RE: Australian power cable requirements.

2001-05-02 Thread Russell, Ray

Cameron,

I had a similar situation some time ago with an internal cable and it had to
do with the insulation thickness. The SJT cord was only rated 300V, and the
insulation thickness did not meet the European standard. We changed to a
600V cord, which was accepted.

Ray Russell
r...@gastmfg.com

-Original Message-
From: Cameron O'phee [mailto:O'p...@ali.com.au]
Sent: Tuesday, May 01, 2001 8:23 PM
To: 'EMC - PSTC Forum'
Subject: Australian power cable requirements.



Hi All,

I have a situation where the test house I normally use for safety will
accept SJT cordage for an internal power cable but a different test house
will not.  The power cable conducts 240v from one power supply to another,
with both supplies internal to the machine. The second test house insists
that the cordage must be H05VVF.  Consequentely, I would like to know the
difference in requirements between the US SJT cordage and European H05VVF.

Regards,

Cameron O'Phee.
EMC  Safety Precompliance.
Aristocrat Technologies Australia.


Telephone   : +61 2  9697 4420
Facsimile   : +61 2  9663 1412
Mobile   :  0418 464 016



--
CONFIDENTIALITY NOTICE
--
This email is intended only to be read or used by the addressee.
The information contained in this e-mail message may be confidential
information. If you are not the intended recipient, any use, interference
with, distribution, disclosure or copying of this material is unauthorised
and prohibited. Confidentiality attached to this communication is not waived
or lost by reason of the mistaken delivery to you.

If you have received this message in error, please delete it and notify us
by return e-mail or telephone Aristocrat Technologies Australia Pty Limited
on +61 2 9413 6300.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




RE: UL listing for foreign manufacturers

2001-02-22 Thread Russell, Ray

Chris,

UL has offices all over the world. In Europe they now own DEMKO, so if you
are close to Denmark that may help. It would be good to check with UL to
find out where the closest follow up office is located. They charge for
their time to travel to your location. We have a manufacturer in the
Philippines. The quarterly inspection is at least $750. That's a big chunk
of money to add to one product. Now they also have annual fees for each
location. You can find the UL offices at their website wwwul.com

Ray Russell

ray_russ...@gastmfg.com

-Original Message-
From: Chris Maxwell [mailto:chris.maxw...@gnnettest.com]
Sent: Wednesday, February 21, 2001 3:46 PM
To: 'EMC-PSTC Internet Forum'
Subject: UL listing for foreign manufacturers



Hi all,

Quick question.

We have a sister company interested in UL listing a product.  Their
manufacturing facility is in Europe.

How are quarterly audits handled for companies outside of the US?  Will they
need to pay for UL personnel to fly to their plant for audits?  Does UL have
agents in certain countries that can perform the audits for them?  Can they
have a European agency certify their product to UL standards and perform the
audits?

Anybody out there been through this?

Chris Maxwell
Design Engineer
NetTest
6 Rhoads Drive, Building 4
Utica,NY 13502
email: chris.maxw...@gnnettest.com
phone:  315-266-5128
fax: 315-797-8024




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Coniferous Wood in Packaging

2000-10-10 Thread Russell, Ray

I'm sure that many of you, as well as myself, under the label of Regulatory
Compliance, receive many issues outside of Safety/EMC. Usually if it has an
acronym, involves a foreign country, falls under the heading of a regulatory
requirement, or sales/marketing don't know who can handle it, it lands on my
desk. Here is one  of those issues. We discussed it some time ago as it
applies to China, but it looks like Europe may take some action, and I
thought some of you may find this useful.

Ray Russell
ray_russ...@gastmfg.com



 NEW PUBLICATION NOTICE

 New publications this week:

 **
 RESTRICTIONS ON ENTRY OF NON-MANUFACTURED CONIFEROUS WOOD MAY BE ADOPTED
 (Business Alert - EU, Issue 20,2000)
 http://www.tdctrade.com/alert/eu0020.htm

 The EU has proposed to introduce emergency measures on non-manufactured
coniferous wood packing originated in China, Canada, Japan and the US to
prevent the spread of pine wood nematode, with effect likely from 1 January
2001.

 **
 We shall e-mail you an update on our newly released publications every
week.
 Should you wish to stop receiving this update, please click here to
unsubscribe.

(http://tpwebapp.tdctrade.com/dm/us.asp?email=swche...@gasthk.com.hktype=re
search)

 Hong Kong Trade Development Council
 4.10.2000


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: Overcurrent Protection: One or Both Sides?

2000-10-09 Thread Russell, Ray

Hi John,

I agree there are many different mains wiring configurations, I was merely
pointing out the case where I believe a 2 pole circuit breaker is required.
How do you handle 230V equipment marketed worldwide, that may encounter any
number of these configurations? 

Ray Russell
ray_russ...@gastmfg.com


-Original Message-
From: Wagner, John P (John) [mailto:johnwag...@avaya.com]
Sent: Monday, October 09, 2000 10:28 AM
To: 'brian_kunde'; emc-pstc; 'Russell, Ray'
Subject: RE: Overcurrent Protection: One or Both Sides?


I take some exception to the response below.

Single phase connections between phases either on a delta or wye system do
not have a neutral connection.
There are two grounded delta systems -- corner ground where one phase is
grounded, or center tapped ground on one of the phases (commonly called high
leg).  There are also variations of  the grounding scheme to allow for
impedance grounded systems where appropriate.

A standard two pole breaker os not designed, nor can it be used to interrupt
neutral.  For that, a special shunt trip braker is needed.

John P. Wagner
AVAYA Communication
11900 N. Pecos St, Room 2F58
Denver CO  80234
email:  johnwag...@avaya.com
phone:  303 538-4241
fax:  303 538-5211

 --
 From: Russell, Ray[SMTP:ray_russ...@gastmfg.com]
 Reply To: Russell, Ray
 Sent: Monday, October 09, 2000 5:15 AM
 To:   'brian_kunde'; emc-pstc
 Subject:  RE: Overcurrent Protection: One or Both Sides?
 
 
 Hi Brian,
 
 I see most of the return postings have focused on the UK, which has a
 terminated neutral system. There are several installations especially in
 the
 US, where the power could be derived from a delta, or unterminated neutral
 system. I believe in this case, overcurrent protection is required on both
 lines. In addition, the 2 pole circuit breaker method provides a suitable
 2
 pole disconnect. 
 
