Air Testing CPVC Piping

2014-02-25 Thread Richard Mote
We have an AHJ requiring a 50 psi test on CPVC piping, we think that is excessive, and have always used 20 psi max. I know the best practice is to do a hydrostatic test, but thanks to the polar vortex we are having freezing temperatures and the builder needs to close up his walls. Right now we

RE: Air Testing CPVC Piping

2014-02-25 Thread Jim Davidson
Most CPVC manufacturers advise against air testing a CPVC piping system since pipe failures usually are very dangerous because of the plastic fragments produced by the pipe failure. There is a lot of energy store in a pipe system being tested with air. The stored energy is capable of causing a

RE: Air Testing CPVC Piping

2014-02-25 Thread Pete Schwab
From Spears http://origin.library.constantcontact.com/download/get/file/1102520706304-39/FG+Air+Test+Provision.pdf Peter Schwab VP of Purchasing Engineering Technologies Wayne Automatic Fire Sprinklers Inc. 222 Capitol Court Ocoee, Fl 34761 Mobile: (407) 468-8248 Direct: (407) 877-5570 Fax:

Re: Air Testing CPVC Piping

2014-02-25 Thread Steven Cook
For what's its worth, I have performed air tests in the past on CPVC systems. A few times with more air pressure than I'd like to admit here. It usually does not help locate any unglued joints. I've witnessed tests with where it held air pressure for an hour, but at 20lbs of water, the

RE: Air Testing CPVC Piping

2014-02-25 Thread Tom Duross
I've always air tested cpvc to 50# for an hour prior to hydro at the rough stage of installation, regardless of manufacturer's caution. Some dry fits can hold almost that much unglued when the pipe is properly supported and braced allowing little room for slipping. I hydro with premix

RE: Air Testing CPVC Piping

2014-02-25 Thread Morey, Mike
NFPA 13 2010 A.10.10.2.2.1 might be worth pointing out, specifically: When systems having rigid thermoplastic piping such as CPVC are pressure tested, the sprinkler system should be filled with water. The air should be bled from the highest and farthest sprinklers. Compressed air or compressed

RE: Air Testing CPVC Piping

2014-02-25 Thread Cahill, Christopher
I fail to see the connection between closing walls and doing a hydro test or substitute air test. Closing the walls is about is the pipe installed, hangars right, size right. Yep it's all there, close it up and test later. Nothing I know of that requires exposed testing. If it leaks as

Re: Air Testing CPVC Piping

2014-02-25 Thread rongreenman .
I think all you guys using 50 psi to test plastic are crazy. I also think that guys that pipe shop air in plastic are crazy. That said I know it's done all the time without mishap. Puff test for holes. Water test for pressure holding ability. And what the hell is a polar vortex. Sounds like

RE: Air Testing CPVC Piping

2014-02-25 Thread Cliff Whitfield
Ron, It's all in their mind. Hasn't anyone read about 'Global Warming'? Don't you know we are all going to die of extreme heat unless we are taxed to death first! And for Mr. Muncy's benefit, be careful with the air tests! Cliff Whitfield, SET President Fire Design, Inc. Ph: 719-488-3479  

Coverage for obstructed sidewalls

2014-02-25 Thread Todd - Work
I have a situation where some sidewalls sprinklers are obstructed by ductwork. Would it be acceptable to install additional pendents under the ductwork to alleviate the issue? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com 860-535-2080 (ofc)

RE: Air Testing CPVC Piping

2014-02-25 Thread Richard Mote
The inspector wants to see an air test we give him an air test within reason. 23° at job site were not putting water in the system under any condition. Richard L. Mote Rowe Sprinkler Systems, Inc. 7994 Route 522, Suite 1 PO Box 407 Middleburg, PA 17842 P 570-837-7647 F 570-837-6335

RE: Air Testing CPVC Piping

2014-02-25 Thread Hinson, Ryan
Check the forecast and do it when the ambient temp remains constant...like the climate (good luck with that). Don't forget your common gas law, P1V1/T1 = P2V2/T2 if the pressure drops as it may be fun trying to prove the entire pressure drop was due to the inverse relationship to a temperature

RE: Air Testing CPVC Piping

2014-02-25 Thread Richard Mote
That's normally what we do, but we are dealing with this inspector at this borough so we have to make him happy. Richard L. Mote Rowe Sprinkler Systems, Inc. 7994 Route 522, Suite 1 PO Box 407 Middleburg, PA 17842 P 570-837-7647 F 570-837-6335 -Original Message- From:

RE: Air Testing CPVC Piping

2014-02-25 Thread Bob
Now, now Ron, play nice. The polar vortex is the thingy that they install on the fire pumps up north to keep the swirly water in check. Duh Thank you, Bob Knight, CET III 208-318-3057 www.firebyknight.com -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org

RE: Air Testing CPVC Piping

2014-02-25 Thread Richard Mote
Heck if I know what a polar vortex is, that's what the weather dude called it. Richard L. Mote Rowe Sprinkler Systems, Inc. 7994 Route 522, Suite 1 PO Box 407 Middleburg, PA 17842 P 570-837-7647 F 570-837-6335 -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org

RE: Coverage for obstructed sidewalls

2014-02-25 Thread G. Tim Stone
Todd, Can the Sidewalls be lowered? Or is the duct to deep? Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering Technician Fire Protection Sprinkler Design and Consulting Services 117 Old Stage Rd. - Essex Jct., VT. 05452 CELL: (802) 373-0638 TEL:

Re: Coverage for obstructed sidewalls

2014-02-25 Thread Todd - Work
Can't lower them because we would then be too far down Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com 860-535-2080 (ofc) On Feb 25, 2014, at 4:11 PM, G. Tim Stone tston...@comcast.net wrote: Todd, Can the Sidewalls be lowered? Or is the duct to deep?

RE: Air Testing CPVC Piping

2014-02-25 Thread Forest Wilson Fire Sprinkler Contractor
I would contact the manufacturer rep and ask for his recommendations in writing and then send that to the AHJ Forest Wilson Fire Sprinkler Contractor 937-736-0425 Notice: This message is confidential. It may also be privileged or otherwise protected by work product immunity or other legal