lugs my shiny new male plug has.
 1-120v leg1 from single phase source
 2-120v leg2 from single phase source
 3- Neutral wire which bonds to ground at building main panel from power 
 company.
 Cloud Core has three wires feeding the power supply.
 1-120v leg (1 or 2) from single phase source
 2-Neutral
 3-Ground
 A) I completely understand how I can take a single 120v wire from leg1 or 
 leg2 of the power source and then take the neutral to 
both neutral and ground of the router power supply and make this work - thats 
easy - but not code.
 B) I also understand how I could take a neutral, a ground and one hot wire 
 with voltage anywhere from 110-250v and it will work 
with cloud core power supply. (but not I do not have this configuration at 
source)
 C) I do not understand how you can take two hots and a neutral and turn that 
 into anything (just by using a cable) that the 
router can use unless that cable is doing nothing more than what I described 
above in A
 Thanks
 Scott Carullo
 Technical Operations
 855-FLSPEED x102

 
 *From*: Faisal Imtiaz fai...@snappytelecom.net
 *Sent*: Thursday, November 06, 2014 8:53 AM
 *To*: sc...@brevardwireless.com, WISPA General List wireless@wispa.org
 *Subject*: Re: [WISPA] Off topic sorta power question
 Here is the info on AC power arrangement
 http://www.oempanels.com/what-does-single-and-three-phase-power-mean
 The CCR specs show it having :
 Dualpowersuppliesforredundancy,110-250Vinput,IECconnectors
 which means that, you can use either 110 or 220 or 240 on the same power 
 supply.
 All you would have to do is match the power cables...
 Regards.
 Faisal Imtiaz
 Snappy Internet  Telecom
 7266 SW 48 Street
 Miami, FL 33155
 Tel: 305 663 5518 x 232
 Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net
 

 *From: *Scott Carullo sc...@brevardwireless.com
 *To: *WISPA General List wireless@wispa.org
 *Sent: *Wednesday, November 5, 2014 11:55:36 PM
 *Subject: *Re: [WISPA] Off topic sorta power question
 Cloud core.  There is a difference between having a hot (80-250v),
 a neutral and a ground, vs. a neutral and two 120v hots.  I
 believe the router can handle more than 120v but not in the sense
 that its being delivered on two 120v legs with a neutral and no
 ground.  Its a 3 prong twist lock type receptacle.  If there is a
 way I'd like to be educated (aside from pulling one of the hots
 and hooking the neutral to ground as well on my new non-code
 engineered power cable.  Educate me.
 I think I'm just going to plug it into the normal 120v 20amp plug
 on the wall behind the rack though, seems like the best way
 forward considering the options I was just trying to accommodate
 the customers request prior to plan B.
 Thanks
 Scott Carullo
 Technical Operations
 855-FLSPEED x102

Re: [WISPA] Off topic sorta power question....

2014-11-06 Thread Blair Davis
I've never had a problem doing this.  While I see the theoretical issues 
you state, in practice it works.

The issue you are describing is caused by a defective outlet or wiring 
job.   While it happens, it is no more or less likely than your 117VAC 
outlet having the same issue with it's ground.   If you assume every 
outlet is defective, then you will need isolation transformers everywhere...

US 3 prong 240VAC outlets are wired as hot/hot/neutral with a strap on 
the device grounding the chassis metal to the neutral as a ground.  This 
was standard.  In most areas, new 240VAC outlets are wired as 4 prong 
hot/hot/neutral/ground and new devices are wired with a 4 prong cord. 
Most devices can have a 3 prong cord installed by following the device 
instructions.

--


On 11/6/2014 7:00 PM, l...@mwtcorp.net wrote:
 On Thu, 06 Nov 2014 18:19:44 -0500
  Blair Davis the...@wmwisp.net wrote:
 Set your device for 220-240VAC  Many devices have a switch on the
 power supply for this.  Some devices simply have an input range of
 100-250VAC.
 Tie your device hot to leg 1
 Tie your device neutral to leg 2
 Tie your device ground to the neutral/ground of the power outlet.

 Can you post a picture of the outlet and of the power cord recptical
 on your device?


 While this should work in theory you cannot assume that
 neutral and ground are the same. The farther you get from the service
 the greater the possibility that neutral varies from ground, and if
 you have a corroded junction somewhere between your location and the
 bonding point
 you can have significant voltage on neutral. Just try and make digital
 equipment work if your feed 5-10 volts AC in on the ground.