 Good Luck,
 
 Ray Russell
 ray_russ...@gastmfg.com
 
 -Original Message-
 From: brian_kunde [mailto:brian_ku...@leco.com]
 Sent: Friday, October 06, 2000 12:32 PM
 To: emc-pstc
 Subject: Overcurrent Protection: One or Both Sides?
 
 
 
 
 The issue of designing in Overcurrent Protection on one side or both sides
 of
 the AC mains keeps coming up.  We deal in Laboratory Equipment so the EN
 61010-1
 is the standard we use.  I'm not sure what EN60950 would say on the
 subject.
 
 The only area I have found that deals with this question is a NOTE in
 section
 9.6 of EN61010-1 which says, Overcurrent protection devices (e.g. fuses)
 should
 preferably be fitted in all supply conductors.
 
 This seems GRAY to me and I get beat up on it all the time.  I feel that
 overcurrent protection should be on all current carrying conductors.  With
 a
 230V~ product you never know where in the world the product will be
 shipped,
 if
 the AC Main has a grounded neutral, or if the receptacle is polarized.
 So,
 I
 feel you never know for sure which line or if both lines will be HOT in
 reference to Earth ground.
 
 If my thinking is correct, shouldn't ALL 230V~ products have overcurrent
 protection on both sides of the line?  I would think so, but I see
 products
 everyday that only have ONE side of the line fused.  My superiors feel
 that
 if
 others can get away with it, why can't we.  Why add the extra cost of
 double
 pole breakers or double fuse holders if it is not necessary?  
 
 Am I being too cautious or do I have a point?
 
 Thank you for your support and advice.
 
 Brian Kunde
 LECO Corp.
 
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Jim Bacher:  jim_bac...@mail.monarch.com
  Michael Garretson:pstc_ad...@garretson.org
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Jim Bacher:  jim_bac...@mail.monarch.com
  Michael Garretson:pstc_ad...@garretson.org
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
 
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad

RE: Overcurrent Protection: One or Both Sides?

2000-10-09 Thread Russell, Ray

Hi Brian,

I see most of the return postings have focused on the UK, which has a
terminated neutral system. There are several installations especially in the
US, where the power could be derived from a delta, or unterminated neutral
system. I believe in this case, overcurrent protection is required on both
lines. In addition, the 2 pole circuit breaker method provides a suitable 2
pole disconnect. 

Good Luck,

Ray Russell
ray_russ...@gastmfg.com

-Original Message-
From: brian_kunde [mailto:brian_ku...@leco.com]
Sent: Friday, October 06, 2000 12:32 PM
To: emc-pstc
Subject: Overcurrent Protection: One or Both Sides?




The issue of designing in Overcurrent Protection on one side or both sides
of
the AC mains keeps coming up.  We deal in Laboratory Equipment so the EN
61010-1
is the standard we use.  I'm not sure what EN60950 would say on the subject.

The only area I have found that deals with this question is a NOTE in
section
9.6 of EN61010-1 which says, Overcurrent protection devices (e.g. fuses)
should
preferably be fitted in all supply conductors.

This seems GRAY to me and I get beat up on it all the time.  I feel that
overcurrent protection should be on all current carrying conductors.  With a
230V~ product you never know where in the world the product will be shipped,
if
the AC Main has a grounded neutral, or if the receptacle is polarized.  So,
I
feel you never know for sure which line or if both lines will be HOT in
reference to Earth ground.

If my thinking is correct, shouldn't ALL 230V~ products have overcurrent
protection on both sides of the line?  I would think so, but I see products
everyday that only have ONE side of the line fused.  My superiors feel that
if
others can get away with it, why can't we.  Why add the extra cost of double
pole breakers or double fuse holders if it is not necessary?  

Am I being too cautious or do I have a point?

Thank you for your support and advice.

Brian Kunde
LECO Corp.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: product cert question

2000-08-03 Thread Russell, Ray

Hello Fabian,
 
The NRTL we deal with uses a scheme called a split inspection. We do the
submittal, and they will inspect at our suppliers facility. It's a little
tricky, but it does work. However, I would be concerned about the
possibility that the supplier does not have an NRTL listing, and may not
meet the product standard. I have suffered many delays due to a component
that does not have an approval, and is not discovered until the end of a
product cycle. This scenario has either caused redesign, or additional
testing at our costs.
 
Good Luck,
 
Ray Russell
ray_russ...@gastmfg.com mailto:ray_russ...@gastmfg.com 

-Original Message-
From: Spadaccini, Fabian [mailto:fspadacc...@tainst.com]
Sent: Thursday, August 03, 2000 11:47 AM
To: 'EMC-PSTC'
Subject: product cert question



Hello, Listmembers. 

We have a potential supplier of an OEM equipment that is not
NRTL listed. They suggested we have it listed (i. e. pay for the testing
ourselves) as part of  our system.  I am not aware of any case histories of
this nature.  Has anyone had this experience?  Can an NRTL issue a listing
for one company (buyer of product), yet audit another (the manufacturer)?  I
am skeptical of this suggestion. 

Regards, 
Fabian Spadaccini 
TA Instruments-Waters LLC 
(p) 302-427-4189 
(f) 302-427-4081 
fspadacc...@tainst.com 
www.tainst.com 


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Japan

2000-07-27 Thread Russell, Ray

Greetings,

I understand that according to Japan's Electrical Appliance and Material
Control Law there are 2 classes of products, A or B. A type are considered
more risky appliances, and require a mandatory approval for the T mark. B
items are considered less risky, and do not require the marking. What we
have run into is that a regular air compressor is considered a B type
appliance, where as if we put an electrical control box on it to control the
inflation of a consumer product, then I'm being told by one source it has to
be a type A. Is there a clear list or definition of these categories? I was
searching the Net for information on Dentori, but have not found any sites.
Do you know of any good sites on Dentori? I've already spoke with UL, and
they quoted a price to do determine the category, but I think this
information should be available somewhere.

Thanks for your assistance, 

Ray Russell
Regulatory Compliance Engineer


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: UL1950/UL2601 Thermals

2000-06-28 Thread Russell, Ray

Hi Dan,

We use UL 1450 Motor Operated Air Compressors, and here is the definition of
constant temperatures:

46.1.11 With reference to those tests that are to be continued until
constant temperatures are attained, thermal

equilibrium is considered to exist when three successive readings taken at
intervals of 10 percent of the previously

elapsed duration of the test, but not less than 5-minute intervals, indicate
no change.

