Re: Distilled spirits

2022-03-07 Thread Fpdcdesign via Sprinklerforum
Steve, I lost out of a similar job over similar arguments. The exception is that this job also had barrels. A couple of points: there was an article in NFPA journal from 2018 that did address this. There is supposedly a DISCUS (Distilled Spirits Council of the United States)

Re: Joining black carbon steel with stainless steel piping

2022-02-28 Thread Fpdcdesign via Sprinklerforum
The last dielectric joint I saw was a 9” piece of CPVC > > On Feb 28, 2022 at 11:22 AM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > Craig, From literature I have, SS has an anodic index of approximately 0.60 > V while

Sprinkler in elevator pit.

2022-02-24 Thread Fpdcdesign via Sprinklerforum
NFPA 13 (2013) section 8.15.5.2 says that sprinklers may be omitted in elevator pits for “enclosed, non-combustible…” elevator shafts. What constitutes an “enclosed” shaft? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080

Re: Obstructed vs Unobstructed Construction

2022-02-16 Thread Fpdcdesign via Sprinklerforum
Scott, If you go to the definitions of Obstructed and Unobstructed construction, it talks about the construction type impeding the heat flow or water distribution. Apply that to your situation. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT

Re: infrared heaters

2022-02-14 Thread Fpdcdesign via Sprinklerforum
I would treat them as is they are a standard unit heater > > On Feb 14, 2022 at 11:20 AM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > I have a question for the forumites regarding infrared heaters. We have a > project that have several

Re: NFPA 13, 1978 Table 2.2.1 (B)

2022-02-08 Thread Fpdcdesign via Sprinklerforum
I have 1980 if you need that. There was a minor change between 1975 and 1980 in the tabular data, but other than tat, they are the same. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054

Re: INDOOR SPORTS FACILITY FIELD HOUSE

2022-02-07 Thread Fpdcdesign via Sprinklerforum
The track, basketball and tennis courts themselves would be Light Hazard. For the climbing wall, take a look at the construction (and beware of concealed spaces). One of the things about Field Houses is that they can become multi-use facilities. You may want to take that into

Re: Maker Space

2022-01-25 Thread Fpdcdesign via Sprinklerforum
inkler.org)> On Behalf Of > Fpdcdesign via Sprinklerforum Sent: Tuesday, January 25, 2022 10:10 AM To: > Sprinklerforum (mailto:sprinklerforum@lists.firesprinkler.org)> Cc: Fpdcdesign > mailto:fpdcdes...@gmail.com)> Subject: Maker Space I > am working on a project wh

Maker Space

2022-01-25 Thread Fpdcdesign via Sprinklerforum
I am working on a project where an existing building (Light Hazard) is being converted to an Innovation Lab and Maker Space. I thinking that this is going to need to be upgraded to Ordinary Hazard. Not sure at this time about 1 or 2. What have others been doing with these spaces?

Re: Food trucks inside a building

2022-01-13 Thread Fpdcdesign via Sprinklerforum
When I saw this, my knee-jerk reaction was EH2 for shielded fire. However, I was on a job site and had a 1:15 ride back to think about it. Most automobiles are enclosed and any fire started inside would be “shielded”. But a parking garage has been OH1 for a long time

Re: Thread connection holding on one thread only

2022-01-05 Thread Fpdcdesign via Sprinklerforum
I wouldn’t think one is sufficient. Any motion due to pressure fluctuations could create a problem. That being said, I would sit across the street in a lawn chair with a couple of beers and watch the 200 psi test. > > On Jan 5, 2022 at 9:33 AM,

Re: Airing of Grievances

2021-12-28 Thread Fpdcdesign via Sprinklerforum
Steve, that stuff happens on the other coast, too. A few years ago I had someone come in at half the design price I quoted. I told the client I can’t come near that, so the other guy got it. A few months later, the low bidder called to hire me to get the plan through review. I told

Re: NFPA #30 Containment

2021-12-15 Thread Fpdcdesign via Sprinklerforum
This occupancy needs an FPE to determine criteria. > > On Dec 15, 2021 at 9:26 AM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > James, I'm curious what is your plan for sprinkler protection of these > materials? For many in the IB

Obstructions below ESFR sprinklers

2021-12-09 Thread Fpdcdesign via Sprinklerforum
I am working on a project with an ESFR system and we have some ductwork installed below it. The duct system is T shaped with 24” wide section 50 ft long and 30” wide section 12’-6” long protruding from the center of the 24”. The top of the duct is 3’-8” below the sprinkler

