RE: Declaration of Conformance - a plea for accuracy of language!

2007-09-18 Thread emc-p...@ieee.org
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of John Woodgate Sent: Tuesday, September 18, 2007 2:44 PM To: emc-p...@ieee.org Subject: Re: Declaration of Conformance - a plea for accuracy of language! In message p06240821c315ebec2ece@[192.168.1.24], dated Tue, 18 Sep 2007,

RE: Residential Wiring of 24vdc for media applications

2007-09-18 Thread emc-p...@ieee.org
If the 24 Vdc supply meets NEC Class 2 requirements, use Class 2 wiring methods. If not, use Class 1 wiring methods. See NEC Article 725. Regards, Peter L. Tarver, PE ptar...@ieee.org From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Stone, Richard Sent: Tuesday,

Re: Declaration of Conformance - a plea for accuracy of language!

2007-09-18 Thread emc-p...@ieee.org
In message p06240821c315ebec2ece@[192.168.1.24], dated Tue, 18 Sep 2007, Nick Williams nick.willi...@conformance.co.uk writes: Given the name I chose for my company, I'm particularly (some would probably say overly) sensitive to this issue, but here goes... There is no such thing as a

RE: Declaration of Conformance - a plea for accuracy of language!

2007-09-18 Thread emc-p...@ieee.org
Ahh, but therein lies the rub Nick. Your determination of what is simple and accurate, may not be the next persons determination of what is simple and, once the marketing people get involved, neither may be what they think is simple and accurate. You will never get agreement on what people want

RE: Declaration of Conformance - a plea for accuracy of language!

2007-09-18 Thread emc-p...@ieee.org
We also have the Declaration of Conformity for the FCC in the US. So there are different styles. Ghery S. Pettit From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Nick Williams Sent: Tuesday, September 18, 2007 2:15 PM To: emc-p...@ieee.org Subject: RE: Declaration of

RE: Declaration of Conformance - a plea for accuracy of language!

2007-09-18 Thread emc-p...@ieee.org
Given the name I chose for my company, I'm particularly (some would probably say overly) sensitive to this issue, but here goes... There is no such thing as a Declaration of Conformance. The proper name for the document is (in the case of the European CE marking directives) is an EC

RE: Declaration of Conformance

2007-09-18 Thread emc-p...@ieee.org
Testing only shows compliance to the tested device. With the DoC the manufacturer declares that each single product he is putting on the market is compliant. This is a totally different dimension and includes changes the manufacturer’s are doing over the lifetime of a product etc. Best

NEMA 5-15R Receptacle Temp. Rating 60 C

2007-09-18 Thread emc-p...@ieee.org
Greetings Regulatory Professionals, I have a need to source for a single-outlet, NEMA 5-15R receptacle that has a temperature rating of at least 70 deg. C. I have reviewed the temperature ratings for several manufacturers of a single-outlet receptacle of this type and cannot find any

Re: EN 60950:2006 VDR's

2007-09-18 Thread emc-p...@ieee.org
In message 74cf408f6fd02b47a20aad68714e9d5d20c...@zeus.ce.test, dated Tue, 18 Sep 2007, Gert Gremmen administra...@ce-test.info writes: After all, VDRs should be given the opportunity to protect now and then. There is a considerable difference between protecting against an occasional spike

RE: EN 60950:2006 VDR's

2007-09-18 Thread emc-p...@ieee.org
RATED VOLTAGE is a defined term in 60950. Tolerances thus need not be taken into account, as they are not defined here. That's what the 20% overrating is meant for. After all, VDRs should be given the opportunity to protect now and then. Don't overrate. Regarding the RATED VOLTAGE RANGE:

Re: EN 60950:2006 VDR's

2007-09-18 Thread emc-p...@ieee.org
In message 12d6af78e37dc842b24ef1593c7a035bbe1...@server15.rossvideo.com, dated Tue, 18 Sep 2007, Donald McElheran dmcelhe...@rossvideo.com writes: The same requirements are spelled out IEC 60065 7h Edition. The requirements make no mention of rated voltage tolerances. The standard quite

RE: EN 60950:2006 VDR's

2007-09-18 Thread emc-p...@ieee.org
Steve: Your interpretations are in line what we have experienced with our national certifying NRTL. The same requirements are spelled out IEC 60065 7h Edition. The requirements make no mention of rated voltage tolerances. The standard quite specifically make reference to the RATED SUPPLY

RE: Plenum in-wall approved

2007-09-18 Thread emc-p...@ieee.org
A few additions to Ted and Jim's excellent responses - Don't assume that these requirements will only apply to cabling. Any device that could be mounted in the air plenum must meet these requirements. If your installation guide states that the device, peripheral, ac/dc converter, etc. can be

RE: Machinery Safety regulations in US

2007-09-18 Thread emc-p...@ieee.org
Also, look into possible applicability of NFPA 79. Regards, Peter L. Tarver, PE ptar...@ieee.org CONFIDENTIALITY This e-mail message and any attachments thereto, is intended only for use by the addressee(s) named herein and may contain legally privileged and/or confidential information. If

RE: EN 60950:2006 VDR's

2007-09-18 Thread emc-p...@ieee.org
Steve, If equipment is rated for a nominal 230V, then it would be reasonable to assume that that is for use on a supply conforming to BS EN 50160:2000, which defines the voltage and frequency limits for all low voltage distibution in Europe, including the UK. The upper limit would thus be

RE: RFID Modular FCC approval : Is shielding mandatory?

2007-09-18 Thread emc-p...@ieee.org
The DA for modular equipment is for modules that can be used anywhere. It is used for those instances where the manufacturer or the final host, except in portable rf configurations, does not need or does not want certification of the host. Consequently the requirement that as a stand a lone unit

Residential Wiring of 24vdc for media applications

2007-09-18 Thread emc-p...@ieee.org
hello Group, If installing a UL approved base box (media) that converts 120vac to 24vdc, are there any restrictions from running this 2 conductor 24vdc secondary output line anywhere in the house? the base is approved to UL 60950. Is a conduit needed?, a certain type of connector required? any

EN 60950:2006 VDR's

2007-09-18 Thread emc-p...@ieee.org
Hello Group, Just looking at Annex Q of EN 60950:2006 regarding the use of VDR's in primary circuits, and the following is stated; b) Maximum continuous voltage (2.1.2 of IEC 61051-2) The maximum continuous a.c. voltage is selected from the list of preferred voltages and shall be at

Re: Plenum in-wall approved

2007-09-18 Thread emc-p...@ieee.org
Hello Kris, Building codes in North America place limits on the flammability of materials used in plenums. The concern is that if a fire starts in an air supply or return plenum, smoke and flame could be distributed through a building before they are detected. For example, the area above a

IEEE Product Safety Engineering Society Announcement

2007-09-18 Thread emc-p...@ieee.org
Dear EMCS-PSTC list member, The 2007 IEEE Symposium on Product Compliance Engineering, sponsored by the IEEE Product Safety Engineering Society, will be held on 22-23 October 2007 in Longmont, Colorado (Denver area). We have a record number of authors presenting this year, see

RE: Plenum in-wall approved

2007-09-18 Thread emc-p...@ieee.org
Kris, There are terms in the National Electrical Code (NEC) that are similar to “plenum-in wall” and are probably what you are looking for. Cables routed to penetrate a floor have the Riser designation of R. (Or an acceptable better rating –designation ends in P. NEC Table 800.154 Cable

Re: Turntable Size in a 3m Semi-anechoic Chamber

2007-09-18 Thread emc-p...@ieee.org
In message 2a93eb060709180432u30064644s6773a6ae8cb85...@mail.gmail.com, dated Tue, 18 Sep 2007, Grace Lin graceli...@gmail.com writes: My question is: what are the disadvantages to have a 1.5 meter turntable?  The only thing that I can think of is the corners of a table holding tabletop EUTs

Plenum in-wall approved

2007-09-18 Thread emc-p...@ieee.org
Hi Group, I got a request if a product is plenum in-wall approved. I suppose it only concerns the attached cables. Can any-one tell what “plenum-in wall” requirements exactly are and which are the requirements applicable in US Canada? Best regards, Kris Carpentier Regulatory

Fw: RFID Modular FCC approval : Is shielding mandatory?

2007-09-18 Thread emc-p...@ieee.org
Thanks to Grace the following link from her sheds new light on the modular transmitter. I have only glanced through the document but there appears to be cases where shielding is not required. For K.Balasubramanian..I would go to the FCC with your question and request an

Turntable Size in a 3m Semi-anechoic Chamber

2007-09-18 Thread emc-p...@ieee.org
Dear Members, I need help to justify the size of a turntable in a fully compliant 3 meter semi-anechoic chamber. The choices are 1.2 meters, 1.5 meters, and 2 meters. The largest EUT expected is 19 for all three dimensions. Turntable size (quiet zone) affects the physical dimensions of a

Re: RFID Modular FCC approval : Is shielding mandatory?

2007-09-18 Thread emc-p...@ieee.org
There is an updated official document issued by the FCC on April 23, 2007 in regard to the module approval. The document number is ET Docket No. 03-201. I have seen a device being certified based on this document (without RF shielding enclosure). Grace On 9/18/07,

Re: RFID Modular FCC approval : Is shielding mandatory?

2007-09-18 Thread emc-p...@ieee.org
The TCB is correct in their interpretation. It is not only a question of passing the limits, it is also a coupling issue. Modular transmitters are meant to be off the shelf items that can go into anything imaginable. Proper shielding design will help prevent coupling problems. You can also ask the

Re: China CNCA 2007 Notice No. 21

2007-09-18 Thread emc-p...@ieee.org
Yes. An EMC lab in China can be accredited by NVLAP or A2LA. You may wish to contact A2LA and NIST NVLAP for more detail information. Please let me know if you need contact information. - Grace On 9/17/07, cgitt...@rochester.rr.com cgitt...@rochester.rr.com wrote: Grace, Are EMC

RFID Modular FCC approval : Is shielding mandatory?

2007-09-18 Thread emc-p...@ieee.org
Dear Experts, For one of our RFID product (13.56 MHz FCC Part 15 sub part C intentional radiating device) we look for modular approval. There is no separate enclosure for this product. There is only one PCBA with USB connector for the host connectivity. This PCBA will get assembled in the

RE: MIL-STD-810F drop testing

2007-09-18 Thread emc-p...@ieee.org
Charlie, Many of the methods used in MIL-STD-810F are designed to apply shocks of a known and controlled amplitude using apparatus such as a drop tower or a shaker. However, free-fall drop tests are recommended to simulate certain conditions that might be experienced in the field, typically