Ray

-Original Message-
From: Joshua Wiseman [mailto:wiseman...@printronix.com]
Sent: Wednesday, June 28, 2000 2:39 PM
To: 'Dan Mitchell'; emc-p...@ieee.org
Subject: RE: UL1950/UL2601 Thermals



Regarding UL1950, IEC950, etc. I can't find proof either. Although I have
been told by several agencies the same thing 1 degree C over 15 minutes. I
too am curious to see this in writing.

Josh 

-Original Message- 
From: Dan Mitchell [ mailto:dan_mitch...@condordc.com
mailto:dan_mitch...@condordc.com ] 
Sent: Wednesday, June 28, 2000 8:32 AM 
To: emc-p...@ieee.org 
Subject: UL1950/UL2601 Thermals 



In UL2601 Clause 42.3.3) Duty Cycle - for Equipment for Continuous 
operation it lists 2 ways to conclude the test a) temperature of the 
windings stabilize and do not increase by more than 2 deg. C in 1 hr, or b) 
2.5 hr, which ever is shorter. 

UL1950 only states that; for continuous operation, until steady conditions 
are established.  I haven't been able to establish what is meant by 
Steady Conditions.  I was told once by a rep. of a large safety company 
that it meant no more than a 1 deg. C rise in 15 minute period.  However, 
since I can't find this written in the standard, I am a bit skeptical. 

If anybody has a good definition of Steady Conditions and can point it 
out to me in UL1950 or in the PAGs, I would appreciate it. 


Daniel W. Mitchell 
Product Safety Engineer 
Condor DC Power Supplies, Inc. 

P: (805) 486-4565 x323 
F: (805) 483-4307 




--- 
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list. 

To cancel your subscription, send mail to: 
 majord...@ieee.org 
with the single line: 
 unsubscribe emc-pstc 

For help, send mail to the list administrators: 
 Jim Bacher:  jim_bac...@mail.monarch.com 
 Michael Garretson:pstc_ad...@garretson.org 

For policy questions, send mail to: 
 Richard Nute:   ri...@ieee.org 


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: Temperature Meters

2000-06-22 Thread Russell, Ray

Hi Joe,

I've been using the Fluke Hydra Data Bucket for a couple of years, and
really like it. It is a little pricey but I think its worth it. It has 20
channels, and you can also configure each channel for volts or ohms. We have
added a current to voltage probe, so we can record the current too. It has
an alarm function that will trigger internally to scan, or an external relay
that we hooked to an audible alarm. 

Good Luck,

Ray

-Original Message-
From: Joe Finlayson [mailto:jfinlay...@telica.com]
Sent: Thursday, June 22, 2000 1:26 PM
To: 'EMC PSTC'
Subject: Temperature Meters



Hello Group,

I'm in the market for a multi-channel (12-15+, the more the better)
temperature meter and would appreciate some leads.  I found a model MTT-40
on the EDD web site that seems to fit my needs but would like to shop
around to see what's out there.  Any input regarding features with pro's and
cons would be greatly appreciated.  Could someone also explain the
differences between the options of glass braid and teflon thermocouple wire.
The only difference shown on the web site was the max temperature supported.

Thx,


Joe

*
 ... 

Joe Finlayson
Manager, Compliance Engineering
Telica, Inc.
734 Forest Street, Bldg. G, Suite 100
Marlboro, MA 01752
Tel:(508) 480-0909 x212
Fax:(508) 480-0922
Email:  jfinlay...@telica.com
Web:www.telica.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



EMC - Declaration of Incorporation?

2000-03-24 Thread Russell, Ray

Greetings,

We sell an air compressor with a DC motor. This motor requires a capacitor
across the DC supply lines to meet the EMC requirements. Of course
management does not want to supply the capacitor, they want to describe it
in the documentation, and add a note on the Declaration of Conformity that a
capacitor is required. Is this acceptable for European customers?

In that scenario, I would like to issue a Declaration of Incorporation, but
after reviewing the directives, I can only find a reference to the
Declaration of Incorporation in the Machinery Directive. Can this be used
for the other directives?

Thank you once again for your assistance,


Ray Russell
Regulatory Compliance Engineer


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: China Packaging/Crating Requirements

2000-01-19 Thread Russell, Ray

Greetings Martin,

It seems that there is a problem in the US and China with using Conifer
(pine) type of pallets. Here is a URL that goes into a little more detail

Ray

http://www.skralaw.com/Articles/china.htm

-Original Message-
From: marti...@pebio.com [mailto:marti...@pebio.com]
Sent: Sunday, January 16, 2000 10:20 PM
To: emc-p...@majordomo.ieee.org
Subject: China Packaging/Crating Requirements





Is anyone aware of any requirements in China on wood packaging/ crating
materials or special wood treatments required for crates or pallets?

All responses are appreciated.

Regards

Joe Martin
EMC/Product Safety Engineer
marti...@pebio.com



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



RE: Compressed Air. Pneumatics, Safety requirements

1999-11-29 Thread Russell, Ray

Greetings Israel,

A standard that we use is EN 1012-1 Compressors and Vacuum Pumps - Safety
Requirements. Depending on the size of the equipment, the Pressure Directive
or Pressure Equipment Directive may also apply. 

Regards,

Ray Russell

ray_russ...@gastmfg.com


-Original Message-
From: Israel Yeshurun [mailto:israel_yeshu...@stcl.scitex.com]
Sent: Monday, November 22, 1999 2:25 AM
To: 'emc-p...@ieee.org'
Subject: FW: Compressed Air. Pneumatics, Safety requirements





 -Original Message-
 From: Israel Yeshurun
 Subject:  Compressed Air. Pneumatics,  Safety requirements
 
 
Dear Group Members,
 
I would appreciate comments to the following:
 
  General:  In some equipment, Compressed Air is used to
 energize mechanical parts (in addition to electrical power used in the
 equipment)  safety Interlocking of those mechanical parts, can be
 performed by draining of the pressured air or by equalizing air pressure
 on both sides of the operating pistons, or by ??  The compressed air can
 be supplied from outside of the machine or be produced inside the machine
 by intended internal air compressor.This may rise the following
 questions: 
 
1)  For Low Voltage Directive Equipment, utilizing compressed air,
 are there any specific Safety requirements?  I looked in UL1950, EN60950
 but could not find such.
 
2)  Regarding Machinery Directive products:   Are there specific
 requirements?  intended standards ?
 
   Any response will be appreciated,  
  
Regards,  Israel Yeshurun,
 Compliance Engineer.   

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Manuals

1999-11-10 Thread Russell, Ray

Greetings,

In this day and age of trying to cover your butt, from liability (especially
in the USA), I have found it interesting that the  information in some User
manuals are going to the extreme to warn the consumer, while other similar
products have very few warnings. 