 To do this properly requires an isolation transformer to separately
 derive the source and
 a new bonding point or better yet a four wire source pigtail where
 neutral and ground are
 separately presented on the plug. (Be careful about over current
 protection.)

 I've had to do this in a remote locations with 240 V generator.
 I used a one-to-one isolation transformer with a center tap. The
 primary is connected to
 the two hot legs. The secondary center tap is bonded to earth ground
 and both neutral
 and ground originate at that point. 110 is present on either end of
 the secondary relative
 to the center tap.
 The whole thing has to go to a fuse/breaker box for protection. All in
 all if there is
 service anywhere close it's easier and cheaper to hire an electrician
 to drop a 110
 receptacle close by. Fires and/or electrocuted kids/pets are a PR
 problem of the first order.

 Larry Ash
 Mountain West Technologies Corp.
 --




 On 11/6/2014 2:40 PM, Scott Carullo wrote:
 Ok...  sorry to beat this horse but I'm apparently not following you.
 There are three lugs my shiny new male plug has.
 1-120v leg1 from single phase source
 2-120v leg2 from single phase source
 3- Neutral wire which bonds to ground at building main panel from
 power company.
 Cloud Core has three wires feeding the power supply.
 1-120v leg (1 or 2) from single phase source
 2-Neutral
 3-Ground
 A) I completely understand how I can take a single 120v wire from
 leg1 or leg2 of the power source and then take the neutral to both
 neutral and ground of the router power supply and make this work -
 thats easy - but not code.
 B) I also understand how I could take a neutral, a ground and one
 hot wire with voltage anywhere from 110-250v and it will work with
 cloud core power supply. (but not I do not have this configuration
 at source)
 C) I do not understand how you can take two hots and a neutral and
 turn that into anything (just by using a cable) that the router can
 use unless that cable is doing nothing more than what I described
 above in A
 Thanks
 Scott Carullo
 Technical Operations
 855-FLSPEED x102

 

 *From*: Faisal Imtiaz fai...@snappytelecom.net
 *Sent*: Thursday, November 06, 2014 8:53 AM
 *To*: sc...@brevardwireless.com, WISPA General List
 wireless@wispa.org
 *Subject*: Re: [WISPA] Off topic sorta power question
 Here is the info on AC power arrangement
 http://www.oempanels.com/what-does-single-and-three-phase-power-mean
 The CCR specs show it having :
 Dualpowersuppliesforredundancy,110-250Vinput,IECconnectors
 which means that, you can use either 110 or 220 or 240 on the same
 power supply.
 All you would have to do is match the power cables...
 Regards.
 Faisal Imtiaz
 Snappy Internet  Telecom
 7266 SW 48 Street
 Miami, FL 33155
 Tel: 305 663 5518 x 232
 Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net
 


 *From: *Scott Carullo sc...@brevardwireless.com
 *To: *WISPA General List wireless@wispa.org
 *Sent: *Wednesday, November 5, 2014 11:55:36 PM
 *Subject: *Re: [WISPA] Off topic sorta power question
 Cloud core.  There is a difference between having a hot (80-250v

[WISPA] Off topic sorta power question....

2014-11-05 Thread Scott Carullo
I need to place a 120v normal 1U router in a rack that only has 240v twist 
lock receptacles available for power.  I need to put a UPS there so I just 
looked for a 240v UPS with the right plugs but because they are made for a 
lot larger load they were way bigger (and more expensive) than what I was 
looking for.  SO...  anyone have a better way to do this?  I have 
considered taking one leg and bonding the neutral and ground, but.
  
 Thanks
  
 Scott Carullo
Technical Operations
855-FLSPEED x102


___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Off topic sorta power question....

2014-11-05 Thread Tim Way
I would think something like this might be the safer option:
http://www.certifiedmtp.com/step-up-step-down-transformer-500w/?gclid=CNWj1Kro48ECFQipaQodB74ADQ

That said I'm not an electrician and I think that question might be best
answered by one.

