Slave Pallets

2014-07-16 Thread James Crawford
I have been asked by an AHJ why if you use a slave pallet, basically a piece
of plywood,  you have to add 20% to the design density, but if you have
solid shelving less than 20 square feet you do not have to do anything. 

 

Looking for input.

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


NFPA #30

2014-11-07 Thread James Crawford
Looking for input

 

NFPA #30 2008 ed.

 

We are looking at a building where the tenant want to store motor oil in 1
quart to 5 gal plastic containers on single and double row racks.

 

Motor oil is a class IIIB combustible liquid, flash point 460°F (some higher
some lower)

 

Stored in plastic containers so we use Table 16.5.2.5 and protect using
scheme “A”

 

Scheme “A call for barriers and provides figures for the installation, but
also allows the barriers to be eliminated if the flashpoint is greater than
450°F. This option calls for a roof density of 0.30 plus in-rack demand.

 

Now my questions.

 

If we eliminate the barriers, do we move the in-racks down one level or
eliminate the top level? 

As for the in-racks, do we still require 50psi at the heads and is it just
one level as there are no barriers?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Flammable Liquids

2014-11-18 Thread James Crawford
Looking for additional information on protecting flammable liquids in a high
building, 45' clear height

 

We have group 1C and II liquids in 5 gal relieving style metal containers
stored on single row racks to 16'

 

All the information I have found limits the building height to 30', any
ideas?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


In-Rack Sprinkler Control Valve

2016-10-12 Thread James Crawford
I just came from a building where the in-rack sprinklers are connected into
the adjacent roof system.

 

The building has two roof zones, north and south, the in-racks are in the
north zone but connected into the south zone (no control valve at the
connection point)

 

I have never ever thought of doing this as it would send two different
signals in the event of a fire, but cannot seem to find anything that says
you can't do this, with the exception of alarm signals.

 

Any comments on this arrangement?  

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: In-Rack Sprinkler Control Valve

2016-10-12 Thread James Crawford
The building is 70,000 sq ft and a multi-tenant building

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rongreenman .
Sent: Wednesday, October 12, 2016 2:19 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: In-Rack Sprinkler Control Valve

 

Why is it zoned? Just because it's bigger than 52K? One big open space? Not 
trying to be a smart ass (or maybe I am) but the FD won't fight a fire in zone 
2 that is happening in Zone 1 bec aide an annunciation says here, not there, 
and it sounds like they'd be able too see the fire on entry. 

On Wednesday, October 12, 2016, James Crawford  wrote:

I just came from a building where the in-rack sprinklers are connected into the 
adjacent roof system.

 

The building has two roof zones, north and south, the in-racks are in the north 
zone but connected into the south zone (no control valve at the connection 
point)

 

I have never ever thought of doing this as it would send two different signals 
in the event of a fire, but cannot seem to find anything that says you can’t do 
this, with the exception of alarm signals.

 

Any comments on this arrangement?  

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca 
 

 



-- 
Sent from Gmail Mobile

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Spirits Storage

2016-11-21 Thread James Crawford
We are getting more craft beer and craft distilleries going up in our area
and as they continue to grow they need space to store the spirits to age.

 

I have been going through the codes and can't seem to find how to protect
spirits (over 20% alcohol) stored in wooden barrels in single, double and
multi row racks.

 

Can someone point me in the right direction

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Compact Mobile Storage Shelves

2017-01-09 Thread James Crawford
We have a client in a retail mall that uses compact mobile storage shelves
at the back of their unit for product storage, I have looked through NFPA
#13 (2013) and can only find information for an office application. (sec
20.6)

 

Is there something I have missed that would allow this type of storage in an
Ordinary Hazard application, retail store?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


NFPA #30 Rack Storage

2017-01-20 Thread James Crawford
Reference NFPA #30 (2008ed)

 

Table 16.5.2.1 for non-relieving style containers for 5-60 gal containers on
single and double row racks to 20'-0"

 

So we are using 0.40/3000 plus in-racks based on layout E

 

Layout E shall mean one line of in-rack sprinklers in the flue space at
every level beginning above the first storage level above the floor and face
sprinklers at the first storage level at each upright. In-racks sprinklers
shall be spaced not more than 9 ft on centre and shall be staggered
vertically.

 

As this option is for single and double row racks, I am unsure about the
layout for the single row racks as we normally do not see face sprinklers on
single row racks. NFPA #30 does not provide any details on this option.

 

Any feedback would be appreciated.

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Artifical Turf

2017-01-31 Thread James Crawford
We are looking at a client the stores artificial turf in rolls and would
like to store on racking.

 

The racking is multi row racking and the turf is made from polyethylene.

 

My first thought is to protect the same as carpet storage, or can it be
protected as non-expanded group ""A" plastics.

 

The existing sprinkler system is ESFR K17 operating at 52 psi.

 

Thoughts

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Paint Booth Exhaust Stack

2017-03-16 Thread James Crawford
NFPA #33 (2016 ed) section 9.4.6 (2) Horizontal Exhaust ducts shall have
sprinklers located on 12'-0" centers beginning no more that 6'-0" from the
duct entrance.

 

If the horizontal run is only 2'-0" do you require a sprinkler head to
protect this section of the duct, (is there a minimum distance)

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Paint Booth Exhaust Stack

2017-03-16 Thread James Crawford
We have a head at the top but as it comes down they had to offset  to miss a 
joist so there are 2 90 degree bends and a small pup piece that make up 24” 
center to center, just trying to see if we need a head in the offset.

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rongreenman .
Sent: Thursday, March 16, 2017 2:53 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Paint Booth Exhaust Stack

 

My read on this would be that if you gave a sprinkler in the middle of a 24" 
horizontal duct you have 12" on center. Don't you need one at the top of each 
vertical run?

On Thu, Mar 16, 2017 at 1:47 PM James Crawford  wrote:

NFPA #33 (2016 ed) section 9.4.6 (2) Horizontal Exhaust ducts shall have 
sprinklers located on 12’-0” centers beginning no more that 6’-0” from the duct 
entrance.

 

If the horizontal run is only 2’-0” do you require a sprinkler head to protect 
this section of the duct, (is there a minimum distance)

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

-- 

Sent from Gmail Mobile

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Paint Booth Exhaust Stack

2017-03-16 Thread James Crawford
The exhaust stack has a total length of 20'-0", there is a head at the top
of the stack and heads behind the filters, the fan is located at the base of
the stack.

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Art Tiroly
Sent: Thursday, March 16, 2017 2:56 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Paint Booth Exhaust Stack

 

Is that the total duct length or is there a riser to the roof?

Are there heads in the plenum behind the filter?

Where is the exhaust  fan?

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of James Crawford
Sent: Thursday, March 16, 2017 4:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Paint Booth Exhaust Stack

 

NFPA #33 (2016 ed) section 9.4.6 (2) Horizontal Exhaust ducts shall have
sprinklers located on 12'-0" centers beginning no more that 6'-0" from the
duct entrance.

 

If the horizontal run is only 2'-0" do you require a sprinkler head to
protect this section of the duct, (is there a minimum distance)

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

 


 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campai
gn=sig-email&utm_content=emailclient&utm_term=icon> 

Virus-free.
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campai
gn=sig-email&utm_content=emailclient&utm_term=link> www.avast.com 

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Dry Horizontal sidewalls

2017-03-20 Thread James Crawford
Reliable has an extended coverage dry side wall with upto 28’ in width spray, 
light hazard only

 

https://www.reliablesprinkler.com/sites/default/files/products/bulletins/055%20Model%20DH80%20Dry.pdf

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matt Grise
Sent: Monday, March 20, 2017 9:36 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Dry Horizontal sidewalls

 

I have never been able to find a dry sidewall that could cover more than 16’ in 
width.

 

As far as turning a sidewall to direct the spray – I don’t know…  I would 
definitely contact the manufacturer to ask about it. If you install the head 
outside of its listing then any problem that comes up with its performance will 
land on you.

 

Matt 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mick Dugal
Sent: Monday, March 20, 2017 11:31 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Dry Horizontal sidewalls

 

no?

 

On Thu, Mar 16, 2017 at 9:37 AM, Mick Dugal  wrote:

I've got a question about installation of dry horizontal sidewall sprinklers. 
Is it permitted to install them at an angle? Not aiming up or down but side to 
side? I have an odd shaped canopy that I'm trying to cover with dry sprinklers 
but one particular area is lacking coverage. If I could angle the sprinkler 
towards this location (on the horizontal plane) I could cover it.

 

Or, as a side question, does anyone know of an extended coverage dry barrel 
sidewall sprinkler with 20 ft spacing on the width? This would also solve my 
problem but options are limited on the dry sprinklers with extended coverage.

 

Thanks,

Mick

 

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Rubber Tire Storage

2017-04-11 Thread James Crawford
We have an existing building protected with ESFR K17 sprinkler heads
operating at 52 psi for 35' storage in a 40' high building.

 

They want to store rubber tires and are asking what they can do, I am using
NFPA #13 (2013ed) for reference.

 

Table 18.4(d) ESFR sprinkler protection for maximum 40' building would allow
rubber tire storage on side in palletized portable racks, and that is all.

 

They would like to use fixed racks without solid shelves, but I do not see
this as an option, any ideas why this has been removed as the building gets
higher?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Rubber Tire Storage

2017-04-11 Thread James Crawford
I was sure that was the reason I just thought that fixed rack storage would 
have been the first test done as this is provided for the lower height building 
30’ and 35’ and the same storage height.

 

I guess it just come down to money for testing

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Bruce Verhei
Sent: Tuesday, April 11, 2017 3:31 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Rubber Tire Storage

 

Full scale fire tests?




On Apr 11, 2017, at 15:24, James Crawford  wrote:

We have an existing building protected with ESFR K17 sprinkler heads operating 
at 52 psi for 35’ storage in a 40’ high building.

 

They want to store rubber tires and are asking what they can do, I am using 
NFPA #13 (2013ed) for reference.

 

Table 18.4(d) ESFR sprinkler protection for maximum 40’ building would allow 
rubber tire storage on side in palletized portable racks, and that is all.

 

They would like to use fixed racks without solid shelves, but I do not see this 
as an option, any ideas why this has been removed as the building gets higher?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: ESFR Sprinkler spacing

2017-04-19 Thread James Crawford
Jerry

 

The 11’ can be used in order to miss joist obstruction but there are other
restrictions that must be met to ensure that the heads on either side are
not over spaced also.

 

So if you need to go to the 11’ for one head the next one cannot be over 9’
keeping the total spacing for these 2 heads at 20’ or (110 ft² + 90
ft²)/2=100 ft²

 

They would rather have one head over spaced then obstructed, just not every
head 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Jerry Van Kolken
Sent: Wednesday, April 19, 2017 9:31 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: ESFR Sprinkler spacing

 

I’m designing a system using the ESFR sprinkler. This building is over
30’-0” tall, and on the cut sheet it says the max. sprinkler spacing is
10’-0”.

 

Does this mean I cannot use the spacing allowancing indicated in NFPA
13-8.12.3.1 (3) or (4) (2013 ed.) spacing the sprinkler up to 11’-0”?

 

 

Jerry Van Kolken

Millennium Fire Protection Corp.

2950 San Luis Rey Rd.

Oceanside, CA 92058

(760) 722-2722 FX 722-2730

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Dip tanks

2017-05-02 Thread James Crawford
I have been looking through NFPA #34 (2007) to find out if there is a
minimum or maximum size for a dip tank and the requirements for them

 

We have a client with a small dip tank for cleaning parts prior to powder
coating, the tank holds less than 2 gallons of flammable liquid and has a
surface area of less than 2 ft². The tank is metal and has a lid when not in
use. The tank is in a ventilated area, inside a paint booth.

 

This is a small operation and the bake oven is also in the paint booth, the
concern I see is the electrical associated with the bake ovens and the
proximity to the dip tank.

 

All the dipping is manual. The sequence is dipping, drying, power coating
then baking, like I said small operation

 

Is there anything I am missing.

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Rubber Tire Storage

2017-05-17 Thread James Crawford
Reference is NFPA #13 (2013 ed)

 

Table 18.4.(d) for a maximum 40'-0" high building there are 3 options.

 

On side in palletized portable rack

 

On tread or laced in open portable steel rack

 

On tread, on side, and laced tires in open portable steel racks or
palletized portable rack

 

I was just wondering what happened to fixed steel racks or are they not
allowed for buildings above 35'.