Re: Wood Frame structure question

2021-12-08 Thread Fpdcdesign via Sprinklerforum
Spacing of trusses? > > On Dec 8, 2021 at 3:27 PM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > Hi, I am working on the wood frame building with Flat roofs. Open Web Wood > trusses are the overhead structure, The roof Deck above is

Re: going paperless

2021-11-17 Thread Fpdcdesign via Sprinklerforum
Are the fitters using the iPads to just to mark ups or for actually doing the install? I have been using Foxit on my iPad for surveys for 5+ years. It is far from perfect but is not bad. I mark up the plan using an Apple Pencil. I load, backup and store in Dropbox. From there I will

Re: 13R Installation of Sprinkler Systems in Low-Rise Residential Occupancies

2021-11-09 Thread Fpdcdesign via Sprinklerforum
Is there a Code information sheet from the architect? Check to see what allowances have been taken. Is the separation enough for this to be treated as two buildings or is it a single building? My gut answer says no to 13R but the differences in construction could make a

Re: Best Common Practices

2021-11-08 Thread Fpdcdesign via Sprinklerforum
Making clients trapeze branch lines is a good way to piss them off. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell)

Re: Display vs. storage

2021-10-28 Thread Fpdcdesign via Sprinklerforum
I think I have posted on this in the past. “Mercantile” is too broad a term for today’s environment and does not reflect what is going on. You almost need to have a Mercantile 1, Mercantile 2 and Mercantile 3 to adjust for different hazards > > On Oct 28,

Re: Attic Piping

2021-10-27 Thread Fpdcdesign via Sprinklerforum
I typically use option 2. Sometimes the framing at the peak can be a little funky and it is easier to adjust a smaller line. Also, I will put 1” outlets on any welded pipe for attic sprinklers, in case sprigs become necessary. Todd G Williams, PE Fire Protection

Re: Gridded dry system

2021-10-26 Thread Fpdcdesign via Sprinklerforum
Look up the definition of a gridded and looped systems in 13. See what fits Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell)

Re: Foam Insulation Spraying

2021-10-12 Thread Fpdcdesign via Sprinklerforum
What jumps out to me is the spray foam insulation. I’m not sure that the requirements for a typical paint spray booth would be applicable. Two very different products. I would look for any research or testing done on that specific product. Also the MSDS for it as a liquid and a

Break Tank

2021-10-12 Thread Fpdcdesign via Sprinklerforum
I have never designed a system with a break tank, however I am working on one project where this may be a viable option. Is there any good information one designing a system with one of these? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT

Partial height walls in OH occupancies.

2021-09-14 Thread Fpdcdesign via Sprinklerforum
I am working on the renovation of an upscale bridal store where there a several partial height walls being installed. The spaces created by the walls are semi-private consulting areas. The top of the walls is 1’-10” below the ceiling. The existing concealed sprinklers are spaced at

Re: Definitions

2021-09-09 Thread Fpdcdesign via Sprinklerforum
The Handbook commentary should be helpful. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell) > > On Sep 9, 2021 at

Pool maintenance area

2021-08-04 Thread Fpdcdesign via Sprinklerforum
I am working on a project with a therapy pool that is recessed into the floor with its own pit. There is a service area (stand up height) in the pit adjacent to the pool for maintenance. The walls, ceiling and floor are concrete and the pool enclosure is metal. Sprinklers in the

Re: Sprinklers in stairways

2021-06-24 Thread Fpdcdesign via Sprinklerforum
Is there any combustible construction within the stairway? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell) > > On

Corridor issue

2021-06-14 Thread Fpdcdesign via Sprinklerforum
I am doing a renovation of the main corridors in a multi-building complex. Standard response sprinklers for any new sprinklers to match the existing to remain. Hydraulic calculations are required. There are 2 section of corridor, about 35 ft each, that are 16 ft wide and will need

Re: Fire Pump intake pipe screen

2021-06-02 Thread Fpdcdesign via Sprinklerforum
James, I’m sure what Craig sent you was pretty thorough, but the Hydraulic Institute Standards has a lot of detail on suction pit design. > > On Jun 2, 2021 at 5:06 PM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > We

Re: 13 / 13R IN SAME BUILDING?