Tim Way

On Wed, Nov 5, 2014 at 9:38 AM, Scott Carullo sc...@brevardwireless.com
wrote:

 I need to place a 120v normal 1U router in a rack that only has 240v twist
 lock receptacles available for power.  I need to put a UPS there so I just
 looked for a 240v UPS with the right plugs but because they are made for a
 lot larger load they were way bigger (and more expensive) than what I was
 looking for.  SO...  anyone have a better way to do this?  I have
 considered taking one leg and bonding the neutral and ground, but.

 Thanks

 Scott Carullo
 Technical Operations
 855-FLSPEED x102


 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless


___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Off topic sorta power question....

2014-11-05 Thread Brett Woollum
Tim, 

In most cases you can split the hot leads on the 240v outlet into two 120v 
circuits. There are adapter pigtails for this if you don't want to hardware it. 

From memory, our local hardware store sells these (in the US). 

A quick Google search revealed this: 
http://www.wayfair.com/Champion-Power-Equipment-Generator-Y-Adapter-for-Champion-Power-Equipment-48035-L771-K~CXP1067.html?refid=GX50899353420-CXP1067device=cptid=75696510540gclid=CJ_Fktv348ECFUdffgod3z4ANw
 


Brett Woollum 
Senior Sales Engineer 
br...@tekify.com 

Tekify Broadband Internet Services 
Web: http://www.tekify.com 
Phone: 510-266-5800 , ext 6200 

- Original Message -

From: Tim Way t...@way.vg 
To: sc...@brevardwireless.com, WISPA General List wireless@wispa.org 
Sent: Wednesday, November 5, 2014 7:50:52 AM 
Subject: Re: [WISPA] Off topic sorta power question 


I would think something like this might be the safer option: 
http://www.certifiedmtp.com/step-up-step-down-transformer-500w/?gclid=CNWj1Kro48ECFQipaQodB74ADQ
 


That said I'm not an electrician and I think that question might be best 
answered by one. 


Tim Way 


On Wed, Nov 5, 2014 at 9:38 AM, Scott Carullo  sc...@brevardwireless.com  
wrote: 



I need to place a 120v normal 1U router in a rack that only has 240v twist lock 
receptacles available for power. I need to put a UPS there so I just looked for 
a 240v UPS with the right plugs but because they are made for a lot larger load 
they were way bigger (and more expensive) than what I was looking for. SO... 
anyone have a better way to do this? I have considered taking one leg and 
bonding the neutral and ground, but. 

Thanks 

Scott Carullo 
Technical Operations 
855-FLSPEED x102 


___ 
Wireless mailing list 
Wireless@wispa.org 
http://lists.wispa.org/mailman/listinfo/wireless 





___ 
Wireless mailing list 
Wireless@wispa.org 
http://lists.wispa.org/mailman/listinfo/wireless 

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Off topic sorta power question....

2014-11-05 Thread Bob M
Keep in mind that it is breakered for 240.  Splitting the legs after a 240 vac  
circuit breaker is not code.


Sent from my Verizon Wireless 4G LTE smartphone


 Original message 
From: Brett Woollum br...@tekify.com 
Date:11/05/2014  12:00 PM  (GMT-05:00) 
To: WISPA General List wireless@wispa.org 
Subject: Re: [WISPA] Off topic sorta power question 

Tim,

In most cases you can split the hot leads on the 240v outlet into two 120v 
circuits. There are adapter pigtails for this if you don't want to hardware it.

From memory, our local hardware store sells these (in the US).

A quick Google search revealed this: 
http://www.wayfair.com/Champion-Power-Equipment-Generator-Y-Adapter-for-Champion-Power-Equipment-48035-L771-K~CXP1067.html?refid=GX50899353420-CXP1067device=cptid=75696510540gclid=CJ_Fktv348ECFUdffgod3z4ANw

Brett Woollum
Senior Sales Engineer
br...@tekify.com

Tekify Broadband Internet Services
Web: http://www.tekify.com
Phone: 510-266-5800, ext 6200

From: Tim Way t...@way.vg
To: sc...@brevardwireless.com, WISPA General List wireless@wispa.org
Sent: Wednesday, November 5, 2014 7:50:52 AM
Subject: Re: [WISPA] Off topic sorta power question

I would think something like this might be the safer option: 
http://www.certifiedmtp.com/step-up-step-down-transformer-500w/?gclid=CNWj1Kro48ECFQipaQodB74ADQ

That said I'm not an electrician and I think that question might be best 
answered by one.