 

I was checking in the FM data sheet and they do not seem to differentiate on
the storage style, fixed, portable or palletized portable.

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Flammable & Combustible storage

2017-05-23 Thread James Crawford
NFPA #30  (2008 ed)

 

We have a client that has a Liquid warehouse (1,200 ft²) that did not
require sprinkler protection by code, but did require sprinkler protection
by the AHJ to get a building permit. The system is an Ordinary hazard group
2 dry system.

 

They store class II and IIIB liquids in steel drums and Plastic IBC,
originally storage was on the floor to 4’-0” one drum or tote high.

 

But as with all thing the company grows and they want to store higher.

 

Table 12.6.2.2 Quantity Limitations for unprotected Liquid Warehouses will
allow 10’-0” of class II and 15’-0” of class IIIB 

 

So my understanding is that unprotected is defined as not protected to NFPA
#30, so based on Table 12.6.2.2 they can store these products to the heights
noted even thou the area is sprinkled to NFPA #13 Ordinary hazard group 2.

 

Am I missing something?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Flammable & Combustible storage

2017-05-24 Thread James Crawford
The maximum allowable quantities have been met, the storage is lower than the 
MAQ even with the increased storage height.

 

If the building was not sprinkled or is sprinkled to light or ordinary hazard 
it would still be considered unprotected storage if I am reading the code 
right, and this is the problem that is stuck in my brain. Logic says that they 
should not be able to store this much flammable or combustible product in a 
building that is not sprinkled to allow it, but I cannot find anything that 
says they cannot.

 

As long as the quantities are below the MAQ and the storage heights are below 
the maximum allowed I see nothing that requires the building to be sprinkled to 
NFPA #30 standard.

 

Is my logic wrong?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: Wednesday, May 24, 2017 7:22 AM
To: SprinklerFORUM
Subject: Re: Flammable & Combustible storage

 

ASSUMING that the maximum allowed limit has anything to do with defining the 
applicable design basis is flawed.  Otherwise, this logic would mean that a 
light hazard classification is adequate.

 

 

Roland Huggins, PE - Senior VP Engineering

American Fire Sprinkler Assn.

Dallas, TX

http://www.firesprinkler.org <http://www.firesprinkler.org/> 

 

Fire Sprinklers Saves Lives

 

 

 

On May 23, 2017, at 4:04 PM, James Crawford  wrote:

 

NFPA #30  (2008 ed)

 

We have a client that has a Liquid warehouse (1,200 ft²) that did not require 
sprinkler protection by code, but did require sprinkler protection by the AHJ 
to get a building permit. The system is an Ordinary hazard group 2 dry system.

 

They store class II and IIIB liquids in steel drums and Plastic IBC, originally 
storage was on the floor to 4’-0” one drum or tote high.

 

But as with all thing the company grows and they want to store higher.

 

Table 12.6.2.2 Quantity Limitations for unprotected Liquid Warehouses will 
allow 10’-0” of class II and 15’-0” of class IIIB 

 

So my understanding is that unprotected is defined as not protected to NFPA 
#30, so based on Table 12.6.2.2 they can store these products to the heights 
noted even thou the area is sprinkled to NFPA #13 Ordinary hazard group 2.

 

Am I missing something?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email   <mailto:jcrawf...@phaserfire.ca> jcrawf...@phaserfire.ca

Web  <http://www.phaserfire.ca/> www.phaserfire.ca

 

___
Sprinklerforum mailing list
 <mailto:Sprinklerforum@lists.firesprinkler.org> 
Sprinklerforum@lists.firesprinkler.org
 <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


NFPA #30 In-Racks

2017-05-25 Thread James Crawford
NFPA #30 3008 ed.

 

We have worked through the tables and have determined that we need layout F
(6)

 

Section 16.5.1.10 (6) Layout F shall mean one line of in-rack sprinklers in
the flue space at every other storage level above the first storage level
and face sprinklers at the first storage level at each upright, in-rack
sprinklers shall be spaced not more than 10 ft on center and staggered
vertically.

 

So we have 5 levels of storage or 4 beam levels, based on the above I would
normally put the flue and face sprinklers above the first level of storage
and the second level of flue sprinklers at the 3rd beam level. But I find
the wording in the code to suggest that the face are above the 1st level of
storage and the flue sprinklers are at the 2nd and 4th storage level.

 

As some of the layouts designs talk about the floor level and others talk
about the first storage level, just looking for a little direction.

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Lithium Batteries

2017-07-18 Thread James Crawford
We have someone that has a 20' x 8' x8' metal shipping container in their
warehouse that they use to test lithium batteries, the AHJ want them to
sprinkler this space, but the application of water to the batteries is not
the best solution.

 

Any ideas out there?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Whiskey in Wooden barrels

2017-08-10 Thread James Crawford
We have been asked to look at protecting a small distillery that will be
storing or aging in wooden barrels stored on multi row racking.

 

As whiskey is more than 20% alcohol I assume we go to flammable liquids NFPA
#30, but they have nothing for protecting product stored in wooden barrels.

 

Can someone point me in the right direction

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Server Rooms

2017-08-16 Thread James Crawford
We have an AHJ that we are dealing with, that when the architect names a
small room as a server room, they are going to NFPA #13 (2016) section 22.14
Protection of Information Technology Equipment.

 

Most of the concerns seem to be from a small business taking a space and
have a room for a special computer or a small server bank, as most
businesses now seem to require.

 

NFPA #75  chapter 3 Definitions 3.3.10 Information Technology Equipment
Systems: Any electronic digital or analog computer, along with all
peripheral support, memory, programming, or other direct associated
equipment, records, storage, and activities.

 

Base on this definition every office that has a computer in it  is an
Information Technology Equipment room, where do we draw the line.

 

So I guess my question is when is a room with a computer in it a server room
and when is it just a room, or maybe when does a computer become a server?

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Server Rooms

2017-08-16 Thread James Crawford
More when we need to use the separate valve

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Matt Grise
Sent: Wednesday, August 16, 2017 12:33 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Server Rooms

 

Is the main  concern the need for a separate valve?

 

Matt 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of James Crawford
Sent: Wednesday, August 16, 2017 2:20 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Server Rooms

 

We have an AHJ that we are dealing with, that when the architect names a
small room as a server room, they are going to NFPA #13 (2016) section 22.14
Protection of Information Technology Equipment.

 

Most of the concerns seem to be from a small business taking a space and
have a room for a special computer or a small server bank, as most
businesses now seem to require.

 

NFPA #75  chapter 3 Definitions 3.3.10 Information Technology Equipment
Systems: Any electronic digital or analog computer, along with all
peripheral support, memory, programming, or other direct associated
equipment, records, storage, and activities.

 

Base on this definition every office that has a computer in it  is an
Information Technology Equipment room, where do we draw the line.

 

So I guess my question is when is a room with a computer in it a server room
and when is it just a room, or maybe when does a computer become a server?

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: [EXTERNAL] Server Rooms

2017-08-16 Thread James Crawford
The room is normally unoccupied

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Kyle.Montgomery
Sent: Wednesday, August 16, 2017 1:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] Server Rooms

 

Well, a server room would be unoccupied the majority of the time, right?

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of James Crawford
Sent: Wednesday, August 16, 2017 12:20 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] Server Rooms

 

We have an AHJ that we are dealing with, that when the architect names a
small room as a server room, they are going to NFPA #13 (2016) section 22.14
Protection of Information Technology Equipment.

 

Most of the concerns seem to be from a small business taking a space and
have a room for a special computer or a small server bank, as most
businesses now seem to require.

 

NFPA #75  chapter 3 Definitions 3.3.10 Information Technology Equipment
Systems: Any electronic digital or analog computer, along with all
peripheral support, memory, programming, or other direct associated
equipment, records, storage, and activities.

 

Base on this definition every office that has a computer in it  is an
Information Technology Equipment room, where do we draw the line.

 

So I guess my question is when is a room with a computer in it a server room
and when is it just a room, or maybe when does a computer become a server?

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Multi Row Racking Calculation

2017-08-23 Thread James Crawford
We are having a discussion in our office regarding the design area for multi
row racking for the in-rack sprinklers

 

We have aerosols stored in 3 deep multi row racks NFPA #30B (2007) Figure
6.3.2.7(b) 

 

We have 4 levels of in-racks spaced every 8' and in every flue space, with a
line feeding each flue space or 4 lines.

 

Design calls for 18 heads @ 30 gpm, 6 on each of the top 3 levels.

 

Discussion is do we calculate 6 heads on one line for 3 levels or do we
group them and do 2 heads on 3 lines for three levels?

 

comments

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Multi Row Racking Calculation

2017-08-23 Thread James Crawford
But section 6.3.2.9.1 says the hydraulically most remote

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of fpdcdes...@gmail.com
Sent: Wednesday, August 23, 2017 4:31 PM
To: Sprinklerforum
Subject: Re: Multi Row Racking Calculation

 

Hydraulically most demanding?


Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 (ofc)

860-553-3553 (fax)

860-608-4559 (cell)






On Aug 23, 2017 at 7:20 PM, mailto:jcrawf...@phaserfire.ca> > 
wrote:

We are having a discussion in our office regarding the design area for multi 
row racking for the in-rack sprinklers

 

We have aerosols stored in 3 deep multi row racks NFPA #30B (2007) Figure 
6.3.2.7(b) 

 

We have 4 levels of in-racks spaced every 8’ and in every flue space, with a 
line feeding each flue space or 4 lines.

 

Design calls for 18 heads @ 30 gpm, 6 on each of the top 3 levels.

 

Discussion is do we calculate 6 heads on one line for 3 levels or do we group 
them and do 2 heads on 3 lines for three levels?

 

comments

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___ Sprinklerforum mailing list 
Sprinklerforum@lists.firesprinkler.org 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: [FWD: CMSA Sprinklers and Isle Widths]

2017-08-24 Thread James Crawford
John

 

I forgot to mention that you cannot use ESFR for this protection scheme as they 
are not allowed on dry systems, and this is a freezer

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of j...@crwnfire.com
Sent: Wednesday, August 23, 2017 5:50 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [FWD: CMSA Sprinklers and Isle Widths]

 






 Original Message 
Subject: CMSA Sprinklers and Isle Widths
From: "John Paulsen" < <mailto:j...@crwnfire.com> j...@crwnfire.com>
Date: Wed, August 23, 2017 5:33 pm
To: "'Sprinklerforum'" < 
<mailto:sprinklerforum-boun...@lists.firesprinkler.org> 
sprinklerforum-boun...@lists.firesprinkler.org>

Good Afternoon Foramites:

 

We are working on a freezer food storage project utilizing K 16.8 CMSA 
sprinklers on double interlock pre-action systems. The deck height is 40’, max 
storage is 35’ and protecting a Class II commodity. 

 

Question #1: The owner wants to reduce the isle width from 10’-6” to 6’-6” and 
he believes this has an impact on the CMSA spacing. As far as I can tell from 
Table 16.3.1.1, isle widths greater than 4’ are permitted without changing the 
10’X10” spacing, correct?

 

Question #2: Now that I’ve starred at Table 16.3.1.1 (2013) for the last hour, 
it appears to me that a single row of rack sprinklers are required at 20’ with 
a horizontal barrier when using CMSA sprinklers, correct? Table 16.3.2.1 only 
serves to confuse me more. 

 

It looks like to me that rack sprinklers can be eliminated when you go to ESFR 
sprinklers in accordance with Table 16.3.3.1

 

Thanks,

 

John Paulsen – SET

Crown Fire System Design

6282 Seeds Rd.

Grove City, OH 43123

P – 614-782-2438

F – 614-782-2374

C – 614-348-8206

 

 

 

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: [FWD: CMSA Sprinklers and Isle Widths]

2017-08-24 Thread James Crawford
John

 

I believe the testing of the CMDA heads for this Table are based on a 4’-0” 
aisle, so any aisle with more than 4’-0” would not change the spacing of the 
sprinkler heads.

 

Table 16.3.1.1 is for CMDA sprinkler heads and depending on the option you 
choose there is a requirement for the solid shelf, but there are many options c 
to g . As in all design it is finding the one that works and is the most cost 
effective and meets the client’s requirements. They may not want a barrier in 
their racking. 