In addition, our European partner is balking at the warnings we now have.
They state that since the instructions require that installation or service
should only be a qualified personnel then this person should know some of
the obvious dangers, such as unplugging the device before servicing. 

Now assuming that a product is approved to US and European standards, can
someone recommend a guide that would help to define additional manual
requirements for US and Europe? 

Thank you,

Ray Russell
Regulatory Compliance Engineer


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



RE: US Circuit breaker requirements

1999-08-31 Thread Russell, Ray

Hi Paul,

I could not put my finger on the paragraph that spells it out in the NEC,
(380-4 has the 6 1/2 foot requirement) but I just installed a switch myself
and the local inspector required it to be a min of 18 off of the ground.

Ray

ray_russ...@gastmfg.com

-Original Message-
From: Paul Smith [mailto:phsm...@excite.co.uk]
Sent: Tuesday, August 31, 1999 8:56 AM
To: emc-p...@majordomo.ieee.org
Subject: US Circuit breaker requirements



Could somebody dispel an 'urban myth' for me.
UL 891 states that circuit breakers in Dead Front Switchboards shall be
placed no higher than 6 1/2 foot (2 metres) from the base of the rack they
are installed in. Thats fine and I can find the references fine in the UL
specification.

But, I am told that they can be placed no lower than 6 inches (or possibly
even 18 inches) above the base of the rack they are installed in. This is
the 'myth' I need some information on. I've read UL 891 but haven't found
any reference to this matter in it (or if I did my brain was switched off at
that point). What is the requirement for the minimum mounting height for
circuit breakers in Dead Front Switchboards? Is it covered by UL891, or is
it hiding in the NEC regulations?

Any ideas?

Paul


Excite -- Control Yourself.
This E-mail brought to you by Excite's free E-mail service.
Get your own E-mail address at http://www.excite.co.uk

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



RE: EN60335 verses EN61010-1

1999-08-23 Thread Russell, Ray

Hi Brian,
 
As Luis points out, the 2 standards are directed at different applications.
However, I believe most of the tests required are the same. But I'm not sure
that the manufacturer of the pump would apply the same tests that I would
seek to apply. So I would look at EN61010-1 and see what test apply. I
believe a locked rotor, dielectric and leakage current would apply. Then I
would ask the manufacturer for evidence that these tests were performed.
(The locked rotor requirements could also be met if the the manufacturer
claims that the unit is impedance protected). 
 
Good Luck,
 
Ray
 
ray_russ...@gastmfg.com mailto:ray_russ...@gastmfg.com 

-Original Message-
From: Luiz Claudio [mailto:arauj...@netville.com.br]
Sent: Saturday, August 21, 1999 11:37 AM
To: Brian At Work
Cc: IEEE Group
Subject: Re: EN60335 verses EN61010-1


Brian, 

My understanding is that EN60331-1 covers only appliances (equipment) that
are destinated to be used in a household environment. For example,
EN60335-2-24 has specific requirements for household refrigerators, but does
not have special requirements for laboratory refrigerators (where you may
have flammable substances nearby or inside the product). 


Therefore, by analogy, the fact that your pump has been tested and approved
to EN60335 does not mean that it is totally safe to be used in a laboratory
equipment. If I were you, I would look closely to EN61010-1 or other
standards to identify other requirements that may not be within the scope of
EN60335-1. 


Regards, 


Luiz 
  
  
  


Brian At Work wrote: 


Our company manufacturers laboratory equipment so we perform safety tests
and evaluation based on EN61010-1 (Safety of Laboratory equipment).  My
understanding is that we can use components, such as Power Supplies, in our
products that has been tested to EN60950 (Safety of IT Equipment) without
additional safety evaluation. Our engineering department wants to use a
small water circulation pump (aquarium pump) in one of our products. This
pump has the CE mark. The DOC says it was evaluated to EN60335 (Safety of
Household electrical appliances). If we use this pump in accordance to the
manufacturer's specifications can we use it in a laboratory instrument
without additional evaluation or testing of the pump? Regards,Brian
KundeGroup LeaderCompliance Testing Center LECO Corporation3000 Lakeview
Ave.St. Joseph, MI  49085(616) 982-5423 phone(616) 982-8964 fax
brian_ku...@leco.com mailto:brian_ku...@leco.com  bkundew...@qtm.net
mailto:bkundew...@qtm.net   


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



RE: Rockwell Modem, need info.?

1999-08-02 Thread Russell, Ray

Hi George,

I my experience, I have used the UL Yellow books to verify UL recognition
and to determine which standards it is recognized to. If I still have
trouble, I have called UL direct, and they have always been helpful. 

Ray

rayruss...@gastmfg.com

-Original Message-
From: sparaci...@andovercontrols.com
[mailto:sparaci...@andovercontrols.com]
Sent: Friday, July 30, 1999 10:43 AM
To: emc-p...@majordomo.ieee.org
Subject: Rockwell Modem, need info.?



Good Day Everyone,

I'm having a heck of a time getting compliance information from Rockwell
regarding one of their Socket Modems
(SMV144AC series). We incorporratte this modem onto our motherboard. Simply,
I need to know if the Rockwell modem that we use in our product has been
recognized to either UL 1459 or UL 1950. I would like to treat the modem as
a recognized component in my system.

No compliance info on their literature, so I contacted the local Rockwell
office in Littleton, Ma.  and they referred me back to our distributor who
has not been able to get a response back from Rockwell...  Also, I contacted
Rockwell headquarters in Newport Beach, CA ... they referred me to their
local office in Littleton.  Are we sensing a pattern here ??

If anyone has the name  contact info of someone at Rockwell that can help,
please forward to me.

Thanks for any help you can give me  have a Great Weekend.
George


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



RE: Flammable Liquids and Vapors

1999-07-28 Thread Russell, Ray

Hi Brian,
 
Sec 13 in EN 601010 doesn't offer much guidance on which standard to go to.
A search at Global found IEC 60079-1 ELECTRICAL APPARATUS FOR EXPLOSIVE GAS
ATMOSPHERES PART 1: CONSTRUCTION AND VERIFICATION TEST OF FLAMEPROOF
ENCLOSURES OF ELECTRICAL APPARATUS but I have not worked with that standard.
 
