Re: Measurement uncertainties for voltage measurement

2003-09-24 Thread John Woodgate

I read in !emc-pstc that Gordon,Ian ian.gor...@bocedwards.com wrote
(in E1BA0362B28ED211A1E80008C71EA3060206FDB3@z-
160-100-30-252.est.ibm.com) about 'Measurement uncertainties for
voltage measurement' on Wed, 24 Sep 2003:
All measurements are less than 15V DC.

How much less and to how many significant figures? If this is DC, the
only obscure source of uncertainty that springs to mind is
thermoelectric voltage, which may be tens of microvolts.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Measurement uncertainties for voltage measurement

2003-09-24 Thread drcuthb...@micron.com

Ian,

I am assuming you are connecting the reference source to the calibrated meter
and to the meter to be calibrated (DUT). I am also assuming that the reference
is a variable voltage source covering the range you need to calibrate. Draw a
diagram of the system and there and list the parts and the errors. Some errors
will be systematic (known) and other errors are random. Errors:

reference source, meter, leads, added noise, and temperature, time.

Depending on what has a lower traceable uncertainty, the source or the meter,
the calibration uncertainty will revolve around that piece. Say the source is
not traceable but the meter is. Then the starting point is the uncertainty of
the meter. This is a random error. The leads affect the measurement in a
systematic way. There is the voltage drop and a thermally generated offset
voltage. The voltage drop of the leads will most likely be in the nanovolt
range. Since this is a systematic error you can add or subtract it from your
measurement as needed. Same thing with the thermal voltage- this will be in
the tens of microvolt range. Unless you are calibrating a 6-1/2 digit meter at
low voltages your calibration uncertainty becomes the uncertainty of the
calibrated meter. Is the lab in the temperature range in which the calibrated
meter spec is valid? The next part is what is the confidence level of your
calibration? Most meters do not specify if the spec is for 2 sigma, 3 sigm!
 a or what. Fluke for example, uses 2.6 sigma. So if they say the accuracy is
0.0026% then the one-sigma accuracy is 0.001%.

Now you need to decide if you need a guardband. The rule-of-thumb is if the
measurement equipment spec exceeds the spec of the gear being measured by 4X
(4:1 TUR) then no guardband is needed. If you don't have a 4:1 TUR (Test
Uncertainty Ratio) you can still do the cal but you will need guardbands. 

But enough rambling. Here is a link that says it better than I can:
http://metrologyforum.tm.agilent.com/uncert.shtml


   Dave Cuthbert
   Micron Technology 


From: Gordon,Ian [mailto:ian.gor...@bocedwards.com]
Sent: Wednesday, September 24, 2003 9:44 AM
To: 'IEEE EMC-PSTC GROUP'
Subject: Measurement uncertainties for voltage measurement



Everyone,
This may seem to be a little out of the groups remit but someone may have
had experience of this.
I am trying to determine the measurement uncertainty associated with
calibrating an instrument which is essentially a voltmeter. This is done
using a reference voltage source and a second, calibrated voltmeter. Does
anyone have any suggestions as to possible sources of uncertainty of
measurement in this arrangement? Ideally, someone will know of an on-line
spreadsheet which I may use.
All measurements are less than 15V DC.

Thanks
Ian Gordon

_
This e-mail has been scanned for viruses by MCI's Internet Managed Scanning
Services - powered by MessageLabs. For further information visit
http://www.mci.com


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Ethernet transformer that meets 60950 basic insulation requirements

2003-09-24 Thread douglas_beckw...@mitel.com

Hi
 Someone on the list was asking a week or so ago about an ethernet
 transformer that meets the 60950 basic insulation requirements.
 Forgive me, my brain is little and I forgot who. I have the
 information on the part, so whoever it was, please email me and I will
 send it to you.

 Regards

 Doug Beckwith
 Mitel Networks




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Measurement uncertainties for voltage measurement

2003-09-24 Thread Gordon,Ian

Everyone,
This may seem to be a little out of the groups remit but someone may have
had experience of this.
I am trying to determine the measurement uncertainty associated with
calibrating an instrument which is essentially a voltmeter. This is done
using a reference voltage source and a second, calibrated voltmeter. Does
anyone have any suggestions as to possible sources of uncertainty of
measurement in this arrangement? Ideally, someone will know of an on-line
spreadsheet which I may use.
All measurements are less than 15V DC.