 

You mentioned CMSA sprinkler protection so you would not use Table 16.3.1.1 you 
would use Table 16.3.2.1

 

Table 16.3.2.1 is for CMSA single, double and multi row racks, you said you 
were protecting class II stored to 35’ in a 40’ high building in a freezer so I 
assume you are using the K16.8 head, this has no in-rack requirement but a 
delivery time is required.

 

Good luck hope this helps

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of j...@crwnfire.com
Sent: Wednesday, August 23, 2017 5:50 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [FWD: CMSA Sprinklers and Isle Widths]

 






 Original Message 
Subject: CMSA Sprinklers and Isle Widths
From: "John Paulsen" < <mailto:j...@crwnfire.com> j...@crwnfire.com>
Date: Wed, August 23, 2017 5:33 pm
To: "'Sprinklerforum'" < 
<mailto:sprinklerforum-boun...@lists.firesprinkler.org> 
sprinklerforum-boun...@lists.firesprinkler.org>

Good Afternoon Foramites:

 

We are working on a freezer food storage project utilizing K 16.8 CMSA 
sprinklers on double interlock pre-action systems. The deck height is 40’, max 
storage is 35’ and protecting a Class II commodity. 

 

Question #1: The owner wants to reduce the isle width from 10’-6” to 6’-6” and 
he believes this has an impact on the CMSA spacing. As far as I can tell from 
Table 16.3.1.1, isle widths greater than 4’ are permitted without changing the 
10’X10” spacing, correct?

 

Question #2: Now that I’ve starred at Table 16.3.1.1 (2013) for the last hour, 
it appears to me that a single row of rack sprinklers are required at 20’ with 
a horizontal barrier when using CMSA sprinklers, correct? Table 16.3.2.1 only 
serves to confuse me more. 

 

It looks like to me that rack sprinklers can be eliminated when you go to ESFR 
sprinklers in accordance with Table 16.3.3.1

 

Thanks,

 

John Paulsen – SET

Crown Fire System Design

6282 Seeds Rd.

Grove City, OH 43123

P – 614-782-2438

F – 614-782-2374

C – 614-348-8206

 

 

 

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Racking Question

2017-08-24 Thread James Crawford
We had a set of double row racks with a 12" flue space, this has been
changed due to seismic requirements to 34".

 

Is this still a double row rack or is it now multi row racking or is it two
single row racks?

 

Longitudinal space is over 24", but total racking width is less than 12'-0",
the 34" is not an aisle as we have structural columns in this space.

 

  --

|
|  28" 



 

 
34"

-

|
| 28"

-----

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Racking Question

2017-08-25 Thread James Crawford
The racking is for flammable and combustible liquids and are stored to
20'-0"

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

From: Anthony Carrizosa [mailto:anth...@archerconstruction.com] 
Sent: Friday, August 25, 2017 7:15 AM
To: 'James Crawford'; sprinklerforum@lists.firesprinkler.org
Subject: RE: Racking Question

 

James

Looking at your email it appears that you have 28" shelves separated by a
34" isle.

 

Look at the definition of shelf storage  3.9.2.6. 

 

If this is the case then you would design for storage on shelving not racks.
You don't say what your commodity is or how high the storage is but I would
assume less than 12'.

Perhaps you will find your storage arrangement in chapter 14. Good Luck.

Anthony Carrizosa 

Fire Protection Division 

OFFICE: 253-872-7222 

Cell: 206-679-5283

cid:703393518@19082013-11F7

 

 

From: James Crawford [mailto:jcrawf...@phaserfire.ca] 
Sent: Thursday, August 24, 2017 2:22 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Racking Question

 

We had a set of double row racks with a 12" flue space, this has been
changed due to seismic requirements to 34".

 

Is this still a double row rack or is it now multi row racking or is it two
single row racks?

 

Longitudinal space is over 24", but total racking width is less than 12'-0",
the 34" is not an aisle as we have structural columns in this space.

 

  --

|
|  28" 



 

 
34"

-

|
| 28"

-----

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Commodities

2017-09-15 Thread James Crawford
We have a client the stores fresh fish in Styrofoam coolers for shipping..

 

The way I see it we are protecting the Styrofoam cooler more that the fish,
but I see very little that provides protection for an expanded Group "A"
plastic product stored on multi row racking in a refrigerated cooler.

 

Suggestion

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Spacing EC heads per FM 3-26

2017-09-22 Thread James Crawford
You would use the 16'x16' once you go over the 14' mark

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Jerry Van Kolken
Sent: Friday, September 22, 2017 9:08 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Spacing EC heads per FM 3-26

 

I have a job where I'm using EC heads per FM 3-26 table 2 in a HC-3 hazard.

 

When calc'n EC normally I've always used the design criteria recommendations
per the cut sheet (ex. for 14x14 spacing use this psi / gpm etc.)

 

But in this this situation would it be recommend to stick to the 14x14 or
16x16 spacing, or could I use the demand requirements for how the head is
space, say 15x15?

 

 

Jerry Van Kolken

Millennium Fire Protection Corp.

2950 San Luis Rey Rd.

Oceanside, CA 92058

(760) 722-2722 FX 722-2730

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Barns & Stables

2017-11-03 Thread James Crawford
We were asked to have a look a sprinkling a horse barn and thought that
should not be a problem, but when we got to site there was a large storage
of hay.

 

NFPA #13 has barns and stables as Ordinary hazard group 2, but I assume only
a small amount of hay bales is expected. 

 

Hay bales are currently about 16'-0" high by about 30' deep and 20' wide.
One pile.

 

Anyone out there that has protected barns that could provide a little
guidance.

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


compressor size

2017-11-08 Thread James Crawford
Is there an easy equation out there to see how many CFM I require to fill a
dry system, I am sizing an air compressor and would like to ensure I do not
over or undersize it.

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Obstructions with CMSA

2017-11-24 Thread James Crawford
Looking for some input as some of the wording does not make sense.

 

NFPA #13 (2013 ed)

CMSA

Section 8.11.5.3.4 Where the bottom of the obstruction is located 24in or
more below the sprinkler deflector, the following shall occur:

 

This would seem to infer that all the items listed must be met, but for item
2b and 3b you require a sprinkler head under the obstruction, so if you put
a head under the obstruction do you still need to meet Item 1 and center the
obstruction between heads. This does not make sense.

 

Opinions please as we have an AHJ that is asking for the obstruction to be
relocated and for the head under it.

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Cartoned Expanded Group "A" Plastics

2017-12-12 Thread James Crawford
There does not seem to be a protection scheme for cartoned expanded Group
"A" plastics for buildings above 32'-0" ceiling heights, but there is now
one for exposed expanded Group "A" plastics for building up to 40'-0"
ceiling heights (NFPA #13 2016 ed).

 

Have I missed something or do you used exposed expanded to protect cartoned
expanded and if so why not state that. We have AHJs that if the code does
not provide a protection scheme you cannot store that product even if there
are schemes to protect a more hazardous product.

 

Comments please.

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Cartoned Expanded Group "A" Plastics

2017-12-12 Thread James Crawford
Thanks Craig

 

I normally use FM data sheets as back up information or design criteria if
there is nothing in the NFPA standards, I just found it strange that there
was information for exposed but not for cartoned.

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Prahl, Craig/GVL
Sent: Tuesday, December 12, 2017 12:14 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Cartoned Expanded Group "A" Plastics

 

When the NFPA Standards do not specifically address a particular situation,
it is common to reach out to other recognized industry standards for
guidance.  FM Data Sheets often provide that info or you may find other
Standards or Industry Practices/Guidelines that address a unique condition
that NFPA does not.

 

Within the NFPA Standards is section 1.5, Equivalency.  Within this section
there is a provision for use of alternate methods or materials which can be
substantiated to achieve an intended equal or better level of protection
when presented and accepted by the AHJ.  

 

I have never had an AHJ reject an alternative methodology when citing a
known industry resource.  

 

Another avenue is to research the various sprinkler manufacturers to see
what new offering they may have recently had Listed and/or Approved.  There
are times when a new sprinkler is released for sale and it is not included
in the current NFPA offering.  Again, present that as your "equivalency" to
the AHJ.

 

As far as using a "higher hazard" criteria to protect a perceived "lesser
hazard", well, could you unequivocally defend that decision?  It's not a
matter of logic or gut feelings, it has to have some basis in actual testing
or calculations to prove the concept.  

 

The differentiating factor dealing with cartooned versus exposed is that,
simply put, cartoned criteria will assume absorption of sprinkler discharge
to help create a delay in ignition of the contents due to the soaked carton
acting as somewhat of a heatsink, preventing direct contact of the plastic
commodity with the flame front. 


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
craig.pr...@ch2m.com



 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of James Crawford
Sent: Tuesday, December 12, 2017 1:04 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Cartoned Expanded Group "A" Plastics [EXTERNAL]

 

There does not seem to be a protection scheme for cartoned expanded Group
"A" plastics for buildings above 32'-0" ceiling heights, but there is now
one for exposed expanded Group "A" plastics for building up to 40'-0"
ceiling heights (NFPA #13 2016 ed).

 

Have I missed something or do you used exposed expanded to protect cartoned
expanded and if so why not state that. We have AHJs that if the code does
not provide a protection scheme you cannot store that product even if there
are schemes to protect a more hazardous product.

 

Comments please.

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


S & L Rule

2017-12-21 Thread James Crawford
We have been having a discussion in the office about the S&L rule for
spacing of sprinkler heads. We received a sprinkler drawing with some
spacing that we do not agree with, see below, but can find no specific
direction in NFPA #13 (2013) that says it is wrong.

 

Basic situation we have a small building with a 20’ bay and a 30’ bay.
Ordinary hazard spacing.

 

For the 20’ wide bay, we have2  lines spaced at 10’ apart , so we have 5’
off the wall then 10’ between the next line and 5’ to the beam line, the
heads are spaced at 13’ along these lines. 

 

Then we have a 30’ bay  where we have 2 lines spaced 15’ apart, 7’6 off the
beam then 15’ between the heads then 7’6 to the wall, heads are spaced at 8’
along the line

 

So our discussion is the sprinkler lines along the beam line which would be
5’-0” plus 7’-6” for 12’-6” between the line. The sprinkler heads in the 20’
bay are spaced at 13’-0”, so if we use the S&L rule these heads are spaced
at 12’-6” x 13’-0” or 162.6 ft². Is this correct?

 

And yes I know we could space the 30’ bay with 3 lines at 10’ apart and that
is what I would do but it is not our design.

 

Comments

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: S & L Rule

2017-12-21 Thread James Crawford
Assumed a flat ceiling

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Joe Burtell
Sent: Thursday, December 21, 2017 2:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: S & L Rule

 

Is the spacing along the branchline measured along the floor or the roof pitch?




Best regards,

Joe Burtell, SET, CFPS

 

Burtell Fire_Small

Phone | Fax | Mobile| Text 406-545-0784  

116 N. 11th Street | Billings, MT 59101

Email: j...@burtellfire.com

Web Site:  <http://www.burtellfire.com/> http://www.burtellfire.com

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

NOTICE:  The information contained in this e-mail transmission is intended only 
for use of the individual or entity named above.  This e-mail transmission, and 
any documents, files, previous e-mail transmissions or other information 
attached to it, may contain confidential information that is legally 
privileged.  If you are not the intended recipient of this e-mail transmission, 
or the employee or agent responsible for delivering it to the intended 
recipient, you are hereby notified that any disclosure, dissemination, 
distribution, copying or other use of this transmission or any of the 
information contained in or attached to this e-mail is strictly prohibited.  If 
you have received this e-mail transmission in error, please immediately notify 
us by return e-mail transmission and destroy the original e-mail transmission 
as well as its attachments without reading or saving it in any manner.  Thank 
you.

 

On Thu, Dec 21, 2017 at 3:00 PM, James Crawford  wrote:

We have been having a discussion in the office about the S&L rule for spacing 
of sprinkler heads. We received a sprinkler drawing with some spacing that we 
do not agree with, see below, but can find no specific direction in NFPA #13 
(2013) that says it is wrong.

 

Basic situation we have a small building with a 20’ bay and a 30’ bay. Ordinary 
hazard spacing.

 

For the 20’ wide bay, we have2  lines spaced at 10’ apart , so we have 5’ off 
the wall then 10’ between the next line and 5’ to the beam line, the heads are 
spaced at 13’ along these lines. 