Good Luck,
 
Ray Russell
 
gastmfg.com
 
 
 
 
 

-Original Message-
From: Brian At Work [mailto:bkundew...@qtm.net]
Sent: Wednesday, July 28, 1999 11:49 AM
To: IEEE Group
Subject: Flamible Liquids and Vapors


Hello Group,
 
Our company is working on a small laboratory device, about the size of a
computer tower, that contains, in addition to electronic components, about 1
gallon (3.8 liter) of a solvent chemical. The solvent can be one or a
combination of several different chemicals such as acetone, methanol,
ethanol, etc..
 
These chemicals and/or vapors are flammable and could possibly cause a fire
or explosion under the right conditions.
 
Protection against the ignition or explosion of a flammable liquid is not
directly covered in the EN61010 safety standard (or not as I have found). 
Is there another standard that addresses these requirements more
specifically? Does anyone with experience in this area have some advice or a
summary of requirements they could give me?
 
Thank you for your time,
Brian Kunde


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



RE: Safety Incident Reporting

1999-06-30 Thread Russell, Ray

Hi Richard,

I recommend you check out the Consumer Product Safety Commission at
http://www.cpsc.gov/
BTW Paul Hill's book is a great resource.

Ray Russell

ray_russ...@gastmfg.com

-Original Message-
From: WOODS, RICHARD [mailto:wo...@sensormatic.com]
Sent: Wednesday, June 30, 1999 11:54 AM
To: 'emc-pstc'
Subject: Safety Incident Reporting



My company is reviewing our plans for handling safety incidents and product
recalls. I would appreciate it if you could point me to documents that
contain such plans or if you could forward any plans that you may have. The
one plan that I do have is from Managing Product Safety Activities by Paul
Hill. Thanks in advance.

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



RE: IEC 417 No 5017 Labels

1999-05-28 Thread Russell, Ray

This bounced yesterday, so I am resending it. 

Ray

-Original Message-
From: Russell, Ray 
Sent: Thursday, May 27, 1999 8:04 AM
To: 'distefa...@panametrics.com'; emc-p...@majordomo.ieee.org
Cc: cleme...@panametrics.com
Subject: RE: IEC 417 No 5017 Labels


We have purchased them from Hazard Communication Systems, Milford PA.
PH 800-748-0241

Website www.hazcomsys.com

Charles Pike was a sales Manager that was real helpful.

Good Luck,

Ray

ray_russ...@gastmfg.com

-Original Message-
From: distefa...@panametrics.com [mailto:distefa...@panametrics.com]
Sent: Wednesday, May 26, 1999 4:18 PM
To: emc-p...@majordomo.ieee.org
Cc: cleme...@panametrics.com
Subject: IEC 417 No 5017 Labels



 Does anyone know a source for the earth ground label/decal specified 
 by IEC 417 No. 5017. 
 
 It would be especially appreciated if said vendor/distributor was 
 local to Central Massachusetts or at least New England.
 
 Thank you in advance!
 
 R.A. Di Stefano

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



RE: Country of origin

1999-04-13 Thread Russell, Ray
Greetings,

I always understood that it was Customs that required the statement as to
the country of origin. I believe it has to do with tariffs. I also believe
that for the US the NAFTA agreement spells out if it can say made or
assembled in by how much of the material is of that countries origin.

Ray Russell

ray_russ...@gastmfg.com

-Original Message-
From: kim.boll.jen...@i-data.com [mailto:kim.boll.jen...@i-data.com]
Sent: Tuesday, April 13, 1999 3:39 AM
To: emc-p...@ieee.org
Subject: Country of origin


Dear groupe,

This question is not a safety or EMC issue but I think that some of you
have been involved in something like this before.

On the label with compliance information we normally also add something
like :  Country of origin  or  Made in this is required by some of the
EU directives and others (normally just the country of the main company who
have the legal responsibility. )

But my questions are;

-what is the rules for this information, is it just country of the company
or is it the country where it is assembled, and what if it is partly made
in different countries ?

-which authoryties requires this informations other than EU directives (and
FCC part 68)

Best regards,

Mr. Kim Boll Jensen
i-data, Denmark




-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


US/ HAR line Cord

1999-03-23 Thread Russell, Ray
Greetings,

I know that at one time, UL had accepted a HAR type cordset. Now,  I have
been told by some line cord vendors that UL does not approve any HAR type
cord any longer. Belden has a jumper cord with C13 and C14 connectors that
has both US and EU approvals, but no other configurations are available.
Does anyone know why UL stepped back away from accepting EU cords?

Thank you,

Ray Russell
Regulatory Compliance Engineer

ray_russ...@gastmfg.com




-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


Capacitors Dry or Wet?

1998-12-15 Thread Russell, Ray
Happy Holidays,

I'm working on a project that will ship to Japan and requires a motor
starting capacitor. Would any one know if there are requirements that
dictate whether a dry or wet type cap are required for Japan? How about the
rest of the world?

Thank you for your assistance,

Ray Russell
Regulatory Compliance Engineer


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


A label for a Tipping Hazard

1998-12-11 Thread Russell, Ray
Happy Holidays,

We're working on a rather large project that has pull out drawers for
servicing some of the sub assemblies.  The drawers are heavy, but low enough
that the unit only tips slightly when all drawers are open. As the drawer
pulls out it catches on the floor and stops it self from over balancing. We
would still like to warn the service personnel, and are looking for a symbol
for tipping. I've seen some on large shipping cartons, but can not find an
example now when I need it. I could not find anything in ISO 3864 that
represents this hazard. If you know of a standard or where there might be a
symbol on the net, could you please let me know?

Thank you for your assistance, 



Ray Russell
Regulatory Compliance Engineer

rayruss...@gastmfg.com

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


RE: Language labeling requirements

1998-11-12 Thread Russell, Ray
Greetings Joe,

I think that you need to look at the consumer of your equipment. If the test
equipment is to be used by an average person, then I believe multiple
languages are required. If you sell a  specialized piece of test equipment,
then I believe the standard offers a different solution. Under Amendment 2,
(EN61010-1:1993/A2) it defines the-

3.5.9 Operator: Person operating equipment for its intended purpose.
Note - The Operator should have received training appropriate for this
purpose. 

and adds

3.5.10 Responsible body: Individual or group responsible for the use and
maintenance of equipment, and for ensuring that the Operators are adequately
trained. 

I believe that through the purchase agreement, that the Responsible body
could become the company that bought the equipment, and then they are
responsible for the training of the individual that operates it. Of course
the appropriate international symbols are always required on any warning
labels. 

I also understand that in most high tech environments English is a common
language, so it would be acceptable. 

I believe it boils down to your customer requirements. 

Regards,

Ray Russell

ray_russ...@gastmfg.com


-Original Message-
From: MartinJP [mailto:marti...@pebio.com]
Sent: Wednesday, November 11, 1998 2:21 PM
To: emc-p...@ieee.org
Subject: Language labeling requirements


 As a manufacturer of laboratory equipment that is designed to meet EN 
 61010-1 per the LVD, what is our obligation/requirement for providing 
 instrument labeling and support documentation in the languages of the 
 many countries that we ship our products.
 
 All responses are appreciated.
 
 Regards
 
 Joe Martin
 EMC/Product Safety Engineer
 P.E. Biosystems
 marti...@pebio.com 

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


RE: Poisonous and Flammable Gases

1998-11-12 Thread Russell, Ray
Greetings Bob,

I do not see much reference to this situation under EN 61010. I believe that
at some point in time, the customer has to take some responsibility for the
process that they use. But the manufacture of the piece of Test equipment
still has some duty to warn of any foreseen hazards. For example, if the
equipment uses gases that could be harmful, then there should be warning
labels and information to user. 

But if the customer puts something into the equipment that could be a
hazard, then they have to take the responsibility for its use and
containment. I think a warning such as - 

Warning - If harmful substances are put into this equipment, there may be
some special ventilation and waste collection requirements. You must consult
with and follow all of the local, state and governmental guidelines when
using hazardous materials. 


Good luck,

Ray

ray_russ...@gastmfg.com 





-Original Message-
From: bob_vanor...@leco.com [mailto:bob_vanor...@leco.com]
Sent: Monday, November 09, 1998 6:17 PM
To: emc-pstc
Subject: Poisonous and Flammable Gases



All,

Could anyone please advise me on the CE requirements for product labeling
and
manual content regarding the use of poisonous and flammable gases by
analytical
instrumentation.  We manufacture a piece of  equipment that is used in a
laboratory and analyzes a wide range of samples and may emit poisonous or
flammable gases. This end product needs to comply with EN 61010.

Thank you for any help you can offer,

Bob VanOrman
EMC Technician
bob_vanor...@leco.com



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


Energized Winding Tester

1998-11-09 Thread Russell, Ray
Greetings,

I recall a recent message looking for a replacement for an Energized Winding
Tester: AVO Biddle, Model 577500. If someone found some information, would
you please pass it on to me?

Thank you,

Ray Russell
Regulatory Compliance Engineer

ray_russ...@gastmfg.com

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


RE: New Argentina Product Requirements

1998-11-03 Thread Russell, Ray
Dear Richard,

I understand that UL is working on an MOU with Argentina. With that in mind,
you might want  to contact the Technical Assistance to Exporters office at
your UL location.

Good Luck,

Ray Russell
ray_russ...@gastmfg.com


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


RE: Indicator color standard

1998-10-27 Thread Russell, Ray
Dear Francis,

I have used IEC 73 (BS  EN 60073) Specification for coding of 
indicating devices and actuators by colours and supplementary means. 
BS EN 60204 Safety of machinery- Electrical equipment of machines also 
has a section on indicating lights.

Ray Russell

ray_russ...@gastmfg.com

--
From:  Francis L. Fiedler[SMTP:ffied...@granville.com]
Sent:  Monday, October 26, 1998 1:58 PM
To:  emc-p...@majordomo.ieee.org
Subject:  Indicator color standard

Greetings,

Is any one familiar with a requirement/s that specify or limits the
color of light (LEDs) indicators used on test or industrial type
equipment per the function?

Does ISO 3864 include this information?

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


RE: EN60950

1998-10-05 Thread Russell, Ray
Greetings,

I have been using a company called Simcom for a couple of years now. 
They are usually the least expensive and have been helpful in 
answering questions about the specific standard before I pay big 
bucks, and find out is a 3 page addendum!

Phone (770) 730-9980
FAX(770) 730-9976

Global Engineering Documents also has a great selection.

Phone 1 800 854 7179
FAX (303) 397 2740

Web  http://global.ihs.com/

Regards,

Ray Russell

ray_russ...@gastmfg.com

--
From:  Dan Mitchell[SMTP:dmitch...@eoscorp.com]
Sent:  Friday, October 02, 1998 5:22 PM
To:  'emc-pstc'
Subject:  EN60950

Members,
I need to find a source to buy the EN60950 Standard.
Daniel W. Mitchell
Product Safety
EOS Corp.

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


RE: Re[2]: Are all these agencies really necessary?

1998-09-11 Thread Russell, Ray
Greetings,

A few years ago at a NEMKO seminar I attended, there was a 
presentation on the key mark. Because it looked like a key and would 
open doors to all markets. I believe this was a proposal from the IEC. 
Anyone hear any recent developments on this possibility? I imagine 
with the CE marking, that the push for something like the key mark was 
put aside in the EU.

Thanks,

Ray Russell

ray_russ...@gastmfg.com



--
From:  ron_pick...@hypercom.com[SMTP:ron_pick...@hypercom.com]
Sent:  Thursday, September 10, 1998 5:27 PM
To:  emc-p...@ieee.org; dmitch...@eoscorp.com
Subject:  Re[2]: Are all these agencies really necessary?

 Dan et al,

 Yes, OM, WM, or any other single mark would be much preferred over 
the current
 system.

 But, let's keep things in perspective. Years back (well, maybe not 
that far
 back), it seemed that every counrty had its own unique approval 
scheme, which
 included unique standards, requirements and marks based on each 
country's
 bureaucratic policies. Now, at least, harmonizing of standards and 
requirements
 are generally in place, which is a big step forward from what was. 
With this
 being said, universal acceptance of a single globally accepted 
approval scheme
 is still years away and will be difficult to achieve due to the human 
 bureaucratic parts of the equation (or until there's a single world 
government,
 but we won't go there).

 I think the USA - EU MRA is a step in the right direction to 
accomplish this,
 but I feel that the OM (one mark) idea is still far beyond the MRA 
once the MRA
 completes. Wishing a thing to come true may be considered to be a 
goal. Working
 to make that wish happen correctly is a means to that goal.

 Just some of my humble thoughts on the subject. And, of course, 
comments are
 invited.

 Best regards,
 Ron Pickard
 ron_pick...@hypercom.com

__ Reply Separator 
_
Subject: RE: Are all these agencies really necessary?
Author:  Dan Mitchell dmitch...@eoscorp.com at INTERNET
List-Post: emc-pstc@listserv.ieee.org
Date:9/10/98 10:52 AM


The OM was just an example for purposes of illustration.  A better 
name for
such a hypothetical beast would be World Mark (WM).  If you read the
earlier thread, you would have read that all the agencies are getting 
out
of hand and that it would be nice to do testing once, then apply for a 
OM?
 or WM? and be allowed to sell your product any place in the world

Daniel W. Mitchell
Product Safety
EOS Corp.

--
From: Grasso, Charles 
(Chaz)[SMTP:gra...@louisville.stortek.com]
Sent: Thursday, September 10, 1998 10:25 AM
To: Dan Mitchell; 'Peter E. Perkins'
Cc: PSNetwork
Subject: RE: Are all these agencies really necessary?

Would someone please explain the OM (Overall Mark)?
Thank you
Charles Grasso
(Captain Hook)
EMC Engineer
StorageTek
2270 Sth 88th Street
Louisville CO 80027 MS 4262
gra...@louisville.stortek.com
Tel:(303)673-2908
Fax(303)661-7115


 --
 From: Peter E. Perkins[SMTP:peperk...@compuserve.com]
 Reply To: Peter E. Perkins
 Sent: Wednesday, September 09, 1998 11:57 PM
 To: Dan Mitchell
 Cc: PSNetwork
 Subject: Are all these agencies really necessary?

 PSNet  Dan,


 The OM (Overall Mark) is a good idea that continues to be
promoted
 by industry, especially multinational businesses.  Oh that they had 
 control
 to proscribe it...  Remember that the underlying basis for all of 
this is
 a
 political issue in that nations want to control commerce in some 
manner -
 and many of the old-time controls have been taken away by treaty 
(the
GATT
 Treaty).  We work in an arena where the high level politicians tug 
and
 pull
 to get their way.  We see it in the expansion of the need to  have 
a
 certification or mark on the products.  Developing nations have 
figured
 out
 that they can easily play this game - just adapt the international
 standards - ISO/IEC/CISPR, etc. - but demand a local mark of 
approval.
The
 country supports a team of technical and bureauocratic personel thru 
the
 tax that you pay to get their bumper sticker.  Americans, 
especially,
like
 free enterprise = no restraints.  Big business promoted the use of 
a
 manufacturer's based mark for Europe (the CE marking), but were not 
too
 happy that there is personal criminal penalty attached to signing 
the
MDoC
 and applying the mark.Much of the rest of the world isn't ready 
for
 the
 whole potato all at once either.  Note the problems that the 
Japanese and
 the Koreans are having trying to reform their old-boy networks to 
open
 their markets and offer opportunity for growth there...  I predict 
that
it
 will get worse before it gets better...  So, look at it as job 
security,
 at
 least you're working (which is better than the alternative)...


 - - - - -

 Peter E Perkins
 Principal Product Safety Consultant
 

RE: Agency approvals on components in CE

1998-09-10 Thread Russell, Ray
Greetings,

From the example below, I would not be as concerned with who tested 
it, but which standard it was tested to. I think that we must remember 
that standards organizations have made progress toward harmonization, 
but the heart of the problem is that US standards and EU standards are 
not interchangeable. And under the LVD, EU Harmonized standards must 
be used where available.

Ray Russell

ray_russ...@gastmfg.com

--
From:  POWELL, DOUG[SMTP:do...@ftc2.aei.com]
Sent:  Wednesday, September 09, 1998 3:37 PM
To:  emc-p...@ieee.org
Subject:  RE: Agency approvals on components in CE

A little clarification by way of example,

Traditionally if we build a power conversion product for North 
America, we
provide a UL/CSA approved circuit breaker as a part of the design. 
 However
if we subsequently apply for certificates from an agency in Europe 
they will
insist upon a European approved circuit breaker.  Historically we have 
had
no success in finding circuit breakers with multiple approvals 
suitable for
both continents.  If the component has approval form an accredited 
test lab
we feel that it is not unsafe to use.  What is the risk of 
self-declaring
compliance to the LVD using only the UL/CSA approved part?  This would 
be a
major cost savings.

A second example would be the use of an EMI filter which is already 
approved
by one agency (not European).

I heard that this question was posed to the European Commission this 
year
(1998) and their response was to the effect that the choice of 
components is
up to the manufacturer.  I am unable to recall which email or 
periodical
made this statement.  Or was it something I read in the Official 
Journal.  I
tried browsing the European Commission's website and was unable to 
find any
document to this effect.  It is a difficult site to navigate.

Doug Powell
Advanced Energy Industries, Inc.
Fort Collins, Colorado USA
 --
From: je...@ftc2.aei.com
To: emc-p...@ieee.org
Subject: Agency approvals on components in CE mar
List-Post: emc-pstc@listserv.ieee.org
Date: Tuesday, September 08, 1998 10:31AM


It is my understanding that the European Commission has stated that a
manufacturer has the freedom to determine the acceptability of 
components
used in CE marked products.  (Or words to that effect.)  I would 
conclude
that this would remove the need for using European agency approved
components in safety critical locations.  Any reputable agency 
approval, or
appropriate evaluation by the manufacturer, would be acceptable.

Does anyone know of where I can obtain this statement in writing?  I'd 
like
to have something to back this up.  Also, I welcome comments on the
conclusions I have drawn based on this alleged EC statement.

Regards,

Jeff Jenkins
Senior Regulatory Compliance Engineer
Advanced Energy Industries, Inc.
Fort Collins, CO  USA




 -
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.com
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
ri...@sdd.hp.com, or roger.volgst...@compaq.co (the list
administrators).

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.com
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
ri...@sdd.hp.com, or roger.volgst...@compaq.co (the list
administrators).



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.com
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
ri...@sdd.hp.com, or roger.volgst...@compaq.co (the list
administrators).


RE: Requirements for Mexico

1998-08-26 Thread Russell, Ray
Greetings Nick,

I have found some good information on Mexico through the US NAFTA 
website. The URL is:

http://www.itaiep.doc.gov/nafta

Look at document 9000 for an overview of Mexico's standard system.

Ray

ray_russ...@gastmfg.com


--
From:  Nick Williams[SMTP:n...@conformance.co.uk]
Sent:  Tuesday, August 25, 1998 5:27 PM
To:  emc-p...@majordomo.ieee.org
Subject:  Requirements for Mexico

Can anyone give me some basic information (or pointers to basic
information) on the requirements for importing machinery into 
Mexico?.

I'm interested both in the legal requirements which are supposed to 
apply
and in the actual realities of the situation.

Any help appreciated - and favours stored for future recall ;-)

Nick.



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.com
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
ri...@sdd.hp.com, or roger.volgst...@compaq.co (the list
administrators).



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.com
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
ri...@sdd.hp.com, or roger.volgst...@compaq.co (the list
administrators).


TABD

1998-07-17 Thread Russell, Ray
Greetings,

The Trans Atlantic Business Dialog has put out a mid year report. It 
includes the status of:

Mutual Recognition Agreement
Regulatory Cooperation
Conformity Assessment and Product Marking
Metric Labeling


You can review the report at:

http://www.tabd.org/recom/scorecard.html


Have a great weekend!

Ray Russell

ray_russ...@gastmfg.com


RE: weatherproof mains connection

1998-07-14 Thread Russell, Ray
Greetings,

We just put a product through UL to be tested for outdoor use. It was 
a fixed line cord, and they required a W/A marking on the line cord. 
The W/A refers to a water absorption characteristic.  I'm  not sure 
what Europe would require, but I assume that it would have to be HAR 
cable and not SJT.

Ray Russell

ray_russ...@gastmfg.com

--
From: 
 jeanmarie.vandenbul...@barco.com[SMTP:jeanmarie.vandenbul...@barco.com  
]
Sent:  Tuesday, July 14, 1998 10:09 AM
To:  emc-p...@ieee.org
Subject:  weatherproof mains connection

Does anybody know if IEC 320 / C13 - C14  mains connectors and 
appliance
inlet/outlets are acceptable for mains connection of equipment for
outdoor use? Do these parts exist in weatherproof version?
If not, what type of connectors are considered acceptable for mains
connection for outdoor use equipment?

Also, is type SJT flexible cord acceptable for outdoor use?

Jean-Marie Vandenbulcke
Snr. Product Safety and Compliance Engr.
Barco NV
Noordlaan 5  B-8520 Kuurne Belgium
Tel: + 32  56 36 83 31  Fax: + 32 56 36 83 55
E-mail: jeanmarie.vandenbul...@barco.com
Web site: http://www.barco.com




AC Mains Termination

1998-07-09 Thread Russell, Ray
Greetings,

We sell some larger motor driven units to Europe, and are evaluating 
them to EN 60204. I believe that Sec 5.1 specifies that if a line cord 
is not included then a terminal block has to be provided. Although my 
experience has seen several applications that have loose leads inside 
of the junction box. Also, many motor vendors are claiming compliance 
with the loose lead approach. My questions are:

1.  Are there alternative acceptable practices?

2.  If a line cord is supplied, are crimped on connectors acceptable?


Thank you for your comments,

Ray

ray_russ...@gastmfg.com


RE: Low Voltage directive and IEC1010

1998-06-10 Thread Russell, Ray
Hi Gary,

At my last employer, I asked the TUV representative in our area to 
come in and do a product review, and a standard review with me and 
other Engineers.  You can all Rick Grumski in Livonia, MI (313) 261 
8881

Also, I see UL has a seminar 6/18-19 in Northbrook IL.  Call (847) 480 
7500.

Good Luck,

Ray Russell

ray_russ...@gastmfg.com

--
From:  Gary Labadie[SMTP:glaba...@acromag.com]
Sent:  Tuesday, June 09, 1998 6:42 PM
To:  emc-p...@ieee.org
Subject:  Low Voltage directive and IEC1010

Does anyone have a suggestion on the quickest way to meet the Low 
Voltage
directive and ramp quickly up on the IEC1010?  Is going to the 
approval
agency the best way the first time around or a seminar instead?  I 
need
to meet the requirements of the low voltage directive and one way is 
the
IEC1010 route and versions thereof.  Anybody have other suggestions?

Best Regards,

Gary Labadie
Marketing

Acromag, Inc.
30765 Wixom Rd.Ph: (248)624-1541 ext. 205
P.O. Box 437   Fax:(248)624-9234
Wixom, MI 48393Email: glaba...@acromag.com


Previous EMC-PSTC Topics

1998-06-01 Thread Russell, Ray
Greetings,

This forum is a great resource and has helped me greatly. Thanks to 
all who have provided information on the recent Twist on connectors 
questions.

There is a way to search on the past items discussed on the group. It 
is called Regulatory Compliance Information Center. The URL is 
http://www.rcic.com/default.htm. Check out the Virtual Conference Hall 
and do a search on EMC-PSTC.


Thanks to Tom Bao and the others that keep this site going.


Ray Russell

ray_russ...@gastmfg.com


ISO Standard for SI units (Metric Directive)

1998-04-30 Thread Russell, Ray
Greetings,

Thanks to all who have provided information on the metric directive. 
As I was researching this issue, I went back to the FAQ by Bill Lyons. 
What a great resource. However, I was not able to find the standard 
that would be used to comply with the directives. Could someone please 
forward the standard number that spells out the metric units of 
measurements?

BTW I sent an email to NIST (from the information supplied by this 
group) and here was Mr. McCracken's response:


Mr. Russell,

At this time no meeting is scheduled to discuss the EU metric-only
directive.  The EU technical staff has proposed a ten year delay of 
the
directive.  Until we know more on the subject a meeting is not 
warranted.

We will continue to make information available.

Jim McCracken
Metric Program




Thank you for your assistance,

Ray Russell
ray_russ...@gastmfg.com


EMC Directive and Small DC motors

1998-04-07 Thread Russell, Ray
Greetings,

We manufacturer a small line of vacuum pumps that use very small (1/16 
hp) 12, 6 and 4 VDC motors. Just a DC motor and a pump. We have had 
some EMC testing performed to the EN 55014 and EN 55104 standards 
where there was some high conducted emissions that required a .1 uf 
capacitor across the positive and negative terminals. But I believe 
this is more of an issue of the power supply source, and lead lengths 
than the motor.

These items are considered components because they need a power supply 
to operate. However, they could use battery power, but I assume that 
there would not be an emission problem in this mode.

We now have another source for motors, and I have been asked to 
retest. I am very reluctant to spend thousands of dollars on testing, 
when I personally do not understand the benefit or risk. Of course the 
test house highly recommends additional testing. So I come seeking 
some advice or alternatives. Here are some of my thoughts:

Since this is a component, could we just assign a declaration of 
incorporation?

Are there any reasonable limits to what should be tested, as far as 
power/frequency/application in the directives?

Is there a justifiable reason to test this product?


Thank you for your consideration, any thoughts would be appreciated.

Ray Russell

ray_russ...@gastmfg.com


Pressure Directive

1998-03-30 Thread Russell, Ray
Dear PSTC  group,

A recent change in employers has brought a whole new series of 
questions. Could some one please provide me with some details on the 
pressure directive, and maybe some sources for information?

Thanks for your input,

Ray Russell