Thanks
Ian Gordon

_
This e-mail has been scanned for viruses by MCI's Internet Managed Scanning
Services - powered by MessageLabs. For further information visit
http://www.mci.com


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: DC PSU for conducted immunity testing to EN61000-4-6

2003-09-24 Thread Ken Javor

Why not build an unregulated linear power supply out of parts from Radio
Shack?  Or buy a cheap 12 Volt lead-acid battery 1 or 2 Amp trickle charger
and put a filter cap on the output.

As long as it is unregulated, it should not respond in any anomalous fashion
to EMI.

 From: Chris Chileshe chris.chile...@ultronics.com
 Reply-To: Chris Chileshe chris.chile...@ultronics.com
 Date: Wed, 24 Sep 2003 09:33:29 +0100
 To: emc-p...@majordomo.ieee.org emc-p...@majordomo.ieee.org
 Subject: DC PSU for conducted immunity testing to EN61000-4-6
 
 
 Group,
 
 After quite a struggle to get a product through conducted immunity
 tests (clamp method), I finally discovered that the weak link in the
 chain was in fact my laboratory power supply which I have been
 taking along with me to a nearby test house.
 
 The problem remained undetected for a number of reasons, not
 least that I had used the same setup before at a different test
 house using their PSU ( Solartron ASxxx) and had better results,
 but mostly because we were using a small chamber dedicated to
 conducted immunity tests and using a camera to monitor the
 behaviour of the EUT behind closed doors and not keeping an eye
 on the PSU.  
 
 When we eventually tracked the anomalous behaviour of the
 EUT to the PSU, we tried LISNs and a different PSU both of
 which improved the test results significantly but the outcome
 was still not good enough from a product compliance point of
 view. 
 
 Question 1: Is anyone aware of a power supply suitable for
 this type of testing? The EUT draws a maximum of 30mA
 at 12VDC. I have been unable to find any Solartron PSUs on
 the web; probably long discontinued.
 
 Question 2: Has anyone tried to build a filter for this sort of
 thing and would this be the way to go?
 
 Best regards
 
 - Chris Chileshe
 - Ultronics Ltd
 - UK
 
 (O.O.O.)
 
 
 
 
 This e-mail has been scanned for all viruses by Star Internet. The
 service is powered by MessageLabs. For more information on a proactive
 anti-virus service working around the clock, around the globe, visit:
 http://www.star.net.uk
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
 majord...@ieee.org
 with the single line:
 unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com
 
 For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org
 
 Archive is being moved, we will announce when it is back on-line.
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieeecommunities.org/emc-pstc
 



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Safety Standards Comparison

2003-09-24 Thread Doug Massey
Hi Reg -

60950, in its various forms, is the safety standard for Information Technology
Equipment. IEC 60950 = 'root' standard. UL60950 = IEC 60950 + US / Canadian
national differences. EN 60950 = IEC 60950 + national deviations of all
EU/EFTA countries.

IEC 60529 is a standard for determining the relative environmental protection
offered by electrical enclosures. This is not a Taiwanese national standard,
although it is accepted in Taiwan, when appropriate. IEC 60529 lays out the
verification test methods for assigning an 'IP Code' - IP standing for Ingress
Protection, and meaning the degree of protection against the ingress of solid
objects and water.

The two have nothing in common, really; however, both can apply to any
particular product. For example, if your Information Technology Equipment
product is to be used out-of-doors, it should have a minimum IP rating of
IPx4, meaning that the enclosure protects the internal electronics from
exposure to water splashed against the enclosure from any direction. 60950
Annex T refers to IEC 60529 for guidance on the protection against ingress of
water.

IEC stands for International Electrotechnical Commission. The International
Electrotechnical Commission (IEC) is the leading global organization that
prepares and publishes international standards for all electrical, electronic
and related technologies. IEC standards are often adopted as national
standards.