 

Then we have a 30’ bay  where we have 2 lines spaced 15’ apart, 7’6 off the 
beam then 15’ between the heads then 7’6 to the wall, heads are spaced at 8’ 
along the line

 

So our discussion is the sprinkler lines along the beam line which would be 
5’-0” plus 7’-6” for 12’-6” between the line. The sprinkler heads in the 20’ 
bay are spaced at 13’-0”, so if we use the S&L rule these heads are spaced at 
12’-6” x 13’-0” or 162.6 ft². Is this correct?

 

And yes I know we could space the 30’ bay with 3 lines at 10’ apart and that is 
what I would do but it is not our design.

 

Comments

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318  

Fax 604-888-4732  

Cel 604-790-0938  

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: S & L Rule

2017-12-22 Thread James Crawford
The building is 120’ long and has multiple bays, just using the 2 bays as an 
example of the spacing.

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Charles Bamford
Sent: Friday, December 22, 2017 7:55 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: S & L Rule

 

30' x 20' =  600 sq ft

600/ 130 = 4.6   round up  6 sprinkler heads

 

Run Branch lines perpendicular to  what you are hanging from.

5' off wall  10' between heads for

100 sq ft per sprinkler head 

or

15' x  6'8" (3'4" off wall)

 

with smaller sq.ft. spacing you get less GPM per head in calcs.

so if its .20 density you flow

20 gpm/hd  (if 120sqft/hd you would flow 24gpm)

 

Merry Christmas

Chuck Bamford

 

 

 

On ‎Thursday‎, ‎December‎ ‎21‎, ‎2017‎ ‎02‎:‎01‎:‎03‎ ‎PM‎ ‎PST, James Crawford 
 wrote: 

 

 

We have been having a discussion in the office about the S&L rule for spacing 
of sprinkler heads. We received a sprinkler drawing with some spacing that we 
do not agree with, see below, but can find no specific direction in NFPA #13 
(2013) that says it is wrong.

 

Basic situation we have a small building with a 20’ bay and a 30’ bay. Ordinary 
hazard spacing.

 

For the 20’ wide bay, we have2  lines spaced at 10’ apart , so we have 5’ off 
the wall then 10’ between the next line and 5’ to the beam line, the heads are 
spaced at 13’ along these lines. 

 

Then we have a 30’ bay  where we have 2 lines spaced 15’ apart, 7’6 off the 
beam then 15’ between the heads then 7’6 to the wall, heads are spaced at 8’ 
along the line

 

So our discussion is the sprinkler lines along the beam line which would be 
5’-0” plus 7’-6” for 12’-6” between the line. The sprinkler heads in the 20’ 
bay are spaced at 13’-0”, so if we use the S&L rule these heads are spaced at 
12’-6” x 13’-0” or 162.6 ft². Is this correct?

 

And yes I know we could space the 30’ bay with 3 lines at 10’ apart and that is 
what I would do but it is not our design.

 

Comments

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Rubber Tire Storage

2018-01-25 Thread James Crawford
NFPA #13 (2013) is my reference.

 

I have an AHJ that is telling me that Rubber Tires are classified as a Group
"A" plastic for the purpose of commodity classifications.

 

I have informed him that Rubber Tires are a commodity classification on
their own, but he disagrees, he says there are a synthetic rubber so are a
Group "A" plastic.

 

I have shown him the Table A5.6.3 for Commodity classifications in NFPA #13
where rubber tires are not mentioned and chapter 18 that deals with Rubber
Tire storage but he still disagrees.

 

Any suggestions?  

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Tank Storage

2018-02-13 Thread James Crawford
I was asked to do a review of a building that collects waste from commercial
grease traps. They take this waste back to their warehouse and put it in
large tanks (120,000 liters) to allow separation. 75% water, 20% vegetable
oils and animal fats, 5% solids.

 

Once separated the waste materials are then disposed of separately.

 

I am trying to classify the mixture that is stored in the tanks, but can
find no direction in NFPA #13, but due to the concentration of water to oils
I am leaning toward a non-combustible liquid. But that being said I can find
no direction on tank storage for a non-combustible liquid.

 

Any help out there

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Glazing Protection with standard spray

2018-02-13 Thread James Crawford
We have always addressed this under an alternative solution as the glazing
and doors are normally in a rated assembly and as such an alternative
solution was required by the architect and provided by a fire protection
engineer or code consultant.

 

We would have WS on the glazing and QR pendants over the doors with baffles
between the SSP and WS

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mike Stossel
Sent: Tuesday, February 13, 2018 3:17 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Glazing Protection with standard spray

 

Not sure if this will help you in anyway, but what about section D.1.1.1.1
in NFPA 13.  

 

Mike Stossel SET

400dpiLogoCropped

36 Barren Road

East Stroudsburg, PA 18302

Office: 973-670-2627

 <mailto:m...@knssprinkler.com> m...@knssprinkler.com

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Jerry Van Kolken
Sent: Tuesday, February 13, 2018 6:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Glazing Protection with standard spray

 

The door is part of the assembly but, I just found out this is the area
where they were intending to Std Spray in lieu of WS. 

 

Jerry Van Kolken

Millennium Fire Protection

(760) 722-2722

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Prahl, Craig/GVL
Sent: Tuesday, February 13, 2018 3:06 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Glazing Protection with standard spray

 

There isn't any prescribed protection for door glazing.  There is a window
sprinkler, I think it was by Tyco that when installed per its listing was
considered equivalent to 2-hour protection but that was for fixed glazing
and with some restrictions.

 

Is this door part of a fire rated assembly or area separation?

 


Craig L. Prahl 
Fire Protection Group Lead/SME
Direct - 864.920.7540

Fax - 864.920.7129
Direct Extension  77540
CH2M is now Jacobs.
200 Verdae Blvd.
Greenville, SC  29607
craig.pr...@ch2m.com
 <http://www.jacobs.com/> http://www.jacobs.com

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Jerry Van Kolken
Sent: Tuesday, February 13, 2018 5:58 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Glazing Protection with standard spray [EXTERNAL]

 

Okay, Is been about a decade since I've dealt glazing protection. Is there
any information on protecting window with standard spray sprinklers. I've
been told this was direction was approved by the AHJ.

 

Jerry Van Kolken

Millennium Fire Protection

(760) 722-2722

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Butane

2018-03-20 Thread James Crawford
I am looking at a space for a client that want to store butane, a lot of
butane.

 

I have been looking through NFPA #30 & #32 for some guidance but I am still
unsure, as one of the MSDS sheets says to protect it as outlined in NFPA #30
but my brain is saying it is more like a Level 3 Aerosol.

 

The building is protected with ESFR K17 @ 35psi

 

Any words of wisdom out there?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180320/15b72ced/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Butane

2018-03-20 Thread James Crawford
Small metal containers in cardboard boxes on pallets then stored on single
and double row racks



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca
Web www.phaserfire.ca




-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Prahl, Craig/GVL
Sent: Tuesday, March 20, 2018 12:39 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Butane

In what type of containers is the butane?

How will it be packaged or stored?  Cartoned, Racks, palletized, etc.?




Craig L. Prahl 
Fire Protection Group Lead/SME
Direct - 864.920.7540
Fax - 864.920.7129
Direct Extension  77540
CH2M is now Jacobs.
200 Verdae Blvd.
Greenville, SC  29607
craig.pr...@ch2m.com
http://www.jacobs.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of James Crawford
Sent: Tuesday, March 20, 2018 3:23 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Butane [EXTERNAL]

I am looking at a space for a client that want to store butane, a lot of
butane.

 

I have been looking through NFPA #30 & #32 for some guidance but I am still
unsure, as one of the MSDS sheets says to protect it as outlined in NFPA #30
but my brain is saying it is more like a Level 3 Aerosol.

 

The building is protected with ESFR K17 @ 35psi

 

Any words of wisdom out there?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

-- next part --
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20180320/15b72ced/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Butane

2018-03-20 Thread James Crawford
Yes they are pressurized



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca
Web www.phaserfire.ca



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Fpdcdesign
Sent: Tuesday, March 20, 2018 1:32 PM
To: Sprinklerforum
Subject: Re: Butane

 
 

 Are the containers pressurized?
 
 
 
 Todd G Williams, PE
Fire Protection Design/Consulting
 
Stonington, CT
 
860-535-2080 (ofc)
 
860-553-3553 (fax)
 
860-608-4559 (cell)
 
 
 
 

 
 
>  
> On Mar 20, 2018 at 3:46 PM,  mailto:rongreen...@gmail.com)>
wrote:
>  
>  
>  
>  Not to sound like I'm diminishing the danger of large quantities of 
> stored butane, and in fact I might be suggesting it is more dangerous 
> than an aerosol, but the definition of aerosol is: A gaseous 
> suspension of fine solid or liquid particles. Butane boils at 30.2 F 
> so at near or above freezing loose butane would be a gas. That might help
in yoir search.
>
>
>
> Ron Greenman
>
> rongreen...@gmail.com
>
> 253.576.9700
>
> The Universe is monstrously indifferent to the presence of man. 
> -Werner Herzog, screenwriter, film director, author, actor and opera 
> director (1942-)
>
> On Tue, Mar 20, 2018 at 12:38 PM, Prahl, Craig/GVL  
> 
> wrote: 
>
> >  In what type of containers is the butane? 
> >  
> >  How will it be packaged or stored? Cartoned, Racks, palletized, etc.? 
> >  
> >  
> >  
> >  
> >  Craig L. Prahl
> >  Fire Protection Group Lead/SME
> >  Direct - 864.920.7540
> >  Fax - 864.920.7129
> >  Direct Extension 77540
> >  CH2M is now Jacobs. 
> >  200 Verdae Blvd. 
> >  Greenville, SC 29607
> >  craig.pr...@ch2m.com
> >  http://www.jacobs.com
> >  
> >  -Original Message-
> >  From: Sprinklerforum
[mailto:sprinklerforum-bounces@lists.firesprinkler. 
> >  org] On Behalf Of James Crawford
> >  Sent: Tuesday, March 20, 2018 3:23 PM
> >  To: sprinklerforum@lists.firesprinkler.org
> >  Subject: Butane [EXTERNAL]
> >  
> >  I am looking at a space for a client that want to store butane, a 
> > lot of  butane.
> >  
> >  
> >  
> >  I have been looking through NFPA #30  &  #32 for some guidance but 
> > I am  still unsure, as one of the MSDS sheets says to protect it as 
> > outlined in  NFPA #30 but my brain is saying it is more like a Level 3
Aerosol.
> >  
> >  
> >  
> >  The building is protected with ESFR K17 @ 35psi
> >  
> >  
> >  
> >  Any words of wisdom out there? 
> >  
> >  
> >  
> >  
> >  
> >  Thank you
> >  
> >  
> >  
> >  
> >  
> >  James Crawford
> >  
> >  Phaser Fire Protection Ltd. 
> >  
> >  Phone 604-888-0318
> >  
> >  Fax 604-888-4732
> >  
> >  Cel 604-790-0938
> >  
> >  Email jcrawf...@phaserfire.ca
> >  
> >  Web www.phaserfire.ca
> >  
> >  
> >  
> >  -- next part --  An HTML attachment was 
> > scrubbed...
> >  URL:  <http://lists.firesprinkler.org/private.cgi/
> >  sprinklerforum-firesprinkler.org/attachments/20180320/
> >  15b72ced/attachment.html>
> >  ___
> >  Sprinklerforum mailing list
> >  Sprinklerforum@lists.firesprinkler.org
> >
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. 
> >  org
> >  ___
> >  Sprinklerforum mailing list
> >  Sprinklerforum@lists.firesprinkler.org
> >
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. 
> >  org
> >  
> -- next part -- An HTML attachment was 
> scrubbed...
> URL:  
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkl
> er.org/attachments/20180320/18030e92/attachment.html>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>  
-- next part --
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20180320/bc50019b/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Water Delivery Times

2018-05-18 Thread James Crawford
I have just been going through FM Data Sheet 8-9 for storage in a
cooler/freezer system and they are asking for a 20 second water delivery
time for a dry system, is this from the activation of the heads or the
activation of the dry pipe valve?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Listed Anti-freeze

2015-01-09 Thread James Crawford
Has anyone heard of a listed anti-freeze yet.

 

We have a dust collection system with spark arrestors and cyclones that are
all located outside. Normally we would use an anti-freeze system but as I
cannot find a listed product, is the only option to heat trace and insulate
the piping?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


NFPA #30 in-racks

2015-01-16 Thread James Crawford
We have a project that has one section of double row racking where they are
storing motor oils in plastic containers, one side would be protected by
scheme "A" and the other by scheme "B", based on size of containers being
stored.

