le. I've used it a lot.
>
> Your help is very much appreciated.
>
> Thank you,
>
> Drake
>
>
> - Original Message -
> From:
> "RE-wrenches"
>
> To:
> "RE-wrenches"
> Cc:
>
> Sent:
> Fri, 13 Sep 2019 09:01:38 -0600
>
tform, neither are fully
reliable at this time.
Challenging.
Kevin
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Howie Michaelson
Sent: September-15-19 9:45 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Communications using the Conext Gateway
Sandra,
Thank you
c troubleshooting steps to
> identify the communication issues for the system.
>
>
>
> Regards
>
>
>
> Sandra Herrera
>
> sandra.herr...@se.com
>
>
>
>
>
>
>
>
>
> *From:* RE-wrenches *On
> Behalf Of *Howie Michaelson
> *Sent:* Thu
The DHCP server will only assign a new IP address if it's lease time has
expired. Otherwise it will continue to use the same IP address it previously
held.A simple power cycle will most likely not result in a new
address.-GlennSent from my 'smart'phone, so please excuse typos and spelling
error
t; To:
> "RE-wrenches"
> Cc:
>
> Sent:
> Fri, 13 Sep 2019 09:01:38 -0600
> Subject:
> Re: [RE-wrenches] Communications using the Conext Gateway
>
>
> Hi Drake,
>
> In general, you want to use DHCP unless its an unusual network. You would
> typicall
esses?
The internet seems stable. I've used it a lot.
Your help is very much appreciated.
Thank you,
Drake
- Original Message -
From:
"RE-wrenches"
To:
"RE-wrenches"
Cc:
Sent:
Fri, 13 Sep 2019 09:01:38 -0600
Subject:
Re: [RE-wrenches] Communications using the
system.
Regards
Sandra Herrera
sandra.herr...@se.com
From: RE-wrenches On Behalf Of
Howie Michaelson
Sent: Thursday, September 12, 2019 8:07 PM
To: RE-wrenches
Subject: [RE-wrenches] Communications using the Conext Gateway
[External email: Use caution with links and attachments
Drake,
I attached a screenshot. I have had zero problems but I was a
Beta field tester for Schneider. I use DHCP only. Everything works that I
need for offgrid to config a remote system on Insight2. Ignore the events
as this is a known problems for firmware, 2 months away I am told.
Make
sure
Hi Drake,
In general, you want to use DHCP unless its an unusual network. You would
typically enter this into the network page of the device. This gives the
router control of the IP address and all of the other networking parameters
of the device on the network. Static is more common in a
comme
I have very similar issues. The Gateway connects
and disconnects continually. I have 14,370 events
listed, mostly the Gateway connected and disconnected.
The first few weeks it was running, the Insight 2
(the Gateway web site) scrolled repeatedly
through all the error messages it could throw
Howie,
So CI2 worked until you did a gateway firmware update?
Can
you verify that 1.04 firmware is running on the gateway and check my
screenshot. I cc'd Sandra on this.
Dave Angelini Offgrid Solar
"we go
where powerlines don't"
http://members.sti.net/offgridsolar/ [1]
e-mail
offgridso...@st
Howie
Was the box set up as DHCP or static IP, if it was static there might be
something that had that same IP address. Also if its static the IP may not
be close enough to find a connection, by close l mean IP range. If it has a
wireless connection it might be stuck on another network. Some system
I have a net metered battery backup Dual stack XW Pro with a Conext
Gateway. The Gateway is communicating on the Xanbus netwark and I'm able to
read and write to the inverters through the gateway as long as I'm
connected to it through the local area network.
I was also able to register the Gateway