Best regards,

Doug Massey

Product Safety Engineer

Advanced Compliance Solutions

Ph. (770) 831-8048

FAX (770) 831-8598

Visit our web home at http://www.acstestlab.com


From: owner-emc-p...@majordomo.ieee.org [
mailto:owner-emc-p...@majordomo.ieee.org] On Behalf Of Reginald Henry
Sent: Wednesday, September 24, 2003 8:34 AM
To: emc-p...@majordomo.ieee.org
Subject: Safety Standards Comparison


Group,

SAFETY: EN60950 vs. IEC60529 (Taiwan ) standard.

Has anyone here worked with these two standards enough to give me  the

basic differences and similarities between the two ?


Thanks in advance 


Reg Henry




This message is from the IEEE EMC Society Product Safety

Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:

 majord...@ieee.org

with the single line:

 unsubscribe emc-pstc

For help, send mail to the list administrators:

 Ron Pickard:  emc-p...@hypercom.com

 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:

 Richard Nute:   ri...@ieee.org

 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc




Re: DC PSU for conducted immunity testing to EN61000-4-6

2003-09-24 Thread John Woodgate

I read in !emc-pstc that Chris Chileshe chris.chile...@ultronics.com
wrote (in 01c3827e.ebde2400.chris.chile...@ultronics.com) about 'DC
PSU for conducted immunity testing to EN61000-4-6' on Wed, 24 Sep 2003:

Question 1: Is anyone aware of a power supply suitable for this type of 
testing? The EUT draws a maximum of 30mA at 12VDC. I have been unable to 
find any Solartron PSUs on the web; probably long discontinued.

I'm not surprised. The AS series had germanium transistors, I think.

Question 2: Has anyone tried to build a filter for this sort of thing 
and would this be the way to go? 

What effect did the power supply have on the immunity? It's difficult to
know with no data what a simple analog power supply would do. One would
certainly need to know that in order to determine whether a filter was
feasible and the optimum solution.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Safety Standards Comparison

2003-09-24 Thread Reginald Henry

Group,

Thank you all for the information.

I got it !

RH


From: Sam Davis [mailto:sda...@ptitest.com]
Sent: Wednesday, September 24, 2003 10:24 AM
To: Reginald Henry; emc-p...@majordomo.ieee.org
Subject: RE: Safety Standards Comparison


60950 (IEC or EN) is a safety standard for Information Technology Equipment
(ITE).  It is the standard for evaluation of a piece of ITE equipment for
electric shock, energy hazards, fire hazards, radiation hazards, chemical
hazards, and mechanical hazards.

60529 (IEC or EN) is the ingress protection standard.  It is a test standard
which enclosures are tested for the extent to which they protect against
personnel access, dust access, and water access in various environmental
conditions.

They are not comparable, they are complementary.  Say you've got an outdoor
computer.  The outdoor concerns, such as rain and dust, could be evaluated
to 60529, where the electrical safety concerns inherent to computers (shock,
fire, etc.) would be evaluated to 60950.

Hope this helps.
Sam
---
Sam Davis
Product Safety Engineer
Professional Testing Inc.
(512)244-3371 x112
www.ptitest.com



From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Reginald Henry
Sent: Wednesday, September 24, 2003 8:34 AM
To: emc-p...@majordomo.ieee.org
Subject: Safety Standards Comparison



Group,

SAFETY: EN60950 vs. IEC60529 (Taiwan ) standard.

Has anyone here worked with these two standards enough to give me  the
basic differences and similarities between the two ?


Thanks in advance


Reg Henry



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Safety Standards Comparison

2003-09-24 Thread Sam Davis

60950 (IEC or EN) is a safety standard for Information Technology Equipment
(ITE).  It is the standard for evaluation of a piece of ITE equipment for
electric shock, energy hazards, fire hazards, radiation hazards, chemical
hazards, and mechanical hazards.

60529 (IEC or EN) is the ingress protection standard.  It is a test standard
which enclosures are tested for the extent to which they protect against
personnel access, dust access, and water access in various environmental
conditions.

They are not comparable, they are complementary.  Say you've got an outdoor
computer.  The outdoor concerns, such as rain and dust, could be evaluated
to 60529, where the electrical safety concerns inherent to computers (shock,
fire, etc.) would be evaluated to 60950.