 

Scheme "A" is every other row and scheme "B" is every row.

 

My question is, because they are back to back would we then protect both
sides as if they are scheme "B" and do every level, or do we protect each
side based on the commodity being stored? Note beam heights are at different
elevation for each side.

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


NFPA #30 in-racks

2015-01-16 Thread James Crawford
We have a project that has one section of double row racking where they are
storing motor oils in plastic containers, one side would be protected by
scheme "A" and the other by scheme "B", based on size of containers being
stored.

 

Scheme "A" is every other row and scheme "B" is every row.

 

My question is, because they are back to back would we then protect both
sides as if they are scheme "B" and do every level, or do we protect each
side based on the commodity being stored? Note beam heights are at different
elevation for each side.

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Rack storage question

2015-01-16 Thread James Crawford
I have always been under the assumption that it was up to the designer to
pick the option that worked the best, as available water pressure, owner
requirements and racking design would all play on which option to choose.
Some work better than others.

Just my opinion



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca

 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Dewayne Martinez
Sent: Wednesday, January 14, 2015 9:05 AM
To: SprinklerFORUM
Subject: FW: Rack storage question

Any takers on this one?



*From:* Dewayne Martinez [mailto:dmarti...@total-mechanical.com]
*Sent:* Tuesday, January 13, 2015 3:43 PM
*To:* 'sprinklerforum@lists.firesprinkler.org'
*Subject:* Rack storage question



NFPA 13 (07ed) Section 17.3.4.1

I have rack storage of plastic over 25ft high without solid shelves, double
row racks,8ft wide aisles.

It seems to comply with both  17.3.4.1.1 and 17.3.4.1.4, do I just pick
which one works out best for me?

Thanks,

Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Listed Anti-freeze

2015-01-21 Thread James Crawford
Spark detection system needs water instantly, there can be no delay.



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca




-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Todd Williams
Sent: Wednesday, January 21, 2015 7:25 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Listed Anti-freeze

What about a dry or preaction system?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com


> On Jan 9, 2015, at 12:19 PM, James Crawford 
wrote:
> 
> Has anyone heard of a listed anti-freeze yet.
> 
> 
> 
> We have a dust collection system with spark arrestors and cyclones 
> that are all located outside. Normally we would use an anti-freeze 
> system but as I cannot find a listed product, is the only option to 
> heat trace and insulate the piping?
> 
> 
> 
> 
> 
> Thank you
> 
> 
> 
> 
> 
> James Crawford
> 
> Phaser Fire Protection Ltd.
> 
> Phone  604-888-0318
> 
> Fax 604-888-4732
> 
> Cel 604-790-0938
> 
> Email  jcrawf...@phaserfire.ca
> 
> 
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


NFPA #30 Rack Storage

2015-01-23 Thread James Crawford
Reference NFPA #30 2008 ed.

 

We have class 1B & 1C in 45 gal metal drums non-relieving, stored on single
row racks to 20'

 

Table 16-5.2.1

 

Ceiling density of 0.40 over 3000 sq.ft plus in-racks following layout "E"

 

Section 16-5.1.10(5) layout E shall mean one line of in-rack sprinklers in
the flue space at every storage level above the floor and face sprinklers at
the first storage level at each rack upright. In-racks sprinklers shall be
spaced not more than 9 ft on center and staggered vertically. 

 

My question is if I have single row racks I have no flue space, so I would
run the piping in the rack, but do I still need the face sprinklers?

 

I have never done face sprinklers on single row racks.

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Fit fittings

2015-03-04 Thread James Crawford
2" Fitt had 2 tightening nuts on each opening end.



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca


 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Todd Williams
Sent: Wednesday, March 04, 2015 7:59 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Fit fittings

Did 2" Fit fittings have 2 tightening nuts or 4?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: ESFR Table 17.2.3.1 2013

2015-03-12 Thread James Crawford
Table 17.2.3.1 2013 ed

25' storage in a 30' high building  has ESFR K25 @ 15 psi, if you go to the
40' high building only the K14 & K17 are listed



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Gregg Fontes
Sent: Thursday, March 12, 2015 3:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: ESFR Table 17.2.3.1 2013

Forgot to add, I should have mentioned the heights in the first post. 

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of mphe...@aerofire.com
Sent: Thursday, March 12, 2015 2:45 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: ESFR Table 17.2.3.1 2013

Turn the page 

Mark at Aero
602 820-7894

Sent from my iPhone

> On Mar 12, 2015, at 4:33 PM, "Gregg Fontes"  wrote:
> 
> Why does the table not list/show the K25 ESFR fire sprinkler protection of
a exposed nonexpanded plastic and cartoned expanded plastics?  
> 
> Thanks,
> Gregg Fontes
> Cen-Cal Fire Systems, Inc.
> 209-334-9119
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: ESFR Table 17.2.3.1 2013

2015-03-12 Thread James Crawford
My error looking at Cartoned not exposed



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca




-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Gregg Fontes
Sent: Thursday, March 12, 2015 3:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: ESFR Table 17.2.3.1 2013

Forgot to add, I should have mentioned the heights in the first post. 

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of mphe...@aerofire.com
Sent: Thursday, March 12, 2015 2:45 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: ESFR Table 17.2.3.1 2013

Turn the page 

Mark at Aero
602 820-7894

Sent from my iPhone

> On Mar 12, 2015, at 4:33 PM, "Gregg Fontes"  wrote:
> 
> Why does the table not list/show the K25 ESFR fire sprinkler protection of
a exposed nonexpanded plastic and cartoned expanded plastics?  
> 
> Thanks,
> Gregg Fontes
> Cen-Cal Fire Systems, Inc.
> 209-334-9119
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


ESFR Sprinkler Heads

2015-03-19 Thread James Crawford
We are doing an addition to an existing warehouse, the existing warehouse is
protected with ESFR K14 uprights, since the building was constructed the AHJ
has dropped the water pressures in the area by 10 psi.

 

Due to the pressure drop I cannot use the K14 heads for the addition, can
you mix ESFR sprinkler heads in the same warehouse area, I would need K17
heads for the addition, The addition would be open to the existing warehouse
space. Or do I need to change all the heads in the existing warehouse to
match?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: ESFR Sprinkler Heads

2015-03-19 Thread James Crawford
Thanks Roland

The AHJ has impose a greater reduction and if I use the new pressures the
existing system is 3 psi short.

My concern with using two different K factor heads is the overlap area where
two different pressures would be required causing over discharge on the K17
heads.


Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Roland Huggins
Sent: Thursday, March 19, 2015 11:05 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: ESFR Sprinkler Heads

you can have multiple design basis covering different portions of a
building.  They could present different K-factors or types of sprinklers.
There are explicit requirements that address the interface between them.

What do you mean the AHJ has dropped the pressure?  Does that mean the water
purveyor has dropped the pressure to the area or that the AHJ has imposed a
greater reduction on the actual supply as a safety factor.  In other words,
is the existing system still providing adequate protection (not an issue for
imposed reductions) ?


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Mar 19, 2015, at 9:40 AM, James Crawford 
wrote:
> 
> We are doing an addition to an existing warehouse, the existing 
> warehouse is protected with ESFR K14 uprights, since the building was 
> constructed the AHJ has dropped the water pressures in the area by 10 psi.
> 
> 
> 
> Due to the pressure drop I cannot use the K14 heads for the addition, 
> can you mix ESFR sprinkler heads in the same warehouse area, I would 
> need K17 heads for the addition, The addition would be open to the 
> existing warehouse space. Or do I need to change all the heads in the 
> existing warehouse to match?
> 
> 
> 
> 
> 
> Thank you
> 
> 
> 
> 
> 
> James Crawford
> 
> Phaser Fire Protection Ltd.
> 
> Phone  604-888-0318
> 
> Fax 604-888-4732
> 
> Cel 604-790-0938
> 
> Email  jcrawf...@phaserfire.ca
> 
> 
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Mattresses

2015-03-20 Thread James Crawford
Looking input

 

We have a client that manufactures and stores mattresses, the raw material
is straight forward.

 

The finished product has always been a bit of a disagreement in our office.
NFPA #13 Table A.5.6.3.2 has mattresses under class 3 (standard box spring)
and group "A" plastics (foam in finished form) Having just purchased a new
mattress and box spring I understand that most new mattresses have a small
amount of foam in them and there are ones now that are all foam.

 

So my question is would a standard box spring mattress with a foam top, be
protected as a class 3 commodity or a Group "A" plastic? 

 

I have always protected as an expanded Group "A" plastic.

 

Agree or disagree

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


PODs Storage

2015-03-25 Thread James Crawford
I know this has been discussed before but I am looking for assistance.

 

We have a client that want to store personal storage bins, they are 6 sided
plywood boxes, 7'8"'x7'8"x7'8"', they are used to store customer's personal
belongings. So could contain almost anything. (no flammable liquids allowed)

 

They want to store them 4 high

 

The building is currently protected with ESFR K25 @ 25 psi

 

Due to the construction of the boxes and storage arrangement, I am unsure
that the ESFR will provide the required protection, but am unable to find
anything in the code about a protection scheme.

 

Any help is appreciated 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: absorbant in plastic drums

2015-03-26 Thread James Crawford
Powder in a paper bag is a class 2

Put it into a plastic barrel, similar to a plastic pallet you would increase
two classes to a class 4 commodity

Class 4 contains within itself or it's packaging an appreciable amount (5 to
15% by weight or 5 to 25% by volume) of group A plastics. What is the weight
of an empty barrel?

Seems to fall in this range.



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca




-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of craig.pr...@ch2m.com
Sent: Thursday, March 26, 2015 9:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: absorbant in plastic drums

The plastic drum will end up driving the design criteria, so treat it like
Group A plastics.  




Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Todd - Work
Sent: Thursday, March 26, 2015 11:09 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: absorbant in plastic drums

I am looking at a job where the product being stored is a granulated
absorbent (think stuff to put on concrete to absorb oil) in 55 gallon
plastic drums. New product, not used. I am teetering between Class IV and
Group A Plastic. Has anyone else working on something like this?

Sent from my iPad
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: flue space sprinkler spacing

2015-04-02 Thread James Crawford
For storage upto 25' use table 16.2.1.4.2.1 and for storage over 25' use
table 16.3.1.1



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Jamie Seidl
Sent: Thursday, April 02, 2015 2:04 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: flue space sprinkler spacing

For the life of me I cannot find the maximum horizontal spacing for in rack
flue sprinklers.
The project is under NFPA 13 2013, Commodity Class III single & double row
racks no solid shelves storage to 30', building height to 36' and I am using
table 16.3.4.1.1.1(c).  I know the diagram states that the storage cube is 4
to 5 feet, and shows sprinklers at every other cube, which would be 10' on
center, but I thought there was something in black and white, or actual
words about that.  I'd prefer not to infer.
Any help would be appreciated.
Thanks again for your help,
Jamie Seidl
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


ESFR & QR heads

2015-04-24 Thread James Crawford
We have a large manufacturing building, no interior walls,  we are looking
at and the owner has asked for OH2, then they have come back and requested
an area that they now wish to store 30' high with no in-rack protection.

 

Storage can be done with ESFR, the remainder of the building can be done
with QR brass uprights.

 

Question is do I require a draft curtain between the ESFR and the QR heads.
NFPA #13 (2013) 8.4.6.4 states the requirement for standard response heads, 

 

Just want to confirm.

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: ESFR & QR heads

2015-04-24 Thread James Crawford
I would like to have them do the entire warehouse 430,000 ft2 but they only
have 20,000 ft2 of storage so probably won't happen



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca




-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Roland Huggins
Sent: Friday, April 24, 2015 2:09 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: ESFR & QR heads

What Cecil said for NFPA 13. Their insurance carrier may whack you since
last time I checked (BEFORE THE BIG REVISION), FM required said separation
from all other sprinkler types and not just those with SR.

You can also do the whole building as ESFR so they can move their racks
around at their pleasure.  ESFR applies to LH and OH too.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Apr 24, 2015, at 1:51 PM, Sprinkler Academy - C Bilbo
 wrote:
> 
> It's all good.  No barrier required in your case.
> 
> It should be recognized that the above is my opinion as a member of the
NFPA, and has not been processed as a formal interpretation in accordance
with the NFPA Regulations Governing Committee Projects and should therefore
not be considered, nor relied upon, as the official position of the the
NFPA, nor any of their technical committees. 
> 
> Sincerely,
> 
> 
> Cecil Bilbo 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Standpipe design pressure

2015-06-08 Thread James Crawford
Our building code allows the pressure be lower if the building is
sprinklered and you do not require a fire pump to get the sprinkler system
to work, no minimum pressure is specified.

