Re: [RE-wrenches] Tesla Powerwall 2.0 - AC Coupling

2020-07-22 Thread rich
Considering the lack of public info available for the Powerwall, does anyone have any insight into the AC coupling limits for a single Powerwall? For example, can we AC couple 10kw Solar Edge to a single Powerwall? Thanks Rich From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.

Re: [RE-wrenches] Tesla Powerwall 2.0 - AC Coupling

2020-07-22 Thread Dave Angelini Offgrid Solar
Schneider uses 1.25 max on an XW for Ac coupling. That would be 1.25 x 6 kw or 7.5kw max from the grid inverter when ac coupling. I doubt your numbers would work well with a 5kw internal powerwall. Maybe if you had 2 poweralls? Better get info from Tesla or the installer on Wrenches. Good Luck!

Re: [RE-wrenches] Tesla Powerwall 2.0 - AC Coupling

2020-07-22 Thread Matt Partymiller
7.6 kW. From: RE-wrenches On Behalf Of r...@solartechvt.com Sent: Wednesday, July 22, 2020 7:25 AM To: 'RE-wrenches' Subject: Re: [RE-wrenches] Tesla Powerwall 2.0 - AC Coupling Considering the lack of public info available for the Powerwall, does anyone have any insight into the A

Re: [RE-wrenches] Tesla Powerwall 2.0 - AC Coupling

2020-07-22 Thread Jason Szumlanski
I'm not privy to the specs, but from what I understand the off-grid allowance is less than the grid-interconnected allowance. I'm guessing here, but I assume they would limit the PV inverter output to the AC power rating of the internal inverter which I believe is 5kW. That way the PV output could

Re: [RE-wrenches] Tesla Powerwall 2.0 - AC Coupling

2020-07-22 Thread August Goers
Tesla's guidelines are 7.6 kW inverter AC rating. August On Wed, Jul 22, 2020 at 12:18 PM Dave Angelini Offgrid Solar < offgridso...@sti.net> wrote: > Schneider uses 1.25 max on an XW for Ac coupling. That would be 1.25 x 6 > kw or 7.5kw max from the grid inverter when ac coupling. > > I doubt

Re: [RE-wrenches] Tesla Powerwall 2.0 - AC Coupling

2020-07-22 Thread Chris Sparadeo
Max AC input is 7.6 kW AC for 10 seconds. If you are designing a system to function off-grid you will want to size your AC input at 5kW as this is the continuous max charge. Anything above 5kW for longer than 10 seconds and the Powerwall will throttle back PV via frequency shift. On Wed, Jul 22,