Hope this helps.
Sam
---
Sam Davis
Product Safety Engineer
Professional Testing Inc.
(512)244-3371 x112
www.ptitest.com



From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Reginald Henry
Sent: Wednesday, September 24, 2003 8:34 AM
To: emc-p...@majordomo.ieee.org
Subject: Safety Standards Comparison



Group,

SAFETY: EN60950 vs. IEC60529 (Taiwan ) standard.

Has anyone here worked with these two standards enough to give me  the
basic differences and similarities between the two ?


Thanks in advance


Reg Henry



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: generic standards and competent bodies

2003-09-24 Thread Ing. Gert Gremmen

Hi Miquel,

Basically you can use the self-certification route with
all 


From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Miguel Abrahams
Sent: Wednesday, September 24, 2003 2:35 PM
To: emc-p...@majordomo.ieee.org
Subject: generic standards and competent bodies



Hello group,

When you are testing according to generic standards, can the
self-certification route be taken, or does a competent bodies needs to be
involved?

Thanks,

Miguel Abrahams
CAE Inc.





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: generic standards and competent bodies

2003-09-24 Thread Ing. Gert Gremmen

Hi Miguel

Yes, all standards listed in the OJ list of
harmonized standards qualify for self certification.

That includes all generic standards.
You may download a list on many sites among ours.

Self certification also includes signing a liability
declaration and of course is no easy way to obtain
a EC Declaration of Conformity.

A NB or CB  or ordinary EMC lab might 
help you in selecting cheaper
ways of testing, and prevent you to invest 
large to huge amounts in test equipment and experience.



Regards,
 
Gert Gremmen
Approvals manager
==
ce-test, qualified testing
Member of EMC committee CENELEC/IEC

+ Independent Consultancy Services
+ Compliance Testing and Design for CE
+ Improvement of product quality and reliability
+ Testing services according to:
  Electro magnetic Compatibility 89/336/EC
  Electrical Safety   73/23/EC
  Medical Devices 93/42/EC
  Radio  Telecommunication Terminal equipment 99/5/EC

Website:  www.cetest.nl

Phone :  +31 10 415 24 26
Fax :+31 10 415 49 53
==
 
 



From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Miguel Abrahams
Sent: Wednesday, September 24, 2003 2:35 PM
To: emc-p...@majordomo.ieee.org
Subject: generic standards and competent bodies



Hello group,

When you are testing according to generic standards, can the
self-certification route be taken, or does a competent bodies needs to be
involved?

Thanks,

Miguel Abrahams
CAE Inc.





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Safety Standards Comparison

2003-09-24 Thread Peter L. Tarver

Reg -

60950 is a product safety standard for ITE

60529 is an ingress protection reference standard for
outdoor use equipment/enclosures


Regards,

Peter L. Tarver, PE
Product Safety Manager
Homologation Services
Sanmina-SCI Corp.
San Jose, CA
peter.tar...@sanmina-sci.com


 From: Reginald Henry
 Sent: Wednesday, September 24, 2003 6:34 AM

 Group,

 SAFETY:   EN60950 vs. IEC60529 (Taiwan ) standard.

 Has anyone here worked with these two standards
 enough to give me  the
 basic differences and similarities between the two ?


 Thanks in advance


 Reg Henry




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Safety Standards Comparison

2003-09-24 Thread Reginald Henry

Group,

SAFETY: EN60950 vs. IEC60529 (Taiwan ) standard.

Has anyone here worked with these two standards enough to give me  the
basic differences and similarities between the two ?


Thanks in advance 


Reg Henry



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: DC PSU for conducted immunity testing to EN61000-4-6

2003-09-24 Thread Chris Chileshe

Group

After reading Ray's reply, I realise I had written LISN instead
of CDN. Kindly replace LISN with CDN in my original posting.

Rgds



From:   r...@rpgarner.freeserve.co.uk [SMTP:r...@rpgarner.freeserve.co.uk]
Sent:   Wednesday, September 24, 2003 1:39 PM
To: Chris Chileshe; emc-p...@majordomo.ieee.org
Subject:Re: DC PSU for conducted immunity testing to EN61000-4-6

Chris,
I would suggest you need to change your test house. A good test house would 
already have power supplies available fed via filters to the test bench. 
 They would also have ambient measurement information available to proof 
that their power supply was suitable for testing.  I am also somewhat 
surprised that you make no reference to an ambient test having been 
performed on your set up.
Also contrary to popular belief LISNs are not filters they only purpose is 
to provide a known impedance.
I have in the past seen test houses cause more problems than they solve by 
not checking or using correct test set ups.