If a fire pump is required then you must meet the minimum of 100 psi as per
NFPA #14



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca




-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of mphe...@aerofire.com
Sent: Monday, June 08, 2015 7:00 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Standpipe design pressure

I have a question for the forum at large, and specifically for the NFPA 14
Committee Members. For the forum community "what is the minimum design
pressure required for a new class I automatic wet standpipe in your
location?" I know what the un-amended  code  says, but it includes the
catch-all qualification about the AHJ being consulted for specific needs.
So what I'm looking for is, in your region/area;

1- Does the local fire code accept the NFPA14 requirement for 100 psi
minimum operating pressure at the required flow rate?

2 - Does the local fire code amend the NFPA14 requirement from 100 psi to
something higher or lower?

3 - Does the local Fire Code Official regulate the NFPA14 requirements
without having amended the current fire code, ie, require a higher or lower
pressure than the written code?


Also, from the NFPA 14 committee, any comments on discussions leading up to
the change from 65psi to 100 psi, and your thoughts on the matter will be
appreciated.

In addition, related comments from the Fire Fighters among us, on actual
experience in the "heat of the battle", are most welcome.

And lastly, in respect of the Forum Traffic Control officials, please
respond to me directly "off forum" at
mphe...@aerofire.com<mailto:mphe...@aerofire.com>.

Mark at Aero
602 820-7894

Sent from my iPad
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Aircraft Hanger

2015-06-25 Thread James Crawford
We have a client in a Group 2 hanger protected with a closed head wet
system, that services helicopters and they drain the tank (100 gallons) but
there is still about 1 gallon left in the tank (1%)

 

NFPA 409 definitions for unfueled aircraft: An aircraft whose fuel system
has flammable or combustible liquid removed such that no tank, cell, or
piping contains more than ½ percent of it’s volumetric capacity.

 

Does this mean that they would not be allowed to use this space as a service
area because of ½ gallon of fuel.

 

I would assume that the ½% was based on larger quantities of fuel but have
not been able to get any answers, any comments.

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Multi row racking

2015-06-25 Thread James Crawford
Does Miscellaneous storage cover multi-row racking when the storage is less
than 12'-0". NFPA #13 Table 13.2.1 only says rack storage.

 

If yes then OH2 would protect class 2 commodities on multi row racking to
12'-0"

 

We have a client whose aisles are less than 3'-6" between single row racks,
so by definition they are multi row racking, used for pick shelving, the
option is to move them farther apart.

 

Comments

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


High Temp ESFR

2015-07-09 Thread James Crawford
As they do not manufacture high temperature ESFR sprinkler heads, what is
being done around unit heaters if the head is located within the 7'-0" high
temp area?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: High Temp ESFR

2015-07-09 Thread James Crawford
With a 10' x 10' spacing and the unit heater in the middle a head will
always be in the high temp zone, just wondering how others deal with this
situation.



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of John Denhardt
Sent: Thursday, July 09, 2015 11:10 AM
To: 
Subject: Re: High Temp ESFR

Move the heater.  

Sprinklers Save

> On Jul 9, 2015, at 1:41 PM, Mike Hairfield  wrote:
> 
> Use the 214 degree ones
> 
>> From: jcrawf...@phaserfire.ca
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: High Temp ESFR
>> Date: Thu, 9 Jul 2015 10:44:17 -0700
>> 
>> As they do not manufacture high temperature ESFR sprinkler heads, 
>> what is being done around unit heaters if the head is located within 
>> the 7'-0" high temp area?
>> 
>> 
>> 
>> 
>> 
>> Thank you
>> 
>> 
>> 
>> 
>> 
>> James Crawford
>> 
>> Phaser Fire Protection Ltd.
>> 
>> Phone  604-888-0318
>> 
>> Fax 604-888-4732
>> 
>> Cel 604-790-0938
>> 
>> Email  jcrawf...@phaserfire.ca
>> 
>> 
>> 
>> ___
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Plastics

2015-07-28 Thread James Crawford
NFPA #13 2013ed defines furniture with foam plastic cushions as Group "A"
plastics.

 

Would this be treated as an expanded Group "A" plastics because of the foam
cushions?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Plastics

2015-07-28 Thread James Crawford
Thanks Roland

This is good information on how NFPA is looking at it.



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca




-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: Tuesday, July 28, 2015 12:45 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Plastics

You can go through the exercise of the percentage allowed for Class IV but it’s 
hard to imagine the foam not being greater than 25% of the volume (using the 
2013 ed).  So that pushed it into a Group A plastic.  In the 2016 ed it will be 
further divided into expanded and non-expanded such that you can only have 5% 
of exposed expanded as a Class IV.  IF the exposed expanded is between %5 and 
25% then it is classified as a Group A Unexpanded.  Beyond that it is a exposed 
expanded.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Jul 28, 2015, at 11:36 AM, James Crawford  wrote:
> 
> NFPA #13 2013ed defines furniture with foam plastic cushions as Group "A"
> plastics.
> 
> 
> 
> Would this be treated as an expanded Group "A" plastics because of the 
> foam cushions?
> 
> 
> 
> 
> 
> Thank you
> 
> 
> 
> 
> 
> James Crawford
> 
> Phaser Fire Protection Ltd.
> 
> Phone  604-888-0318
> 
> Fax 604-888-4732
> 
> Cel 604-790-0938
> 
> Email  jcrawf...@phaserfire.ca
> 
> 
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Plastics

2015-07-28 Thread James Crawford
Roland

Has NFPA #13 provided any protection schemes for exposed expanded Group "A" 
plastics in the new edition?


Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: Tuesday, July 28, 2015 12:45 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Plastics

You can go through the exercise of the percentage allowed for Class IV but it’s 
hard to imagine the foam not being greater than 25% of the volume (using the 
2013 ed).  So that pushed it into a Group A plastic.  In the 2016 ed it will be 
further divided into expanded and non-expanded such that you can only have 5% 
of exposed expanded as a Class IV.  IF the exposed expanded is between %5 and 
25% then it is classified as a Group A Unexpanded.  Beyond that it is a exposed 
expanded.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Jul 28, 2015, at 11:36 AM, James Crawford  wrote:
> 
> NFPA #13 2013ed defines furniture with foam plastic cushions as Group "A"
> plastics.
> 
> 
> 
> Would this be treated as an expanded Group "A" plastics because of the 
> foam cushions?
> 
> 
> 
> 
> 
> Thank you
> 
> 
> 
> 
> 
> James Crawford
> 
> Phaser Fire Protection Ltd.
> 
> Phone  604-888-0318
> 
> Fax 604-888-4732
> 
> Cel 604-790-0938
> 
> Email  jcrawf...@phaserfire.ca
> 
> 
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Anti-freeze

2015-07-29 Thread James Crawford
My understanding is that there are no new systems unless you use a listed
anti-freeze and as there are none, so no new systems, you can service
existing systems but must use a factory pre-mix solution.

My understanding

Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca




-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack, SET
Sent: Wednesday, July 29, 2015 4:35 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Anti-freeze

A bit of a discussion with an engineer on a project:

Is it permitted to install anti-freeze in a system (NFPA 13, 2013 and IBC
2012 are governing documents) employing standard spray uprights and pendents
using a factory pre-mix anti-freeze solution in a car dealership occupancy?

My answer is no because TIA says only use listed mixture, and to my
knowledge, none is available at this date.

Engineer states that the TIA permits it (but it is only allowed in 13D), so
we can use pre-mix.

What does the forum collective think?


--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Crowley

2015-08-04 Thread James Crawford
We still use the Crowley program and you do have to manually input the fire
pump boost into your water supply, we try to get four points when ever
possible, we use the static boost plus city and two residuals (100% & 150%)
as well as the maximum city supply.

Hope this helps

Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Parsley Consulting
Sent: Tuesday, August 04, 2015 11:51 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Crowley

Does anyone on the forum use the Crowley calculation program?
A client of mine is having an awful time figuring out how to include a pump
into that software, and I've never used it.
Anyone have a manual or notes?
Respond off forum if so, please.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: "HANGING"

2015-08-28 Thread James Crawford
It also states that the pipe needs to be secured to the structure to prevent
movement.



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca




-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack, SET
Sent: Friday, August 28, 2015 11:30 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: "HANGING"

When installing piping through TJI, are you required to provide a hanger on
the piping?

For years in this area, guys drill the TJI and run CPVC through them without
a hanger.  A new inspector is now requiring the fitter to go back and add
hangers on a large 4 story building.

What are your thoughts?  I was under the impression that installing in this
manner, you are laying the piping on the structure and the structure is
essentially your hanger, so no additional hangers are needed.

--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


In-Rack Sprinkler

2015-09-22 Thread James Crawford
We have a row of single row racking and we are protecting with two levels of
in-rack sprinklers, the levels of the beams are not standard, there is a
difference of 12" between some of the levels.

 

My question is if we are installing heads every transverse flue space (4' to
5' apart) what do you do when there is a step down or step up in the beam
levels?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Multi Row Racks & In-racks

2015-09-23 Thread James Crawford
We are looking at a project with multi row racks, some 4 deep and some 5
deep, all over 25' high (38' high)

 

Reference is NFPA #13 (2013 ed) figure 16.3.1.3.1.3(A)(b)

 

The drawing indicated that the face sprinklers are at the end of the racking
not the loading side and this seems wrong to me. Exhibit 16.23 in the
handbook shows the same thing. To me it make more sense to have the face
sprinklers on the loading aisle not the end of the racking.

 

Am I looking at this wrong or have the sketches been rotated?

 

On the same matter we would have one level at the 15' elevation and the 30'
elevation with face sprinklers at the 30' elevation, for 4 deep this works
great for 5 deep a little different, do I end up with a face sprinkler at
the 15' level as I need 3 heads across the rack, 2 in the flue space and
then I run out of flue space.

 

Looking for info

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Existing sprinklers

2015-10-02 Thread James Crawford
We have a building that was built about 30 years ago the sprinkler system
was designed to NFPA 231C with a ceiling density of 0.45 gpm over 2000
square feet. There is good water pressure and the sprinkler heads are 5.6K
and 286°F

 

We have a new tenant and they require 0.45/2000 and the AHJ says the heads
need to be changed to 11.2K because the density is above 0.34, I said that
NFPA 25 (2008ed) section 4.1.6 Addressing Changes in Hazard, indicates that
the system needs to be evaluated and if the system provides the required
protection then no changes are required.

 

Comments please I seem to be hitting a wall.

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Existing sprinklers

2015-10-02 Thread James Crawford
This is a sprinkler system that was designed to have in-rack sprinklers 
installed at a future date if required, and for this tenant we were planning on 
installing two levels of in-racks with a ceiling density of 0.45, this is what 
is currently in this building.

I see no need to change the roof system heads if they work.



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca




-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Cahill, Christopher
Sent: Friday, October 02, 2015 12:35 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Existing sprinklers

If the density didn't changed how did the hazard change?  Although at 0.45 with 
5.6 do you have a sprinkler system or a mist system, lol.

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: Friday, October 02, 2015 2:29 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Existing sprinklers



Hitting a wall how? I Thing The AHJ is on point, unless there's something else 
to the story.

Steve Leyton

 Original message ----
From: James Crawford 
Date: 10/02/2015  2:01 PM  (GMT-06:00)
To: sprinklerforum@lists.firesprinkler.org
Subject: Existing sprinklers 

We have a building that was built about 30 years ago the sprinkler system was 
designed to NFPA 231C with a ceiling density of 0.45 gpm over 2000 square feet. 
There is good water pressure and the sprinkler heads are 5.6K and 286°F

 

We have a new tenant and they require 0.45/2000 and the AHJ says the heads need 
to be changed to 11.2K because the density is above 0.34, I said that NFPA 25 
(2008ed) section 4.1.6 Addressing Changes in Hazard, indicates that the system 
needs to be evaluated and if the system provides the required protection then 
no changes are required.

 

Comments please I seem to be hitting a wall.

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Existing sprinklers

2015-10-08 Thread James Crawford
Thanks Roland

Existing heads are spaced at 72 sq.ft. so end head pressure is 33.5 psi, but we 
are also looking at adding one more row of in-racks to reduce the ceiling 
demand to 0.30/2000 to further reduce the end head pressure.