2021-05-11 Thread Fpdcdesign via Sprinklerforum
Look under “Scope” in NFPA 13R, both the main part and the appendix. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell)

Re: Commodity Classification

2021-05-06 Thread Fpdcdesign via Sprinklerforum
et) -Original > Message- From: Sprinklerforum > (mailto:sprinklerforum-boun...@lists.firesprinkler.org)> On Behalf Of > Fpdcdesign via Sprinklerforum Sent: Thursday, May 6, 2021 11:32 AM To: > Sprinklerforum (mailto:sprinklerforum@lists.firesprinkler.org)> Cc:

Re: Commodity Classification

2021-05-06 Thread Fpdcdesign via Sprinklerforum
Tim, I think this is one of those issues that is going to require engineering judgement and should probably be made by a PE. My first question would be ‘they may be nonflammable , but are they noncombustible?’ See NFPA 30 for the definitions. Next I would look at the

Re: Exposed unexpanded Group A plastic storage

2021-04-29 Thread Fpdcdesign via Sprinklerforum
Micah, For you to even begin to apply that, they would have to be segregated storage racks no more than 12 ft high. If you are talking about just storing the plastics in the 25 ft racks but only to 12 ft high, that doesn’t work. See section 5.6.1.2 (2016 edition)

Re: Fire pump test through flow meter

2021-04-19 Thread Fpdcdesign via Sprinklerforum
The question is now moot because they went and tested the pump by actually flowing water and it ran fine. The problem lies in the testing process and that is someone else’s headache. > > On Apr 19, 2021 at 5:05 PM,

Re: Same size orifice in a room

2021-04-19 Thread Fpdcdesign via Sprinklerforum
How do you prove the designer did it to balance flow? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell) > > On Apr

Re: Same size orifice in a room

2021-04-19 Thread Fpdcdesign via Sprinklerforum
I’m not sure there is such a section. I’ve had extended sidewalls in parts of a room and regular pendants in the other. > > On Apr 19, 2021 at 2:24 PM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > I'm trying to locate the

Fire pump test through flow meter

2021-04-19 Thread Fpdcdesign via Sprinklerforum
Are they’re any good resources about testing a fire pump with a flow meter where it feeds back into the suction piping? I have been given a couple of tests with very screwy results. Thanks Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT

Re: "Calculating" a Pipe Scheduled system for Backflow Retro

2021-04-13 Thread Fpdcdesign via Sprinklerforum
I have done a few of these. I am not sure about 2019, but 2016 main and appendix describe how to do this. You are pretty much in the right track > > On Apr 13, 2021 at 6:51 PM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > Any takers? Does

Re: Best Pressure Loss RPDA

2021-04-01 Thread Fpdcdesign via Sprinklerforum
OS valves Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell) > > On Apr 1, 2021 at 5:29 PM,

Re: Head or Not?

2021-04-01 Thread Fpdcdesign via Sprinklerforum
Also dimensions might help > > On Apr 1, 2021 at 9:31 AM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > In the absence of language about what that obstruction is, and what might be > below it, it seems clear the intent is to allow

Re: leaving abandoned sprinkler piping in place

2021-03-17 Thread Fpdcdesign via Sprinklerforum
The goal is to make it not look like a sprinkler system. The one issue may come across is if the pipe is painted red. People may automatically look at that as active sprinkler. You may want to consider doing something (paint, stripe, etc) to make it contrast the actual sprinkler pipe.

Re: [External] Re: Does a remote free standing FDC require a valve pit?

2021-03-11 Thread Fpdcdesign via Sprinklerforum
How can you isolate a check valve in a line that specifically excludes control valves? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559

Re: Group III Aircraft Hangar

2021-02-20 Thread Fpdcdesign via Sprinklerforum
Who’s stamp goes on the drawing? > > On Feb 20, 2021 at 8:17 AM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > While I agree it is not our “job” as NICET techs to classify the hazard, > that doesn’t exempt us from all

Re: Group III Aircraft Hangar

2021-02-19 Thread Fpdcdesign via Sprinklerforum
EH1 due in part to the aircraft being an obstruction to discharge.I didn’t pull out 409 to check on the specifics of Group III. > > On Feb 19, 2021 at 6:21 PM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > I have been