Tim Way

On Wed, Nov 5, 2014 at 9:38 AM, Scott Carullo sc...@brevardwireless.com wrote:
I need to place a 120v normal 1U router in a rack that only has 240v twist lock 
receptacles available for power.  I need to put a UPS there so I just looked 
for a 240v UPS with the right plugs but because they are made for a lot larger 
load they were way bigger (and more expensive) than what I was looking for.  
SO...  anyone have a better way to do this?  I have considered taking one leg 
and bonding the neutral and ground, but.
 
Thanks
 
Scott Carullo
Technical Operations
855-FLSPEED x102



___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless



___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Off topic sorta power question....

2014-11-05 Thread TJ Trout
What model is the router
On Nov 5, 2014 12:10 PM, Bob M lakel...@gbcx.net wrote:

 Keep in mind that it is breakered for 240.  Splitting the legs after a 240
 vac  circuit breaker is not code.


 Sent from my Verizon Wireless 4G LTE smartphone


  Original message 
 From: Brett Woollum br...@tekify.com
 Date:11/05/2014 12:00 PM (GMT-05:00)
 To: WISPA General List wireless@wispa.org
 Subject: Re: [WISPA] Off topic sorta power question

 Tim,

 In most cases you can split the hot leads on the 240v outlet into two 120v
 circuits. There are adapter pigtails for this if you don't want to hardware
 it.

 From memory, our local hardware store sells these (in the US).

 A quick Google search revealed this:
 http://www.wayfair.com/Champion-Power-Equipment-Generator-Y-Adapter-for-Champion-Power-Equipment-48035-L771-K~CXP1067.html?refid=GX50899353420-CXP1067device=cptid=75696510540gclid=CJ_Fktv348ECFUdffgod3z4ANw

 Brett Woollum
 Senior Sales Engineer
 br...@tekify.com

 *Tekify Broadband Internet Services*
 Web: http://www.tekify.com
 Phone: 510-266-5800, ext 6200

 --
 *From: *Tim Way t...@way.vg
 *To: *sc...@brevardwireless.com, WISPA General List wireless@wispa.org
 *Sent: *Wednesday, November 5, 2014 7:50:52 AM
 *Subject: *Re: [WISPA] Off topic sorta power question

 I would think something like this might be the safer option:
 http://www.certifiedmtp.com/step-up-step-down-transformer-500w/?gclid=CNWj1Kro48ECFQipaQodB74ADQ

 That said I'm not an electrician and I think that question might be best
 answered by one.

 Tim Way

 On Wed, Nov 5, 2014 at 9:38 AM, Scott Carullo sc...@brevardwireless.com
 wrote:

 I need to place a 120v normal 1U router in a rack that only has 240v
 twist lock receptacles available for power.  I need to put a UPS there so I
 just looked for a 240v UPS with the right plugs but because they are made
 for a lot larger load they were way bigger (and more expensive) than what I
 was looking for.  SO...  anyone have a better way to do this?  I have
 considered taking one leg and bonding the neutral and ground, but.

 Thanks

 Scott Carullo
 Technical Operations
 855-FLSPEED x102


 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless



 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless


 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless


___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Off topic sorta power question....

2014-11-05 Thread TJ Trout
Everything can use 240 now days probably just need a new power cord
On Nov 5, 2014 12:10 PM, Bob M lakel...@gbcx.net wrote:

 Keep in mind that it is breakered for 240.  Splitting the legs after a 240
 vac  circuit breaker is not code.


 Sent from my Verizon Wireless 4G LTE smartphone


  Original message 
 From: Brett Woollum br...@tekify.com
 Date:11/05/2014 12:00 PM (GMT-05:00)
 To: WISPA General List wireless@wispa.org
 Subject: Re: [WISPA] Off topic sorta power question

 Tim,

 In most cases you can split the hot leads on the 240v outlet into two 120v
 circuits. There are adapter pigtails for this if you don't want to hardware
 it.

 From memory, our local hardware store sells these (in the US).