Ray Garner
EMC Consultant WRSL




Message date : Sep 24 2003, 12:19 PM
From : Chris Chileshe
To : emc-p...@majordomo.ieee.org
Copy to :
Subject : DC PSU for conducted immunity testing to EN61000-4-6

Group,

After quite a struggle to get a product through conducted immunity
tests (clamp method), I finally discovered that the weak link in the
chain was in fact my laboratory power supply which I have been
taking along with me to a nearby test house.

The problem remained undetected for a number of reasons, not
least that I had used the same setup before at a different test
house using their PSU ( Solartron ASxxx) and had better results,
but mostly because we were using a small chamber dedicated to
conducted immunity tests and using a camera to monitor the
behaviour of the EUT behind closed doors and not keeping an eye
on the PSU.

When we eventually tracked the anomalous behaviour of the
EUT to the PSU, we tried LISNs and a different PSU both of
which improved the test results significantly but the outcome
was still not good enough from a product compliance point of
view.

Question 1: Is anyone aware of a power supply suitable for
this type of testing? The EUT draws a maximum of 30mA
at 12VDC. I have been unable to find any Solartron PSUs on
the web; probably long discontinued.

Question 2: Has anyone tried to build a filter for this sort of
thing and would this be the way to go?

Best regards

- Chris Chileshe
- Ultronics Ltd
- UK

(O.O.O.)




This e-mail has been scanned for all viruses by Star Internet. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard: emc-p...@hypercom.com
Dave Heald: emc_p...@symbol.com

For policy questions, send mail to:
Richard Nute: ri...@ieee.org
Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This e-mail has been scanned for all viruses by Star Internet. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk
  
File: ATT00011.htm  


This e-mail has been scanned for all viruses by Star Internet. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:

Re: DC PSU for conducted immunity testing to EN61000-4-6

2003-09-24 Thread r...@rpgarner.freeserve.co.uk
Chris,

I would suggest you need to change your test house. A good test house would
already have power supplies available fed via filters to the test bench.  They
would also have ambient measurement information available to proof that their
power supply was suitable for testing.  I am also somewhat surprised that you
make no reference to an ambient test having been performed on your set up.
Also contrary to popular belief LISNs are not filters they only purpose is to
provide a known impedance.

I have in the past seen test houses cause more problems than they solve by not
checking or using correct test set ups.

 

Ray Garner

EMC Consultant WRSL




 

Message date : Sep 24 2003, 12:19 PM 
From : Chris Chileshe 
To : emc-p...@majordomo.ieee.org 
Copy to : 
Subject : DC PSU for conducted immunity testing to EN61000-4-6 

Group, 

After quite a struggle to get a product through conducted immunity 
tests (clamp method), I finally discovered that the weak link in the 
chain was in fact my laboratory power supply which I have been 
taking along with me to a nearby test house. 

The problem remained undetected for a number of reasons, not 
least that I had used the same setup before at a different test 
house using their PSU ( Solartron ASxxx) and had better results, 
but mostly because we were using a small chamber dedicated to 
conducted immunity tests and using a camera to monitor the 
behaviour of the EUT behind closed doors and not keeping an eye 
on the PSU. 

When we eventually tracked the anomalous behaviour of the 
EUT to the PSU, we tried LISNs and a different PSU both of 
which improved the test results significantly but the outcome 
was still not good enough from a product compliance point of 
view. 

Question 1: Is anyone aware of a power supply suitable for 
this type of testing? The EUT draws a maximum of 30mA 
at 12VDC. I have been unable to find any Solartron PSUs on 
the web; probably long discontinued. 

Question 2: Has anyone tried to build a filter for this sort of 
thing and would this be the way to go? 

Best regards 

- Chris Chileshe 
- Ultronics Ltd 
- UK 

(O.O.O.) 



 
This e-mail has been scanned for all viruses by Star Internet. The 
service is powered by MessageLabs. For more information on a proactive 
anti-virus service working around the clock, around the globe, visit: 
http://www.star.net.uk 
 

--- 
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list. 

Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ 

To cancel your subscription, send mail to: 
majord...@ieee.org 
with the single line: 
unsubscribe emc-pstc 

For help, send mail to the list administrators: 
Ron Pickard: emc-p...@hypercom.com 
Dave Heald: emc_p...@symbol.com 

For policy questions, send mail to: 
Richard Nute: ri...@ieee.org 
Jim Bacher: j.bac...@ieee.org 

Archive is being moved, we will announce when it is back on-line. 
All emc-pstc postings are archived and searchable on the web at: 
http://www.ieeecommunities.org/emc-pstc 






generic standards and competent bodies

2003-09-24 Thread Miguel Abrahams

Hello group,

When you are testing according to generic standards, can the
self-certification route be taken, or does a competent bodies needs to be
involved?

Thanks,

Miguel Abrahams
CAE Inc.





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: DC PSU for conducted immunity testing to EN61000-4-6

2003-09-24 Thread Ing. Gert Gremmen

Hi Chris,

The power supply definitely should be decoupled by a standard CDN (f.a.
CDN-T2)
in order to couple the RF current from the calmp to ground.
Then any standard power supply will probably do the job.
This is exactly one of the major drawback (apart from needing higher power
amps)
that goes with the application of the EM-clamp.
You might opt for  CDN's for all cables to get better results
on all tests. Note that the new EN 61000-4-6 allows for
using only 2 CDN at a time.




Regards,

Gert Gremmen
Approvals manager
==
ce-test, qualified testing
Member of EMC committee CENELEC/IEC

+ Independent Consultancy Services
+ Compliance Testing and Design for CE
+ Improvement of product quality and reliability
+ Testing services according to:
  Electro magnetic Compatibility 89/336/EC
  Electrical Safety   73/23/EC
  Medical Devices 93/42/EC
  Radio  Telecommunication Terminal equipment 99/5/EC

Website:  www.ce-test.nl
Phone :  +31 10 415 24 26
Fax :+31 10 415 49 53
==




From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Chris Chileshe
Sent: Wednesday, September 24, 2003 10:33 AM
To: emc-p...@majordomo.ieee.org
Subject: DC PSU for conducted immunity testing to EN61000-4-6



Group,

After quite a struggle to get a product through conducted immunity
tests (clamp method), I finally discovered that the weak link in the
chain was in fact my laboratory power supply which I have been
taking along with me to a nearby test house.

The problem remained undetected for a number of reasons, not
least that I had used the same setup before at a different test
house using their PSU ( Solartron ASxxx) and had better results,
but mostly because we were using a small chamber dedicated to
conducted immunity tests and using a camera to monitor the
behaviour of the EUT behind closed doors and not keeping an eye
on the PSU.

When we eventually tracked the anomalous behaviour of the
EUT to the PSU, we tried LISNs and a different PSU both of
which improved the test results significantly but the outcome
was still not good enough from a product compliance point of
view.

Question 1: Is anyone aware of a power supply suitable for
this type of testing? The EUT draws a maximum of 30mA
at 12VDC. I have been unable to find any Solartron PSUs on
the web; probably long discontinued.

Question 2: Has anyone tried to build a filter for this sort of
thing and would this be the way to go?

Best regards

- Chris Chileshe
- Ultronics Ltd
- UK

(O.O.O.)




This e-mail has been scanned for all viruses by Star Internet. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Country Homologation Requirements for .......

2003-09-24 Thread Collins, Jeffrey


 Group,
 
 I'm looking for your opinion on telecommunication requirements for the
following countries. Specifically, this is in reference to the following types
of telecom gear:  -48VDC, No PSTN connection, normally found in Central
Office locations
 As this information seems to be vague or contradictory depending on the
source, all comments on any of these countries are appreciated.
 
