Change order. Cha-ching!

Wet or Dry system w/ pump, oh yeah!

Or he could just remove the pull downs, his choice.


Jamie Seidl
Affordable Fire Protection, Inc.
Design Department
P - (800) 862-7860
F - (704) 892-0157

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Friday, December 01, 2006 3:46 PM
To: [email protected]
Subject: Attics in 13r and 13d


OK,

So what do you do when the builder decides to frame the attic at the end
of the job with pull down stair access for storage purposes after the
pipe is run and sized?

Exposed wood, sloped structure 6/12. If we have to use 13 with upright
heads there is absolutely no way the calcs will work for these 6 heads.

Thanks,
Greg McGahan