 A quick Google search revealed this:
 http://www.wayfair.com/Champion-Power-Equipment-Generator-Y-Adapter-for-Champion-Power-Equipment-48035-L771-K~CXP1067.html?refid=GX50899353420-CXP1067device=cptid=75696510540gclid=CJ_Fktv348ECFUdffgod3z4ANw

 Brett Woollum
 Senior Sales Engineer
 br...@tekify.com

 *Tekify Broadband Internet Services*
 Web: http://www.tekify.com
 Phone: 510-266-5800, ext 6200

 --
 *From: *Tim Way t...@way.vg
 *To: *sc...@brevardwireless.com, WISPA General List wireless@wispa.org
 *Sent: *Wednesday, November 5, 2014 7:50:52 AM
 *Subject: *Re: [WISPA] Off topic sorta power question

 I would think something like this might be the safer option:
 http://www.certifiedmtp.com/step-up-step-down-transformer-500w/?gclid=CNWj1Kro48ECFQipaQodB74ADQ

 That said I'm not an electrician and I think that question might be best
 answered by one.

 Tim Way

 On Wed, Nov 5, 2014 at 9:38 AM, Scott Carullo sc...@brevardwireless.com
 wrote:

 I need to place a 120v normal 1U router in a rack that only has 240v
 twist lock receptacles available for power.  I need to put a UPS there so I
 just looked for a 240v UPS with the right plugs but because they are made
 for a lot larger load they were way bigger (and more expensive) than what I
 was looking for.  SO...  anyone have a better way to do this?  I have
 considered taking one leg and bonding the neutral and ground, but.

 Thanks

 Scott Carullo
 Technical Operations
 855-FLSPEED x102


 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless



 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless


 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless


___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Off topic sorta power question....

2014-11-05 Thread Scott Carullo
Cloud core.  There is a difference between having a hot (80-250v), a 
neutral and a ground, vs. a neutral and two 120v hots.  I believe the 
router can handle more than 120v but not in the sense that its being 
delivered on two 120v legs with a neutral and no ground.  Its a 3 prong 
twist lock type receptacle.  If there is a way I'd like to be educated 
(aside from pulling one of the hots and hooking the neutral to ground as 
well on my new non-code engineered power cable.  Educate me.
  
 I think I'm just going to plug it into the normal 120v 20amp plug on the 
wall behind the rack though, seems like the best way forward considering 
the options I was just trying to accommodate the customers request prior to 
plan B.
  
 Thanks
  
 Scott Carullo
Technical Operations
855-FLSPEED x102

  


 From: TJ Trout t...@voltbb.com
Sent: Wednesday, November 05, 2014 3:21 PM
To: WISPA General List wireless@wispa.org
Subject: Re: [WISPA] Off topic sorta power question   

Everything can use 240 now days probably just need a new power cord  On Nov 
5, 2014 12:10 PM, Bob M lakel...@gbcx.net wrote:Keep in mind that 
it is breakered for 240.  Splitting the legs after a 240 vac  circuit 
breaker is not code.
  
  
  Sent from my Verizon Wireless 4G LTE smartphone

  

 Original message 
From: Brett Woollum br...@tekify.com
Date:11/05/2014 12:00 PM (GMT-05:00)
To: WISPA General List wireless@wispa.org
Subject: Re: [WISPA] Off topic sorta power question
  Tim,

In most cases you can split the hot leads on the 240v outlet into two 120v 
circuits. There are adapter pigtails for this if you don't want to hardware 
it.

From memory, our local hardware store sells these (in the US).

A quick Google search revealed this: 
http://www.wayfair.com/Champion-Power-Equipment-Generator-Y-Adapter-for-Cham
pion-Power-Equipment-48035-L771-K~CXP1067.html?refid=GX50899353420-CXP1067d
evice=cptid=75696510540gclid=CJ_Fktv348ECFUdffgod3z4ANw
  Brett Woollum
Senior Sales Engineer
br...@tekify.com

Tekify Broadband Internet Services
Web: http://www.tekify.com
Phone: 510-266-5800 , ext 6200  


 From: Tim Way t...@way.vg
To: sc...@brevardwireless.com, WISPA General List wireless@wispa.org
Sent: Wednesday, November 5, 2014 7:50:52 AM
Subject: Re: [WISPA] Off topic sorta power question
  I would think something like this might be the safer option: 
http://www.certifiedmtp.com/step-up-step-down-transformer-500w/?gclid=CNWj1K
ro48ECFQipaQodB74ADQ   
 That said I'm not an electrician and I think that question might be best 
answered by one.
  