 
 Saudi Arabia
 EMC -
 Safety- 
 Network Access License-
 Telecom Testing-
 In Country Testing -
 
 India
 EMC -
 Safety- 
 Network Access License-
 Telecom Testing-
 In Country Testing -
 
 United Arab Emerites ( UAE)
 EMC -
 Safety- 
 Network Access License-
 Telecom Testing-
 In Country Testing -
 
 Pakistan
 EMC -
 Safety- 
 Network Access License-
 Telecom Testing-
 In Country Testing -
 
 Sri Lanka
 EMC -
 Safety- 
 Network Access License-
 Telecom Testing-
 In Country Testing -
 
 Bangladesh
 EMC -
 Safety- 
 Network Access License-
 Telecom Testing-
 In Country Testing -
 
 Malaysia
 EMC -
 Safety- 
 Network Access License-
 Telecom Testing-
 In Country Testing -
 
 Egypt
 EMC -
 Safety- 
 Network Access License-
 Telecom Testing-
 In Country Testing -
 
 Tunisia
 EMC -
 Safety- 
 Network Access License-
 Telecom Testing-
 In Country Testing -
 
 Thailand
 EMC -
 Safety- 
 Network Access License-
 Telecom Testing-
 In Country Testing -
 
 Russia
 EMC -
 Safety- 
 Network Access License-
 Telecom Testing-
 In Country Testing -
 
 Estonia
 EMC -
 Safety- 
 Network Access License-
 Telecom Testing-
 In Country Testing -
 
 Lithuania
 EMC -
 Safety- 
 Network Access License-
 Telecom Testing-
 In Country Testing -
 
 Latvia
 EMC -
 Safety- 
 Network Access License-
 Telecom Testing-
 In Country Testing -
 
 Poland
 EMC -
 Safety- 
 Network Access License-
 Telecom Testing-
 In Country Testing -
 
 
 Regards,
 
   Jeffrey Collins 
   Sr. HW Engineering Manager 
   Corporate Compliance  Homologations
   CIENA  Corporation
   5965 Silver Creek Valley Rd. 
   San Jose, CA. 95138
   (408) 571-3002, Fax (408) 965-2705
   jcoll...@ciena.com
   www.ciena.com
 
 


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re:

2003-09-24 Thread John Woodgate

I read in !emc-pstc that Lothar Schmidt lothar.schm...@cetecomusa.com
wrote (in 5EFB06767D7DD211828C0008C74CE95BEB7C68@calvin) about '' on
Tue, 23 Sep 2003:

The standard is not harmonized yet, but recently published.

ALL ENs are identical in all CENELEC countries, which is the real,
original meaning of 'harmonization'. I suspect you mean it has not been
*notified* in the Official Journal yet.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Arcing Sparking

2003-09-24 Thread Speakman, Jim

Fellow Listers,

Many thanks to all those that responded to my query on arcing and sparking.
I now have a much better appreciation of the difference.  All of your
answers will be passed to the original design review team from whence the
query came.

Cheers

Jim

__
Jim Speakman
(Design Safety Representative (Southern Sites)

Thales Defence Ltd
Thales Sensors 
Manor Royal
Crawley
West Sussex
RH10 9PZ


 * Tel:+44(0)1293 644911
 * Mob:+44(0)7968 529439
 *  Fax :  +44(0)1293 644194
 *e-mail   jim.speak...@uk.thalesgroup.com
 
__
This e-mail contains confidential information for the addressee only.  If a
transmission error has misdirected this e-mail, please notify us on
+44(0)1293 644911 and delete it and all copies from your system.  You should
not use, disclose, distribute or copy this communication if received in
error.



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



DC PSU for conducted immunity testing to EN61000-4-6

2003-09-24 Thread Chris Chileshe

Group,

After quite a struggle to get a product through conducted immunity
tests (clamp method), I finally discovered that the weak link in the 
chain was in fact my laboratory power supply which I have been 
taking along with me to a nearby test house.

The problem remained undetected for a number of reasons, not 
least that I had used the same setup before at a different test 
house using their PSU ( Solartron ASxxx) and had better results, 
but mostly because we were using a small chamber dedicated to 
conducted immunity tests and using a camera to monitor the 
behaviour of the EUT behind closed doors and not keeping an eye 
on the PSU.  

When we eventually tracked the anomalous behaviour of the 
EUT to the PSU, we tried LISNs and a different PSU both of
which improved the test results significantly but the outcome 
was still not good enough from a product compliance point of 
view. 

Question 1: Is anyone aware of a power supply suitable for 
this type of testing? The EUT draws a maximum of 30mA
at 12VDC. I have been unable to find any Solartron PSUs on
the web; probably long discontinued.

