Cameron,
I had a similar situation some time ago with an internal cable and it had to
do with the insulation thickness. The SJT cord was only rated 300V, and the
insulation thickness did not meet the European standard. We changed to a
600V cord, which was accepted.
Ray Russell
r...@gastmfg.com
Chris,
UL has offices all over the world. In Europe they now own DEMKO, so if you
are close to Denmark that may help. It would be good to check with UL to
find out where the closest follow up office is located. They charge for
their time to travel to your location. We have a manufacturer in the
P
I'm sure that many of you, as well as myself, under the label of Regulatory
Compliance, receive many issues outside of Safety/EMC. Usually if it has an
acronym, involves a foreign country, falls under the heading of a regulatory
requirement, or sales/marketing don't know who can handle it, it land
...@gastmfg.com
-Original Message-
From: Wagner, John P (John) [mailto:johnwag...@avaya.com]
Sent: Monday, October 09, 2000 10:28 AM
To: 'brian_kunde'; emc-pstc; 'Russell, Ray'
Subject: RE: Overcurrent Protection: One or Both Sides?
I take some exception to the response
Hi Brian,
I see most of the return postings have focused on the UK, which has a
terminated neutral system. There are several installations especially in the
US, where the power could be derived from a delta, or unterminated neutral
system. I believe in this case, overcurrent protection is require
Hello Fabian,
The NRTL we deal with uses a scheme called a split inspection. We do the
submittal, and they will inspect at our suppliers facility. It's a little
tricky, but it does work. However, I would be concerned about the
possibility that the supplier does not have an NRTL listing, and may
Greetings,
I understand that according to Japan's Electrical Appliance and Material
Control Law there are 2 "classes" of products, A or B. A type are considered
more risky appliances, and require a mandatory approval for the T mark. B
items are considered less risky, and do not require the markin
Hi Dan,
We use UL 1450 Motor Operated Air Compressors, and here is the definition of
constant temperatures:
46.1.11 With reference to those tests that are to be continued until
constant temperatures are attained, thermal
equilibrium is considered to exist when three successive readings taken at
Hi Joe,
I've been using the Fluke Hydra Data Bucket for a couple of years, and
really like it. It is a little pricey but I think its worth it. It has 20
channels, and you can also configure each channel for volts or ohms. We have
added a current to voltage probe, so we can record the current too.
Greetings,
We sell an air compressor with a DC motor. This motor requires a capacitor
across the DC supply lines to meet the EMC requirements. Of course
management does not want to supply the capacitor, they want to describe it
in the documentation, and add a note on the Declaration of Conformity
Greetings Martin,
It seems that there is a problem in the US and China with using Conifer
(pine) type of pallets. Here is a URL that goes into a little more detail
Ray
http://www.skralaw.com/Articles/china.htm
-Original Message-
From: marti...@pebio.com [mailto:marti...@pebio.com]
Sent
Seasons Greetings!
We are having some trouble with the bottom openings in a piece of equipment,
and I'm wondering if you might be able to provide a source for the screen
mentioned in UL1950 Sec 4.4.6.
Thank you and I hope you all have a great Holiday!
Ray Russell
Regulatory Compliance Engineer
Greetings Israel,
A standard that we use is EN 1012-1 Compressors and Vacuum Pumps - Safety
Requirements. Depending on the size of the equipment, the Pressure Directive
or Pressure Equipment Directive may also apply.
Regards,
Ray Russell
ray_russ...@gastmfg.com
-Original Message-
Fr
Greetings,
In this day and age of trying to cover your butt, from liability (especially
in the USA), I have found it interesting that the information in some User
manuals are going to the extreme to warn the consumer, while other similar
products have very few warnings.
In addition, our Europe
Hi Paul,
I could not put my finger on the paragraph that spells it out in the NEC,
(380-4 has the 6 1/2 foot requirement) but I just installed a switch myself
and the local inspector required it to be a min of 18" off of the ground.
Ray
ray_russ...@gastmfg.com
-Original Message-
From:
Hi Brian,
As Luis points out, the 2 standards are directed at different applications.
However, I believe most of the tests required are the same. But I'm not sure
that the manufacturer of the pump would apply the same tests that I would
seek to apply. So I would look at EN61010-1 and see what te
Hello Jasmine,
I believe the reference is to IEC 417, Graphic Symbols, and No. 5172 refers
to the Class II symbol for a double insulated system. It is the symbol with
a box inside a box. There is a site that has some of these symbols, but my
paranoid IS administrator has blocked our internet acce
Hi George,
I my experience, I have used the UL Yellow books to verify UL recognition
and to determine which standards it is recognized to. If I still have
trouble, I have called UL direct, and they have always been helpful.
Ray
rayruss...@gastmfg.com
-Original Message-
From: sparaci..
Hi Brian,
Sec 13 in EN 601010 doesn't offer much guidance on which standard to go to.
A search at Global found IEC 60079-1 ELECTRICAL APPARATUS FOR EXPLOSIVE GAS
ATMOSPHERES PART 1: CONSTRUCTION AND VERIFICATION TEST OF FLAMEPROOF
ENCLOSURES OF ELECTRICAL APPARATUS but I have not worked with tha
Hi Richard,
I recommend you check out the Consumer Product Safety Commission at
http://www.cpsc.gov/
BTW Paul Hill's book is a great resource.
Ray Russell
ray_russ...@gastmfg.com
-Original Message-
From: WOODS, RICHARD [mailto:wo...@sensormatic.com]
Sent: Wednesday, June 30, 1999 11:54
Dear James,
First, UL has reduced spacings for motors less than 178 mm diameter.
Additionally, I see a footnote that for film coated wire that is rigidly
supported and held in place, spacings may be reduced to 2.4 mm.
Good Luck,
Ray
ray_russ...@gastmfg.com
-Original Message-
From: ja
This bounced yesterday, so I am resending it.
Ray
-Original Message-
From: Russell, Ray
Sent: Thursday, May 27, 1999 8:04 AM
To: 'distefa...@panametrics.com'; emc-p...@majordomo.ieee.org
Cc: cleme...@panametrics.com
Subject: RE: IEC 417 No 5017 Labels
We have purchased
Greetings,
I always understood that it was "Customs" that required the statement as to
the country of origin. I believe it has to do with tariffs. I also believe
that for the US the NAFTA agreement spells out if it can say made or
assembled in by how much of the material is of that countries origi
Greetings,
I hope everyone had a happy holiday.
I am looking for a comparison of IEC 60529 IP ratings for enclosures to the
NEMA equivalents.
Thank you for your assistance,
Ray Russell
Regulatory Compliance Engineer
ray_russ...@gastmfg.com
-
This message is coming from the emc-ps
Greetings,
I know that at one time, UL had accepted a HAR type cordset. Now, I have
been told by some line cord vendors that UL does not approve any HAR type
cord any longer. Belden has a jumper cord with C13 and C14 connectors that
has both US and EU approvals, but no other configurations are av
Greetings,
I have used the ED&D leakage current for my previous 2 employers. I really
liked it. They were dependable and very easy to use.
They are also on the web at http://www.productsafet.com/prodsafety/
We currently use a test box built in house to the specifications of UL,
found in most UL
Happy Holidays,
I'm working on a project that will ship to Japan and requires a motor
starting capacitor. Would any one know if there are requirements that
dictate whether a dry or wet type cap are required for Japan? How about the
rest of the world?
Thank you for your assistance,
Ray Russell
Re
Happy Holidays,
We're working on a rather large project that has pull out drawers for
servicing some of the sub assemblies. The drawers are heavy, but low enough
that the unit only tips slightly when all drawers are open. As the drawer
pulls out it catches on the floor and stops it self from over
Greetings,
At a former company, we were able to have the plastic vendor mold the
information right into the part or put in on the outside of the shipping
carton. All of the agencies that we delt with accepted this. The molded in
information also helped in some of the recycling requirements for Ger
Greetings Bob,
I do not see much reference to this situation under EN 61010. I believe that
at some point in time, the customer has to take some responsibility for the
process that they use. But the manufacture of the piece of Test equipment
still has some "duty to warn of any foreseen hazards". F
Greetings Joe,
I think that you need to look at the consumer of your equipment. If the test
equipment is to be used by an average person, then I believe multiple
languages are required. If you sell a specialized piece of test equipment,
then I believe the standard offers a different solution. Und
Greetings,
I recall a recent message looking for a replacement for an Energized Winding
Tester: AVO Biddle, Model 577500. If someone found some information, would
you please pass it on to me?
Thank you,
Ray Russell
Regulatory Compliance Engineer
ray_russ...@gastmfg.com
-
This message i
Dear Richard,
I understand that UL is working on an MOU with Argentina. With that in mind,
you might want to contact the Technical Assistance to Exporters office at
your UL location.
Good Luck,
Ray Russell
ray_russ...@gastmfg.com
-
This message is coming from the emc-pstc discussion l
Dear Francis,
I have used IEC 73 (BS EN 60073) Specification for coding of
indicating devices and actuators by colours and supplementary means.
BS EN 60204 Safety of machinery- Electrical equipment of machines also
has a section on indicating lights.
Ray Russell
ray_russ...@gastmfg.com
Greetings,
I have been using a company called Simcom for a couple of years now.
They are usually the least expensive and have been helpful in
answering questions about the specific standard before I pay big
bucks, and find out is a 3 page addendum!
Phone (770) 730-9980
FAX(770) 730-9976
G
Greetings,
A few years ago at a NEMKO seminar I attended, there was a
presentation on the "key mark". Because it looked like a key and would
open doors to all markets. I believe this was a proposal from the IEC.
Anyone hear any recent developments on this possibility? I imagine
with the CE mar
Greetings,
>From the example below, I would not be as concerned with "who" tested
it, but which standard it was tested to. I think that we must remember
that standards organizations have made progress toward harmonization,
but the heart of the problem is that US standards and EU standards are
Greetings Nick,
I have found some good information on Mexico through the US NAFTA
website. The URL is:
http://www.itaiep.doc.gov/nafta
Look at document 9000 for an overview of Mexico's standard system.
Ray
ray_russ...@gastmfg.com
--
From: Nick Williams[SMTP:n...@conformance.co.uk]
Greetings,
The Trans Atlantic Business Dialog has put out a mid year report. It
includes the status of:
Mutual Recognition Agreement
Regulatory Cooperation
Conformity Assessment and Product Marking
Metric Labeling
You can review the report at:
http://www.tabd.org/recom/scorecard.html
Have a
Greetings,
We just put a product through UL to be tested for outdoor use. It was
a fixed line cord, and they required a W/A marking on the line cord.
The W/A refers to a water absorption characteristic. I'm not sure
what Europe would require, but I assume that it would have to be HAR
cable a
Greetings,
We sell some larger motor driven units to Europe, and are evaluating
them to EN 60204. I believe that Sec 5.1 specifies that if a line cord
is not included then a terminal block has to be provided. Although my
experience has seen several applications that have loose leads inside
of
Hi Gary,
At my last employer, I asked the TUV representative in our area to
come in and do a product review, and a standard review with me and
other Engineers. You can all Rick Grumski in Livonia, MI (313) 261
8881
Also, I see UL has a seminar 6/18-19 in Northbrook IL. Call (847) 480
7500.
Greetings,
This forum is a great resource and has helped me greatly. Thanks to
all who have provided information on the recent Twist on connectors
questions.
There is a way to search on the past items discussed on the group. It
is called Regulatory Compliance Information Center. The URL is
ht
Greetings,
Thanks to all who have provided information on the metric directive.
As I was researching this issue, I went back to the FAQ by Bill Lyons.
What a great resource. However, I was not able to find the standard
that would be used to comply with the directives. Could someone please
forw
Greetings,
We manufacturer a small line of vacuum pumps that use very small (1/16
hp) 12, 6 and 4 VDC motors. Just a DC motor and a pump. We have had
some EMC testing performed to the EN 55014 and EN 55104 standards
where there was some high conducted emissions that required a .1 uf
capacitor
Dear PSTC group,
A recent change in employers has brought a whole new series of
questions. Could some one please provide me with some details on the
pressure directive, and maybe some sources for information?
Thanks for your input,
Ray Russell
Gast Corportaion
ray_russ...@gast.com
46 matches