Re: Activity

2021-02-15 Thread Fpdcdesign via Sprinklerforum
> > "George has a warehouse, that is storing nothing, how should he protect it?" > > > > Is this a fire official’s definition of nothing or a building owner’s definition of nothing? Todd G Williams, PE Fire Protection Design/Consulting

Re: [EXTERNAL] RE: Multiple System Calculation

2021-02-11 Thread Fpdcdesign via Sprinklerforum
My thoughts exactly, Mr Prahl. > > On Feb 11, 2021 at 3:46 PM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > If I have 4-heads of OH2 in a 500 sf space I have to calc it and size > everything as if I had a 1500 sf design

Re: Fire Retardant Coating used in Combustible concealed spaces

2021-02-10 Thread Fpdcdesign via Sprinklerforum
Flame retardant coatings has to be installed according to strict guidelines and the thickness of the coating needs to be verified after installation. Tends to be expensive. Most projects I have worked on have junked that idea for that reason. > > On Feb 10, 2021

Re: [EXTERNAL] RE: Existing Dry System

2021-02-04 Thread Fpdcdesign via Sprinklerforum
What liability do you assume by removing an existing, operating sprinkler system? > > On Feb 4, 2021 at 1:42 PM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > One approach that I have seen in a similar situation: If the are not > separated

Re: Pan-Type Construction

2021-02-01 Thread Fpdcdesign via Sprinklerforum
Is this is what you are looking at? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell) > > On Feb 1, 2021 at

Re: Cut sheet

2020-12-19 Thread Fpdcdesign via Sprinklerforum
Tyco has all of that stuff on file > > On Dec 19, 2020 at 6:26 PM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > Anyone have a old cut sheet on a central SSP52? Have a fire marshal wanting > to know how far the deflector should protrude

Re: [EXTERNAL] 23.4.4.2.5: What is the purpose and how does it apply?

2020-12-11 Thread Fpdcdesign via Sprinklerforum
Sean, Doesn’t 12.7.2 address your example? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell) >

Re: Hersey BFP

2020-12-01 Thread Fpdcdesign via Sprinklerforum
https://www.bavco.com/ref-manual-manufacturer.php?id=11=beeco-hersey-backflow-repair > > On Dec 1, 2020 at 12:47 PM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > Can anyone tell me where to find a pressure loss graph for a 6" Hersey #2 >

Re: Class IA Flammable Liquids

2020-11-05 Thread Fpdcdesign via Sprinklerforum
This needs to be reviewed and criteria specified by an FPE > > On Nov 5, 2020 at 1:11 PM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > I'm confused about how to treat Class IA flammable liquids. We've got a > cosmetics manufacturer that is

Re: pharmacy

2020-10-09 Thread Fpdcdesign via Sprinklerforum
I tried to make an argument once that a jewelry store could be OH1 (rocks and metal in metal and glass cases) and got nowhere. > > On Oct 9, 2020 at 5:20 PM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > Is there any world where a

Re: ssu - concealed space - small room???

2020-10-07 Thread Fpdcdesign via Sprinklerforum
Are you required to use concealed space sprinklers? If it meets the NFPA definition of a room and the requirements of 11.2.3.3 are met, then you should be able to use it above a ceiling. Be sure of any fire resistance rating requirements. Todd G Williams, PE

Re: Code requiring inclusion of possible concurrent flow

2020-09-10 Thread Fpdcdesign via Sprinklerforum
Potable water? Sprinkler, standpipe or both? > > On Sep 10, 2020 at 10:33 PM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > Yeah, house boats lol On Thu, Sep 10, 2020 at 1:18 PM Prahl, Craig/GVL via > Sprinklerforum <

Re: Missing hydraulic data plates

2020-08-07 Thread Fpdcdesign via Sprinklerforum
Give them a price to survey, do a flow test, draw and Calc the system. If everything is above Sheetrock ceilings or is otherwise buried, give them your competition’s number. > > On Aug 6, 2020 at 8:07 PM, (mailto:sprinklerforum@lists.firesprinkler.org)>

Re: Combustible Stairs

2020-07-24 Thread Fpdcdesign via Sprinklerforum
Are the stairs wood? > > On Jul 24, 2020 at 12:43 PM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > Is Sprinkler Protection required under intermediate landings of Combustible > Construction Stairways even though all finished surfaces are to be

Re: 13R and Well Pump?

2020-07-21 Thread Fpdcdesign via Sprinklerforum
Not for.a 13R. For one thing, would the well pump be able to 60 gpm (4 sprinklers at 13 gpm + overage)?And do that at a 40 psi pressure? And sustain that for 30 minutes? Not likely that a well pump or residential sized well could do that. Todd G Williams, PE Fire

Re: Movie Sound Stages

2020-06-30 Thread Fpdcdesign via Sprinklerforum
Are you concerned about permanent obstructions or temporary obstructions? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell)

Re: Uprights in non combustible concealed space

2020-06-19 Thread Fpdcdesign via Sprinklerforum
Ed, I think you need at least one more post. Your reflections of your time in this industry. I echo everyone else in thanking you for all you have contributed. > > On Jun 19, 2020 at 4:48 AM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > >

Re: [EXTERNAL] RE: Floor area less than required

2020-06-16 Thread Fpdcdesign via Sprinklerforum
14 K8.0 sprinklers at 7 psi calculates to min 296 gallons. > > On Jun 16, 2020 at 7:49 PM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > > > The spec is demanding 8.0K for the LH areas. > > > > > > > > >

Re: mattress storage

2020-06-04 Thread Fpdcdesign via Sprinklerforum
I am actually working on a foam mattress manufacturer right now. Expanded Group A plastic. You would have to check if they are exposed or in cardboard boxes. Some mattresses are compressed and put into boxes. I’m not sure how a compressed foam mattress would behave in a fire

Re: Under-scoped and under-bid

2020-05-31 Thread Fpdcdesign via Sprinklerforum
I might as well add my crap into this as well... The first thing I see is that there is a major disconnect between fire protection and installing sprinkler systems. Unless they have been through it, nobody gives a shit about fire protection and fewer understand it. That

Re: Dust Collection

2020-05-22 Thread Fpdcdesign via Sprinklerforum
The N95 masks that everyone is talking about means that is will filter out of 95% of the 3 microns or larger. The Covid 19 virus is approximately 0.17 microns but usually travels attached to a fluid droplet, which is larger. The thickness of a piece of paper is about 100 microns.

Re: [External] Re: I-B construction - ABS plumbing piping

2020-05-21 Thread Fpdcdesign via Sprinklerforum
Is the data cable rated? > > On May 21, 2020 at 11:44 AM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > > > > Or as in many jurisdictions, file an appeal. > > > > > > John Drucker > > > > >

Re: [EXTERNAL] Re: Fabric canopies

2020-04-16 Thread Fpdcdesign via Sprinklerforum
ctures, but it > > could be read that way. If that was the argument, then someone would be > > saying that an aluminum frame was less fire safe than one made of FRT wood. > > That also seems unlikely. > > > > > > > > > > > > > > > > My vote

Re: Fabric canopies

2020-04-16 Thread Fpdcdesign via Sprinklerforum
covered with > inherently flame resistant fabric overlay. > > > > > > > > Matt > > > > > > > > > > > > > > From: Sprinklerforum On > Behalf Of Fpdcdesign via Sprinklerforum > Sent:

Fabric canopies

2020-04-16 Thread Fpdcdesign via Sprinklerforum
I am working on a building that has two 22 ft wide x 10 ft deep exterior canopies. The construction is fire retardant fabric over an aluminum frame. There is no storage underneath. NFPA 13 section 8.15.2.7 reference omitting sprinklers where fire retardant wood is present, but

Re: NFPA 13 Code Editions

2020-03-26 Thread Fpdcdesign via Sprinklerforum
.15? > > > > > > > > > Jerry Van Kolken > > > > Millennium Fire Protection Corp. > > > > 2950 San Luis Rey Rd. > > > > Oceanside, CA 92058 > > > > (760) 722-2722 FX 722-2730 > > > > >

Re: NFPA 13 Code Editions

2020-03-26 Thread Fpdcdesign via Sprinklerforum
I have all of the Codes/Handbooks from 1980, 1983, 1985, 1987... complete up to 2016. There was not an 18 year gap Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054)

Re: [EXTERNAL] RE: Boat and RV storage units

2020-03-18 Thread Fpdcdesign via Sprinklerforum
The issue is the fact that you could have a fire shielded from the sprinklers until it is fully involved. At that point, is OH2 adequate? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054

Re: Boat and RV storage units

2020-03-18 Thread Fpdcdesign via Sprinklerforum
Extra Hazard Group 7? Niagara Falls? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell) > > On Mar

Re: Boat and RV storage units

2020-03-18 Thread Fpdcdesign via Sprinklerforum
I assume you are talking about on ground and not rack storage. Ground storage I use Extra Hazard Group II. I don’t believe you can take the QR reduction with EH occupancies. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080

Re: How are you guys handling calcs for 13R balconies?

2020-03-10 Thread Fpdcdesign via Sprinklerforum
First, even if it is not required by the standard, you would calculate it as if it was. Second, is the design such that a single balcony requires 4 or more sprinklers? > > On Mar 10, 2020 at 12:23 AM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > >

Re: electronic PE stamps

2020-03-06 Thread Fpdcdesign via Sprinklerforum
I have been doing this for a while. My stamp is on my plot sheets on a separate layer that can be turned on and off. I have a picture file of my stamps in Foxit PDF that I can insert on calculations, etc. I use DocuSign for signature. That allows you to use an actual signature

Re: Flammable liquid tanks in a garage

2020-02-26 Thread Fpdcdesign via Sprinklerforum
Could you give a few more details? What is in the tanks? Why are they there? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell)

Re: RadioShuttle High Density Pallet Racking System

2020-02-19 Thread Fpdcdesign via Sprinklerforum
I did one last year. A pain in the butt Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell) > > On Feb 18, 2020 at

Re: Anybody hit this wall?

2020-02-17 Thread Fpdcdesign via Sprinklerforum
Scot beat me to it. It is a Code issue and the AHJ and the insurance company will have input. If it is not your expertise, keep away from it. There may also be restrictions on pipe penetrations as well. Todd G Williams, PE Fire Protection Design/Consulting Stonington,

Re: Corrugated Metal Deck - smooth??

2020-02-17 Thread Fpdcdesign via Sprinklerforum
What is supporting the metal deck? > > On Feb 17, 2020 at 9:05 AM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > > > I have a customer that intended to use horizontal sidewall sprinklers under > an exposed corrugated metal

Valves in dry systems

2020-01-31 Thread Fpdcdesign via Sprinklerforum
I am working on a rather unique project where a dry system in being installed in one building that is going to protect that plus a second building. (Logistically impossible to get underground to second building. Think boathouse on a dock.) The plans call for valves in the dry system

Re: LEVELS OF COORDINATION

2020-01-31 Thread Fpdcdesign via Sprinklerforum
My guess is that this is really BIM vs non-BIM. I have been finding that some design packages are eliminating the term BIM and but requiring all the BIM-type coordination. I think this is to not trigger BIM exclusions in contracts and to get the same stuff without having to pay the

Re: Hemp Processing

2019-10-31 Thread Fpdcdesign via Sprinklerforum
Craig beat me to the send button with those comments. The other thing to consider would be if the oil is flammable, it may not be able to be stored in the same room with the hemp. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080

Re: NFPA 909

2019-10-24 Thread Fpdcdesign via Sprinklerforum
Tony, I would say only those considered Cultural Resources. I think section 1.1.1 kind of clarifies this. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-553-3553 (fax) 860-608-4559 (cell) > > On Oct 24,

Re: Hotel washroom & closets

2019-10-15 Thread Fpdcdesign via Sprinklerforum
I don’t recall anything in 13 about duration of stay in a hotel. > > On Oct 15, 2019 at 5:18 PM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > > NFPA 13 does not require sprinklers in washrooms & closets (depending on > size)

Re: Atypical Remote Areas

2019-09-12 Thread Fpdcdesign via Sprinklerforum
23.4.4.1. Replace “Remote” with “hydraulically most demanding”. Hydraulically most demanding is not always a perfect rectangle. Use the 1.2X as the starting point and go from there. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080

Re: Ice Build-up on Linear Heat Detection for Double Interlock Pre-Action Sprinkler System

2019-09-03 Thread Fpdcdesign via Sprinklerforum
Could the LHD be moved away from the door? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-553-3553 (fax) 860-608-4559 (cell) > > On Sep 3, 2019 at 7:25 AM,

Re: Water supply test data

2019-08-28 Thread Fpdcdesign via Sprinklerforum
A flow test with multiple residual pressures is often done as a hydraulic gradient to determine where a potential problem exists in a water main. I haven’t done one in a while but may have something deep in the archives. Todd G Williams, PE Fire Protection