If there are grey areas we normally discuss with the AHJ, but I thought it was 
spelled out nicely in NFPA #13.

Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: Thursday, October 08, 2015 1:24 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Existing sprinklers

The 65 psi end head pressure is a bitter pill but NFPA 13 allows them to be 
retained for modifications to existing systems.  That clause is part of the 
current standard so bringing the system up to current standards does not 
exclude it’s application.  Mediocre fire protection at best but allowed.  A 
discussion with the AHJ at the BEGINNING beats a fight after the fact since 
interpretation enters the fray.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Oct 2, 2015, at 12:41 PM, James Crawford  wrote:
> 
> This is a sprinkler system that was designed to have in-rack sprinklers 
> installed at a future date if required, and for this tenant we were planning 
> on installing two levels of in-racks with a ceiling density of 0.45, this is 
> what is currently in this building.
> 
> I see no need to change the roof system heads if they work.
> 
> 
> 
> Thank you
> 
> 
> James Crawford

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Tyco EC-25 CMSA requirements

2015-10-13 Thread James Crawford
See NFPA #13 2013 ed section 16.2.2.3 in the handbook give a good
explanation on this and it would be 4x4.

The square root of your total square footage time 1.2 divided by the
distance between the heads.

47.41 divided by 13.42 = 3.54 or 4 heads

Trust this helps

Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca


 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack, SET
Sent: Tuesday, October 13, 2015 9:10 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Tyco EC-25 CMSA requirements

When using the EC-25 as a CMSA sprinkler (current spacing 10-5 X 13-5), the
criteria for our application is 8 sprinklers at 40 psi. When calculating, do
you calculate 4+4 or do you do 3+3+2?  Tyco's data sheet does not give
guidance, nor does NFPA 13, Chap 21.

I've been told use 1.2 * Sqrt (area).  But is that the area based on max
coverage of 14x14 (8*196 = 1568) or do you use area per sprinkler (140*8 =
1120).

The difference is that at 1568, my length down remote area is 48' which
requires 4x2.  The 1120 is 40.  This is a weird configuration, so my heads
are spaced at 13-5 on center.  As such, that puts me at 3 sprinklers per
line.

In this particular project, much of the piping is existing, and the
difference is 17 psi between the 4+4 and 3+3+2.  That difference requires
removing existing 6" piping and replacing with existing 8" piping.

Does anyone have any guidance on this?  My gut is that it is 4+4. My
customer is saying it is 3+3+2.

--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Tyco EC-25 CMSA requirements

2015-10-13 Thread James Crawford
Section 16.2.2.3 send you to 24.4.4.2.1 and in the hand book it says to use
the maximum allowable spacing per sprinklers.





Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca




-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack, SET
Sent: Tuesday, October 13, 2015 9:51 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Tyco EC-25 CMSA requirements

Yes..that is exactly it.  The area of the remote area is the driving factor.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 10/13/2015 9:49 AM, Cliff Whitfield wrote:
> The question is - what is your 'total sq footage' based on?  The sq 
> footage of the actual sprinkler spacing (1120 sf) or of the spacing 
> based on 14 x 14 coverage per head (1568)?
>
> Cliff
>
> -Original Message-
> From: Sprinklerforum 
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of James Crawford
> Sent: Tuesday, October 13, 2015 10:44 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Tyco EC-25 CMSA requirements
>
> See NFPA #13 2013 ed section 16.2.2.3 in the handbook give a good 
> explanation on this and it would be 4x4.
>
> The square root of your total square footage time 1.2 divided by the 
> distance between the heads.
>
> 47.41 divided by 13.42 = 3.54 or 4 heads
>
> Trust this helps
>
> Thank you
>
>
> James Crawford
> Phaser Fire Protection Ltd.
> Phone  604-888-0318
> Fax 604-888-4732
> Cel 604-790-0938
> Email  jcrawf...@phaserfire.ca
>
>
>   
>
> -Original Message-
> From: Sprinklerforum 
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Travis Mack, SET
> Sent: Tuesday, October 13, 2015 9:10 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Tyco EC-25 CMSA requirements
>
> When using the EC-25 as a CMSA sprinkler (current spacing 10-5 X 
> 13-5), the criteria for our application is 8 sprinklers at 40 psi. 
> When calculating, do you calculate 4+4 or do you do 3+3+2?  Tyco's 
> data sheet does not give guidance, nor does NFPA 13, Chap 21.
>
> I've been told use 1.2 * Sqrt (area).  But is that the area based on 
> max coverage of 14x14 (8*196 = 1568) or do you use area per sprinkler 
> (140*8 = 1120).
>
> The difference is that at 1568, my length down remote area is 48' 
> which requires 4x2.  The 1120 is 40.  This is a weird configuration, 
> so my heads are spaced at 13-5 on center.  As such, that puts me at 3 
> sprinklers per line.
>
> In this particular project, much of the piping is existing, and the 
> difference is 17 psi between the 4+4 and 3+3+2.  That difference 
> requires removing existing 6" piping and replacing with existing 8"
piping.
>
> Does anyone have any guidance on this?  My gut is that it is 4+4. My 
> customer is saying it is 3+3+2.
>
> --
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:tm...@mfpdesign.com
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Tyco EC-25 CMSA requirements

2015-10-13 Thread James Crawford
2013 edition handbook



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca




-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack, SET
Sent: Tuesday, October 13, 2015 10:19 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Tyco EC-25 CMSA requirements

What edition of 13 are you using?

 From 2013 edition, nothing is 16.2.2.3 gets you to maximum areas that I can
see:

*16.2.2.3 *Protection shall be provided as specified in Table 16.2.2.1 or
appropriate NFPA standards in terms of minimum operating pressure and the
number of sprinklers to be included in the design area.

And Chapter 24 only goes to 24.2

I agree with the information you are stating to use maximum area.  I just
need to be able to provide it to the customer.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 10/13/2015 10:08 AM, James Crawford wrote:
> Section 16.2.2.3 send you to 24.4.4.2.1 and in the hand book it says 
> to use the maximum allowable spacing per sprinklers.
>
>
>
>
>
> Thank you
>
>
> James Crawford
> Phaser Fire Protection Ltd.
> Phone  604-888-0318
> Fax 604-888-4732
> Cel 604-790-0938
> Email  jcrawf...@phaserfire.ca
>
>
>
>
> -Original Message-
> From: Sprinklerforum 
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Travis Mack, SET
> Sent: Tuesday, October 13, 2015 9:51 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Tyco EC-25 CMSA requirements
>
> Yes..that is exactly it.  The area of the remote area is the driving
factor.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:tm...@mfpdesign.com
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> On 10/13/2015 9:49 AM, Cliff Whitfield wrote:
>> The question is - what is your 'total sq footage' based on?  The sq 
>> footage of the actual sprinkler spacing (1120 sf) or of the spacing 
>> based on 14 x 14 coverage per head (1568)?
>>
>> Cliff
>>
>> -Original Message-
>> From: Sprinklerforum
>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
>> On Behalf Of James Crawford
>> Sent: Tuesday, October 13, 2015 10:44 AM
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: RE: Tyco EC-25 CMSA requirements
>>
>> See NFPA #13 2013 ed section 16.2.2.3 in the handbook give a good 
>> explanation on this and it would be 4x4.
>>
>> The square root of your total square footage time 1.2 divided by the 
>> distance between the heads.
>>
>> 47.41 divided by 13.42 = 3.54 or 4 heads
>>
>> Trust this helps
>>
>> Thank you
>>
>>
>> James Crawford
>> Phaser Fire Protection Ltd.
>> Phone  604-888-0318
>> Fax 604-888-4732
>> Cel 604-790-0938
>> Email  jcrawf...@phaserfire.ca
>>
>>
>>
>>
>> -Original Message-
>> From: Sprinklerforum
>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
>> On Behalf Of Travis Mack, SET
>> Sent: Tuesday, October 13, 2015 9:10 AM
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: Tyco EC-25 CMSA requirements
>>
>> When using the EC-25 as a CMSA sprinkler (current spacing 10-5 X 
>> 13-5), the criteria for our application is 8 sprinklers at 40 psi.
>> When calculating, do you calculate 4+4 or do you do 3+3+2?  Tyco's 
>> data sheet does not give guidance, nor does NFPA 13, Chap 21.
>>
>> I've been told use 1.2 * Sqrt (area).  But is that the area based on 
>> max coverage of 14x14 (8*196 = 1568) or do you use area per sprinkler
>> (140*8 = 1120).
>>
>> The difference is that at 1568, my length down remote area is 48'
>> which requires 4x2.  The 1120 is 40.  This is a weird configuration, 
>> so my heads are spaced at 13-5 on center.  As such, that puts me at 3 
>> sprinklers per line.
>>
>> In this particular project, much of the piping is existing, and the 
>> difference is 17 psi between the 4+4 and 3+3+2.  That difference 
>> requires removing existing 6" piping and replacing with existing 8"
> piping.
>> Does anyone have any guidance on this?  M

Composite Wood Joists

2015-10-21 Thread James Crawford
We have a project that is using TJI wood joist (composite wood Joists), they
are 16” deep spaces 18” on center and are 20’ long. There is gypsum board
attached directly to the bottom of the joists along with 3” of insulation at
the bottom to reduce sound transmission. The area is about 1400 sq.ft.

 

Reference is NFPA #13 2013 edition section 11.2.3.1.4(4)(j)

 

Light or ordinary hazard occupancies where noncombustible or limited
combustible ceilings are attached to the bottom of composite wood joists
either directly or on to metal channels not exceeding 1” in depth, provided
the adjacent joist space channels are firestopped into volumes not exceeding
160 cubic feet using materials equivalent to ½” gypsum board and at least 3
½” of batt insulation is installed at the bottom of the joist channels when
the ceiling is attached utilizing metal channels.

 

If each channel space formed by two joist is 40 cubic feet, so the adjacent
space is 40 cubic feet, I see no need to fire stop them into volumes less
than 160 cubic feet as they are already less than 160. The AHJ is saying
that we must firestop every 4th joist space with gypsum to create spaces of
160 cubic feet, so we would need to break the space into 12 spaces of 160
cubic feet for the 1400 sq ft area.

 

Am I reading this correctly or do we need to break the space into sections
of 160 cubic feet?

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Composite Wood Joists

2015-10-22 Thread James Crawford
Thanks Roland

But my coffee has not kicked in, So I agree with 8.15.1.2.6 allows the omission 
of the sprinkler heads as we meet those requirements, and  11.2.3.1.4(4)(j) 
allows us to not use a 3000 sf design area if we firestop the joist channels 
into 160 cu ft blocks, or in our case about every fourth joist channel and the 
firestop material needs to be 1/2" gypsum or equal


Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: Thursday, October 22, 2015 9:23 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Composite Wood Joists

Allow me a bit of a long winded response instead of a simple yes or no.

First off, although your question is not about whether you can omit sprinklers 
but whether you have to have a 3,000 sf remote area (not stated but understood 
since you are referencing chap 11), let’s start in 8.15.1.2.6 that allow the 
omission.  It states - the joist channels are firestopped into volumes EACH not 
exceeding 160 cu ft.  Obviously the volume is per individual channel.  Now 
jumping to 11.2.3.1.4(4)(j) it states - provide the adjacent joist space 
channels are firestopped into volumes not exceeding 160 cubic feet.  I could 
stop here but the coffee is kicking in.  IF it were meant to be a single 
channel, the text would have been copied as stated in 8.15.1.2.6.  Stating 
“adjacent channels” when read without the preconception from 8.15 is pretty 
plain but it was known that the per channel was well ingrained so Annex 
material was provided.  It states - restrict the ability for fire to spread 
beyond 160 cu ft zones covering MULTIPLE joist channels.

Prior to the 2010 edition, you ALWAYS had to use a 3,000 sf remote area with 
unprotected spaces of composite wood joists.  By breaking the overall space 
into volumes of NMT 160 cu ft, it presents a similar risk that that of solid 
wood joists with bigger individual channels.  For our sprinkler scientist, yes 
it is a slightly bigger risk since TJI's burn more vigorously and fail more 
quickly than solid wood joist (thus the prior difference) but for driving the 
need for a bigger remote area, the difference is insignificant.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Oct 21, 2015, at 5:08 PM, James Crawford  wrote:
> 
> We have a project that is using TJI wood joist (composite wood 
> Joists), they are 16” deep spaces 18” on center and are 20’ long. 
> There is gypsum board attached directly to the bottom of the joists 
> along with 3” of insulation at the bottom to reduce sound transmission. The 
> area is about 1400 sq.ft.
> 
> 
> 
> Reference is NFPA #13 2013 edition section 11.2.3.1.4(4)(j)
> 
> 
> 
> Light or ordinary hazard occupancies where noncombustible or limited 
> combustible ceilings are attached to the bottom of composite wood 
> joists either directly or on to metal channels not exceeding 1” in 
> depth, provided the adjacent joist space channels are firestopped into 
> volumes not exceeding
> 160 cubic feet using materials equivalent to ˝” gypsum board and at 
> least 3 ˝” of batt insulation is installed at the bottom of the joist 
> channels when the ceiling is attached utilizing metal channels.
> 
> 
> 
> If each channel space formed by two joist is 40 cubic feet, so the 
> adjacent space is 40 cubic feet, I see no need to fire stop them into 
> volumes less than 160 cubic feet as they are already less than 160. 
> The AHJ is saying that we must firestop every 4th joist space with 
> gypsum to create spaces of
> 160 cubic feet, so we would need to break the space into 12 spaces of 
> 160 cubic feet for the 1400 sq ft area.
> 
> 
> 
> Am I reading this correctly or do we need to break the space into 
> sections of 160 cubic feet?
> 
> 
> 
> Thank you
> 
> 
> 
> 
> 
> James Crawford
> 
> Phaser Fire Protection Ltd.
> 
> Phone  604-888-0318
> 
> Fax 604-888-4732
> 
> Cel 604-790-0938
> 
> Email  jcrawf...@phaserfire.ca
> 
> 
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Electrical Equipment room

2015-11-19 Thread James Crawford
Opinions please

 

NFPA #13 2013 ed section 8.15.11 Electrical Equipment.

 

Room is used as a server room, only the server and the UPS are in the room,
the room is 2 hour fire rated.

 

Section 8.15.11.3 Sprinklers shall not be required in electrical equipment
room where all of the following conditions are met:

 

(1)Room is dedicated to electrical equipment onlyyes

(2)Only dry-type electrical equipment is used.Yes

(3)Electrical equipment is installed in a 2 hour rated enclosure
including protection of penetrations  yes

(4)No combustibles storage is permitted to be stored in the room.
yes

 

Based on this can the sprinkler heads be eliminated from this room?

 

Would still have to get it by the AHJ.

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Electrical Equipment room

2015-11-19 Thread James Crawford
I agree and I always provide protection in a server room, note a SERVER ROOM
not electrical equipment room, this was suggested by an architect to help
his client.

Just wanted to get some feed back on this matter before I give him the bad
news.


Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca





-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Roland Huggins
Sent: Thursday, November 19, 2015 12:00 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Electrical Equipment room

BULLSEYE

Sounds like someone is doing the A/E dance.  Not the first time one has
attempted to say this means equipment that uses electricity.

If the value of the data or continuity of business warrants it, suggest they
do a double interlock preaction system.

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Nov 19, 2015, at 11:47 AM, 
 wrote:
> 
> A server and a UPS is not an electrical room nor considered "electrical
equipment".
> 
> "Electrical Rooms" house Transformers, MCCs and Switchgear.  The clue is
the mention of dry type equipment.   You haven't seen any oil cooled
computers have you?
> 
> So technically this doesn't apply but it depends on what you convince the
AHJ it means.
> 
> 
> If they are adamant about not putting sprinklers in the room, the better
argument is found in the Fire Code in 903.3.1.1.1 EXEMPT LOCATIONS where you
could use exemption (2)"Any room or space where sprinklers are considered
undesirable because of the nature of the contents, when approved by the fire
code official."  Now the room will require the installation of smoke
detectors if you omit the sprinklers. Run that by the AHJ and see if it
flies.
> 
> 
> 
> Craig L. Prahl 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Storage Tanks

2015-11-20 Thread James Crawford
Looking for input as I have not come across this before.

 

Looking for a protection scheme to protect a 65' tall storage tank filled
with water and coffee beans (decaffeinating) 

 

Just not sure what code would cover this.

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Storage Tanks

2015-11-20 Thread James Crawford
My wife would agree that this is wrong but that’s the way life is.

I am just thinking that due to the height of the building and the commodity 
being stored, that it is not a normal protection scheme.

I don't feel that the metal tanks full of water is much of a fire hazard, so 
having one that is 65' tall does not change a lot but what I think and what I 
can prove are often two separate items. So I was just looking for back up when 
I address the local AHJ. 

Is there something in the code that would provide some additional information 
on sprinkler protection for this situation.


Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: Friday, November 20, 2015 3:52 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Storage Tanks

First off I have to say it’s just wrong to decaffeinate coffee

What exactly do you mean protect?  A tank full of water (even with beans) poses 
what kind of risk?

Confused 


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Nov 20, 2015, at 3:44 PM, James Crawford  wrote:
> 
> Looking for input as I have not come across this before.
> 
> 
> 
> Looking for a protection scheme to protect a 65' tall storage tank 
> filled with water and coffee beans (decaffeinating)
> 
> 
> 
> Just not sure what code would cover this.
> 
> 
> 
> 
> 
> Thank you
> 
> 
> 
> 
> 
> James Crawford
> 
> Phaser Fire Protection Ltd.
> 
> Phone  604-888-0318
> 
> Fax 604-888-4732
> 
> Cel 604-790-0938
> 
> Email  jcrawf...@phaserfire.ca
> 
> 
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Canopies Over gads Pumps

2015-12-08 Thread James Crawford
Looking for some direction on the protection of a Gas Service station canopy
over the gas pumps.

 

We have an AHJ that want the canopy protected, but I can't find anything
that outlines the protection requirements for this area. My first thought is
Extra Hazard group 1.

 

Can someone point me in the right direction

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Canopies Over gads Pumps

2015-12-08 Thread James Crawford
Richard

Yes it is in Canada and as always the AHJ will not say what they want only
that they want it protected. I have never seen one protected here in the
lower mainland of BC, just fire extinguishers.

I have assumed a water based system, but have been unable to find any
direction in the codes, so thought I would through it out there and see who
takes a swing.

Always interesting discussions.

Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca




-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Richard Lindner
Sent: Tuesday, December 08, 2015 4:44 PM
To: sprinklerforum@lists firesprinkler. org
Subject: Re: Canopies Over gads Pumps

James,

I am going to assume you're talking about something in Canada?  You also
don't state what type of system the AHJ is looking for, as others are
assuming water-based.

Based on what I have seen on inspections of gas stations (due diligence
reports), I have seen several with a system that would be typical of the one
found here:  http://www.pyrochem.com/html/prodatten.html

Worth a phone call at least to the company to get a better explanation.

Richard

On Tue, Dec 8, 2015 at 1:04 PM, James Crawford 
wrote:

> Looking for some direction on the protection of a Gas Service station 
> canopy over the gas pumps.
>
>
>
> We have an AHJ that want the canopy protected, but I can't find 
> anything that outlines the protection requirements for this area. My 
> first thought is Extra Hazard group 1.
>
>
>
> Can someone point me in the right direction
>
>
>
>
>
> Thank you
>
>
>
>
>
> James Crawford
>
> Phaser Fire Protection Ltd.
>
> Phone  604-888-0318
>
> Fax 604-888-4732
>
> Cel 604-790-0938
>
> Email  jcrawf...@phaserfire.ca
>
>
>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Locker Rooms

2016-01-04 Thread James Crawford
We have always protected locker rooms as light hazard, we have been advised
by a local AHJ that they see these rooms as storage areas and will need to
be protected as ordinary hazard group 1.

 

Any thoughts

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Mixing ESFR Heads

2016-01-05 Thread James Crawford
Looking at a 400,000 sq.ft. building with multiple storage arrangements, on
the floor, on single and double row racks. Each about half the building.

 

Can you use K25 ESFR heads for the rack storage (exposed expanded Group A
plastics) and K17 heads for the storage on the floor (class 4 commodities)?

 

Thoughts as I cannot find anything that says you can't.

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Mixing ESFR Heads

2016-01-05 Thread James Crawford
Ceiling elevation is the same across the entire building



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack, SET
Sent: Tuesday, January 05, 2016 3:13 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Mixing ESFR Heads

We do it when we have high bays that require the larger k-factor and then
lower roof areas that the smaller works.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 1/5/2016 4:11 PM, James Crawford wrote:
> Looking at a 400,000 sq.ft. building with multiple storage 
> arrangements, on the floor, on single and double row racks. Each about
half the building.
>
>   
>
> Can you use K25 ESFR heads for the rack storage (exposed expanded 
> Group A
> plastics) and K17 heads for the storage on the floor (class 4
commodities)?
>
>   
>
> Thoughts as I cannot find anything that says you can't.
>
>   
>
> Thank you
>
>   
>
>   
>
> James Crawford
>
> Phaser Fire Protection Ltd.
>
> Phone  604-888-0318
>
> Fax 604-888-4732
>
> Cel 604-790-0938
>
> Email  jcrawf...@phaserfire.ca
>
>   
>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Mixing ESFR Heads

2016-01-06 Thread James Crawford
Thanks all

I always discuss any restrictions that may be required with the owner and if
the flexibility is required or future growth would be anticipated, then the
entire building will be designed to the higher hazard. Just looking at
options.


Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca





-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Roland Huggins
Sent: Wednesday, January 06, 2016 1:31 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Mixing ESFR Heads

AS Mark and Duane have already flagged, it is addressed by 13.  Although 13
says 15 ft, check the cut sheet regarding the possible 20 ft.  I seem to
remember there is something on ESFR (a very hazy recollection).

The point I want to make is to ensure you have something in writing showing
the owner is aware that they can not later change the contents of the lower
hazard area by expanding their higher hazard stuff (done without a second
thought).  The flexibility may be worth the cost difference to the owner.
The CYA for you down the road - priceless.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Jan 5, 2016, at 3:11 PM, James Crawford 
wrote:
> 
> Looking at a 400,000 sq.ft. building with multiple storage 
> arrangements, on the floor, on single and double row racks. Each about
half the building.
> 
> 
> 
> Can you use K25 ESFR heads for the rack storage (exposed expanded 
> Group A
> plastics) and K17 heads for the storage on the floor (class 4
commodities)?
> 
> 
> 
> Thoughts as I cannot find anything that says you can't.
> 
> 
> 
> Thank you
> 
> 
> 
> 
> 
> James Crawford
> 
> Phaser Fire Protection Ltd.
> 
> Phone  604-888-0318
> 
> Fax 604-888-4732
> 
> Cel 604-790-0938
> 
> Email  jcrawf...@phaserfire.ca
> 
> 
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


max Load of Influence Chart

2016-01-14 Thread James Crawford
Trying to locate a chart for Maximum load of influence for Sch. 7 pipe.

 

Can someone point me in the right direction

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: max Load of Influence Chart

2016-01-14 Thread James Crawford
Thanks, I had found this one but noticed that some of the numbers are lower
that the sch 5 chart in NFPA 13, would have thought they would be somewhere
in the middle due to the thicker wall on sch 7 pipe.



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack, SET
Sent: Thursday, January 14, 2016 12:46 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: max Load of Influence Chart

There is one in this packet from AFSA seminar

https://www.firesprinkler.org/wp-content/uploads/2014/08/0929_0930_Seismic.p
df

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 1/14/2016 1:43 PM, James Crawford wrote:
> Trying to locate a chart for Maximum load of influence for Sch. 7 pipe.
>
>   
>
> Can someone point me in the right direction
>
>   
>
>   
>
> Thank you
>
>   
>
>   
>
> James Crawford
>
> Phaser Fire Protection Ltd.
>
> Phone  604-888-0318
>
> Fax 604-888-4732
>
> Cel 604-790-0938
>
> Email  jcrawf...@phaserfire.ca
>
>   
>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Wooden Pallet Storage

2016-01-21 Thread James Crawford
We have a client that will be storing wooden pallets inside the warehouse,
building is protected with ESFR sprinkler heads which would allow 25'-0"
storage of wooden pallets on the floor.

 

What I cannot seem to find is the pile size requirement, reference is NFPA
#13 2013 ed.

 

Can someone point me in the right direction or is there no restriction on
the pile size.

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


  1   2   >