 Tim Way

   On Wed, Nov 5, 2014 at 9:38 AM, Scott Carullo 
sc...@brevardwireless.com wrote:   I need to place a 120v normal 1U 
router in a rack that only has 240v twist lock receptacles available for 
power.  I need to put a UPS there so I just looked for a 240v UPS with the 
right plugs but because they are made for a lot larger load they were way 
bigger (and more expensive) than what I was looking for.  SO...  anyone 
have a better way to do this?  I have considered taking one leg and bonding 
the neutral and ground, but.
  
 Thanks
  
 Scott Carullo
Technical Operations
855-FLSPEED x102

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless
  

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless
  


___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Off topic sorta power question....

2014-11-05 Thread TJ Trout
2 hots is 240 right ? Ccr pdu is good for 240? I don't know anything more
than that. You can't get a cable to go from your outlet to a atx style
power cord for the Ccr ?
On Nov 5, 2014 8:53 PM, Scott Carullo sc...@brevardwireless.com wrote:

 Cloud core.  There is a difference between having a hot (80-250v), a
 neutral and a ground, vs. a neutral and two 120v hots.  I believe the
 router can handle more than 120v but not in the sense that its being
 delivered on two 120v legs with a neutral and no ground.  Its a 3 prong
 twist lock type receptacle.  If there is a way I'd like to be educated
 (aside from pulling one of the hots and hooking the neutral to ground as
 well on my new non-code engineered power cable.  Educate me.

 I think I'm just going to plug it into the normal 120v 20amp plug on the
 wall behind the rack though, seems like the best way forward considering
 the options I was just trying to accommodate the customers request prior to
 plan B.

 Thanks

 Scott Carullo
 Technical Operations
 855-FLSPEED x102


 --
 *From*: TJ Trout t...@voltbb.com
 *Sent*: Wednesday, November 05, 2014 3:21 PM
 *To*: WISPA General List wireless@wispa.org
 *Subject*: Re: [WISPA] Off topic sorta power question


 Everything can use 240 now days probably just need a new power cord
 On Nov 5, 2014 12:10 PM, Bob M lakel...@gbcx.net wrote:

  Keep in mind that it is breakered for 240.  Splitting the legs after a
 240 vac  circuit breaker is not code.


  Sent from my Verizon Wireless 4G LTE smartphone



  Original message 
 From: Brett Woollum br...@tekify.com
 Date:11/05/2014 12:00 PM (GMT-05:00)
 To: WISPA General List wireless@wispa.org
 Subject: Re: [WISPA] Off topic sorta power question

 Tim,

 In most cases you can split the hot leads on the 240v outlet into two
 120v circuits. There are adapter pigtails for this if you don't want to
 hardware it.

 From memory, our local hardware store sells these (in the US).

 A quick Google search revealed this:
 http://www.wayfair.com/Champion-Power-Equipment-Generator-Y-Adapter-for-Champion-Power-Equipment-48035-L771-K~CXP1067.html?refid=GX50899353420-CXP1067device=cptid=75696510540gclid=CJ_Fktv348ECFUdffgod3z4ANw

 Brett Woollum
 Senior Sales Engineer
 br...@tekify.com

 *Tekify Broadband Internet Services*
 Web: http://www.tekify.com
 Phone: 510-266-5800, ext 6200
  --
 *From: *Tim Way t...@way.vg
 *To: *sc...@brevardwireless.com, WISPA General List wireless@wispa.org
 
 *Sent: *Wednesday, November 5, 2014 7:50:52 AM
 *Subject: *Re: [WISPA] Off topic sorta power question

 I would think something like this might be the safer option:
 http://www.certifiedmtp.com/step-up-step-down-transformer-500w/?gclid=CNWj1Kro48ECFQipaQodB74ADQ

 That said I'm not an electrician and I think that question might be best
 answered by one.

 Tim Way

 On Wed, Nov 5, 2014 at 9:38 AM, Scott Carullo sc...@brevardwireless.com
 wrote:

 I need to place a 120v normal 1U router in a rack that only has 240v
 twist lock receptacles available for power.  I need to put a UPS there so I
 just looked for a 240v UPS with the right plugs but because they are made
 for a lot larger load they were way bigger (and more expensive) than what I
 was looking for.  SO...  anyone have a better way to do this?  I have
 considered taking one leg and bonding the neutral and ground, but.

 Thanks

 Scott Carullo
 Technical Operations
 855-FLSPEED x102


 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless



 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless

 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless



 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless


___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless