Re: What is a Bucket Test? (TIA Needed)

2008-04-16 Thread bverhei
Ron, I think the water districts in our area all use one inch taps off the main regardless. I personally haven't been on any that were changed. If it others in the office have had this experience I've missed it. On the technical side, the 5/8 x 3/4 and 1 x 1 meter use the same main tap. Cha

Re: Mechanical access walkway

2008-04-16 Thread IPA
I think Joe had you in the right spot: nfpa #13 8.15.1.5. ('07 ed.)... since your walkway is only 3 ft wide the way I see it you would only have one row of sprinklers spaced at the appropriate light hazard spacing. On 4/15/08, Russell <[EMAIL PROTECTED]> wrote: > > Well, I looked at that but I'v

RE: Plans Examiner rights to customer contracts

2008-04-16 Thread John Drucker
In our fee ordinance the fire protection permit fees are determined by the work and not its value. The permit and plan review fees are calculated based on the system and its components, i.e. number of dry valves, sprinklers, hose outlets, fire pump, etc. etc. By doing this the permit fee is unifo

Re: Re[2]: Help with jockey pump listing

2008-04-16 Thread Ron Greenman
For want of a nail On Wed, Apr 16, 2008 at 12:27 PM, Charles Thurston <[EMAIL PROTECTED]> wrote: > Hello Craig, > > Emergency Pager went off at 6pm one Friday. It turned out to be a customer > where we had replaced the jockey pump the day before. His electrician had > been out that morning

RE: Re[2]: Help with jockey pump listing

2008-04-16 Thread Craig.Prahl
And there you go. And some people think we just make this stuff up. LOL Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http:/

RE: Plans Examiner rights to customer contracts

2008-04-16 Thread Eric Tysinger
These are all valid points, but the issue I see is that this "contract" paperwork becomes part of the submitted plans which in turns becomes public records. The majority of the jurisdictions we deal with base the permit and inspection cost on sprinkler head counts or device counts for FA systems. W

Re[2]: Help with jockey pump listing

2008-04-16 Thread Charles Thurston
Hello Craig, Emergency Pager went off at 6pm one Friday. It turned out to be a customer where we had replaced the jockey pump the day before. His electrician had been out that morning and wired up the new jockey pump and life was good UNTIL The pump need to run... Well the electrician did not

Re: Plans Examiner rights to customer contracts

2008-04-16 Thread Thom McMahon
We've been doing that for years. Ever since they found out that some contractors were "Low Balling" those numbers to make their permit fee's lower. The One problem I have with it is, that your paying for a permit that includes the design/layout portion of the project. When the Arch or Mech Engi

RE: Plans Examiner rights to customer contracts

2008-04-16 Thread Smith, David (VFD)
Mike, Have you asked them to provide a code reference? An AHJ can not legally come up with their own "Because I Said So" code. I suggest all contractors to request a code reference when there is a question on scope of authority. If the AHJ can't provide a reference, then what right will they hav

RE: Plans Examiner rights to customer contracts

2008-04-16 Thread Steve Leyton
I'm almost certain that they can't. Valuation is supposed to be based on tabled values or an owners declaration. Earlier versions of the CBC included valuation charts for purposes of establishing permit and plan check fees. Check with CALBO, the California Building Officials web site at www

Plans Examiner rights to customer contracts

2008-04-16 Thread firedynam
In a certain southern California city a sprinkler contractor fills out an application to install a system. On that application the job valuation must be included. The valuation is used by the city to determine the fees for that particular job. The plans examiner is now requiring the contractors

RE: Help with jockey pump listing

2008-04-16 Thread Craig.Prahl
But make sure that electrical components (motors especially) are U.L. labeled. Some AHJ's do look for that label. Some of the cheap overseas knock-off products aren't UL tested or labeled. It would be real sad to have a fire in a pump room/house started by one of the fire protection system compo

RE: Help with jockey pump listing

2008-04-16 Thread John Denhardt
Agree - Jockey pumps or Pressure maintenance pumps as the standard calls them, do not have to be listed. Hope this helps, John John August Denhardt, P.E. Strickland Fire Protection Incorporated 5113 Berwyn Road College Park, Maryland 20740 Office Telephone Number: 301-474-1136 Mobile Telephone N

Re: Help with jockey pump listing

2008-04-16 Thread Roland Huggins
this section is addressing the use of other types of FIRE pumps. The standard does not identify types of Jockey pumps that you can deviate from. They are not required to be listed. This will be better clarified in the next edition (based on the outcome of the recent ROP) Roland On Apr 1

Re: Corrosion Resistant Concealed Sprinkler & Plate

2008-04-16 Thread Jeff Hewitt
We recenly went through this for a USDA application in a clean room for meat cutting, where hot water and steam are used to clean up every day, causing a corrosive environment to exposed sprinkler heads. We looked, and no such animal exists. The closest you can get is an "MRI" room head that

Help with jockey pump listing

2008-04-16 Thread Rod DiBona
When I look at NFPA #20 section 5.1.2.1 it looks like a jockey pump must be listed. I had it in my mind that it didn't. My mind vs the standard? ...probably not a fair contest but just wanted to check and see if I am missing something. Thanks. Rod DiBona Vice President Rapid Fire Protection [EMAI

Corrosion Resistant Concealed Sprinkler & Plate

2008-04-16 Thread Bobby McCullough
Does anyone know of a concealed sprinkler and plate with a corrosion resistant finish? I have a spec requiring this sprinkler over a pool. Thanks, Bobby McCullough Allsouth Sprinkler Company678-730-4312 [EMAIL PROTECTED] ___ Sprinklerforum mailin

RE: Very Large Ceiling Fans

2008-04-16 Thread Chris Cahill
GAP Research A Publication of Global Asset Protection Services Fire Test Evaluation On The Effects Of High Volume Low Speed Fans On Ceiling Sprinklers Not ESFR Group A Plastics + Fan = 73 heads 0.6 density Class II no fan = 21 heads 0.2 density Same test Class II + Fan = 26 heads 0.2 density I c

RE: Table 8.6.2.2.1(a)

2008-04-16 Thread Mark Hasenmyer
Duane: The vendor doesn't have a choice between the two. If the attic meets the unoccupied wood joist, etc. criteria then 120-max. Mark Hasenmyer, PE MEH Fire Protection Engineering LLC 1311 River Oaks Drive Flower Mound, TX 75028 Office (972) 874-2662 Fax (972) 874-5591 -Original Message-

Table 8.6.2.2.1(a)

2008-04-16 Thread Fox Duane T. (FireMarshal)
I have a project where the sprinkler vendor has covered an attic space using 130 sqft spacing. The attic is wood trusses on 24" centers with a 6/12 pitch. I think his installation should be based on the unoccupied attics having combustible wood truss construction with members less than 3 ft on c

RE: What is a Bucket Test? (TIA Needed)

2008-04-16 Thread John Drucker
Bruce, All valid concerns. As a sounding post one of the many benefits of this forum. While some subjects may get beat to death the discussions are healthy and allow everyone to weigh in. In a sense its no different then attending a code hearing albeit everyone has access. If we do see a TIA for