Question 2: Has anyone tried to build a filter for this sort of
thing and would this be the way to go? 

Best regards

- Chris Chileshe
- Ultronics Ltd
- UK

(O.O.O.)




This e-mail has been scanned for all viruses by Star Internet. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Measurement of touch current

2003-09-24 Thread Neil Helsby

I am not into 3-phase but from my long ago college days I would see no 
reason for the star to star not being correct and I guess that the 
critical factor is the star isolating transformer. I would also agree 
with your transforms for different voltages / frequencies. You don't say 
which of the three measuring networks specified in EN 60990 that you 
intend to use, but that of Fig 4 is the same as that used in EN 60950 
which may, or may not, be a reason for selecting that version.
Checking the two standards, I find that of figure 5B in EN 60950 to be 
easier to understand, but as I have already mentioned, I'm not really 
familiar with 3-phase.
Regards,
Neil Helsby



**
This email and any files transmitted with it are confidential and
intended solely for the use of the individual or entity to whom they
are addressed. If you have received this email in error please notify
the system manager.

This footnote also confirms that this email message has been swept by
MIMEsweeper for the presence of computer viruses.

www.mimesweeper.com
**




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



TONIGHT - Chicago PSTC Meeting - CCC Chinese Compulsory Certification - THURS Sept 25th, 5:30pm for 6pm

2003-09-24 Thread Glyn Garside

Reminder:

Ken Thomas ktho...@productsafetyinc.com
08/15/2003 15:26
To: list
Subject: Chicago PSTC Meeting Announcement

Please  see  the attached for information on our next meeting.  Guests
are  welcome.   Please  ask any guest to RSVP so that we can make sure
we have enough seats and refreshments. Hope to see you there!

Check out our new web page at  http://ewh.ieee.org/r4/chicago/pstc/
(Thanks go out to Ron Borowski at QTI)

Best regards,

Ken Thomas
Chair - Chicago PSTC

IEEE's PRODUCT SAFETY TECHNICAL COMMITTEE -- CHICAGO CHAPTER
List-Post: emc-pstc@listserv.ieee.org
List-Post: emc-pstc@listserv.ieee.org
List-Post: emc-pstc@listserv.ieee.org
List-Post: emc-pstc@listserv.ieee.org
Date: Thursday, September 25, 2003

Place: TUV Rheinland of North America
1945 Techny Rd.,  Unit 4
Northbrook, IL 60062

Time: 5:30 - 7:30pm
Please let us know if you plan on attending so we can plan accordingly.
Visitors or new members are welcome to join us.
RSVP:   Ken Thomas  - 630/238-0188 (cell - 630-330-3525)
mailto:ktho...@productsafetyinc.com

Agenda Items
   1. Review of Meeting Minutes from Previous Meeting
   2. New Issues/Concerns
   3. Chicago PSTC Web Site
   4. Presentation -- See description below.
  Presentation starts at 6:00PM.

Presentation: CCC -- Chinese Compulsory Certification

As  of  Aug 1, 2003 of this year a new Compulsory Certification system
was  implemented  in China.This system will be reviewed and topics
covered  will  include identification of which products are  affected,
the  process  to  obtain certification,  the  Agent Role in CCC  cert-
ification  and  the  Organization  and Structure behind  CCC  and  its
adoption.

Presenter: Jonathan Kotrba -- TUV Rheinland N.A.

Jonathan  has 13 years experience in the product safety field  working
for Underwriters Laboratories and TUV Rheinland.   He is presently  an
Engineering Group Leader for TUV Rheinland  and has recently served as
International Certification Manager for TUV Rheinland of North America.

Jonathan  assists  applicants  obtain  world-wide  certifications  and
approvals  for  their products, while advancing TUV Rheinland of North
America's  accreditation  and  certification  programs.   In addition,
Jonathan  serves on several working groups within the CB scheme and is
a  Peer  Assessor  for  the  IECEE.   Jonathan's  most recent speaking
engagements  regarding  Chinese Compulsory Certification occurred this
year  with  the  US Department of Commerce  in  Illinois,  Indiana and
Wisconsin.


Special  thanks  to TUV Rheinland of North America  for sponsoring the
meeting site and Intertek Testing Services for sponsoring the evening's
refreshments.





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc