Maybe the inspector just didn't like the look of it for some reason?
Sometimes it's just easiest to ask the inspector what he would like to see.

If he didnt give the code reference it may be one of these items below:

* 2020 NEC*
Article 110.12 Workmanship ( the catch all of many issues for some
inspectors)
Article 300.2(B) Conductor & ground needs to be in the same raceway ( this
might be the one).
Article 352.12(C) Subject to physical damage (not likely?)
Article 352.28 Trimming and removing all rough edges ( maybe?)
Article 352.46 Bushings installed where conduit enters
box/enclosure-provided to protect conductors ( maybe?)


Please let us know how this one ends up.

Happy Trails & Good Luck.


James B. Rudolph


Independent Energy

C-39784 ES #10816

NABCEP Certified PV Installer since 2009  #091209-155

C. 808.313.9701













On Tue, Mar 22, 2022 at 2:25 PM Jay  wrote:

> I’m not the code expert.
> But here is a company making parts used for code installations.
>
> https://www.cabproducts.com/solar/
>
> Maybe one of theirs will work instead of the plastic chase.
>
> Jay
>
>
>
> On Mar 22, 2022, at 5:20 PM, Jerry Shafer 
> wrote:
>
> 
> Without question the wires are either supported via a rail or strut
> between the rows of modules or trenched underground if a ground mount. I
> have seen fly over and it will be a point of failure by someone that should
> be there but is and if you damage one JB/diode pack on the back of a module
> you will pay more than the trench would cost.
> Jerry
> NABCEP PV Inspector
>
> On Tue, Mar 22, 2022 at 1:43 PM Dave Tedeyan 
> wrote:
>
>> Hi All,
>>
>> I have an inspector giving me a hard time about wire management between
>> two ground mounted arrays. The racking is Unirac GFT, and the system was
>> too large to have one continuous array. So there are two arrays, side by
>> side, with only a 1' gap between the rails and modules from the two
>> separate arrays.
>>
>> We jumped the PV wire between the arrays through a short section of PVC
>> for protection, and the wires are secured to the rails about a foot past
>> the PVC on either end. The inspector is citing the following:
>> 
>> Array conductors found disconnected or improperly connected, which may be
>> causing portions of the array to be inoperable and/or pose a shock hazard.
>> 
>> They say that they are citing this because there is no strain relief as
>> the wires enter and exit the 18" piece of conduit. My question to you all
>> is, do you know of any code reference that says that this setup is or is
>> not okay? I would also be curious to hear what others do to span a 1' gap
>> on a ground mount. It almost seems as if I just left the conductors exposed
>> for that gap, there would have been no problem.
>>
>> I attached a couple of photos to help with my written description.
>> I appreciate the knowledge of this hive mind!
>> Cheers,
>> Dave
>>
>> --
>> [image: Logo] 
>> Dave Tedeyan, P.E.
>> Owner | Sungineer Solar
>> p: he | him | his
>> a: 1653 Slaterville Rd. | Ithaca, NY 14850
>> w: www.sungineersolar.com 
>> c: (607) 288-2898
>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> 

Re: [RE-wrenches] Wires between arrays

2022-03-22 Thread Jay
I’m not the code expert. 
But here is a company making parts used for code installations. 

https://www.cabproducts.com/solar/

Maybe one of theirs will work instead of the plastic chase. 

Jay



> On Mar 22, 2022, at 5:20 PM, Jerry Shafer  wrote:
> 
> 
> Without question the wires are either supported via a rail or strut between 
> the rows of modules or trenched underground if a ground mount. I have seen 
> fly over and it will be a point of failure by someone that should be there 
> but is and if you damage one JB/diode pack on the back of a module you will 
> pay more than the trench would cost.
> Jerry 
> NABCEP PV Inspector
> 
>> On Tue, Mar 22, 2022 at 1:43 PM Dave Tedeyan  wrote:
>> Hi All, 
>> 
>> I have an inspector giving me a hard time about wire management between two 
>> ground mounted arrays. The racking is Unirac GFT, and the system was too 
>> large to have one continuous array. So there are two arrays, side by side, 
>> with only a 1' gap between the rails and modules from the two separate 
>> arrays. 
>> 
>> We jumped the PV wire between the arrays through a short section of PVC for 
>> protection, and the wires are secured to the rails about a foot past the PVC 
>> on either end. The inspector is citing the following:
>> 
>> Array conductors found disconnected or improperly connected, which may be 
>> causing portions of the array to be inoperable and/or pose a shock hazard.
>> 
>> They say that they are citing this because there is no strain relief as the 
>> wires enter and exit the 18" piece of conduit. My question to you all is, do 
>> you know of any code reference that says that this setup is or is not okay? 
>> I would also be curious to hear what others do to span a 1' gap on a ground 
>> mount. It almost seems as if I just left the conductors exposed for that 
>> gap, there would have been no problem.
>> 
>> I attached a couple of photos to help with my written description.
>> I appreciate the knowledge of this hive mind!
>> Cheers, 
>> Dave
>> 
>> -- 
>>  
>> Dave Tedeyan, P.E.
>> Owner | Sungineer Solar
>> p: he | him | his
>> a: 1653 Slaterville Rd. | Ithaca, NY 14850
>> w: www.sungineersolar.com
>> c: (607) 288-2898
>> ___
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Wires between arrays

2022-03-22 Thread Jerry Shafer
Without question the wires are either supported via a rail or strut between
the rows of modules or trenched underground if a ground mount. I have seen
fly over and it will be a point of failure by someone that should be there
but is and if you damage one JB/diode pack on the back of a module you will
pay more than the trench would cost.
Jerry
NABCEP PV Inspector

On Tue, Mar 22, 2022 at 1:43 PM Dave Tedeyan 
wrote:

> Hi All,
>
> I have an inspector giving me a hard time about wire management between
> two ground mounted arrays. The racking is Unirac GFT, and the system was
> too large to have one continuous array. So there are two arrays, side by
> side, with only a 1' gap between the rails and modules from the two
> separate arrays.
>
> We jumped the PV wire between the arrays through a short section of PVC
> for protection, and the wires are secured to the rails about a foot past
> the PVC on either end. The inspector is citing the following:
> 
> Array conductors found disconnected or improperly connected, which may be
> causing portions of the array to be inoperable and/or pose a shock hazard.
> 
> They say that they are citing this because there is no strain relief as
> the wires enter and exit the 18" piece of conduit. My question to you all
> is, do you know of any code reference that says that this setup is or is
> not okay? I would also be curious to hear what others do to span a 1' gap
> on a ground mount. It almost seems as if I just left the conductors exposed
> for that gap, there would have been no problem.
>
> I attached a couple of photos to help with my written description.
> I appreciate the knowledge of this hive mind!
> Cheers,
> Dave
>
> --
> [image: Logo] 
> Dave Tedeyan, P.E.
> Owner | Sungineer Solar
> p: he | him | his
> a: 1653 Slaterville Rd. | Ithaca, NY 14850
> w: www.sungineersolar.com 
> c: (607) 288-2898
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Wires between arrays

2022-03-22 Thread August Goers
This IAEI Magazine article may address this issue a bit:

https://iaeimagazine.org/features/electrical-systems-are-you-protected/

Your inspector might be concerned with the rough edges portion of the
article:

[image: image.png]
You may be able to argue with the inspector that you have simply used the
PVC as a sleeve, and properly smoothed off the edges to avoid conductor
abrasion. Otherwise, typically you would need to install a connector and
plastic pull bushing, strain relief, or box of some sort.

Best,

August
Luminalt


On Tue, Mar 22, 2022 at 3:32 PM Glenn Burt  wrote:

> There is a code citation that prohibits the use of conduit without an end
> or fitting of some kind.
>
> -Glenn
> Sent from my 'smart'phone, so please excuse typos and spelling errors.
>
> -- Original message--
> *From: *Darryl Thayer
> *Date: *Tue, Mar 22, 2022 5:48 PM
> *To: *RE-wrenches;
> *Cc: *
> *Subject:*Re: [RE-wrenches] Wires between arrays
>
> Once in my life i had an inspector concerned about strain relief, i used a
> GBC on each end of the pipe, it surficed. I think i could have used a bell
> mouth connector.
>
> On Tue, Mar 22, 2022, 3:43 PM Dave Tedeyan 
> wrote:
>
>> Hi All,
>>
>> I have an inspector giving me a hard time about wire management between
>> two ground mounted arrays. The racking is Unirac GFT, and the system was
>> too large to have one continuous array. So there are two arrays, side by
>> side, with only a 1' gap between the rails and modules from the two
>> separate arrays.
>>
>> We jumped the PV wire between the arrays through a short section of PVC
>> for protection, and the wires are secured to the rails about a foot past
>> the PVC on either end. The inspector is citing the following:
>> 
>> Array conductors found disconnected or improperly connected, which may be
>> causing portions of the array to be inoperable and/or pose a shock hazard.
>> 
>> They say that they are citing this because there is no strain relief as
>> the wires enter and exit the 18" piece of conduit. My question to you all
>> is, do you know of any code reference that says that this setup is or is
>> not okay? I would also be curious to hear what others do to span a 1' gap
>> on a ground mount. It almost seems as if I just left the conductors exposed
>> for that gap, there would have been no problem.
>>
>> I attached a couple of photos to help with my written description.
>> I appreciate the knowledge of this hive mind!
>> Cheers,
>> Dave
>>
>> --
>> [image: Logo] 
>> Dave Tedeyan, P.E.
>> Owner | Sungineer Solar
>> p: he | him | his
>> a: 1653 Slaterville Rd. | Ithaca, NY 14850
>> w:  www.sungineersolar.com
>> 
>> c: (607) 288-2898
>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Wires between arrays

2022-03-22 Thread William Miller
Dave:



If there is a child-proof fence around this installation, please disregard
everything I write below.  I am curious:  Is there such a fence?



Question:  Is that plastic snow fence attached to the back of the racking
with Tek screws?



You are lucky I am not your inspector.  The smallest issue I see is the
flimsy wire bridge.  I don’t think any part of this looks code complaint
regarding wire protection.  The guarding is supposed to keep little fingers
away from the conductors, insulated or not.  You would not cover a gutter
or pull-box with this snow fence material would you?  It is not suitable as
conductor covering material.



Remember the code is designed to protect people of all ages from harm.
Kids view ground mount arrays as jungle gyms.  The first kid that grabs
onto the snow fence attached with Tek screws and no fender washers is going
to rip the plastic right off of that array.



While swinging around they could easily pull hard on a wire, pulling it out
of a crimp connector or across a sharp edge, exposing some of the energized
conductor.  The possibility of death from this installation is
significantly greater than zero.



I see a lot of ground mount arrays that are kind of guarded but not
really.  We should be doing better with our craftsmanship.  We have a
responsibility.



If you want some pointers on how to fix this, I’d be happy to help.
Contact me off-line.



William



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Dave Tedeyan
*Sent:* Tuesday, March 22, 2022 1:43 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Wires between arrays



Hi All,



I have an inspector giving me a hard time about wire management between two
ground mounted arrays. The racking is Unirac GFT, and the system was too
large to have one continuous array. So there are two arrays, side by side,
with only a 1' gap between the rails and modules from the two separate
arrays.



We jumped the PV wire between the arrays through a short section of PVC for
protection, and the wires are secured to the rails about a foot past the
PVC on either end. The inspector is citing the following:



Array conductors found disconnected or improperly connected, which may be
causing portions of the array to be inoperable and/or pose a shock hazard.



They say that they are citing this because there is no strain relief as the
wires enter and exit the 18" piece of conduit. My question to you all is,
do you know of any code reference that says that this setup is or is not
okay? I would also be curious to hear what others do to span a 1' gap on a
ground mount. It almost seems as if I just left the conductors exposed for
that gap, there would have been no problem.



I attached a couple of photos to help with my written description.

I appreciate the knowledge of this hive mind!

Cheers,

Dave



-- 

[image: Logo] 


*Dave Tedeyan, P.E.Owner | Sungineer Solar*

*p: *he | him | his
*a: *1653 Slaterville Rd. | Ithaca, NY 14850
*w:* www.sungineersolar.com 
*c:* (607) 288-2898
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Wires between arrays

2022-03-22 Thread Glenn Burt
There is a code citation that prohibits the use of conduit without an end or 
fitting of some kind.-GlennSent from my 'smart'phone, so please excuse typos 
and spelling errors.-- Original message--From: Darryl ThayerDate: Tue, 
Mar 22, 2022 5:48 PMTo: RE-wrenches;Cc: Subject:Re: [RE-wrenches] Wires between 
arraysOnce in my life i had an inspector concerned about strain relief, i used 
a GBC on each end of the pipe, it surficed. I think i could have used a bell 
mouth connector.  On Tue, Mar 22, 2022, 3:43 PM Dave Tedeyan 
 wrote:Hi All, I have an inspector giving me a hard 
time about wire management between two ground mounted arrays. The racking is 
Unirac GFT, and the system was too large to have one continuous array. So there 
are two arrays, side by side, with only a 1' gap between the rails and modules 
from the two separate arrays. We jumped the PV wire between the arrays through 
a short section of PVC for protection, and the wires are secured to the
 rails about a foot past the PVC on either end. The inspector is citing the 
following:Array conductors found disconnected or
improperly connected, which may be
causing portions of the array to be
inoperable and/or pose a shock hazard.They say that they are citing this 
because there is no strain relief as the wires enter and exit the 18" piece of 
conduit. My question to you all is, do you know of any code reference that says 
that this setup is or is not okay? I would also be curious to hear what others 
do to span a 1' gap on a ground mount. It almost seems as if I just left the 
conductors exposed for that gap, there would have been no problem.I attached a 
couple of photos to help with my written description.I appreciate the knowledge 
of this hive mind!Cheers, Dave-- Dave Tedeyan, P.E.Owner | Sungineer Solarp: he 
| him | hisa: 1653 Slaterville Rd. | Ithaca, NY 14850w: 
www.sungineersolar.comc: (607) 288-2898
___
List sponsored by
 Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Wires between arrays

2022-03-22 Thread Chris Worcester
I would slide 3" of 3/4" 600 volt heat shrink over the end of a stainless steel 
hose clamp and secure the wire to the rail where it comes out of the conduit at 
each end. Chris Worcester chris@solarwindworks.com530-448-9692Sent from my 
Samsung Galaxy s9.
 Original message From: Dave Tedeyan  
Date: 3/22/22  1:44 PM  (GMT-08:00) To: RE-wrenches 
 Subject: [RE-wrenches] Wires between arrays 
Hi All, I have an inspector giving me a hard time about wire management between 
two ground mounted arrays. The racking is Unirac GFT, and the system was too 
large to have one continuous array. So there are two arrays, side by side, with 
only a 1' gap between the rails and modules from the two separate arrays. We 
jumped the PV wire between the arrays through a short section of PVC for 
protection, and the wires are secured to the rails about a foot past the PVC on 
either end. The inspector is citing the following:Array conductors found 
disconnected or
improperly connected, which may be
causing portions of the array to be
inoperable and/or pose a shock hazard.They say that they are citing this 
because there is no strain relief as the wires enter and exit the 18" piece of 
conduit. My question to you all is, do you know of any code reference that says 
that this setup is or is not okay? I would also be curious to hear what others 
do to span a 1' gap on a ground mount. It almost seems as if I just left the 
conductors exposed for that gap, there would have been no problem.I attached a 
couple of photos to help with my written description.I appreciate the knowledge 
of this hive mind!Cheers, Dave-- Dave Tedeyan, P.E.Owner | Sungineer Solarp: he 
| him | hisa: 1653 Slaterville Rd. | Ithaca, NY 14850w: 
www.sungineersolar.comc: (607) 288-2898
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Wires between arrays

2022-03-22 Thread Darryl Thayer
Once in my life i had an inspector concerned about strain relief, i used a
GBC on each end of the pipe, it surficed. I think i could have used a bell
mouth connector.

On Tue, Mar 22, 2022, 3:43 PM Dave Tedeyan  wrote:

> Hi All,
>
> I have an inspector giving me a hard time about wire management between
> two ground mounted arrays. The racking is Unirac GFT, and the system was
> too large to have one continuous array. So there are two arrays, side by
> side, with only a 1' gap between the rails and modules from the two
> separate arrays.
>
> We jumped the PV wire between the arrays through a short section of PVC
> for protection, and the wires are secured to the rails about a foot past
> the PVC on either end. The inspector is citing the following:
> 
> Array conductors found disconnected or improperly connected, which may be
> causing portions of the array to be inoperable and/or pose a shock hazard.
> 
> They say that they are citing this because there is no strain relief as
> the wires enter and exit the 18" piece of conduit. My question to you all
> is, do you know of any code reference that says that this setup is or is
> not okay? I would also be curious to hear what others do to span a 1' gap
> on a ground mount. It almost seems as if I just left the conductors exposed
> for that gap, there would have been no problem.
>
> I attached a couple of photos to help with my written description.
> I appreciate the knowledge of this hive mind!
> Cheers,
> Dave
>
> --
> [image: Logo] 
> Dave Tedeyan, P.E.
> Owner | Sungineer Solar
> p: he | him | his
> a: 1653 Slaterville Rd. | Ithaca, NY 14850
> w: www.sungineersolar.com 
> c: (607) 288-2898
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Wires between arrays

2022-03-22 Thread Chris Sparadeo
Hi Dave,

I typically use the same method you do for running conductors between two
non-continuous arrays. I have never had an issue with either AHJ blowback
or actual compromised conductors due to a lack of strain relief.

The only code reference I can think of is 300.4 regarding protection
against physical damage, but you have that covered with the use of a
secured conduit.

To appease the AHJ, you could add some pvc female adapters and gland seals.

Best,

Chris

On Tue, Mar 22, 2022 at 4:43 PM Dave Tedeyan 
wrote:

> Hi All,
>
> I have an inspector giving me a hard time about wire management between
> two ground mounted arrays. The racking is Unirac GFT, and the system was
> too large to have one continuous array. So there are two arrays, side by
> side, with only a 1' gap between the rails and modules from the two
> separate arrays.
>
> We jumped the PV wire between the arrays through a short section of PVC
> for protection, and the wires are secured to the rails about a foot past
> the PVC on either end. The inspector is citing the following:
> 
> Array conductors found disconnected or improperly connected, which may be
> causing portions of the array to be inoperable and/or pose a shock hazard.
> 
> They say that they are citing this because there is no strain relief as
> the wires enter and exit the 18" piece of conduit. My question to you all
> is, do you know of any code reference that says that this setup is or is
> not okay? I would also be curious to hear what others do to span a 1' gap
> on a ground mount. It almost seems as if I just left the conductors exposed
> for that gap, there would have been no problem.
>
> I attached a couple of photos to help with my written description.
> I appreciate the knowledge of this hive mind!
> Cheers,
> Dave
>
> --
> [image: Logo] 
> Dave Tedeyan, P.E.
> Owner | Sungineer Solar
> p: he | him | his
> a: 1653 Slaterville Rd.
> 
>
> |
>  Ithaca,
> NY 14850
> 
> w: www.sungineersolar.com 
> c: (607) 288-2898
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --
Chris Sparadeo


C_802-369-4458
H_802-728-3059
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Wires between arrays

2022-03-22 Thread Jason Szumlanski
In Florida, the AHJ is required to cite the section of code when rejecting
work. I always ask for that if rejected. I'm not sure how things work in NY.

You might start with 690.31(C)(1) that allows PV wire to be exposed within
the PV array. The array boundary is defined elsewhere as within 1 ft of the
array in all directions, although that pertains to rapid shutdown
specifically.

You're right - you might just remove the PVC and ask them how it doesn't
comply then, considering you only have to support it at 4.5 ft intervals.

Jason Szumlanski
Florida Solar Design Group




On Tue, Mar 22, 2022 at 4:43 PM Dave Tedeyan 
wrote:

> Hi All,
>
> I have an inspector giving me a hard time about wire management between
> two ground mounted arrays. The racking is Unirac GFT, and the system was
> too large to have one continuous array. So there are two arrays, side by
> side, with only a 1' gap between the rails and modules from the two
> separate arrays.
>
> We jumped the PV wire between the arrays through a short section of PVC
> for protection, and the wires are secured to the rails about a foot past
> the PVC on either end. The inspector is citing the following:
> 
> Array conductors found disconnected or improperly connected, which may be
> causing portions of the array to be inoperable and/or pose a shock hazard.
> 
> They say that they are citing this because there is no strain relief as
> the wires enter and exit the 18" piece of conduit. My question to you all
> is, do you know of any code reference that says that this setup is or is
> not okay? I would also be curious to hear what others do to span a 1' gap
> on a ground mount. It almost seems as if I just left the conductors exposed
> for that gap, there would have been no problem.
>
> I attached a couple of photos to help with my written description.
> I appreciate the knowledge of this hive mind!
> Cheers,
> Dave
>
> --
> [image: Logo] 
> Dave Tedeyan, P.E.
> Owner | Sungineer Solar
> p: he | him | his
> a: 1653 Slaterville Rd. | Ithaca, NY 14850
> w: www.sungineersolar.com 
> c: (607) 288-2898
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Monitoring on Remote Sites

2022-03-22 Thread Dan Fink
John - It appears that Ubiquiti does still have a 900 MHz bridge available,
looks like a very small dish instead of a flat panel. I suggest giving them
a call or an email. They were very helpful in email and on the phone when
my first 2.4 GHz system was intermittent (worked fine in winter, not in
summer...trees grow leaves! duh.) and didn't seem to mind that I didn't
speak IT jargon.

I'm in a similar situation as you, my guest cabin is 800 feet away with
some mid size aspen trees in the way, so 2.4GHz didn't work. Ordered
Starlink just over a year ago, their latest guess is next month(!!!) to
receive mine.

I think the only issue with 900 MHz and Starlink is that your blazing
speeds (when it finally arrives) might be limited a bit. 5 GHz and up might
keep up with your newfound speed better. Yes, you can do a 2-part bridge,
but make sure you look closely at what they mean by "obstructions" and
where in your line of sight they are located. Will let you know how it goes
with mine when Dishy arrives.

Dan Fink
Owner, Buckville Energy Consulting LLC
IREC Certified Instructor for PV and Small Wind Installation
NABCEP Certified PV System Inspector
NABCEP PV Associate
d anbo...@gmail.com
970-672-4342




On Tue, Mar 22, 2022 at 8:27 AM John Blittersdorf <
john.blittersd...@gmail.com> wrote:

> Dan, are the 900 MHz flat panels still available.   I’m looking at a need
> for a 1000’ bridge with some trees in the way.  I could also do a two step
> going from my house to my barn 800’ away clear shot and then to the cabin
> another 300’ clear shot. Is that possible? I’m getting Starlink to replace
> my Viasat and need internet at the guest cabin.
>
> John Blittersdorf
>
> On Mon, Mar 14, 2022 at 2:52 PM Dan Fink  wrote:
>
>> I concur with Luke Christy below - I have had great success with Ubiquiti
>> wireless bridges. If the line of sight is not completely clear, their 2 and
>> 5gHz dishes can be problematic, but their 900mHz flat panels will work
>> through a moderate amount of vegetation. I'm using that one to write this
>> email right now in fact, have not had to touch or reboot anything in 4
>> years. Note that they are *not* wifi extenders, you need another wifi
>> router on the other end connected to the far side of the bridge.
>>
>> Dan Fink
>> Owner, Buckville Energy Consulting LLC
>> IREC Certified Instructor for PV and Small Wind Installation
>> NABCEP Certified PV System Inspector
>> NABCEP PV Associate
>> d anbo...@gmail.com
>> 970-672-4342
>>
>> On Mon, Mar 14, 2022 at 12:39 PM Dave Tedeyan 
>> wrote:
>>
>>> Luke,
>>> I wanted to try out Ubiquiti products, and bought a NanoStation M2, but
>>> haven't installed it yet. With the Lighbeam, can any device connect to it?
>>> If so, I know at least the SMA SB wifi can only connect to 2Ghz, and not
>>> 5Ghz. I'll have to see if there is a 2Ghz option. This is why I cannot use
>>> the Engenius equipment anymore, since their 202 replacement is 5Ghz only.
>>> Cheers,
>>> Dave
>>>
>>> On Mon, Mar 14, 2022 at 2:28 PM Luke Christy 
>>> wrote:
>>>
 Adam,
 I would second Dave’s suggestion to use wireless bridges for this
 application -if hardwired internet access is available elsewhere on the
 property and if there is decent line of sight access between that point and
 where your equipment lives.

 I have used a lot of Ubiquiti Litebeam point-to-point links for this
 sort of thing and they are awesome. They have given me rock solid
 dependability once they are set up and configured, they function just like
 a virtual ethernet cable over the radio link, and you can even have a
 single access point transmit to multiple stations. Range for the
 entry-level Litebeam M5 unit is up to 10km and you can get a pre-configured
 pair of antenna dishes on Amazon for less than $200. Two devices can be had
 for around $100 if you are willing to configure them yourself with a laptop
 or the UISP app from Ubiquiti.   Worth checking out. Other versions are
 available with longer range and more features but I have found the Litebeam
 M5 is very affordable and works well for most shorter-range applications.


 Luke Christy

 Renewable energy consultant.

 NABCEP Certified PV Installation Professional™:

 Solar Gain Services, LLC
 PO Box 531
 Monte Vista, CO. 81144
 sgsrenewab...@gmail.com 
 719.588.3044


>>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules 

Re: [RE-wrenches] Monitoring on Remote Sites

2022-03-22 Thread John Blittersdorf
Dan, are the 900 MHz flat panels still available.   I’m looking at a need
for a 1000’ bridge with some trees in the way.  I could also do a two step
going from my house to my barn 800’ away clear shot and then to the cabin
another 300’ clear shot. Is that possible? I’m getting Starlink to replace
my Viasat and need internet at the guest cabin.

John Blittersdorf

On Mon, Mar 14, 2022 at 2:52 PM Dan Fink  wrote:

> I concur with Luke Christy below - I have had great success with Ubiquiti
> wireless bridges. If the line of sight is not completely clear, their 2 and
> 5gHz dishes can be problematic, but their 900mHz flat panels will work
> through a moderate amount of vegetation. I'm using that one to write this
> email right now in fact, have not had to touch or reboot anything in 4
> years. Note that they are *not* wifi extenders, you need another wifi
> router on the other end connected to the far side of the bridge.
>
> Dan Fink
> Owner, Buckville Energy Consulting LLC
> IREC Certified Instructor for PV and Small Wind Installation
> NABCEP Certified PV System Inspector
> NABCEP PV Associate
> d anbo...@gmail.com
> 970-672-4342
>
> On Mon, Mar 14, 2022 at 12:39 PM Dave Tedeyan 
> wrote:
>
>> Luke,
>> I wanted to try out Ubiquiti products, and bought a NanoStation M2, but
>> haven't installed it yet. With the Lighbeam, can any device connect to it?
>> If so, I know at least the SMA SB wifi can only connect to 2Ghz, and not
>> 5Ghz. I'll have to see if there is a 2Ghz option. This is why I cannot use
>> the Engenius equipment anymore, since their 202 replacement is 5Ghz only.
>> Cheers,
>> Dave
>>
>> On Mon, Mar 14, 2022 at 2:28 PM Luke Christy 
>> wrote:
>>
>>> Adam,
>>> I would second Dave’s suggestion to use wireless bridges for this
>>> application -if hardwired internet access is available elsewhere on the
>>> property and if there is decent line of sight access between that point and
>>> where your equipment lives.
>>>
>>> I have used a lot of Ubiquiti Litebeam point-to-point links for this
>>> sort of thing and they are awesome. They have given me rock solid
>>> dependability once they are set up and configured, they function just like
>>> a virtual ethernet cable over the radio link, and you can even have a
>>> single access point transmit to multiple stations. Range for the
>>> entry-level Litebeam M5 unit is up to 10km and you can get a pre-configured
>>> pair of antenna dishes on Amazon for less than $200. Two devices can be had
>>> for around $100 if you are willing to configure them yourself with a laptop
>>> or the UISP app from Ubiquiti.   Worth checking out. Other versions are
>>> available with longer range and more features but I have found the Litebeam
>>> M5 is very affordable and works well for most shorter-range applications.
>>>
>>>
>>> Luke Christy
>>>
>>> Renewable energy consultant.
>>>
>>> NABCEP Certified PV Installation Professional™:
>>>
>>> Solar Gain Services, LLC
>>> PO Box 531
>>> Monte Vista, CO. 81144
>>> sgsrenewab...@gmail.com 
>>> 719.588.3044
>>>
>>>
>> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Discover AES Battery Rack Options

2022-03-22 Thread Glenn Burt
Discover makes a wall mounting bracket for these batteries. I have installed a 
half dozen thus way.I think if I were ground mounting them I would build a 
simple platform from wood. I dont like the idea of their metal cases resting 
directly on a concrete floor from a corrosion and temperature 
perspective.-GlennSent from my 'smart'phone, so please excuse typos and 
spelling errors.-- Original message--From: Chris SparadeoDate: Tue, Mar 
22, 2022 9:28 AMTo: RE-wrenches;Cc: Subject:[RE-wrenches] Discover AES Battery 
Rack OptionsHi Wrenches,Wondering how people are installing the Discover AES. I 
get that they can be floor or wall mounted, but I'm trying to avoid exposed 
conductors and a rack seems like the best option. Any insights?Kindly,Chris 
Sparadeo
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Discover AES Battery Rack Options

2022-03-22 Thread Chris Sparadeo
Hi Wrenches,

Wondering how people are installing the Discover AES. I get that they can
be floor or wall mounted, but I'm trying to avoid exposed conductors and a
rack seems like the best option. Any insights?

Kindly,

Chris Sparadeo
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org